Old 09-18-2019, 08:48 AM   #21
Junior Member
 
Join Date: Jun 2017
Location: USA
Posts: 25
Update "No More Extension Cords"

Thanks to all who made the observations (and errors) on my RV Power Box installation. I check my local township electrical codes and did confirm 3 feet minimum from gas regulator. I have relocated box to 42" from gas regulator and installed waterproof outdoor PVC conduit. In the words of Canadian contractor and TV show host Mike Holmes "Make It Right".
Attached Thumbnails
Click image for larger version

Name:	RV Box1a.jpg
Views:	155
Size:	540.0 KB
ID:	215277   Click image for larger version

Name:	RV Box1.jpg
Views:	150
Size:	510.2 KB
ID:	215278   Click image for larger version

Name:	RV Box2.jpg
Views:	142
Size:	535.9 KB
ID:	215279   Click image for larger version

Name:	RV Box3.jpg
Views:	140
Size:	312.1 KB
ID:	215280  
__________________
John and Janis Blaskowski
The fur-kids; Pedro, Penelope, Amigo
Macomb, Michigan
2013 Ford F-150 XTR 3.5L Ecoboost Max Tow Package
2022 Flagstaff MicroLite 25FKBS
John-n-Janis is offline   Reply With Quote
Old 09-18-2019, 08:53 AM   #22
Senior Member
 
frank4711's Avatar
 
Join Date: Jan 2019
Location: North Port Florida
Posts: 2,050
Quote:
Originally Posted by John-n-Janis View Post
Thanks to all who made the observations (and errors) on my RV Power Box installation. I check my local township electrical codes and did confirm 3 feet minimum from gas regulator. I have relocated box to 42" from gas regulator and installed waterproof outdoor PVC conduit. In the words of Canadian contractor and TV show host Mike Holmes "Make It Right".
As I said before Well Done ... Enjoy
__________________
Frank & Cindy--- (SOB) 5th Wheel ---2019 Ram 3500 Cummins 6.7 SRW 4x4 8' bed--- Payload 4394------Remi & Sage camping pups---TST 507 TPMS ... B&W Patriot 18K---3.73 axle ... Predator 3500---2019 48 days ---2020 28 days Camping
frank4711 is offline   Reply With Quote
Old 09-18-2019, 08:53 AM   #23
Senior Member
 
Join Date: Apr 2016
Location: Port Charlotte Fl/Hinsdale Ma
Posts: 4,823
Quote:
Originally Posted by John-n-Janis View Post
Thanks to all who made the observations (and errors) on my RV Power Box installation. I check my local township electrical codes and did confirm 3 feet minimum from gas regulator. I have relocated box to 42" from gas regulator and installed waterproof outdoor PVC conduit. In the words of Canadian contractor and TV show host Mike Holmes "Make It Right".
Not PVC conduit but weatherproof and code legal just the same. What you used is called seal tight and or seal flex depending on who you talk to. It is what I would have used.
cavie is offline   Reply With Quote
Old 09-18-2019, 09:33 AM   #24
Senior Member
 
DouglasReid's Avatar
 
Join Date: Jun 2016
Location: Maurice, LA
Posts: 4,095
Quote:
Originally Posted by John-n-Janis View Post
In the words of Canadian contractor and TV show host Mike Holmes "Make It Right".

Good Advice anywhere!
__________________
2012 Wildcat Sterling 32RL, Gladiator Qr35 ST235/85R16 Load rating G, TST 507 TPMS w/ Flow-thru Sensors & Repeater, Reese Sidewinder 16K Pin Box, PI EMS HW50C
2009 Chevy Silverado 2500HD CCSB LTZ Diesel, Fumoto Oil Drain Valve, Turbo Brake activated, 39 gal Aux Tank W/ Fuel Pump transfer, Air Lift Loadlifter 5000 air bags.
DouglasReid is offline   Reply With Quote
Old 09-18-2019, 01:18 PM   #25
Senior Member
 
Dodge Guy's Avatar
 
Join Date: Oct 2006
Posts: 1,630
Quote:
Originally Posted by kenandterry View Post
I’m just wondering how soon you’ll wish it was a 50 amp service box.

