Old 01-11-2017, 08:54 AM   #21
NC...for now
 
formerFR's Avatar
 
Join Date: Jan 2017
Posts: 148
this was our main drawback in our first journey into RVing ... a 5vr bunkhouse with no generator. i purchased two Honda units, the second was the 30a companion model. I tested them, they worked well together for the 30a output, and were not overly loud, especially when well away from the RV. These Honda models, though, will vary in speed as the need applies, so when little amperage is needed, they idle pretty quietly.

i never used either before we decided to trade to a new Georgetown ClassA with the onboard generator... sold both Hondas right away on craigslist at a very good price.
__________________

__________________
formerFR is offline   Reply With Quote
Old 01-11-2017, 09:05 AM   #22
Senior Member
 
Join Date: Oct 2015
Posts: 2,198
Quote:
Originally Posted by Musky Dave View Post
The standard, non inverter generators are fine. They are what's used in every medical facility, business, and home for emergency power backup. They run entire buildings without any problems. Sensitive medical equipment works just fine, I'm sure our fancy flat screens will survive. I'm not an expert by any means, just looking at the obvious.

Just my $.02

Dave
Not to argue but the generators we install in buildings as back up are not your average contractor type champion or whatever brand. I've powered site trailers at times with standard generators and I am proof sometimes electronic items don't like them. Forget a flat screen. Try a Dell precision laptop, an HP plotter, and a ups with surge turned into useless toast to the tune of about $5K or better. They're fine for a circular saw but I went to inverters for the field offices and never looked back.
__________________

__________________
Mr Havercamp is offline   Reply With Quote
Old 01-11-2017, 09:51 AM   #23
Usually Confused Member
 
emm-dee's Avatar
 
Join Date: Nov 2015
Location: Georgia
Posts: 1,304
Quote:
Originally Posted by 5picker View Post
It's all about the efficiency of the fuel.
Propane is less efficient than gasoline and therefore won't 'react' to loading as well as gasoline especially as temperatures get colder.

You are correct when referring to the genny purring along at 3600 RPM it really doesn't matter what is powering it at that point.
But it is when you introduce a load(s) to the generator, as to which fuel can react better to keeping it purring at 3600 RPM. Propane simply cannot as it's BTU's per gallon (combustion power) is less than gas. Simply put, a propane powered engine just doesn't produce as much horsepower as a gas fueled engine, therefore the derating of the wattage.
Just so I understand correctly, are you saying that the generator has more reduction in RPM when surge loaded while running propane than it does while operating with gas? To expand further, would there be a difference in motor output fluctuations when loaded while running 89 octane vs 91 octane fuel?
__________________
At some point during every day you suddenly realize nothing else productive is going to happen the rest of that day. For me, it usually occurs around 9 am.

Vengeance 25V (the Harley needed a home)
emm-dee is online now   Reply With Quote
Old 01-11-2017, 10:57 AM   #24
Senior Member
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 3,455
Quote:
Originally Posted by emm-dee View Post
Just so I understand correctly, are you saying that the generator has more reduction in RPM when surge loaded while running propane than it does while operating with gas? To expand further, would there be a difference in motor output fluctuations when loaded while running 89 octane vs 91 octane fuel?
What I'm saying (well not really me but the manufacturers of these things) is that the generator, under load, (and typically more noticeable at FULL load) simply doesn't have enough horsepower to supply the rated wattage it would be able to produce if using gasoline.

The combustion (explosion) inside the engine (on propane) just doesn't produce as much 'power' to push the piston. So yes, it would bog down (reduction in RPM) more so than when using gasoline.

If you want to split hairs on 89 -vs- 91 octane, that's up to you.
I'm sure there might be some small difference unless the engine's internal combustion components were designed to produce maximum horsepower on 87 or 89 octane. Then using 91 (or higher) would just be wasting money.
__________________
_________________________________________
2016 Flagstaff 8529IKBS Diamond Package 5th Wheel
Ford F-Series SCREW 4x4
TST Tire Monitor - Sinemate 3500w Gen.
Nights Camped: '15 = 22'16 = 46
5picker is offline   Reply With Quote
Old 01-11-2017, 12:09 PM   #25
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 13,097
Quote:
Originally Posted by youroo View Post
Charles,have you tried your New Genny with the Surge Guard plugged into it? On the Champion Inverter type the Surge Gard will prevent Power u

nless you install a "Edison Plug" then All is well! Just asking,our Hondas didn't require the Edison Plug but the Champions did when using the Surge Gard! Youroo!!
I was confused at the terminology there of an "Edison plug", which is a term often used for a common regular old 15 amp and/or 20 amp household outlet/plug.

I then remembered that Mike Sokol used the terminology in his youtube video, when he made the ground/neutral bond plug to insert into the generators 15/20 amp outlet (aka Edison outlet)

Here is his video, which may help clear it up as he made a g-n bond plug to insert in the "Edison" outlet of the generator.

