Old 11-24-2015, 03:22 PM   #21
Pickin' & Campin'
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 5,017
Quote:
Originally Posted by twojump36 View Post
This is the first time I've had the outside cover off the Motorhome... it was just to winterize it and drain the water heater. The thing still works.
We have camped at the Oregon Coast and it gets wet, and wet and windy....
I can say it was very windy once (80 mph winds) in September but nothing that wild since. We turn off all the switches inside on the panel before we drive the coach.
I have never turned off the propane bottle at the tank. I've only filled it once. I don't think it was caused by anything I've done. I don't believe there are any spiders in the thing but I'm not taking it apart to look either.... The dealer can deal with that.
I'm starting to figure out this Motorhome though... I think it might be a lemon?
The stereo didn't work
The TV quit working,
The Heater stopped working
The back storage compartment leaks
Now this...
I'm guessing it likely happened during the 80 mph winds and you just now noticed it.
I've had several campers that wind gusts blew out the WH flame. Luckily it didn't cause this same kind of damage.

When the weather turns that nasty, switching the WH off or to electric is just another thing to add to the list of things you can't do in severe weather.
__________________

__________________
_________________________________________
2016 Flagstaff 8529IKBS Diamond Package 5th Wheel
2017 Ford F-Series SCREW 4x4
TST Tire Monitor w/Repeater - Sinemate 3500w Gen.
Days Camped: '15=22 '16=46 '17=30
5picker is offline   Reply With Quote
Old 11-24-2015, 03:23 PM   #22
Senior Member
 
Join Date: Oct 2014
Posts: 112
I don't know if this would cause it but we had a problem with stink bugs getting in our line. We did not know it and when the water heater came on, there was smoke pouring out - all of the stink bugs that had crawled in there burned up. Also, twice we had a stink bug in our check valve for the black tank flush behind the shower wall which caused water to leak. When we went to buy a new check valve, another customer came in with a clogged check valve and I tapped it on the counter and a stink bug came out! Stink Bugs!!!!!
__________________

__________________
CLewis is offline   Reply With Quote
Old 11-24-2015, 04:02 PM   #23
Senior Member
 
Join Date: Apr 2012
Location: West Michigan/Fort Myers
Posts: 3,927
Quote:
Originally Posted by twojump36 View Post
This is the first time I've had the outside cover off the Motorhome... it was just to winterize it and drain the water heater. The thing still works.
We have camped at the Oregon Coast and it gets wet, and wet and windy....
I can say it was very windy once (80 mph winds) in September but nothing that wild since. We turn off all the switches inside on the panel before we drive the coach.
I have never turned off the propane bottle at the tank. I've only filled it once. I don't think it was caused by anything I've done. I don't believe there are any spiders in the thing but I'm not taking it apart to look either.... The dealer can deal with that.
I'm starting to figure out this Motorhome though... I think it might be a lemon?
The stereo didn't work
The TV quit working,
The Heater stopped working
The back storage compartment leaks
Now this...

Sounds about normal. Next month you will have a whole new list of things that need fixing. Good luck with the WH. Let us know what the dealer says.
__________________
Phil57 is offline   Reply With Quote
Old 11-24-2015, 07:29 PM   #24
Senior Member
 
twojump36's Avatar
 
Join Date: Jun 2015
Location: Keizer Oregon
Posts: 191
I showed the picture to the dealer today and they said it's probably spiders....
I don't know how a spider got through there because of the screen over the cover, but I believe this may be their way of saying it won't be covered by warrantee.
__________________
2015 FR3 30 DS
1995 Wrangler
Miles 4600
Days Camped 45
twojump36 is offline   Reply With Quote
Old 11-25-2015, 05:49 PM   #25
CDR USN Ret
 
Join Date: Oct 2015
Location: Full-Time
Posts: 104
My suspicion is a shorted gas valve coil.
Brown (burned) wire provides 12V from control board (on back of heater) to both coils visible on the gas valve. This wire comes through a hole below, behind and to lower left of valve. Since this wire passes very close to both the upper (ECO/120V thermostat and 12V thermostat) and lower (120V element connections) plastic covers, if the brown wire got hot enough to burn, it would have scorched both covers. A shorted gas valve coil would have causes excess current and overheating of this wire.

