Old 01-30-2016, 04:12 PM   #61
Senior Member
 
deartruc's Avatar
 
Join Date: Sep 2014
Location: Southern New England
Posts: 862
In my region, cg's charge more for 50amp service.
__________________
2017 GMC Yukon
2018 Roo 23 ikss
deartruc is offline   Reply With Quote
Old 01-30-2016, 05:53 PM   #62
Senior Member
 
Join Date: May 2014
Location: Halifax Nova Scotia Canada
Posts: 833
Nobody has considered that the trailer cable and wiring and main breaker is only rated for 30 amps...BE CAREFUL!!!!!!!!!!!!!!!!!!! j
Jim in Halifax is offline   Reply With Quote
Old 01-30-2016, 07:10 PM   #63
Canadian Member
 
Join Date: Feb 2012
Location: Eastern GTA, Ontario, Canada
Posts: 6,229
As a lay person, I'm a bit confused about how the RV's power cord is at risk here. I understand that if you plug a 30A cord into a 50A receptacle using the proper dogbone adapter, you don't have the extra benefit of a 30A breaker at the power pedestal, but doesn't the 30A breaker in your converter (assuming its functioning as designed) prevent the entire system (internal electrical system and external power cord) from seeing more than 30A? Is the electricity a wave coming down the power cord that hits and trips the breaker?
__________________
2023 Rockwood Signature 8262RBS
2016 Ford F-250 XLT SuperCrew, 6.2L, 4x4, 6'9" bed
2019 Rockwood Signature 8290BS (2019 - 2022)
2011 Rockwood Signature 8293SS (2015 - 2018)
2010 Rockwood Roo 23SS (2012 - 2014)

itat is offline   Reply With Quote
Old 01-30-2016, 07:26 PM   #64
Member
 
Join Date: Dec 2015
Posts: 37
There should be a 30 A breaker in the distribution panel that feeds the converter among other loads.

The issue with plugging into the 50 A socket with an adapter is that if there is a short to the return the power cable is protected at 50 A by the breaker in the box instead of 30 A as rated. Reality. is that any power cable can easily handle a short term 100% overload without damage. The real limiter on conductor size in that application is voltage drop. The issue is technical correctness per code vs what will really happen.
nothermark is offline   Reply With Quote
Old 01-31-2016, 10:52 AM   #65
Senior Member
 
Join Date: Sep 2015
Posts: 1,022
Interesting reading. Not to hijack this thread, but I was reading a thread the other day about the 30 to 50 and 50 to 30 amp adapters, and surge protectors, and it was brought up that the loss of the neutral in a 50 amp setup could cause an over voltage on either leg. Someone there was advocating using the 30 amp supply and adapting up to your 50 amp cord (if that is your setup) to protect against that. Can an expert here clarify this for me?
__________________
David and Vicki
19-month-old English Springer Spaniel "Sadie"
2019 Silverado LTZ Duramax
2023 GDRV Reflection 150 226RK
Springerdad is offline   Reply With Quote
Old 01-31-2016, 11:08 AM   #66
Senior Member
 
Join Date: Jul 2010
Location: Waynesville
Posts: 14,428
Quote:
Originally Posted by oldtool2 View Post
I just looked at the list of errors my potable surge protector has and it appears the unit is primarily a voltage monitoring device. For an over currant problem the breaker on the converter will have to trip. but, figuring in ohms law, an over currant problem could be caused by a low voltage problem tripping the surge protector. PI covers everything pretty well. They don't miss any problem that I can think of off the top of my head. They make the best affordable device I have seen.

All the trailers I have had, 5 so far, have been 30 amp units. I carry a 50 to 30 amp converter plug but I have not had to use it yet. IMO it is like insurance, a waste of money till you need it, if you ever need it. When I rolled my Jeep and trailer I was glad I had it!

Jim
There are C/G in KY and Wi that ONLY have 50A Outlets so Keep your adapter handy! Youroo!!
Attached Thumbnails
Click image for larger version

Name:	2014 fall 875.jpg
Views:	161
Size:	245.4 KB
ID:	98674  
youroo is offline   Reply With Quote
Old 01-31-2016, 11:32 AM   #67
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Quote:
Originally Posted by youroo View Post
There are C/G in KY and Wi that ONLY have 50A Outlets so Keep your adapter handy! Youroo!!

Youroo, people just won't be able to camp at those c/g's so they don't blow up their 30 amp camper.


2015 Columbus 320RS
2008 2500HD Duramax
2015 nights camped "34"
TURBS is offline   Reply With Quote
Old 01-31-2016, 11:39 AM   #68
Senior Member
 
Join Date: Jul 2010
Location: Waynesville
Posts: 14,428
Quote:
Originally Posted by TURBS View Post
Youroo, people just won't be able to camp at those c/g's so they don't blow up their 30 amp camper.


2015 Columbus 320RS
2008 2500HD Duramax
2015 nights camped "34"
Yes there is one in Bardstown,KY that is Very Close to the Bourbon Trail! This could be Devastating! Youroo!!
youroo is offline   Reply With Quote
Old 01-31-2016, 11:56 AM   #69
Senior Member
 
Wobbles's Avatar
 
Join Date: Feb 2015
Location: Southern, IL
Posts: 3,272
Quote:
Originally Posted by TURBS View Post
When In Nashville last year I was plugged into 30 amp, about noon I was down to 102 volts.
Plugged into the 50 and was back up to 112v
My recent experience.


