AC unit froze up 8312 SS 2016

Second time out, 90 degrees thermostat at 70 . Unit froze, leaking small drops on kitchen floor. No cooling like usual. Thawed unit , climb down, restart , froze 20 minutes later. What's up Forest River?


Sent from my iPhone using Forest River Forums
Lookin2camp is offline   Reply With Quote
Old 05-29-2016, 04:34 PM   #2
Senior Member
 
Join Date: Jan 2016
Location: Apollo, PA
Posts: 588
I'm not a HVAC tech but I've heard AC units will freeze up when they are low on refrigerant. Very annoying on a new unit.
__________________

2017 Rockwood 2703WS - Sold
2015 Keystone Sprinter 333FWFLS
2017 F250, 6.2 Gas, 3.73 Axle, 2902 lb Payload
If women don't find you handsome, at least they should find you handy!
andymil is offline   Reply With Quote
Old 05-29-2016, 04:48 PM   #3
Senior Member
 
DaveSchwartz's Avatar
 
Join Date: May 2014
Location: Waterloo Region
Posts: 729
They also freeze up if you start with high humidity and not enough airflow. Try opening the cold-air quick-cool vents (the sliding grills around the edges of the ceiling bezel) when you restart after thawing.

Also, open the filter cover and ensure the freeze sensor is properly clipped to the evaporator fins. You can Google for the Airxcel/Coleman-Mach installation manual and search on the word 'freeze' within that PDF.
__________________
2015 Rockwood Signature UltraLite 8282WS Platinum, GY Marathon LRD, TST 507RV TPMS
2005 GMC 2500HD CCSB D/A, Curt E16, Prodigy P2, Garmin RV760LMT w/BC-20 b/u cam

Self restraint is for the young. I'm old and want it NOW!
DaveSchwartz is offline   Reply With Quote
Old 05-29-2016, 08:09 PM   #4
Senior Member
 
TimVWulp's Avatar
 
Join Date: Jan 2015
Location: West Michigan
Posts: 641
Quote:
Originally Posted by Lookin2camp View Post
Second time out, 90 degrees thermostat at 70 . Unit froze, leaking small drops on kitchen floor. No cooling like usual. Thawed unit , climb down, restart , froze 20 minutes later. What's up Forest River?


Sent from my iPhone using Forest River Forums
Is the fan speed on high of low? Air flow is every thing with air conditioning. Low air flow dose not bring enough warm air though the cooling coil to keep it above freezing.
I have read about some Air conditioner not positioned on the roof opening correctly causing the cold supply air to enter the return air and drop the return air temp to low. This short cycles the a/c unit air and will freeze the unit up.

Hope This Helps Tim
TimVWulp is offline   Reply With Quote
Old 05-30-2016, 08:44 AM   #5
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
There are a lot of reasons that RV A/C's freeze up. High humidity and low air flow is a common reason. There's also a freeze coil on the evaporator coils that commonly gets left just hanging loose. They will also freeze up if there's an air leak between the discharge and return.

On our last RV the freeze coil wasn't attached to the evap coil and there was an air leak between the outlet and return. I clipped the freeze coil to the evap and sealed up the leaks with aluminum backed foam tape and it didn't freeze up the 10 years we had it.

I'd check those things and I'd run the fan on high when first starting the unit after sitting off for a while.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 05-30-2016, 08:52 AM   #6
Senior Member
 
SeaDog's Avatar
 
Join Date: Jan 2016
Location: x
Posts: 12,423
My experience with both home and commercial units is that freezing up is caused by low refrigerant or plugged (dirty) return air filter.
__________________
Retired Navy
Jake my sidekick (yellow Lab) 10/04 - 05/20
2017 RAM 2500 CC 4X4 Cummins Diesel
2016 Flagstaff 26 FKWS
AF&AM & El Korah Shrine of Idaho
SeaDog is offline   Reply With Quote
Old 05-30-2016, 12:17 PM   #7
Senior Member
 
Join Date: May 2016
Location: Tucson AZ
Posts: 16
What happens is that folks close off some of the AC ceiling vents to "increase" flow to other areas of the coach. Many time this reduces overall air flow to a point where the AC unit will freeze up. Keep all of the vents open if "freeze-up" is an issue.
pkeene is offline   Reply With Quote
Old 05-30-2016, 03:14 PM   #8
Member
 