Just sayin’
I still have the 30A outlet from our trailer. The MH runs everything I need it to on the 30A. The only extra I have over the trailer is one more AC unit. I only run one AC when I need to. Otherwise I am happy with my 30A box.
__________________
2012 Georgetown XL 350TS, Hellwig front/rear sway bars, Sumo Springs, Blue OX True Center steering damper
2013 Ford Explorer LTD toad, Roadmaster Stowmaster 5000, VIP><Tow Brake

Better to have a bad day of camping than a good day at work!
Dodge Guy is offline   Reply With Quote
Old 09-23-2019, 07:27 PM   #26
Member
 
Join Date: Mar 2019
Posts: 41
Quote:
Originally Posted by John-n-Janis View Post
Finally got 30 amp service box installed. Replaced unused 20 amp breaker with 30 amp breaker in house service panel, ran 10/2 wire to service box. Goodbye extension cord!
https://inspectapedia.com/plumbing/G...Clearances.php


Check this out, 3 feet is the min distance from the natural gas or propane meter vent. Arc flash is the concern.
Chief55 is offline   Reply With Quote
Old 09-23-2019, 07:54 PM   #27
Senior Member
 
Join Date: Jun 2012
Location: Central Wyoming
Posts: 142
Quote:
Originally Posted by Chief55 View Post
https://inspectapedia.com/plumbing/G...Clearances.php


Check this out, 3 feet is the min distance from the natural gas or propane meter vent. Arc flash is the concern.
I think I stated that in post #5!
WY Husker Fan is offline   Reply With Quote
Old 09-23-2019, 10:40 PM   #28
NXR
Senior Member
 
NXR's Avatar
 
Join Date: Mar 2019
Location: Family room couch
Posts: 4,556
Quote:
Originally Posted by Chief55 View Post
https://inspectapedia.com/plumbing/G...Clearances.php


Check this out, 3 feet is the min distance from the natural gas or propane meter vent. Arc flash is the concern.
Hey, thanks! That was interesting reading.

Ray
__________________
2020 Georgetown GT5 34H5
2020 Equinox Premier AWD 2.0L/9-speed
NXR is offline   Reply With Quote
Old 09-24-2019, 06:47 AM   #29
Junior Member
 
Join Date: Aug 2017
Posts: 2
husker fan is correct . I have worked as a Supt. of a gas utility for 23 years and we require any electrical appl . outlet, etc be a min. of 3' from a gas regulator . Just be safe you never know when if ever that regulator will start venting .
curt songer is offline   Reply With Quote
Old 09-24-2019, 07:44 AM   #30
Member
 
Join Date: Mar 2019
Posts: 41
Quote:
Originally Posted by Chief55 View Post
https://inspectapedia.com/plumbing/G...Clearances.php


Check this out, 3 feet is the min distance from the natural gas or propane meter vent. Arc flash is the concern.
I should have said check out this link, it may provide additional information.
https://inspectapedia.com/plumbing/G...Clearances.php
Chief55 is offline   Reply With Quote
Old 09-24-2019, 10:25 AM   #31
Senior Member
 
Join Date: Jun 2013
Posts: 1,114
I've been a mechanical contractor for 40+ years and never knew about the 36" rule from a gas vent (don't do much residential or electrical work though) so good to know this, will be more observant.
nayther is offline   Reply With Quote
Old 09-24-2019, 11:21 AM   #32
Member
 
Join Date: Oct 2014
Posts: 87
Nice clean install.
I would urge caution on the wire size. 10/2 is a bit thin for 30 amps, depending on the length of the run. I would have suggested 8 or even 6 gauge, depending on how far from box to breaker.
dlambers is offline   Reply With Quote
Old 09-24-2019, 09:32 PM   #33
Member
 
Join Date: May 2015
Location: Cairo Georgia
Posts: 95
Voltage Drop Calculation

Quote:
Originally Posted by dlambers View Post
Nice clean install.
I would urge caution on the wire size. 10/2 is a bit thin for 30 amps, depending on the length of the run. I would have suggested 8 or even 6 gauge, depending on how far from box to breaker.
Since my power cable AND my RV extension cord are 10 gauge and the code in our neck of the woods calls for 10 AWG minimum on a 30 AMP 120v circuit, I figured 10 gauge would be good for our 30 AMP RV power connection.

I used a Voltage Drop Calculator to see if my 36 foot run of wire from the subpanel would result in a voltage drop requiring heavier wire... it did not.

I seem to remember the code page stating "no more than a 5% drop in voltage" before needing to go bigger. I would have needed nearly a 100 foot run before the drop would have been 5%, at least according to this calculator... https://www.calculator.net/voltage-drop-calculator.html
__________________
******
Dave & Cindy
2015 Flagstaff MicroLite 21FBRS Sapphire Edition
1999 Chevy Silverado 2500
campkasten is offline   Reply With Quote
Old 09-25-2019, 12:07 AM   #34
Senior Member
 
Join Date: Apr 2016
Location: Port Charlotte Fl/Hinsdale Ma
Posts: 4,823
Quote:
Originally Posted by campkasten View Post
Since my power cable AND my RV extension cord are 10 gauge and the code in our neck of the woods calls for 10 AWG minimum on a 30 AMP 120v circuit, I figured 10 gauge would be good for our 30 AMP RV power connection.

