Came up with an idea to save the money of buying all that expensive wire!! I Put the 50 amp box next to breaker box in garage and plug into 50 amp box with 50 amp extention cord. ( I used the money for the wire for an ext cord, cause I needed an extention cord anyways.
__________________

__________________
quick83 is offline   Reply With Quote
Old 05-05-2014, 04:15 PM   #12
Senior Member
 
Join Date: Jul 2013
Location: Roxboro, NC
Posts: 267
RV dealers call it a 120 volt 50 amp outlet. This doesn't exist it is a 240 volt 50 amp plug all day long.
I installed a 50 amp, water and sewer connections at home, go all the way if you are doing it.

Master Electrician
Robert Whitlow


Sent from my SCH-I545 using Forest River Forums mobile app
__________________

__________________
2007 GMC 2500 Duramax Crew Cab LB
2008 5th Wheel Cardinal 36LE
R Whitlow is offline   Reply With Quote
Old 05-07-2014, 01:56 PM   #13
Member
 
supercab79's Avatar
 
Join Date: Sep 2012
Posts: 98
Had a 30 at the front garage and put a second one in for the winter time storage on the back rear garage. Being cheap was the reason for the 30's then we bought our 365 and usually like you set it up as a guest house when family stay for awhile. Well as old Murphy would have it every time the ac and the occupants would use the toaster, hair dryer, etc or both ac's would come on pop goes the 30. So like they say do it right or do it twice and now the front garage has a 50 and love it no more calls at work " hay seething happened we were curling our hair laying on a heating pad running the ac watching TV using a crock pot and all of a sudden everything went off. How do I do the breaker thingy where's it at?" Well thank God after the 50 went in no more of that. Just my 2 cents but 50amp all the way....

Plus here in Pa my parents usually stay in it in late fall while up from Fl and they like electric space heaters better than the noise of the propane furnace and with the 50 it's no sweat..

Good luck
Marc
__________________
06 3500 Laramie Dodge Mega Cab 4x4 5.9CTD Short Bed Dually
13 Sandpiper 365SAQ Fifth Wheel
05 Chevrolet Tahoe
93 F-250 XLT 4x4 Diesel Banks Sidewinder (gone but not forgotten)
79 Jeep CJ-7
77 F-250 Crew Cab Short Bed 4x4
supercab79 is offline   Reply With Quote
Old 05-07-2014, 02:06 PM   #14
Senior Member
 
jevanb's Avatar
 
Join Date: Dec 2012
Location: Michigan
Posts: 1,441
Quote:
Originally Posted by R Whitlow View Post
RV dealers call it a 120 volt 50 amp outlet. This doesn't exist it is a 240 volt 50 amp plug all day long.
I installed a 50 amp, water and sewer connections at home, go all the way if you are doing it.

Master Electrician
Robert Whitlow


Sent from my SCH-I545 using Forest River Forums mobile app
so if I replace my receptacle 220VAC for the generator/welder in the garage with a 50 RV receptacle I will be ok.
Attached Thumbnails
Click image for larger version

Name:	plug.jpg
Views:	104
Size:	27.9 KB
ID:	51927  
__________________
2012 Wildcat 344QB

06 LBZ ,CC 4x
lots of mods
Superglide
jevanb is offline   Reply With Quote
Old 05-07-2014, 02:47 PM   #15
Phat Phrog Stunt Team
 
AquaMan's Avatar
 
Join Date: Apr 2012
Location: Tipp City, OH
Posts: 6,477
Quote:
Originally Posted by jevanb View Post
so if I replace my receptacle 220VAC for the generator/welder in the garage with a 50 RV receptacle I will be ok.
It doesn't appear that the wiring is heavy enough for a full 50amp draw, but to answer your question, yes. As long as you wire the plug correctly. You could also make your own adapter to use your existing outlet. Just don't change the breaker for a heavier one.
__________________
2016 Georgetown 364TS
Nights Camped 2017 - 49
AquaMan is offline   Reply With Quote
Old 05-07-2014, 06:32 PM   #16
Senior Member
 
Join Date: Jul 2013
Location: Roxboro, NC
Posts: 267
Quote:
Originally Posted by jevanb View Post
so if I replace my receptacle 220VAC for the generator/welder in the garage with a 50 RV receptacle I will be ok.
You will have to leave the 30 amp beaker in the panel because you have 10 gage wire going to the outlet , but yes it would work. If you have two AC units they will have to be on two different hots in the rv panel to run both, that should be the only issue you might have.

I would leave the welder outlet and add the rv outlet under the welder outlet. Most twist lock outlets have a flat plate that the wire connects under, you can place the wire going to the RV outlet under the same plates on the other side of the screw. This way you can use the welder pr the RV.


Sent from my SCH-I545 using Forest River Forums mobile app
__________________
2007 GMC 2500 Duramax Crew Cab LB
2008 5th Wheel Cardinal 36LE
R Whitlow is offline   Reply With Quote
Old 05-07-2014, 06:44 PM   #17
Senior Member
 
dretired's Avatar
 
Join Date: Feb 2011
Location: Michigan
Posts: 1,037
Click image for larger version

Name:	SAM_1200.jpg
Views:	132
Size:	53.6 KB
ID:	51942 I had wanted a rv plug in on the garage..this is what Menards had..
__________________
2014 Crusader 325 TE....2012.. F 250.. Supercab XLT, 4x2 , diesel....days camped 2011 ... 28.... days camped 2012...115 ... days camped 2013...155...2014...171 and counting
dretired is offline   Reply With Quote
Old 05-07-2014, 08:29 PM   #18
Member
 
cookie12's Avatar
 
Join Date: Feb 2012
Location: Moose Jaw, SK
Posts: 51
Great idea on the extension cord. For someone who does not have a 50A extension cord it totally makes sense to buy and extension and use it off of the sub panel outlet. The #6 gauge is quite pricey and #4 is worse.

Love that box, very clean install. Heading to Menard's this weekend and will have to check it out.
__________________
2014 Sierra 365SAQ
2011 Ford F350 King Ranch 6.7L Air Lift LoadLifter 5000, Air Lift WirelessONE, Reese Elite 18K w Fifth wheel Prep Package, H&S Mini Maxx
cookie12 is offline   Reply With Quote
Old 05-07-2014, 10:25 PM   #19
Senior Member
 
Join Date: Jul 2013
Location: Roxboro, NC
Posts: 267
This is what I installed. http://www.amazon.com/gp/aw/d/B0009R...110_SY165_QL70


Sent from my SCH-I545 using Forest River Forums mobile app
Attached Images
 
__________________

__________________
2007 GMC 2500 Duramax Crew Cab LB
2008 5th Wheel Cardinal 36LE
R Whitlow is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 06:47 AM.