rockwood 8289 underfloor heating

Hi all,
we now have reason to use the heater more often, and have noticed the vent in the shower is very powerful and then the other 3 get gradually weaker, the further they are away from the furnace, is this normal? It seems odd that the space that needs most heat (living area) gets the least. Is there a way to remedy this, or is it just bad design?
Peter
the old geezer is offline   Reply With Quote
Old 01-07-2016, 06:14 AM   #2
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
It is just plain bad design, your bath is probably the shortest run on it's own, then they just run a duct branching off. If you can trace the duct to the plenum and blank off 50% of that line you can get more air back where you want it
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 01-07-2016, 06:32 AM   #3
Member
 
Join Date: Jun 2015
Posts: 46
Thanks for the quick reply
the furnace has 4 ducts attached to it and I am presuming they all come from the same source internally so if I cover the bathroom vent wil this divert more air to the living area without causing overheating of the furnace?
Peter
the old geezer is offline   Reply With Quote
Old 01-07-2016, 07:36 AM   #4
Left Coast
 
Join Date: Dec 2014
Location: vancouver,washington
Posts: 15,649
Send a message via Yahoo to bob caldwell
If there's room, try switch'n hoses around on furnace....sides have less flow that the 2 in line with furnace
bob caldwell is offline   Reply With Quote
Old 01-07-2016, 07:52 AM   #5
Senior Member
 
Join Date: Oct 2015
Posts: 2,270
Can you find somewhere that you can get to the ducts, which I assume are 4" flex, to install one of these in the one going to bathroom. Ideally one of these on all 4 ducts and you could custom balance everything.

Master Flow 4 in. Inline Damper-ILD4 - The Home Depot

The furnace will have a high limit, so it would cut off if you restrict it too much. Think of it this way. They probably use that exact same furnace for different rigs and only use 1 or 2 of the duct taps.
Mr Havercamp is offline   Reply With Quote
Old 01-07-2016, 07:54 AM   #6
Member
 
Join Date: Jun 2015
Posts: 46
Thanks Bob, Good tip I will see if that is possible, doesn't look like there is room but I need to remove all the junk from the locker first to check for sure.
Peter
the old geezer is offline   Reply With Quote
Old 01-07-2016, 07:59 AM   #7
Member
 
Join Date: Jun 2015
Posts: 46
Thanks Mr Havercamp also,
I am in England, but I am sure we have a similar device over here so after I get to the furnace, that will be another thing to try, if I can't switch the ducts around.
Peter
the old geezer is offline   Reply With Quote
Old 01-07-2016, 08:31 AM   #8
Senior Member
 
nomad297's Avatar
 
Join Date: Jul 2015
Posts: 7,053
We just happened to have a heavy, memory foam-type bathroom floor mat. I noticed we were getting tons of extra air in the bathroom diffuser, so I scooted the mat over a little so it covered the diffuser and it is heavy enough to completely block the air. It made a marked improvement on the flow of the other diffusers in the camper.

Bruce
__________________
2016 Rockwood Windjammer 3029W Diamond Edition
2015 Chevy 3500HD LTZ 6.0 Crew Cab 4x4 Long Bed 4.10:1 SRW
nomad297 is offline   Reply With Quote
Old 01-07-2016, 08:38 AM   #9
Senior Member
 
Join Date: Jul 2010
Location: Waynesville
Posts: 14,428
When we had the Heat Flow problem I used a Heavy Trailer Life Directory to cover part of the Bathroom heat register,Boy I sure miss reading that after the New Duct was installed to the Rear of unit! Youroo!!
youroo is offline   Reply With Quote
Old 01-07-2016, 08:38 AM   #10
Left Coast
 
Join Date: Dec 2014
Location: vancouver,washington
Posts: 15,649
Send a message via Yahoo to bob caldwell
Can also tie a ribbon on registers to check air flow
bob caldwell is offline   Reply With Quote
Old 01-07-2016, 08:40 AM   #11
Left Coast
 
Join Date: Dec 2014
Location: vancouver,washington
Posts: 15,649
Send a message via Yahoo to bob caldwell
Cut the chain off it....it'd be portable! Oh wait...there's no pages left...
bob caldwell is offline   Reply With Quote
Old 01-07-2016, 10:58 AM   #12
Member
 