2015 Columbus 320RS
2008 2500HD Duramax
2015 nights camped "34"
Turbs,
Did you use a 50 to 30 dog bone adapter? I am starting to read about hard wired protection vs what I plug into the post. Sheesh, it occurs to me now that I would have never been alerted to the low voltage.

__________________
Bob & Michelle
2016 Ford F-250 Lariat 4x4
2017 Flagstaff Super Lite 526RLWS
Wobbles is offline   Reply With Quote
Old 01-31-2016, 12:02 PM   #70
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
I have used a 50 to 30 adapter for 10 years.
If I find low voltage in the heat of the day on the 30 amp line I adapt to the 50


2015 Columbus 320RS
2008 2500HD Duramax
2015 nights camped "34"
TURBS is offline   Reply With Quote
Old 01-31-2016, 01:18 PM   #71
Member
 
genehorn's Avatar
 
Join Date: Nov 2015
Location: Arkansas
Posts: 53
My understanding is that the 50 amp service is 50 amp per leg.
genehorn is offline   Reply With Quote
Old 01-31-2016, 01:21 PM   #72
Senior Member
 
Swampy's Avatar
 
Join Date: Dec 2015
Posts: 241
Quote:
Originally Posted by Springerdad View Post
Interesting reading. Not to hijack this thread, but I was reading a thread the other day about the 30 to 50 and 50 to 30 amp adapters, and surge protectors, and it was brought up that the loss of the neutral in a 50 amp setup could cause an over voltage on either leg. Someone there was advocating using the 30 amp supply and adapting up to your 50 amp cord (if that is your setup) to protect against that. Can an expert here clarify this for me?
With a true 50A RV service, you have 2 - 120V, 50A services. If you measure Hot to hot , you have 240Volts, if you measure either hot to neutral, you have 120 Volts. Since all TT loads are 120Volt loads, you have the amperage on hot on one leg flowing back to the source on the neutral. If you were to have an equal current on both hot legs, the neutral current would drop to zero due to the amperage being 180 degrees out of phase. In reality, the neutral is also the reference point for measuring the voltage, so if you lose that reference point Neutral, the voltage from the reference point could be as high as the full 240 volts or as low as zero volts all depending on what is connected to the other hot leg and how poor(high the resistance) the physical connection of the neutral. You always have this risk with 120V loads working from different phases when the neutral return path is compromised. The loose neutral connection can happen in the pedestal or even from the power company providing the service.
With regaqrds to converting a 50A service to a pair of 30A, I would ask how often do you really lose the Neutral connection in the TT? Even with parallel 30 Amp cables, if the neutral is open anywhere from the
CG pedestal, all the way back to the serving transformer, you still have the risk of a lost neutral. Is the second cable worth the expense?

Jim Knoch
Swampy is offline   Reply With Quote
Old 01-31-2016, 02:06 PM   #73
Senior Member
 
Join Date: Sep 2015
Posts: 1,022
Quote:
Originally Posted by Swampy View Post
With a true 50A RV service, you have 2 - 120V, 50A services. If you measure Hot to hot , you have 240Volts, if you measure either hot to neutral, you have 120 Volts. Since all TT loads are 120Volt loads, you have the amperage on hot on one leg flowing back to the source on the neutral. If you were to have an equal current on both hot legs, the neutral current would drop to zero due to the amperage being 180 degrees out of phase. In reality, the neutral is also the reference point for measuring the voltage, so if you lose that reference point Neutral, the voltage from the reference point could be as high as the full 240 volts or as low as zero volts all depending on what is connected to the other hot leg and how poor(high the resistance) the physical connection of the neutral. You always have this risk with 120V loads working from different phases when the neutral return path is compromised. The loose neutral connection can happen in the pedestal or even from the power company providing the service.
With regaqrds to converting a 50A service to a pair of 30A, I would ask how often do you really lose the Neutral connection in the TT? Even with parallel 30 Amp cables, if the neutral is open anywhere from the
CG pedestal, all the way back to the serving transformer, you still have the risk of a lost neutral. Is the second cable worth the expense?

Jim Knoch
Thanks for your input Jim. My TT is set up for 50A service as an option for a second A/C if wanted, which we don't have, but it uses a 50A power cable. I'd set up a power supply at the house for my prior unit, which was 30A. Rather than rewire for 50A I simply bought an adapter dog bone, which works for me. So at this point, I have the option of plugging into the tower on either amp supply. I've been using the cable on the 50A side, simply because it's easier. My question was in part as to whether I have 'protection' against an over voltage caused by an open neutral by using the 30A adapter. And, like others have said, the 30A supply often looks questionable compared to the 50A supply.
__________________
David and Vicki
19-month-old English Springer Spaniel "Sadie"
2019 Silverado LTZ Duramax
2023 GDRV Reflection 150 226RK
Springerdad is offline   Reply With Quote
Old 01-31-2016, 08:04 PM   #74
jkoenig24
 
Join Date: Apr 2015
Location: Box Elder, SD (formerly NY)
Posts: 953
Quote:
Originally Posted by Springerdad View Post
Interesting reading. Not to hijack this thread, but I was reading a thread the other day about the 30 to 50 and 50 to 30 amp adapters, and surge protectors, and it was brought up that the loss of the neutral in a 50 amp setup could cause an over voltage on either leg. Someone there was advocating using the 30 amp supply and adapting up to your 50 amp cord (if that is your setup) to protect against that. Can an expert here clarify this for me?


