Connecting 30 amp RV to a 50 amp campground pedestal

So I can plug my 30 amp rig to 50 amp state parks pedestal?
__________________
raptor
2016 Forester MBS 2401R
America is great
raptor is offline   Reply With Quote
Old 09-10-2017, 08:54 AM   #2
Senior Member
 
Join Date: Nov 2016
Posts: 918
"So I can plug my 30 amp rig to 50 amp state parks pedestal?"

YES , just purchase the proper adapter that has a 50A 240v end for the park and the 120v 30A socket your coach uses.

The adapter will tie into only one 120V leg on the 240V plug making it proper for your rig.

These are a must when traveling as the 240V 50A is common.
FFred is offline   Reply With Quote
Old 12-07-2017, 05:14 PM   #3
Senior Member
 
Kirk S's Avatar
 
Join Date: Jan 2017
Location: Savannah
Posts: 792
Quote:
Originally Posted by FFred View Post
"So I can plug my 30 amp rig to 50 amp state parks pedestal?"

YES , just purchase the proper adapter that has a 50A 240v end for the park and the 120v 30A socket your coach uses.

The adapter will tie into only one 120V leg on the 240V plug making it proper for your rig.

These are a must when traveling as the 240V 50A is common.
I've encountered more than one park with a damaged 30 amp receptacle. There were no other sites available. The 50 amp 240v to 30 amp 120v adapter was the only thing between staying or finding another park. I reported the issue and used the adapter which I purchased thanks to reading this forum ahead of our trip.
__________________
Kirk
2017 Forester 3051S
Kirk S is offline   Reply With Quote
Old 12-07-2017, 05:19 PM   #4
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,959
The 50 amp male to 30 amp female adapter just uses one of the 120 volt hot legs of a 50 amp outlet, as per this diagram:

__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 12-07-2017, 06:11 PM   #5
Senior Member
 
gectisme's Avatar
 
Join Date: Sep 2015
Location: SF Bay Area
Posts: 849
Quote:
Originally Posted by Netgain View Post
I've encountered more than one park with a damaged 30 amp receptacle. There were no other sites available. The 50 amp 240v to 30 amp 120v adapter was the only thing between staying or finding another park. I reported the issue and used the adapter which I purchased thanks to reading this forum ahead of our trip.
In our travels we have noticed the sites that have 30 and 50 amp on the same pedestal, more often than not, the 30 amp is worn and the 50amp is in good condition. I think this is because there are more 30 amp RV's. I now always plug into the 50 amp side and use the 50amp to 30amp adapter to get a better connection.
__________________
2016 Windjammer 3006WK - Sold July 2018
2002 Lance Lite 835EC TC - Sold July 2015
2010 Dodge Ram 2500, 4x4, Diesel, Front Hitch, Air Lift 5000 Rear Air Bags, Sold Mar 2019.

MISSION COMPLETED!
gectisme is offline   Reply With Quote
Old 12-07-2017, 07:43 PM   #6
Senior Member
 
Join Date: Oct 2017
Location: Sooke
Posts: 112
Quote:
Originally Posted by wmtire View Post
The 50 amp male to 30 amp female adapter just uses one of the 120 volt hot legs of a 50 amp outlet, as per this diagram:



Thanks. I wondered how the 50-30 dog bone worked ..
emjayuu is offline   Reply With Quote
Old 12-07-2017, 08:18 PM   #7
Senior Member
 
Join Date: Jul 2017
Location: Suffolk, Va.
Posts: 1,413
Quote:
Originally Posted by wmtire View Post
The 50 amp male to 30 amp female adapter just uses one of the 120 volt hot legs of a 50 amp outlet, as per this diagram:

So the outlet is protected at 50 amps from the post to the RV breaker?
__________________
Michael & Fran Dilday (Baxter & Honey 2 Labs)
'18 Cedar Creek Champagne 38EL - '17 Ford F350 Lariat DRW w/Reese hitch - TST 507 Color TPMS - Garmin RV 770 LMT GPS
mwdilday is offline   Reply With Quote
Old 12-07-2017, 08:24 PM   #8
Senior Member
 
