Ac and hair dryer flip breaker

I'm sure this has been addressed somewhere but I am on an iPad and it takes forever and a day to find what I am looking for. Ac with micro or hairdryer flips breaker. I need a why and a fix please

Thanks
__________________
Sandy and Steve
Chooie, Baby, Grizzly, Sophie the 4 fur babies
2018 Rockwood 8301WS fiver
2003 Ford F-250 super duty diesel
Vinemont, AL
Triple SS is offline   Reply With Quote
Old 06-27-2015, 04:38 PM   #2
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
What size is your main breaker? 30 amps?
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
fonzie is offline   Reply With Quote
Old 06-27-2015, 05:06 PM   #3
Site Team
 
KyDan's Avatar
 
Join Date: Mar 2008
Location: Louisville, KY
Posts: 10,525
If you have a 30 amp unit that is normal.
Turn off AC while using other hi load items like you mentioned.
__________________
Peace!
Dan & Rita D
2017 Nissan Titan 5.6L King cab 4wd
2016 Evergreen Everlite 242RBS
29' empty nest model. Blue Ox WD hitch
(1 queen bed, large main cabin and huge bathroom)
Camping days 2010-53, 2011-47, 2012-41, 2013-41, 2014-31, 2015-40, 2016-44, 2017-63, 2018-75, 2019-32, 2020-41, 2021-49, 2022-43, 2023-66
KyDan is offline   Reply With Quote
Old 06-27-2015, 05:19 PM   #4
Senior Member
 
Join Date: Dec 2012
Posts: 1,255
Yeah. He's 30amp. But unfortunately, there is no "fix" per say. You could run an extension cord from the camp pedestal or your generator to run your microwave, hair dryer, or other such.

With 30amp service though it's just one of those things that takes a little planning to run high loads.
rana is offline   Reply With Quote
Old 06-27-2015, 05:35 PM   #5
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,954
Yep, as other stated you have to keep total wattage under 3600 watts, which equates to 30 amps.

120 volts X 30 amps = 3600 watts.

You might can also get a lower wattage hair dryer, and get by too.

Here are some other threads with links that may help you understand this all better.:

http://www.forestriverforums.com/for...tml#post801443

http://www.forestriverforums.com/for...ter-45322.html

http://www.forestriverforums.com/for...tml#post846629

http://www.forestriverforums.com/for...tml#post783351

http://www.forestriverforums.com/for...tml#post547299
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is offline   Reply With Quote
Old 06-27-2015, 05:47 PM   #6
Senior Member
 
Join Date: Dec 2012
Posts: 1,255
Quote:
Originally Posted by wmtire View Post
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ
Buwahahaha..

Now that's a goodin!

Or should I say, "¡uıpooƃ ɐ s,ʇɐɥʇ ʍou ˙˙ʎɐs ı plnoɥs ɹo"
rana is offline   Reply With Quote
Old 06-27-2015, 07:32 PM   #7
Senior Member
 
Join Date: Oct 2014
Posts: 438
Well, that is not exactly what I wanted to hear. If nothing can be done, I guess I will have to live with it. Thanks everyone for your replies. I was hoping that perhaps we could put in a bigger inverter or something like that.
__________________
Sandy and Steve
Chooie, Baby, Grizzly, Sophie the 4 fur babies
2018 Rockwood 8301WS fiver
2003 Ford F-250 super duty diesel
Vinemont, AL
Triple SS is offline   Reply With Quote
Old 06-27-2015, 07:37 PM   #8
Senior Member
 
heavynlori's Avatar
 
Join Date: Oct 2013
Posts: 1,460
We have 50 amp

Can run television, fridge and water heater on elec, A/C , electric skillet all at same time but it will throw the breaker if we turn on toaster too😉.

Just have to learn what to turn on at same time
heavynlori is offline   Reply With Quote
Old 06-27-2015, 07:47 PM   #9
Senior Member
 
Join Date: Dec 2012
Posts: 1,255
If it really cramps your style, a lot of campground power pedestals will also have a standard 3-prong 20amp outlet. You could add a male 3-prong connector to the outside of your rig. Run that to a dedicated outlet inside, then just run an extension cord from the pedestal to your outdoor plug.