Lookin2camp's Avatar
 
Join Date: Mar 2016
Posts: 51
Thanks for the advice by all. The unit only turns on and blows air when the high or low fan speed is on or in auto . The unit will not kick on just by adjusting the thermostat. If I just switch it to cool the unit does nothing. Thinking this could be a thermostat issue, but why won't it cool? Freon leak out? I cleaned the roof unit and drip pan , which increased the water drip flow, however the unit never froze back up, but never cooled either. Both filters were cleaned too. Drop off CW On Wed this week. Irritated 😡🙄🙃


Sent from my iPhone using Forest River Forums
Lookin2camp is offline   Reply With Quote
Old 05-30-2016, 05:07 PM   #9
Senior Member
 
Join Date: May 2015
Posts: 230
Pull the ceiling cover or filter cover down , look up inside and you will see a sensor that should be pushed into the finned area. The sensor will , if properly in place , sense temp and shut off compressor if freezing begins. This is for high humidity days. It could be it was not put in place when it was installed at the plant.
hillsdaletc is offline   Reply With Quote
Old 05-30-2016, 05:25 PM   #10
Dahagen
 
Join Date: Apr 2013
Location: Cascade Idaho
Posts: 562
My AC froze up several times on the Texas coast this winter. But it never does it in the mountains of the West. I would think that hi humidity is the problem.
dahagen is offline   Reply With Quote
Old 05-30-2016, 10:34 PM   #11
Senior Member
 
Join Date: Dec 2014
Posts: 423
High temp and high humidity, run fan on high. The unit will work a lot more efficiently and not ice up. At night when the temp drops turn the fan back to auto. This was a recommendation by a Dometic A/C factory rep.
tomrob1161 is offline   Reply With Quote
Old 05-31-2016, 07:32 AM   #12
Senior Member
 
Wolverine 1945's Avatar
 
Join Date: Jul 2014
Location: SouthWest Michigan
Posts: 5,977
Quote:
Originally Posted by andymil View Post
I'm not a HVAC tech but I've heard AC units will freeze up when they are low on refrigerant. Very annoying on a new unit.
RIGHT ON Andy !!!
Low on Refrigerant or Low air flow ???
Wolverine 1945 is offline   Reply With Quote
Old 06-04-2016, 05:11 PM   #13
Junior Member
 
Join Date: Jun 2015
Posts: 15
Quote:
Originally Posted by hillsdaletc View Post
Pull the ceiling cover or filter cover down , look up inside and you will see a sensor that should be pushed into the finned area. The sensor will , if properly in place , sense temp and shut off compressor if freezing begins. This is for high humidity days. It could be it was not put in place when it was installed at the plant.
Our A/C unit froze up several times in a row last summer (in the Mojave Desert). Had to run it with the compressor off and fan on to blow the air over the ice to thaw it out in about 10 to 15 minutes (being 100+ degrees also helped thaw it out quickly...)

After getting tired of it continually freezing up and it being over 90 degrees inside, I did the above to check on the thermocouple sensor placement. It was pushed into the fins at the bottom by the drip tray where it never freezes. The fins above would be covered in a thick layer of ice.

I simply pulled the thermocouple temp sensor out of its incorrect position and pushed it back into the fins much higher up ( near the middle where the ice first forms). Never froze up again. It was always as cool inside as we wanted it to be for the rest of our 6 week trip through the desert southwest in August!
__________________
2012 Nissan Aramada
2016 Rockwood Mini Lite 2504s
Victron Miltiplus 3000, Victron BlueSolar 100/50, 750W solar, 400 Ahr Lithium BattleBorn Batteries, Trimetric 2030
SLOArmada is offline   Reply With Quote
Old 06-05-2016, 10:19 AM   #14
Member
 
Lookin2camp's Avatar
 
Join Date: Mar 2016
Posts: 51
Thanks for all the positive experiences. My issue was covered under warranty ( only 2 months old) haha. This was two things , the freeze sensor was bad and not hooked up properly. My thermostat was bad too. Everything replaced by CW. The was checked and not ammonia based product leaked out. (No freon in these units )

We'll see how it works end of the month at the beachClick image for larger version

Name:	ImageUploadedByForest River Forums1465139933.725902.jpg
Views:	154
Size:	83.5 KB
ID:	110195Click image for larger version

Name:	ImageUploadedByForest River Forums1465139975.496362.jpg
Views:	151
Size:	62.2 KB
ID:	110196


Sent from my iPhone using Forest River Forums
Lookin2camp is offline   Reply With Quote
Old 06-05-2016, 10:46 AM   #15
Site Team
 
Flybob's Avatar
 
Join Date: Oct 2014
Posts: 15,300
X2 on using quick cool dump vent when first turning on while hot and humid. Once unit cools down and reduces humidity it can be closed and use the duct vents.
__________________

