Hi Foxhunt,
I'm sorry but I could only guess why your unit is not working with the Auto Fan setting. The Auto fan works fine for me with the unit installed as described.

Guesses ...

Verify your wires are correct. I have read that some wiring may not have been done correctly by color so its always wise to have first labeled your wires regardless of color as you disassembled your old thermostat.

Try to switch the fan operation setting inside the t-stat between HE and HG and see if that has any effect (long shot but worth a try).

Good luck!
__________________

__________________
Scott
DW, 3 Kids and our Goldens

2012 Shamrock 233S
2008 Toyota Sequoia 5.7L 4WD
Triguy is offline   Reply With Quote
Old 05-29-2014, 09:11 PM   #12
2005 Fleetwood Pride 38RL
 
Join Date: Jan 2012
Location: Apopka, Fl
Posts: 50
Honeywell RTH2300 to Coleman Mach - Help


Ok, Guys I have worked now for two days (nights) trying to make this stat work correctly.

My current symptoms are:
All works fine except the A/C fan comes on when the heat comes on. (not the a/c compressor, just the fan)

To get this far, I set the gas/electric switch to "electric". (moving this switch to the "gas" selection, the A/C fan only runs when fan mode is selected to "on". The a/c fan then also runs when the heat come on. NO fan period when set to auto.)

The wiring is set as follows:
A/c side Stat side
White to white
Yellow to yellow
Green to green
Red to R/Rh (with jumper on)

blue not used
grey not used

notes:
Blue, when touched to red "sparks"
Grey, when touched to red causes a/c fan to run (not sure if low or high)
Green when touched to red causes a/c fan to run (not sure if low or high)
connecting the green and grey together and installed in the G terminal does not seem to make the fan sound any different (unknown hi or low)

Like I said, all is working except that the a/c fan runs when the heat is turned on.
I have an Atwood 8535IVDCLP furnace

I called Honeywell support and after about 20 minutes, the guy told me this stat will not work on 12 volt systems. He left me hanging 2 time to go back and verify his statement.
He also told me I would have to bring in an a/c professional to resolve my digital thermostat needs.

I went through this whole same scenario last year with a Hunter stat in my old TT. We now have a new to us Fleetwood Pride 5th wheel and Atwood furnace and Honeywell stat. (Still love our Forest River Friends!!!)

Can anyone help me resolve this issue?

Thanks
Randy
(I am using this thread because I followed the wiring from TRrguy to get this far)
__________________

__________________
BBDAWG is offline   Reply With Quote
Old 05-31-2014, 10:06 AM   #13
Member
 
Join Date: Apr 2013
Posts: 74
On mine the green is the high fan and grey is the low fan. Make sure you didn't pop the 12v fuse for the furnace. Mine was a 7.5a fuse and I pooped it twice before figuring out my wiring.
__________________
Silverado HD 2500 6.0 Crew Cab
2014 Roo 21ss
sdelam is offline   Reply With Quote
Old 05-31-2014, 11:16 AM   #14
2005 Fleetwood Pride 38RL
 
Join Date: Jan 2012
Location: Apopka, Fl
Posts: 50
Quote:
Originally Posted by sdelam View Post
On mine the green is the high fan and grey is the low fan. Make sure you didn't pop the 12v fuse for the furnace. Mine was a 7.5a fuse and I pooped it twice before figuring out my wiring.
Thank You for continuing to help. I know someone has the answer out there and I sure hope they will pop up and help figure this out.

Yes, I did blow the fuse, it was a 15amp. I also created another problem with the lights over the stove area (in a slide out) as they quit working at the same time. (4 lights on two switches) I have checked every fuse but no luck on fixing those yet.

Anyway, my a/c and thermostat are working except that one issues remains. When I turn on the furnace, the a/c fan comes on.
The furnace blower works the furnace ignites and seems to work as it should.

This one a/c fan issue is really bugging me and I know I have the stat he/hg set wrong but it is the only way it will work, as good as it is.

Randy
__________________
BBDAWG is offline   Reply With Quote
Old 05-31-2014, 11:42 AM   #15
Member
 
Join Date: Apr 2013
Posts: 74
My a/c fan also did this at first. I switched it from elec to gas and now it works like its supposed to.