Join Date: Jan 2015
Location: eastern NC
Posts: 1,783
we have found that a 50m to 30F and a 30m to 15f are two adapters that are certainly good to have on hand for a "just in case" situation, .... once we were at a cg that had only 50amp service on all their power poles, they provided the 50m to 30f adapters for loan to anyone who needed them, .... we run our electric heaters off the 15amp service when available and one of our favorite cg has several power poles that the 110 outlets do not work, .... at those sites we just draw 15amp from the 30/with adapter and the 30amp service from the 50/with adapter, .... both are very handy to have and they do what they're made for without any problem, ....

https://www.amazon.com/dp/B01N8UDPIJ...&pd_rd_w=7LbM2

https://www.amazon.com/RV-Power-Cord...15f+rv+adapter
__________________


fella10 is offline   Reply With Quote
Old 12-07-2017, 09:00 PM   #9
Just as confused as you
 
Scrapper's Avatar
 
Join Date: Aug 2013
Location: south central Wisconsin
Posts: 5,108
Quote:
Originally Posted by mwdilday View Post
So the outlet is protected at 50 amps from the post to the RV breaker?
Yes, but your 30 amp breaker inside your RV will limit your amp draw to no more than 30 amps.
__________________
Richard & Jill
2014 Flagstaff 832IKBS Classic Super Lite
2018 Silverado 1500 Crew Cab Z71 4WD All Star Edition
Camping since 1989, Seasonal since 2000.
Car Shredder Op/Tech, Scrap Metal Recycling - retired
Scrapper is offline   Reply With Quote
Old 12-07-2017, 09:07 PM   #10
Senior Member
 
Join Date: Jul 2017
Location: Suffolk, Va.
Posts: 1,413
Quote:
Originally Posted by Scrapper View Post
Yes, but your 30 amp breaker inside your RV will limit your amp draw to no more than 30 amps.
Yes but a short between the post and the 30 amp breaker may fry something.
__________________
Michael & Fran Dilday (Baxter & Honey 2 Labs)
'18 Cedar Creek Champagne 38EL - '17 Ford F350 Lariat DRW w/Reese hitch - TST 507 Color TPMS - Garmin RV 770 LMT GPS
mwdilday is offline   Reply With Quote
Old 12-07-2017, 09:34 PM   #11
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,959
Quote:
Originally Posted by mwdilday View Post
Yes but a short between the post and the 30 amp breaker may fry something.
mwdilday is correct in that the 30 amp shore power cord does become the weak link in the circuit between the campground outlet being capable of 50 amps AND the RV's 30 amp main breaker in the distribution panel.

In a normal 30 amp campground outlet to 30 amp main RV distribution panel, everything is protected by either the RV's 30 amp main circuit breaker all the way to the campgrounds 30 amp main circuit breaker. Should an overload/short occur in the circuit, then hopefully one or the other 30 amp circuit breakers would trip, thus protecting the entire circuit/wiring.

When using this adapter, if the RV's main 30 amp circuit breaker fails to trip, then the campgrounds 50 amp main circuit breaker will not trip until 50 amps is reached.... which would be over the shore power cords 30 amp safe limit. You just have one 30 amp circuit breaker (the RV's) protecting the circuit in this scenario instead of two (the RV's and the campground pedestals).

1. Can this happen....yes
2. Will it happen..... probably not

It is a possibility with low probability. Many RV'ers use this adapter with absolutely no problem, which is why it's produced by manufacturers. It's also why you will see it used in those campgrounds with only a 50 amp outlet at the pedestal.

If a RV'er with a 30 amp RV just utilizes his RV in the same manner as they normally would when connected to the 50 amp outlet via this adapter (don't try to use more than 30 amps), then they probably will be fine, absent a cascading failure.
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 12-07-2017, 09:41 PM   #12
Senior Member
 
Kirk S's Avatar
 
Join Date: Jan 2017
Location: Savannah
Posts: 792
It would add to the cost, but a 30 amp circuit breaker on the 50 to 30 adapter wouldn't be a bad idea. Agree with wmtire's statement ... possibility with low probability.
__________________
Kirk
2017 Forester 3051S
Kirk S is offline   Reply With Quote
Old 12-07-2017, 09:48 PM   #13
Senior Member
 