If the problem had originated behind the upper cover, it should have burned completely through this plastic cover before the brown wire's insulation burned.

It was not a flame roll-out (flame backing up through the mixing tube). Ignition of the gas/air mix takes place at the far outlet of the mixing tube. Although hard to see on picture, your gas orifice and mixing tube inlet are below and well in front of the burned wire. Other wires and plastic-potted solenoid coils are between this inlet end of the mixing tube and burned wire, would have also been burned if roll-out occurred. These do not appear damaged. In addition, a flame roll-out would have caused flame-proving sensor at outlet (far end) of flame tube to lose rectification and gas valve would have VERY rapidly shut off gas flow.

There is no missing air shutter. LP-only burners are not fitted with a shutter (natural gas and convertible burners are, however). If gas pressure is correctly set (11 IWC), a venturi effect draws in exactly the correct amount of air for complete combustion.

"spiders" are a problem when they block the tiny orifice that meters gas into the mixing tube. This orifice is at the inlet end of the mixing tube. Blocking the orifice prevents the ignition of the air/gas mixture (either there is no gas available, or the mix is far too rich to burn). A flammable concentration does not develop because the flame-proving sensor at the tube outlet will closes the gas valve after a short "trial for ignition" interval. (It tries to ignite a total of 3 times only - the control module will lock the heater off (gas side only), and you have to cycle the 12V ON-OFF switch to clear this lockout).
__________________
DSQR is offline   Reply With Quote
Old 11-26-2015, 07:09 PM   #26
Senior Member
 
Jack350's Avatar
 
Join Date: Oct 2013
Location: Central New York
Posts: 128
Had a similar problem with my Atwood wh. Fixed and replaced all burned items and there was no blockage or bug problem.
All I can assume for the cause was the bug screen on the wh restricted the air flow and caused the flame to fry most of the electronics. Took off the bug screen and it has been perfect for the whole season. Seems like the air flow is very important to the proper funtion of the wh.
__________________
Jack350 is offline   Reply With Quote
Old 12-18-2015, 04:58 PM   #27
Senior Member
 
twojump36's Avatar
 
Join Date: Jun 2015
Location: Keizer Oregon
Posts: 191
Update:
The dealer has completed the repair.... all they did was replace the wire and said it was a burn out or something?... there were no spiders in the tube. They said it happened when the gas quit going through the tube somehow?
I'm not sure how the thing works but they fixed the one burned up wire and told me I'm good to go.
I'm not so sure I have a warm and fuzzy feeling of confidence in spending the night in it for a while though.
They didn't repair the burned plastic or anything else... I suppose they tested it to make sure it was working properly....
We'll see...!
__________________
2015 FR3 30 DS
1995 Wrangler
Miles 4600
Days Camped 45
twojump36 is offline   Reply With Quote
Old 12-19-2015, 03:03 AM   #28
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 7,623
Quote:
Originally Posted by twojump36 View Post
Update:
The dealer has completed the repair.... all they did was replace the wire and said it was a burn out or something?... there were no spiders in the tube. They said it happened when the gas quit going through the tube somehow?
I'm not sure how the thing works but they fixed the one burned up wire and told me I'm good to go.
I'm not so sure I have a warm and fuzzy feeling of confidence in spending the night in it for a while though.
They didn't repair the burned plastic or anything else... I suppose they tested it to make sure it was working properly....
We'll see...!
I would think they would have still replaced the valve. If I were you I would take a small piece of wire and clean the orifice. That had to happen from roll out. Those are called direct shot burners, no combustion air adjustment....Just for safety sake.....
__________________

__________________
Rockwood #8289 WS 2012
F250 6.0 / Husky 16k
With 4 point leveling system
Witch Doctor is offline   Reply With Quote
Reply

Tags
heater, hot water, water, water heater

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 05:47 AM.