Silly question but, did you wait a few minutes after turning it on and off initially to give the built in delay time to reset?
__________________
Silverado HD 2500 6.0 Crew Cab
2014 Roo 21ss
sdelam is offline   Reply With Quote
Old 05-31-2014, 12:12 PM   #16
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 7,628
Take the green wire off and add the gray to the green terminal, then see what happens. Also look in your R/A and see if there is a green wire going to the board, it's easy to see. It hard to try and tell you how to wire it being all units are different. What will work on 1 unit may not work on yours. FR doesn't do anything consistently.
__________________
Rockwood #8289 WS 2012
F250 6.0 / Husky 16k
With 4 point leveling system
Witch Doctor is offline   Reply With Quote
Old 05-31-2014, 12:27 PM   #17
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 7,628
The green wire might be a ground. All you need are the white and red to bring your furnace on blower will start then burner. A/C side red hot, yellow compressor, blue or gray high and low speed (normally). Fan only for your unit would be red to gray/blue only use one. when set to on not auto should just bring on the a/c blower. Like I said it's hard to tell how they wire it. When you call for a/c your sub base will bring on the compressor yellow and the gray for the blower in auto or fan on without the compressor kicking in. It's the best I can say with out seeing it, SORRY you should not see a spark touching the blue to red the blower should come on only. The way triguy told you is correct but remember this is FR. Make sure it is set to gas not electric. I'll check back at 1:30 PM East time let me know what happens. easy way to check your wire is disconnect them all from the stat with red to yellow only compressor will come on, red to gray a/c fan only , red to white furnace should start, It sounds like they made your blue wire ground and the green low speed. Your lighting problem sounds like a fuse to me. Also you have a different stat then triguy, Honeywell might be right just noticed that, but hard to read his model #
__________________
Rockwood #8289 WS 2012
F250 6.0 / Husky 16k
With 4 point leveling system
Witch Doctor is offline   Reply With Quote
Old 05-31-2014, 01:24 PM   #18
2005 Fleetwood Pride 38RL
 
Join Date: Jan 2012
Location: Apopka, Fl
Posts: 50
Ok, first off what is the R/A?
Yes, I did wait for the time limit, not at first with the other stat.
When I touch red to Yellow, compressor come on, no fan
When I touch red to white, the furnace come on
When I touch red to grey, a/c fan comes on
When I touch rd to green, a/c fan comes on
When I touch red to blue - SPARKS

If I put the hg/he switch to h/g, the a/c compressor comes on but NO FAN (with the Green attached to the G stat lug). Heater seems to work OK.
e
Can I take photos of anything and post them?

We are having a large storm right now so will have to do this later.

Thanks so much for the help but gotta run now.
Randy
__________________
BBDAWG is offline   Reply With Quote
Old 05-31-2014, 01:44 PM   #19
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 7,628
Quote:
Originally Posted by BBDAWG View Post
Ok, first off what is the R/A?
Yes, I did wait for the time limit, not at first with the other stat.
When I touch red to Yellow, compressor come on, no fan
When I touch red to white, the furnace come on
When I touch red to grey, a/c fan comes on
When I touch rd to green, a/c fan comes on
When I touch red to blue - SPARKS

If I put the hg/he switch to h/g, the a/c compressor comes on but NO FAN (with the Green attached to the G stat lug). Heater seems to work OK.
e
Can I take photos of anything and post them?

We are having a large storm right now so will have to do this later.

Thanks so much for the help but gotta run now.
Randy
The green and gray are high and low speed, for some reason the blue is ground causing the spark or it's touching something and grounding out. . Use the gray only and hook it up as you stated do not use the green or blue tape them off. Reinstall and it should work. Lets cross our fingers make sure your batteries are in. I'll check back in the am. If your a/c is on the roof you have a split panel in the ceiling 1 side you will see with twist black knobs, that is where your return air filter is located and your a/c control board from the stat. what is hg/he stand for in your install book? Then turn down the a/c to 60 to make sure it comes on, then shut it off to 90 and put your fan switch to on the fan will come on only I hope. Your furnace is fine you just need the white and red.
__________________
Rockwood #8289 WS 2012
F250 6.0 / Husky 16k
With 4 point leveling system
Witch Doctor is offline   Reply With Quote
Old 06-01-2014, 11:16 AM   #20
2005 Fleetwood Pride 38RL
 
Join Date: Jan 2012
Location: Apopka, Fl
Posts: 50
ALRIGHT!
I removed the green and attached the grey to the "G" terminal. I set the switch back to (HG) for the gas furnace setting. I turned the breaker back on and waited for the protect circuit to kick in and it came on.

Then checked the heat cycle and there was no a/c fan with the heater running. SUCCESS!

final step - the a/c fan still sounds like it is in "lo" speed so I went back and added the green wire to the grey and reinstalled it.

The fan now seems a little louder, not much sound difference but I do think it is louder (faster) I'm going to leave it like this for a while and see if all goes well but I do think it is all working again.

I know I had this config once or twice before and I had the problems. I guess I was wrapped around the axle and not seeing things (or remembering) correctly.

I really appreciate YOU Guys stepping in to help us wayward mechanic wanna be's, dig ourselves out of these holes..

Now I have to figure out what I did to the circuit with 4 - 12 volt lights that quit working. I have checked each fuse in the two fuse boxes so I need to do more digging. Ugghhh

(and NO, I am not having fun yet!!)

Thanks again!!
Randy
__________________

__________________
BBDAWG is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 10:02 PM.