Page 6 here for inverter... It would seem there would be a sub panel for the inverter outlets...
http://www.magnum-dimensions.com/sit...s%29_Web_1.pdf
As far as generator I would assume because it has two 35 amp lugs, @ 120v) it would supply both side's of the PD panel..
We can also assume the two a/c breakers in the pd panel are on separate sides of panel
The rare instance you need to charge dead batterys from the generator through the converter may be problematic.
The PD takes 1550 watts to charge at full rate 90 amps. Thats about 13 amps. Leaves 20 amps on that side of panel that the charging circuit is on I assume..
If a/c is running on that same charging side of panel, and then the microwave is run, you may trip the breaker. ( @ gen)
But thats only if batts are dead. A way around it would be to put the charge wizard in 13.6 mode to draw less amps.
Just a thought is all.. Just posting info I have been finding online.