Old 05-25-2016, 11:52 AM   #1
Member
 
tdidad's Avatar
 
Join Date: Feb 2015
Location: Cambridge Ontario
Posts: 77
Furnace Issues 2014 8289WS

A few times last season as well as this past weekend my furnace comes on intermittently. The fan starts first as it should then it shuts itself down. Sometimes it runs correctly but most of the time not, any suggestions?
I had it back at my dealer last season but he indicated all is "normal", yeah right😡
__________________
‘17 Rockwood Signature 8328BS
tdidad is offline   Reply With Quote
Old 05-25-2016, 11:53 AM   #2
I go RV'ing not Camping
 
jgourlie's Avatar
 
Join Date: Nov 2013
Location: Lethbridge, Ab, Canada
Posts: 1,482
sounds to me like you are hitting the high limit switch. Do you have any of your floor vents covered on closed off??

I covered some of my vents last year and it shut my furnace down cause it got too hot.

Fan would run for a minute and then just shut off


Hope that helps,
__________________
312QBUD Owners Thread
2015 Wildwood Heritage Glen 312QBUD
2000 Chev 2500 Extended Cab 6 Liter
1400lbs Equal-i-zer Hitch
jgourlie is offline   Reply With Quote
Old 05-25-2016, 11:56 AM   #3
Member
 
tdidad's Avatar
 
Join Date: Feb 2015
Location: Cambridge Ontario
Posts: 77
Thank you, all vents are open and unobstructed.
__________________
‘17 Rockwood Signature 8328BS
tdidad is offline   Reply With Quote
Old 05-25-2016, 12:09 PM   #4
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,074
When calling for heat, the furnace is designed to come on, run the fan a few moments and prove out it is running via a sail switch. This is necessary because they use part of the fan for the combustion chamber. (in a separate part of the furnace)

If the control board/module doesn't see voltage (through the sail switch) it won't try to light the furnace because it deems it unsafe to light.

If the sail switch circuitry is working OK, the furnace will try to light three times.
If it fails to light, the control board/module goes into lock-out and it is necessary to shut the furnace off to retry.

You didn't mention what part of the process your gets to before it shuts down.
Once the fan starts, do you hear a faint clicking like the igniter is trying to light the propane?

You could have electrical or propane delivery issues depending on the result.

Post the brand and model # of the furnace for better answers as well.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2017 Ford F-Series SCREW 4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=86
5picker is offline   Reply With Quote
Old 05-25-2016, 12:14 PM   #5
Member
 
tdidad's Avatar
 
Join Date: Feb 2015
Location: Cambridge Ontario
Posts: 77
Ok thank you, I'll get those specs tonight.
__________________
‘17 Rockwood Signature 8328BS
tdidad is offline   Reply With Quote
Old 05-25-2016, 05:09 PM   #6
Senior Member
 
Join Date: Jun 2012
Posts: 10,907
I had a similar issue with my Roo 19. Can't explain it, but I replaced the crappy analog thermostat with a digital and never had another problem.
__________________
1988 Coleman Sequoia - popup (1987-2009) - outlasted 3 Dodge Grand Caravans!
2012 Roo19 - hybrid (2012-2015)

2016 Mini Lite 2503S - tt (2015 - ???)
2011 Traverse LT, 3.6L, FWD
2009 Silverado 1500 Ext Cab, 5.3L, 4x4, 3.73
2016 Silverado 2500HD Dbl Cab, 6.0L 4x4, 4.10
rockfordroo is offline   Reply With Quote
Old 05-25-2016, 06:15 PM   #7
Member
 
tdidad's Avatar
 
Join Date: Feb 2015
Location: Cambridge Ontario
Posts: 77
OK here are the specs for my furnace:
Make, Suburban
Model, NT-30SP

Sometimes the fan runs for 5-10 seconds then shuts down. I do hear it start then after 30 seconds or so a click and heat begins to flow. Most of the time though the fan runs for about 30 seconds and the system shuts down😡😡
__________________
‘17 Rockwood Signature 8328BS
tdidad is offline   Reply With Quote
Old 05-26-2016, 10:10 AM   #8
2016 Rockwood Ultra-Lite
 
radarman's Avatar
 
Join Date: Apr 2015
Location: Silver City, NM
Posts: 34
Good info by 5picker that everyone should make note of. Sounds like an intermittent sail switch. You can bypass it temporarily for a test with a jumper wire as long as your fan is starting up at first, which sounds like it is. 30 seconds or so after your fan starts up until you hear a click to start the burner sounds too long to me.
__________________
Jim and Connie w/3 lb. Chihuahua= Nugget
2016 Rockwood Ultra-Lite 2608WS
2004 Dodge Ram 2500


radarman is offline   Reply With Quote
Old 05-26-2016, 10:22 AM   #9
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,074
tdidad,
I sounds like you have an intermittent problem which often times is very hard to diagnose.
You are going to have to do some troubleshooting on your own to determine what part of the control system isn't working.
If you are uncomfortable with doing testing yourself, find a good service repair facility or mobile tech.
If you feel capable of following troubleshooting procedures, **HERE** is a link to the Suburban Furnace Service Guide.