2015 Freedom Express 248RBS
TV 2015 Silverado HD2500 Duramax
TST Tire Monitors
Honda 2000I + Companion
2 100W solar panels
Flybob is offline   Reply With Quote
Old 06-05-2016, 03:07 PM   #16
Senior Member
 
Join Date: Jan 2016
Location: Phoenix, Arizona
Posts: 306
Quote:
Originally Posted by Lookin2camp View Post
Thanks for all the positive experiences. My issue was covered under warranty ( only 2 months old) haha. This was two things , the freeze sensor was bad and not hooked up properly. My thermostat was bad too. Everything replaced by CagW. The was checked and not ammonia based product leaked out. (No freon in these units )

We'll see how it works end of the month at the beach


Sent from my iPhone using Forest River Forums
Glad you got it fixed. Having no AC sucks in the summer time.
Not understanding your last sentence though. You are showing a picture of a compressor designed to pump refrigerant (aka freon which is a brand name).
Ammonia can't be used with copper lines like the ones brazed to your compressor.Also ammonia is used in absorption units like a propane fridge and even 12 volt AC units. It is heated by propane or electric elements. The nomenclature tag on your unit should identify the refrigerant being used.
Maybe there is a new refrigerant out that I'm not familiar with (highly likely). I have been in the HVAC business for 40 years (started at 18)and the last couple of years I have semi-retired and have not kept up in the world.
A lot of these AC threads have gotten me curious about leaks, control boards and what not. When I get back home this week I'm pulling the top off of mine to see what has changed over the years besides the type of refrigerant. They used to use R12 and R-22 with mechanical controllers. The last I new of was R-134a and under-rated (amps)solid state control boards.
__________________
2016 Forester 2401WS MBS
Life is short...eat the cookie
bob dirt is offline   Reply With Quote
Old 06-05-2016, 06:32 PM   #17
Member
 
Lookin2camp's Avatar
 
Join Date: Mar 2016
Posts: 51
This is the reason I'm posting pics. I'm not sure myself but I am being told this. I'm trying to learn these things as I go. Here is the info pic of the sticker on this unit. Unfortunately I don't have a pic of what was froze , but it was the coper line. Please respond Click image for larger version

Name:	ImageUploadedByForest River Forums1465169549.845013.jpg
Views:	175
Size:	72.3 KB
ID:	110229


Sent from my iPhone using Forest River Forums
Lookin2camp is offline   Reply With Quote
Old 06-05-2016, 07:20 PM   #18
Senior Member
 
DaveSchwartz's Avatar
 
Join Date: May 2014
Location: Waterloo Region
Posts: 729
R-410A is a 50/50 mixture of R-32 (difluoromethane) and R-125 (pentafluoroethane) - no ammonia involved. Would have been just the freeze sensor involved in it freezing up. I thought it might be mis-positioned but didn't count on it being bad too. Thermostat would not have had anything to do with it freezing up... just not running at the times or conditions expected.
__________________
2015 Rockwood Signature UltraLite 8282WS Platinum, GY Marathon LRD, TST 507RV TPMS
2005 GMC 2500HD CCSB D/A, Curt E16, Prodigy P2, Garmin RV760LMT w/BC-20 b/u cam

Self restraint is for the young. I'm old and want it NOW!
DaveSchwartz is offline   Reply With Quote
Old 06-05-2016, 07:51 PM   #19
Senior Member
 
Join Date: Jan 2016
Location: Phoenix, Arizona
Posts: 306
Quote:
Originally Posted by DaveSchwartz View Post
R-410A is a 50/50 mixture of R-32 (difluoromethane) and R-125 (pentafluoroethane) - no ammonia involved. Would have been just the freeze sensor involved in it freezing up. I thought it might be mis-positioned but didn't count on it being bad too. Thermostat would not have had anything to do with it freezing up... just not running at the times or conditions expected.
What he said^^^^^^


If 410A is being used in these units, no wonder they are leaking. It runs very high pressures.
__________________
2016 Forester 2401WS MBS
Life is short...eat the cookie
bob dirt is offline   Reply With Quote
Old 06-05-2016, 09:15 PM   #20
Member
 
Lookin2camp's Avatar
 
Join Date: Mar 2016
Posts: 51
Ok I'll run this thing in my driveway on the next hot day. If it doesn't cool I'll address CW. Can I check the levels of the 410A ? Or not accessible with the proper tools? apparently CW doesn't understand the system, which now im very concerned. Glad I posted pics. On the flip side , I'm hoping it was a freeze sensor issue. Thanks


Sent from my iPhone using Forest River Forums
Lookin2camp is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 02:16 AM.