Quote:
Originally Posted by Simpso13 View Post
I was hoping that the camper would split this up or maybe the cord 50 amp cord that came with the camper would only utilize on of the 120v wires leaving the other dead.
It actually utilizes each of the 120 volts sides at 50 amps per side. This is how you get 100 amps total......from a 120/240 volt 50 amp service........which is over 3 times as much as a 120 volt 30 amp service.
__________________

__________________
2011 Flagstaff 831 RLBSS

Ducks are just all-terrain chickens
wmtire is offline   Reply With Quote
Old 07-21-2013, 05:19 PM   #12
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,157
Quote:
Originally Posted by wmtire View Post
Didn't the OP say his travel trailer was of the 50 amp variety?

If the generators 120/240 outlet is wired the same as a campgrounds 120/240 50 amp outlet, it should be OK. Maybe need the generator gurus to chime in on this one.

A TT wired for 50 amps is made to plug into a 240 outlet, then it uses the L1 and L2 as two different 120 volt sides inside the trailer.

However, we need to make absolutely sure the OP has a 50 amp TT. Does your power cord to the trailer have four prongs or three prongs?
You are forgetting the neutral that is required for a 50- amp service. A generator's 220 outlet does NOT have a neutral. FRY CITY if he makes an adapter improperly.
__________________

__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Old 07-21-2013, 05:34 PM   #13
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 15,006
Quote:
Originally Posted by herk7769 View Post
FRY CITY if he makes an adapter improperly.
I don't guess I'm understanding where he needs an adapter, as it appeared the Champion generator had a regular 120/240 outlet that one could plug a 50 amp travel trailer into.

I do admit, I'm not a generator genius.
__________________
2011 Flagstaff 831 RLBSS

Ducks are just all-terrain chickens
wmtire is offline   Reply With Quote
Old 07-21-2013, 05:34 PM   #14
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
Quote:
Originally Posted by Simpso13 View Post
The way I understand it is that each X and Y side of the 50 am plug is 120v. I was hoping that the camper would split this up or maybe the cord 50 amp cord that came with the camper would only utilize on of the 120v wires leaving the other dead. I am definitely not an electrician. I think I have uploaded a picture of the generator.
Based on the picture, which shows a 50-amp RV plug, you're probably good. It would certainly be worth your time however to use a volt meter to verify that the voltage readings are as shown in this diagram:
Click image for larger version

Name:	image-1680339365.jpg
Views:	373
Size:	29.8 KB
ID:	35898

(Having a Progressive Industries EMS unit would alleviate any risk from the generator being wired incorrectly.)
__________________
BarryD0706 is offline   Reply With Quote
Old 07-21-2013, 05:44 PM   #15
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 15,006
Do we know for sure it's actually a 50 amp supply from the generator? It could possibly be less amps, but just a 120/240 outlet.

Can the OP be so kind as to tell us how many watt generator this Champion is?
Attached Images
 
__________________
2011 Flagstaff 831 RLBSS

Ducks are just all-terrain chickens
wmtire is offline   Reply With Quote
Old 07-21-2013, 05:45 PM   #16
Senior Member
 
Join Date: Jun 2012
Posts: 6,721
Your house wiring works the same way. Look in your homes circuit breaker box and you'll see both 120 volt breakers and 240 volt breakers (typically 240 volts are for well pumps, electric stoves, electric dryers). There's usually 2 vertical rows of breakers, with one row tied to the L1 line and the other tied to the L2 line. The 240 breakers are tied across both L1 and L2 (i.e., L1 + L2).
__________________
rockfordroo is offline   Reply With Quote
Old 07-21-2013, 05:49 PM   #17
Junior Member
 
Join Date: Jul 2013
Posts: 15
7500 watt
Attached Thumbnails
Click image for larger version

Name:	image-1072069033.jpg
Views:	75
Size:	40.8 KB
ID:	35902   Click image for larger version

Name:	image-3147502245.jpg
Views:	79
Size:	48.3 KB
ID:	35904  
__________________
Simpso13 is offline   Reply With Quote
Old 07-21-2013, 06:02 PM   #18
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,157
Quote:
Originally Posted by herk7769 View Post
You are forgetting the neutral that is required for a 50- amp service. A generator's 220 outlet does NOT have a neutral. FRY CITY if he makes an adapter improperly.
Serves me right for not scrolling down and actually LOOKING at the generator.
Yes, Virginia; there is a 50 amp RV service outlet! (with correct Neutral!)
__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Old 07-21-2013, 06:04 PM   #19
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,157
Quote:
Originally Posted by Simpso13 View Post
7500 watt
Looks like 2x~30 amp circuits on that "50 amp RV service" outlet.
__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Old 07-21-2013, 06:08 PM   #20
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 15,006
Quote:
Originally Posted by Simpso13 View Post
7500 watt
Ok, Thanks. You probably won't be able to run just everything at once, with that size, but you should be able to run an awful lot if not most. It all depends on how your TT is configured with the loads on each side (L1 and L2)

You still have twice as much power as a regular 30 amp TT which you can compute as:

Volts X amps = watts
120 volts X 30 amps = 3600 watts

BTW, if the OP decides he no longer wants this generator, I'll give you $100 for it. LOL
__________________

__________________
2011 Flagstaff 831 RLBSS

Ducks are just all-terrain chickens
wmtire is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 06:26 AM.