That would give you an additional 20amp dedicated outlet to run other loads on. I've seen a number of folks that have done that in order to run their electric heaters or other such.

There is 'always' a work around.
rana is offline   Reply With Quote
Old 06-27-2015, 08:25 PM   #10
Senior Member
 
davel1971's Avatar
 
Join Date: Nov 2013
Location: Seaford, De
Posts: 2,377
or just take your hairdryer outside to plug it in
__________________
David & Lynn
2014 Coachmen Chaparral Signature 327 RLKS
2016 Ford F350 Lariat CC Dually
davel1971 is offline   Reply With Quote
Old 06-27-2015, 08:57 PM   #11
Senior Member
 
dan-nickie's Avatar
 
Join Date: Feb 2014
Location: Dallas TX
Posts: 1,675
Is your Water Heater on electric too?
If so, turn it to propane and try again.
__________________
Dan
2014 Berkshire 390RB-60
dan-nickie is offline   Reply With Quote
Old 06-28-2015, 12:41 PM   #12
7 Year Class A RV'er
 
Join Date: Oct 2014
Location: Winter Park, FL
Posts: 1,068
I definitely would NOT recommend trying to run the blow dryer off the 20A outlet in the pedestal unless it is a GFI. Very dangerous! Blow dryers are just toasters with fans in them and toasters are the biggest issue you can get (usually) in wiring. They'll kick a breaker in a heartbeat. Here's a thought.....try using the blow dryer on cool air only (no heat). Bet that won't kick the breaker, although I don't know if it will dry your hair. It's a lot easier to dry my hair - both the remaining strands practically dry themselves without any help! Also wondering why the GFI you hopefully have the blow dryer plugged into is not popping before the 30A breaker - that in itself seems problematic, not to mention dangerous.
__________________
2015 Legacy SR340 360RB
2014 Jeep Wrangler Unlimited Toad

Gigi, Poppy and Sadie Lady...On the road, but not full time!
conceptumator is offline   Reply With Quote
Old 06-28-2015, 01:11 PM   #13
Cyber Phrenologist
 
Radio's Avatar
 
Join Date: Jun 2007
Location: Southern Crescent
Posts: 1,806
We carry an extra heavy extension cord in the winter so we can heat with a space heater AND make toast and coffee at the same time.

We run the extension cord out via the slide seal to the 15/20 amp outlet on the pedestal. This bypasses all the trailers breakers. Your hair dryer may require such an arrangement. We purpose bought a hair dryer to keep in the trailer. Took forever to find one around 1200 watts as they are all 1600 or better now.
__________________
KU4OJ
2008 (or is it 2009?) Rockwood 8280SS - 2022 F-250 7.3L
Lot's of mostly Kenwood radios

Radio is offline   Reply With Quote
Old 06-28-2015, 02:14 PM   #14
Senior Member
 
Join Date: Dec 2012
Posts: 1,255
Quote:
Originally Posted by conceptumator View Post
I definitely would NOT recommend trying to run the blow dryer off the 20A outlet in the pedestal unless it is a GFI. Very dangerous!

Also wondering why the GFI you hopefully have the blow dryer plugged into is not popping before the 30A breaker - that in itself seems problematic, not to mention dangerous.
GFCI's have nothing to do with protecting against an overload, only circuit variation, so there is nothing wrong with his system.

According to the CPSC (Consumer Product Safety Commission), since the 1987 UL standard change, and as older units have been replaced with newer units with the ALCI or IDCI immersion protection, hair dryer related deaths have decreased dramatically. 1991-1997 there were 12, and from 1998-2005 there was 1. Additional laws have been passed that now require hair dryers to have their own GFI protection built into the unit (the big brick at the end of the cord with the 'test' and 'reset' buttons).