Best of luck and let us know what you find.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2017 Ford F-Series SCREW 4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=86
5picker is offline   Reply With Quote
Old 05-26-2016, 10:30 AM   #10
Senior Member
 
northstar1960's Avatar
 
Join Date: Feb 2015
Location: in my new 29hfsxlr
Posts: 1,658
you can have a bad sail switch but more likely it's a carbon-ed up flame sensor or a bad high limit that tripped one to many times . a furnace is nothing to mess with if you don't know what your doing . if you do great if not call someone
northstar1960 is offline   Reply With Quote
Old 05-26-2016, 10:31 AM   #11
Member
 
jhoppmann's Avatar
 
Join Date: May 2015
Posts: 61
You may want to read the following threads. Some of us have figured out it has to do with the sail switch, vent covers, battery power, and/or elevation.

http://www.forestriverforums.com/for...33s-84324.html

http://www.forestriverforums.com/for...ion-87970.html

http://www.forestriverforums.com/for...pen-86385.html

Hope this helps!
__________________
2015 Rockwood Mini-Lite 2306
2012 F-250 FX4 6.7 diesel
10k Equalizer Hitch
jhoppmann is offline   Reply With Quote
Old 05-26-2016, 11:58 AM   #12
Senior Member
 
DustyRoads's Avatar
 
Join Date: Mar 2014
Location: NY Capital District
Posts: 429
I has a similar problem. I reset the thermostat and all was back to normal. You just might want to try that first.
__________________
2017 Forest River Surveyor 251rks
2022 Chevy 3500HD High Country

DustyRoads is offline   Reply With Quote
Old 05-26-2016, 05:09 PM   #13
Senior Member
 
TimVWulp's Avatar
 
Join Date: Jan 2015
Location: West Michigan
Posts: 641
Quote:
Originally Posted by tdidad View Post
OK here are the specs for my furnace:
Make, Suburban
Model, NT-30SP

Sometimes the fan runs for 5-10 seconds then shuts down. I do hear it start then after 30 seconds or so a click and heat begins to flow. Most of the time though the fan runs for about 30 seconds and the system shuts down😡😡
Is the RV unit plugged into 110 volt shore power or just on battery? Furnace needs 12 V DC to control board. It will operate down to 9.5 volts but not any lower. From what you are describing it sound like the furnace is having intermittent prof of ignition problem. When the pilot in the furnace lite's with the spark ignition the pilot flame is in contact with a flame rod the control board passes a small DC current though the flame to prove the pilot gas is burning. If it dose not see the DC current in less than 5 sec. it will shut the gas off and shut the fan down. after 30 sec. it will try to lite again and will do this 3 times and lock out the furnace if it dose not light. The only way to reset the furnace if this happens is to turn the heat off at the thermostat to cycle the 12 V DC power to start the furnace. In short it sound like you have a pilot ignition problem. If you don't have a good working knowledge of propane don't play with it. If the dealer you have can't fix it take it to an other dealer or call Suburban for a dealer near you that is a factory rep.

Hope This Helped Tim
TimVWulp is offline   Reply With Quote
Old 05-26-2016, 05:26 PM   #14
Member
 
tdidad's Avatar
 
Join Date: Feb 2015
Location: Cambridge Ontario
Posts: 77
Thank you all, great info on this forum. Going to check the furnace this wknd. and will report my findings early next week.
Cheers!
__________________
‘17 Rockwood Signature 8328BS
tdidad is offline   Reply With Quote
Old 05-26-2016, 05:40 PM   #15
Senior Member
 
northstar1960's Avatar
 
Join Date: Feb 2015
Location: in my new 29hfsxlr
Posts: 1,658
you can go off of others threads and solutions for a good place to start and trace but do not think the answer for every furnace problem is always the sail-switch or
altitude . you need to verify all for yourself .your safety and family's is at stake
northstar1960 is offline   Reply With Quote
Reply

Tags
2014, furnace

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 03:49 AM.