Join Date: Jun 2015
Posts: 46
I tried covering the vents but it didn't seem to make much difference, will get access to the Furness, in a day or two will try and change the ducting over
the old geezer is offline   Reply With Quote
Old 01-07-2016, 11:07 AM   #13
Left Coast
 
Join Date: Dec 2014
Location: vancouver,washington
Posts: 15,649
Send a message via Yahoo to bob caldwell
I was not gett'n much out of 2 of the 3 in here. Cut access hole in underbelly. found 2 hoses that had been smashed and torn when underbelly was installed...hoses had been pulled tight around holding tanks, so I replaced them. If you find that's your problem, a sheet metal shop could make a short metal pipe style connector to slip inside the bad area and add a couple screw clamps. Also, the factory hoses are thin, and loose some heat .
bob caldwell is offline   Reply With Quote
Old 01-07-2016, 01:32 PM   #14
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Quote:
Originally Posted by the old geezer View Post
I tried covering the vents but it didn't seem to make much difference, will get access to the Furness, in a day or two will try and change the ducting over
You really need to block it at the unit to produce more noticeable air flow. Do not block off more then 30% you will have limit problems. Remember these units only produce a little over 300 CFM If you just block the register you will increase your static pressure not good for the blower.....
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 01-07-2016, 02:43 PM   #15
Senior Member
 
Join Date: Dec 2014
Location: oakdale, ca
Posts: 292
They sell heater duct blockers that are 10 by 16 inch magnetic strips that you can cut to size and place over vents to detour flow to other vents. They come in white and brown and run approx. $14 for two at camping world. What's great about them is you can cut them so you can still allow a little heat in the area your blocking from.
j free is offline   Reply With Quote
Old 01-07-2016, 04:01 PM   #16
Senior Member
 
heavyodie's Avatar
 
Join Date: Aug 2012
Location: Battle Creek
Posts: 108
The other problem I had was that the register in the hall was blowing on the thermostat. The furnace kept cycling until I blocked that vent.
__________________
2019 3500 SWR Silverado Duramax
2019 Cedar Creek 31IK
heavyodie is offline   Reply With Quote
Old 01-07-2016, 04:12 PM   #17
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,074
Quote:
Originally Posted by j free View Post
They sell heater duct blockers that are 10 by 16 inch magnetic strips that you can cut to size and place over vents to detour flow to other vents. They come in white and brown and run approx. $14 for two at camping world. What's great about them is you can cut them so you can still allow a little heat in the area your blocking from.
My registers were plastic so that wouldn't work for me.
I went to Lowe's and bought replacements with a dampener.
The new ones are metal but with the dampener, I don't need the magnetic mats.
That helped and I also repositioned the ducts on the furnace to improve air flow to the back of the unit.

Partially closing the one that blew on the t/stat helped too but I suspect at some point I'll have to drop the coroplast (underbelly) and see what horrors I might find there.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2017 Ford F-Series SCREW 4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=86
5picker is offline   Reply With Quote
Old 01-07-2016, 08:06 PM   #18
Member
 
camping baba's Avatar
 
Join Date: Jun 2015
Location: Mass
Posts: 215
The ducts lines to the bathroom and the hallway are found it the storage area .The big box stores sell vent dampers . You may have to install a solid piece of pipe to put the damper in but it is a easy install .
__________________
2013 Silverado extended cab 4x4 1500 Series
camping baba is offline   Reply With Quote
Old 01-07-2016, 11:13 PM   #19
RetiredRVer
 
Join Date: Feb 2014
Location: Ohio
Posts: 264
If you're on shore power, get a couple of electric space heaters to warm your cold areas.
checkmate99 is offline   Reply With Quote
Old 01-10-2016, 10:05 PM   #20
MCTroy
 
Join Date: Sep 2014
Location: Troy.Ohio
Posts: 1,176
[QUOTE=nomad297;1073295]We just happened to have a heavy, memory foam-type bathroom floor mat. I noticed we were getting tons of extra air in the bathroom diffuser, so I scooted the mat over a little so it covered the diffuser and it is heavy enough to completely block the air. It made a marked improvement on the flow of the other diffusers in the camper.

Bruce[/QUOTE

2x, we did the same thing with the bathroom rug. Didn't block all air flow but enough to keep the bath from being a sauna! Even the front bedroom was warm on some very chilly nights.
__________________
2015 Windjammer 3029 Diamond Edition
2018 Ram 2500
Ohio River Rat
MCTroy is offline   Reply With Quote
Reply

Tags
heating, rockwood

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts