Quote:
Originally Posted by Kenny kustom
A 3% voltage drop is not acceptable in my installs.
|
Kenny, I know, I know. 20 feet is the way it is and 4/0 is as big as it gets. At 200 amps, that means that the feed would be dissipating 78 watts, dropping something like .39 volts, while the inverter peaks out at 2,400 (same 3%) We both know that the batteries won't support that wattage for long and I would expect that his average loads would be closer to 1,000 to 1,500 or less.
Would I like that .39 volts back when the batteries drop closer to the 50% SOC limit...sure.