Just spent the last 3 days going through the propane tanks, regulators, and now the "pig tails". After all this is finished and IT IS WORKING ( if ever) guaranty the dealer is going to get a call. Should have made them show us that the gas lines were really working after more than 5 minutes.
So much fun. So much for something new that is SUPPOSED to work.
__________________

__________________
desertrat is offline   Reply With Quote
Old 07-05-2011, 08:41 AM   #2
Junior Member
 
Join Date: Jul 2011
Location: Wisconsin
Posts: 23
I might of had the same issue. My tanks would work when freshly filled for about 5 minutes then nothing. I disassembled everything and started replacing stuff, untill I found the check valves in the pigtails, on the tank end, were too strong and not letting gas pass through. Since there are additional check valves on my auto switch, I drilled out the check valves in the pigtails, and everything seems to work great.
__________________

__________________
pschnetts is offline   Reply With Quote
Old 07-05-2011, 08:49 AM   #3
Moderator Emeritus
 
MtnGuy's Avatar
 
Join Date: Sep 2008
Location: Shenandoah Valley
Posts: 9,274
Quote:
Originally Posted by pschnetts View Post
I might of had the same issue. My tanks would work when freshly filled for about 5 minutes then nothing. I disassembled everything and started replacing stuff, untill I found the check valves in the pigtails, on the tank end, were too strong and not letting gas pass through. Since there are additional check valves on my auto switch, I drilled out the check valves in the pigtails, and everything seems to work great.
Those pigtail check valves serve a purpose. If there is a free-flow of gas because of a broken line or something, the check valve will shut the supply off. Better to replace the pigtails and throw away the drilled out units. Just speculating, but going down the road with non-working check valves and the gas on may be illegal.
__________________

Chap , DW Joy, and Fur Baby Sango
2017 F350 Lariat CCSB, SRW, 4x4, 6.7 PS
2017 Grand Design Reflection 337RLS
MtnGuy is offline   Reply With Quote
Old 07-05-2011, 09:04 AM   #4
Site Team
 
KyDan's Avatar
 
Join Date: Mar 2008
Location: Louisville, KY
Posts: 6,733
New LP tanks have built in free flow preventers.
In other words if the tank sees too much flow it shuts off.
Not sure why pig tails have them too.
__________________
Peace!
Dan & Rita D
2004 5.3L Silverado 1500 ext. cab 2WD
1999 Suzuki Intruder Motorcycle
Blue Ox WD hitch, AirLift load levelers

Camping days 2010-53, 2011-47, 2012-41,
2013-41, 2014-31, 2015-40, 2016-44, 2017-63
KyDan is offline   Reply With Quote
Old 07-05-2011, 09:08 AM   #5
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,169
Pig tails have one way check valves (not shut offs). They tend to stick from oil and general crap in the gas.
Once they start sticking; replace them.
__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Old 07-05-2011, 11:13 AM   #6
Moderator Emeritus
 
MtnGuy's Avatar
 
Join Date: Sep 2008
Location: Shenandoah Valley
Posts: 9,274
I hate to differ with you guys, but sometimes I just gotta.

Acccording to this article (Propane Safety and Use) (about 1/2 way down starting beside the pigtail photo), the tanks have a overfill protection device (OPD), but doesn't state anything about a limiting device. I have read on this forum that turning the valve on too quickly with a full tank will sometimes make this valve shut.

The pigtails have 2 safety devices. Besides the "flow limiting device", there is a thermal-sensitive bushing that will melt under extreme heat, closing a piston at the cylinder valve, shutting off gas. That is the 1st time I have read about that safety feature.

The paragraph under that explains how the "flow limiting device" works. I had no idea it was so complicated, but that may have been what was happening in Post #2.
__________________

Chap , DW Joy, and Fur Baby Sango
2017 F350 Lariat CCSB, SRW, 4x4, 6.7 PS
2017 Grand Design Reflection 337RLS
MtnGuy is offline   Reply With Quote
Old 07-05-2011, 12:23 PM   #7
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,169
Chap,

I think we are talking about the same thing. I was talking about the pigtail and not the OPD which is INSIDE the tank and valve body.

The pigtail goes from the threaded part of the valve to the regulator. Acme Nut (or POL fitting) to the hose to a NPT fitting. It is the Acme Nut I was referring to.

There is a spring loaded valve in the Acme Nut that allows propane flow from the bottle to the regulator but not from the regulator back to the bottle. That way you can change out the bottles without a gas leak. They stick when dirty, especially when cold. Drilling them out is a really bad idea for the reason you stated. In a fire, they melt SHUT and prevent a huge propane torch. The down side of course is if the fire lasts a long time that tank is a bomb.

Propane 101-The basics

Was my reference, but having read your article it makes more sense regarding the flow limiter.
__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Old 07-05-2011, 12:35 PM   #8
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,169
I spent a lot more time re-reading both articles and Chap is the most correct. In any case, replace that pigtail.
__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Old 07-05-2011, 12:43 PM   #9
Junior Member
 
Join Date: Jul 2011
Location: Wisconsin
Posts: 23
I didn't expect this many replies, but thanks for the help. Our camper has done this since new and the dealer said nothing is wrong. I drilled the check valves in fustration as a hungry family was waiting inpatiently. Do you still think I need to replace them when 12" further down the line there is another check valve on the switching valve/regulator?
__________________
pschnetts is offline   Reply With Quote
Old 07-05-2011, 12:49 PM   #10
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,169
I believe Chap will back me up when I say "Yes, you should." They are not all that expensive and it would be a DoT violation if you were ever stopped.

Additionally, you have bypassed a required safety item on your camper. it would be the same as replacing all your GFCI electrical outlets with standard ones or taking the batteries out of your smoke detectors.
__________________

__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 08:02 AM.