You're perfectly fine to use that type plugging directly into a CG power pedestal. If it overloads the circuit the pedestal breaker will trip. If it shorts out on you, the hair dryers GFI will trip.

If you install a dedicated outlet inside of your rig to be used with a 20A extension cord, it's never a bad idea to make it a GFI outlet.

Problem solved.
rana is offline   Reply With Quote
Old 06-29-2015, 07:01 AM   #15
Senior Member
 
Wolverine 1945's Avatar
 
Join Date: Jul 2014
Location: SouthWest Michigan
Posts: 5,977
3SS,,, hopefully your not trying to use a cord that is not heavy enough to carry 30 amps,,, hair dryers & toasters will surprise you on the amount of juice they draw !!!
I have not had a problem with a hair dryer in many years,,,
no hair,,, no dryer,,, just use a towel !!!
LOL !!!
Wolverine 1945 is offline   Reply With Quote
Old 06-29-2015, 08:18 AM   #16
Senior Member
 
Join Date: Oct 2014
Posts: 438
Thanks everyone for the responses. I am just turning off the ac and then drying hair. Micro will run for 30 seconds to 1 minute without tripping breaker. We will just have to adjust. Was a new experience for means thought a bigger inverter would help. Guess not. Have a great summer camping. Until next time.....
__________________
Sandy and Steve
Chooie, Baby, Grizzly, Sophie the 4 fur babies
2018 Rockwood 8301WS fiver
2003 Ford F-250 super duty diesel
Vinemont, AL
Triple SS is offline   Reply With Quote
Old 06-29-2015, 08:35 AM   #17
Mod free 5er
 
Join Date: Mar 2008
Location: Concord, NC
Posts: 24,702
Quote:
Originally Posted by Triple SS View Post
Thanks everyone for the responses. I am just turning off the ac and then drying hair. Micro will run for 30 seconds to 1 minute without tripping breaker. We will just have to adjust. Was a new experience for means thought a bigger inverter would help. Guess not. Have a great summer camping. Until next time.....
BTW, it is not an inverter, it is a converter. Inverter converts 12VDC to 120VAC and your converter coverts 120VAC to 12VDC.
__________________
OldCoot is offline   Reply With Quote
Old 06-29-2015, 08:41 AM   #18
Senior Member
 
Join Date: Oct 2014
Posts: 438
Give me a break you old coot. I am still in the learning stage and will be there a long time Just kidding thanks for the correction
__________________
Sandy and Steve
Chooie, Baby, Grizzly, Sophie the 4 fur babies
2018 Rockwood 8301WS fiver
2003 Ford F-250 super duty diesel
Vinemont, AL
Triple SS is offline   Reply With Quote
Old 06-29-2015, 08:45 AM   #19
Mod free 5er
 
Join Date: Mar 2008
Location: Concord, NC
Posts: 24,702
Quote:
Originally Posted by Triple SS View Post
Give me a break you old coot. I am still in the learning stage and will be there a long time Just kidding thanks for the correction
I did give you a break, you are sure not the first one or the last to confuse the two.
__________________
OldCoot is offline   Reply With Quote
Old 06-29-2015, 09:01 AM   #20
Senior Member
 
jeff64's Avatar
 
Join Date: Mar 2015
Location: N. Illinois
Posts: 2,371
Quote:
Originally Posted by Triple SS View Post
Give me a break you old coot. I am still in the learning stage and will be there a long time Just kidding thanks for the correction
Buy yourself a plug in voltmeter from CW. Put it in the most in your face outlet and look at it regularly. Then, you will know what to expect in terms of breakers popping or equipment failure. The green areas are from probably 110-125 or so. More campers, hotter weather, more ACs on spells lower voltage at the post.
I recall a Memorial Day weekend a couple years back, it was so hot out we couldn't get over 100 vac with everything running on LP that could.... we left and said the heck with it. It wasn't worth a burned out AC unit
jeff64 is offline   Reply With Quote
Reply

Tags
breaker


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 07:57 PM.