I used a Voltage Drop Calculator to see if my 36 foot run of wire from the subpanel would result in a voltage drop requiring heavier wire... it did not.

I seem to remember the code page stating "no more than a 5% drop in voltage" before needing to go bigger. I would have needed nearly a 100 foot run before the drop would have been 5%, at least according to this calculator... https://www.calculator.net/voltage-drop-calculator.html
Click image for larger version

Name:	What he said in that comment up there (1).jpg
Views:	63
Size:	17.1 KB
ID:	215771
cavie is offline   Reply With Quote
Old 09-25-2019, 05:17 AM   #35
Senior Member
 
Papadave's Avatar
 
Join Date: Sep 2018
Location: Murphy NC
Posts: 303
Good better best

Building codes are the work of committees and common sense can work better sometimes. Common sense says that the switch or plug can arc and spark light a gas leak. Conduit is for mechanical protection and water proofing. This was a good better and best tutorial on getting it right and legal. The building codes were started by insurance companies and they are happy to take premiums deny claims if you don’t cross your t’s and dot your i’s. While we sometimes say it’s good enough because we are competent the next owner of the house may be a doofus.
Papadave is offline   Reply With Quote
Old 09-25-2019, 05:42 AM   #36
Senior Member
 
Join Date: Nov 2016
Posts: 918
If someone is going to pay an electrician to install an outside box , the 50A 240V would make the most sense.

A bigger RV may or may not be in your future but there is little question some sort of electric car will be forced on all of us.

Might as well pay the electrician only once.
FFred is offline   Reply With Quote
Old 09-25-2019, 05:44 AM   #37
"On the road again"
 
rjshiflet's Avatar
 
Join Date: Feb 2012
Location: Parker County Texas
Posts: 1,152
Quote:
Originally Posted by kenandterry View Post
I’m just wondering how soon you’ll wish it was a 50 amp service box.

Just sayin’

I ran a 30-amp to our fifth wheel, and have never regretted having only 30 amp.

We can run two of our three A/C units if necessary (not using a microwave, blow dryer, curling iron, etc.)- but our main purpose in having electricity is keeping our residential fridge cold so we don't have to unload and re-load each month.
__________________


Robert & Estha Shiflet
Georgetown XL 378TS
Jeep Gladiator Willys Tow Vehicle
rjshiflet is offline   Reply With Quote
Old 09-25-2019, 06:05 PM   #38
I'm Lost
 
wabakami's Avatar
 
Join Date: Mar 2014
Location: Algonquin Provincial Park, Ontario
Posts: 1,340
Another cable that works great for home trailer plug-ins is "Teck Cable".

Developed in Kirkland Lake Ontario for the mining industry. Two, three or four conductors are standard, rated to 600v.

It is suitable for direct burial in most jurisdictions and can be laid directly across ground under certain conditions.

In Canada most cabling lists only the insulated conductors, the ground is a given unless you specify a cable without the ground conductor.

10/2 = 2 insulated and a ground. 10/3 = 3 insulated plus a ground, etc.


Geoff
.
__________________
Geoff, Francesca and Lucy the Golden holy terror (I mean retriever, BD Nov. 2018)
2023 F150 Screw, 3.5L, HDPP, LT tyres.
2013 Rockwood Signature 8310SS
2023 F150 Lariat 502A (After all rebates, price protection and dealer discounts, I saved $12,600Cdn. (Cavalcade Ford). If pays to shop dealers! (April 2023)
wabakami is offline   Reply With Quote
Old 09-27-2019, 05:44 PM   #39
Member
 
Join Date: Feb 2013
Posts: 89
Just did the same thing. Shoulda done it years ago!
Jan Gerstner. is offline   Reply With Quote
Old 09-27-2019, 09:18 PM   #40
Senior Member
 
DavidBo's Avatar
 
Join Date: Jul 2015
Location: Texas Coastal Bend
Posts: 844
Good choice to use the Liquid-Tite, much better than the metal conduit for that installation.
I do have to ask though, when you say you're using 10/2, does that mean you are running Romex in the conduit? I know local codes vary, but to my understanding nonmetallic shielded cable is for indoor use only, outdoor installations require separate insulated wires run through conduit.
Just checking...
DavidBo is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 12:28 PM.