Join Date: Jul 2017
Location: Suffolk, Va.
Posts: 1,413
Quote:
Originally Posted by Netgain View Post
It would add to the cost, but a 30 amp circuit breaker on the 50 to 30 adapter wouldn't be a bad idea. Agree with wmtire's statement ... possibility with low probability.
I like the idea of a breaker.
__________________
Michael & Fran Dilday (Baxter & Honey 2 Labs)
'18 Cedar Creek Champagne 38EL - '17 Ford F350 Lariat DRW w/Reese hitch - TST 507 Color TPMS - Garmin RV 770 LMT GPS
mwdilday is offline   Reply With Quote
Old 12-07-2017, 10:06 PM   #14
geezer with gadgets
 
757Dave's Avatar
 
Join Date: Feb 2015
Location: SE Virginia
Posts: 672
We have had good results using a 50 amp splitter. Here's the one that we use.

https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1

Happy travels...

__________________


Sent from my Atari 2600
2011 Sunseeker 3170ds "Ladybug"
2017 Jeep Grand Cherokee TOAD
Days camped 2015: 37; 2016: 66; 2017: 86 2018: 57 2019: 30
757Dave is offline   Reply With Quote
Old 12-07-2017, 10:23 PM   #15
Senior Member
 
Join Date: Jan 2015
Location: eastern NC
Posts: 1,783
30a + 20a,.... do I have a 50amp service?

Since we're all electric(don't carry propane), I use a #12 extension cord(yellow cord in photo) to power our two small ceramic heaters from the 110 outlet on the power pole, .... that takes those amps off the 30 amp system, ... since the photos below were taken, I've included wiring to allow me to power the wh off that 110 system in the summer when the ac is almost full time on the 30 amp system, again, to remove those amps from the 30 amp system , .... works great, with no problems whatsoever, ....
Attached Thumbnails
Click image for larger version

Name:	DSCN0542.jpg
Views:	119
Size:	376.6 KB
ID:	157805   Click image for larger version

Name:	DSCN0537.jpg
Views:	128
Size:	331.8 KB
ID:	157806  
__________________


fella10 is offline   Reply With Quote
Old 12-07-2017, 10:38 PM   #16
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,959
Quote:
Originally Posted by fella10 View Post
Since we're all electric(don't carry propane), I use a #12 extension cord(yellow cord in photo) to power our two small ceramic heaters from the 110 outlet on the power pole, .... that takes those amps off the 30 amp system, ... since the photos below were taken, I've included wiring to allow me to power the wh off that 110 system in the summer when the ac if almost full time on the 30 amp system, again, to remove those amps from the 30 amp system , .... works great, with no problems whatsoever, ....
That sounds good, depending on how long your #12 extension cord is, and the total amount of amps your two space heaters combined are using.

I noticed a ? in your post title asking if 30 amps + 20 amps made you 50 amps. Yes and no

Yes, as in it would allow you up to 50 amps of power, or 6000 watts total.

No, as in this is not the same as a 120/240 volt split phase 50 amp outlet or the way a 50 amp RV utilizes such.....which is 12000 watts total.

This link may help explain it.

https://www.rvtechmag.com/electrical/chapter3.php
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 12-07-2017, 10:48 PM   #17
Senior Member
 
Join Date: Jan 2015
Location: eastern NC
Posts: 1,783
Quote:
Originally Posted by wmtire View Post
That sounds good, depending on how long your #12 extension cord is, and the total amount of amps your two space heaters combined are using
50 amp? was tongue in cheek, but ... 30 + 20 has always = 50, ..... 28ft #12 cord, ... kill-a-watt monitor says running both heaters on high 12.1amp, both on low 7.8amp, .... no problem whatsoever, ....
__________________


fella10 is offline   Reply With Quote
Old 12-07-2017, 11:06 PM   #18
Just as confused as you
 
Scrapper's Avatar
 
Join Date: Aug 2013
Location: south central Wisconsin
Posts: 5,108
Quote:
Originally Posted by mwdilday View Post
Yes but a short between the post and the 30 amp breaker may fry something.
Yes, but a short in the wiring between the 50 amp pedestal breaker and the 30 amp breaker will trip the 50 amp breaker. It doesn't matter if you have a 30 amp pedestal or 50 amp pedestal breaker, a short will between the pedestal and the distribution panel will trip only the one at the pedestal.