????? How is the Neutral being "lost"??????



A 50A service has four prongs; one ground, one neutral and two legs of 50A each. The only thing that might be considered "lost" is one of the 50A legs. The ground, neutral and ONE of the 50A legs are carried over from the 50A four prong service to the 30A three prong service via the adapter / dogbone. Even though 50A are available, a rig wired for 30A is still limited and protected by the 30A master breaker.
jkoenig24 is offline   Reply With Quote
Old 01-31-2016, 08:59 PM   #75
Senior Member
 
Join Date: Oct 2015
Location: Western, MA
Posts: 430
Quote:
Originally Posted by Papa GLS View Post
You still have a 30A cord & plug ends being protected by a 50A breaker.

I plug my 28 gauge iPhone charger cord into a 20 amp circuit as do millions of others. You can plug a smaller rated cord into a larger rated circuit. It's whatever is at the end of it can draw that is the concern. If there is a breaker at the end of the cord (the RV's main) restricting the load that can hit the cord, then there is no issue no matter how big the breaker is feeding the outlet and the attached cord.
Karl4Cat is offline   Reply With Quote
Old 01-31-2016, 09:04 PM   #76
Senior Member
 
Join Date: Oct 2015
Location: Western, MA
Posts: 430
Quote:
Originally Posted by Papa GLS View Post
Your I phone charger reduces the voltage going down the cord.

OK, I have an 18 gauge cord feeding my lamp plugged into a 20 amp circuit. The example doesn't matter. Smaller gauge cords are plugged into larger circuits all over your house.
Karl4Cat is offline   Reply With Quote
Old 01-31-2016, 09:08 PM   #77
Senior Member
 
Join Date: Oct 2015
Location: Western, MA
Posts: 430
Quote:
Originally Posted by Papa GLS View Post
Install a new water heater in your house that is rated for 30A wired with #10 wire & connect it to 50A breaker. Then call for inspection & see what happens.


Plug in any lamp you buy at Walmart with smaller gauge cord than your outlet is wired with, don't call an inspector because who cares, and see what happens. Inspectors have nothing to do with what's plugged into an outlet. Only with how an outlet is wired.

Cords of a smaller gauge than the feed cable and breaker ratings of the outlets they are plugged into are all over your house. End of story.
Karl4Cat is offline   Reply With Quote
Old 01-31-2016, 09:15 PM   #78
Canadian Member
 
Join Date: Feb 2012
Location: Eastern GTA, Ontario, Canada
Posts: 6,229
Guys, I could be wrong but from what I'm reading, you're both right.

The risk with plugging your 30A cord into a 50A protected plug with a dogbone is the potential for a short along the cord and inside the RV along the main line up to the 30A breaker in your converter. Past the 30A breaker in the RV that same risk of a short still exists with smaller gauge wiring potentially being exposed to whatever amperage the individual circuit breaker will allow, usually 15A.

Maybe one of the resident electricians can confirm this?
__________________
2023 Rockwood Signature 8262RBS
2016 Ford F-250 XLT SuperCrew, 6.2L, 4x4, 6'9" bed
2019 Rockwood Signature 8290BS (2019 - 2022)
2011 Rockwood Signature 8293SS (2015 - 2018)
2010 Rockwood Roo 23SS (2012 - 2014)

itat is offline   Reply With Quote
Old 01-31-2016, 09:18 PM   #79
Senior Member
 
Join Date: Oct 2015
Location: Western, MA
Posts: 430
There is always potential of a short in a cord. Cords are very frequently not the same gauge and rating as the outlet and breaker they are plugged into. A short in a 30 amp cord will pop a 50 amp breaker. A short in a lamp cord will pop a 20 amp breaker. Shorts draw much more that the cords rating.
Karl4Cat is offline   Reply With Quote
Old 01-31-2016, 09:19 PM   #80
Senior Member
 
Join Date: Oct 2015
Location: Western, MA
Posts: 430
Quote:
Originally Posted by Papa GLS View Post
You are correct Karl4Cat. I only worked in the electrical industry for about 40 years, so I probably don't know what I'm talking about. Just trying to keep someone from damaging their plug ends or cable, that's all. Do as you will, as will I, & good luck.

I know I'm correct but thanks for confirming.

I hope you upgraded the cord sizes of all the electronics and lighting in your house because 90% of it will be below the breaker rating and cable of the outlet feeding it. Or is your concern only to the singular issue of an RV umbilical?
Karl4Cat is offline   Reply With Quote
Reply

Tags
50 amp, power

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 04:44 AM.