__________________
2011 Flagstaff 831 RLBSS

Materialism: buying things we don’t need with money we don’t have to impress people that don’t matter.
wmtire is online now   Reply With Quote
Old 01-11-2017, 02:04 PM   #26
Senior Member
 
Join Date: Sep 2016
Location: SE Michigan
Posts: 1,796
Quote:
Originally Posted by Mr Havercamp View Post
Not to argue but the generators we install in buildings as back up are not your average contractor type champion or whatever brand. I've powered site trailers at times with standard generators and I am proof sometimes electronic items don't like them. Forget a flat screen. Try a Dell precision laptop, an HP plotter, and a ups with surge turned into useless toast to the tune of about $5K or better. They're fine for a circular saw but I went to inverters for the field offices and never looked back.
Thank you...

A little electricity 101....

A 2 pole 3600 rpm non electronically controlled generator ( the Champion the OP has) and others produce a modified sine pattern and more importantly, the CPS (Hertz) is mechanically regulated by the throttle setting, consequently, as you load the unit, the RPM drops and the CPS drops as well

Electronics don't like either. In fact some electronics will cease working.

An inverter on the other hand produces a DC current which is 'inverted' to 110 /1 or in commercial units, 220/1/3 and the CPS (Hertz) is electronically produced and regulated.

Not here to argue and powering electronic devices in modified sine wave / varying hertz power may or may not cause a failure, but it's certainly a crapshoot.

I use an inverter myself. Your mileage may vary. It's your dime, not mine.
__________________
Enjoying my solitude.....
SidecarFlip is offline   Reply With Quote
Old 01-12-2017, 04:04 AM   #27
Senior Member
 
Join Date: Feb 2014
Location: Rochester WA
Posts: 158
Send a message via Skype™ to chuckw5kav
Quote:
Originally Posted by youroo View Post
Charles,have you tried your New Genny with the Surge Guard plugged into it? On the Champion Inverter type the Surge Gard will prevent Power u

nless you install a "Edison Plug" then All is well! Just asking,our Hondas didn't require the Edison Plug but the Champions did when using the Surge Gard! Youroo!!
We have the Honda 6.5 ISU and when we plug in the trailer to it we
have to disable the surge protector in the 5th wheel.
__________________
2017 Durango Gold G384RLT
Coachmen Owners Association
2005 Ford F350 Dually
W5KAV
This years Camping 25 days Ugh
chuckw5kav is offline   Reply With Quote
Old 01-12-2017, 04:16 AM   #28
Senior Member
 
Join Date: Oct 2015
Posts: 2,198
Quote:
Originally Posted by chuckw5kav View Post
We have the Honda 6.5 ISU and when we plug in the trailer to it we
have to disable the surge protector in the 5th wheel.
Because it is probably detecting over or under voltage when the load increases or decreases if your EMS has that feature, and you possibly need the "edision plug" as youroo calls it that he mentioned.
__________________
Mr Havercamp is offline   Reply With Quote
Old 01-12-2017, 12:43 PM   #29
Member
 
Charles.maine's Avatar
 
Join Date: Jan 2016
Location: North Texas
Posts: 86
Going to let the generator run for probably 2 hours this weekend maybe like 1 with no load and 1 with a load just to get a broke in a little. Got some sta-bil for the fuel. I have 4 5-gal jugs that I am going to take with me. Used Mobile 1 synthetic 10W30 oil in it. Going to only run 91 octane fuel. Try to take care of it as much as possible.
__________________
2015 Chevrolet Silverado 2500HD 4x4 Z71 Duramax/Allison Combo Pull Rite, ISR Series Superglide 16K, LoadLifter 5000 Ultimate W/ WirelessOne
Current RV: 2016 Palomino Columbus 381FL Fifth Wheel
Lippert Flex Air Pin Box, LT235-85-16 GY G614
Nights Camped 2013 - 6 • 2014 - 7 • 2015 - 12 • 2016 - 29 • 2017 - 4
Charles.maine is offline   Reply With Quote
Old 01-16-2017, 07:59 PM   #30
Senior Member
 
Join Date: Jul 2015
Location: OK
Posts: 101
I use a Honda EM5000SX contractor style generator. I run 2 flat screens, my Surface Pro 3, the 15k AC, and whatever else I want and have never had an issue.

When you first start a generator, it will run a little faster at no load. This will give you a little more voltage and frequency, typically less than 130VAC and 61Hz. As you load the generator, you have "droop" and the volts and Hz will drop. Frequency is more speed dependent than voltage, so it will vary more with fluctuations in speed.

If something gets "fried," it is from undervoltage, or more frequently, overvoltage. If the mechanical speed regulator doesn't react quickly enough, or the voltage regulator fails, this can create high voltage. However, most electronic items convert AC back to D.C., so small fluctuations are not really going to affect them.

Where am I going with this? I started with a Champion 4000/3500W generator. It had a 6HP motor on it and any medium size load would cause .5 Hz and 3-5 V fluctuations until the governor stabilized speed and I never had a failure. The Honda is a 4500 running watt genny and has a 13HP motor on it, so it doesn't have the speed variations that the champion had. If you have a surge protector, you should be OK.
__________________

__________________
2016 26RR carrying-
KX65
KX100
CR250R
TRX250ES
mxdad is offline   Reply With Quote
Reply

Tags
generator

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 10:52 PM.