The breaker only protects the load side of the breaker from shorts or overloads. The line side (supply) is not protected by said breaker.
__________________
Richard & Jill
2014 Flagstaff 832IKBS Classic Super Lite
2018 Silverado 1500 Crew Cab Z71 4WD All Star Edition
Camping since 1989, Seasonal since 2000.
Car Shredder Op/Tech, Scrap Metal Recycling - retired
Scrapper is offline   Reply With Quote
Old 12-07-2017, 11:36 PM   #19
Senior Member
 
Join Date: Jun 2012
Posts: 10,907
Quote:
Originally Posted by wmtire View Post
mwdilday is correct in that the 30 amp shore power cord does become the weak link in the circuit between the campground outlet being capable of 50 amps AND the RV's 30 amp main breaker in the distribution panel.

In a normal 30 amp campground outlet to 30 amp main RV distribution panel, everything is protected by either the RV's 30 amp main circuit breaker all the way to the campgrounds 30 amp main circuit breaker. Should an overload/short occur in the circuit, then hopefully one or the other 30 amp circuit breakers would trip, thus protecting the entire circuit/wiring.

When using this adapter, if the RV's main 30 amp circuit breaker fails to trip, then the campgrounds 50 amp main circuit breaker will not trip until 50 amps is reached.... which would be over the shore power cords 30 amp safe limit. You just have one 30 amp circuit breaker (the RV's) protecting the circuit in this scenario instead of two (the RV's and the campground pedestals).

1. Can this happen....yes
2. Will it happen..... probably not

It is a possibility with low probability. Many RV'ers use this adapter with absolutely no problem, which is why it's produced by manufacturers. It's also why you will see it used in those campgrounds with only a 50 amp outlet at the pedestal.

If a RV'er with a 30 amp RV just utilizes his RV in the same manner as they normally would when connected to the 50 amp outlet via this adapter (don't try to use more than 30 amps), then they probably will be fine, absent a cascading failure.
And this is really no different than your house. You've got a 15 amp or 20 amp breaker in the basement. If it fails, then you've got a 100 amp or 200 amp breaker above it. Only difference is that in your house, the distance between the two breakers is inches of bus bar, while in your RV, it's the length of 30 amp cord.

That being said, I've never, ever seen or heard of a breaker that failed to open. I'm not saying they don't - I'm just saying I've never heard of one.
__________________
1988 Coleman Sequoia - popup (1987-2009) - outlasted 3 Dodge Grand Caravans!
2012 Roo19 - hybrid (2012-2015)

2016 Mini Lite 2503S - tt (2015 - ???)
2011 Traverse LT, 3.6L, FWD
2009 Silverado 1500 Ext Cab, 5.3L, 4x4, 3.73
2016 Silverado 2500HD Dbl Cab, 6.0L 4x4, 4.10
rockfordroo is offline   Reply With Quote
Old 12-08-2017, 12:36 AM   #20
Senior Member
 
SailorSam20500's Avatar
 
Join Date: Jun 2016
Posts: 5,061
Quote:
Originally Posted by mwdilday View Post
Yes but a short between the post and the 30 amp breaker may fry something.
If you have a short between the post and the 30 amp breaker, the breaker on the post will trip.
This situation is no different than power at your S&B. Outside your house, is well over 200 amps. You have a main breaker of between 100 and 200 amps or so. Individual circuits in your house are usually 15 or 20 amps.

I was at the Kentucky Horse park this summer. They apparently have dual power loops with separate feeds to the 50 and 30 amp outlets. The 30 amp circuit was browning out which caused my Progressive EMS to shut down my camper. Put in my 50 amp adapter and was good to go. Fewer trailers on the 50 amp supply
__________________
Al
I am starting to think, that I will never be old enough--------to know better.
Tolerance will reach such a level that intelligent people will be banned from thinking so as not to offend the imbeciles. Fyodor Mikhailovich Dostoevsky, Russian Novelist
S.E. Mich. Flagstaff 26FKWS / 2022 F-150 3.5 EcoBoost SCrew Propride
SailorSam20500 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 06:07 PM.