On a previous trailer we had to leave the door open so enough "oxygen" could get to the heater. As long as the door was open the heater would fire, close the door and it would shut off. Took it to our dealer and came back with same issue. Hopefully the dealer where we purchased our 25RR has better techs
__________________

__________________
Night_Wolf is offline   Reply With Quote
Old 01-06-2013, 05:29 AM   #12
Senior Member
 
Join Date: Apr 2012
Location: South Carolina
Posts: 1,254
I had the same problem with our water heater. I could hear the spark sanpping, but sometimes it would make three tries and time (or lock) out. Sometimes after several tries it would ignite with a bang. The flame was fine once it ignited. I removed the burner and cleaned the gas orifice with caburetor cleaner and compressed air, but that didn't help.

I put my finger over the orifice while my dearly beloved switched it on. This prevented gas from entering the burner while I looked into it. I wore a face shield just in case! The spark was weak and not consistent. I reached in with some pliers and squeezed the two electrodes a little closer. It fires on the first try now.
__________________

__________________
RamblerGuy is offline   Reply With Quote
Old 01-06-2013, 05:38 AM   #13
Senior Member
 
cpaulsen's Avatar
 
Join Date: Mar 2012
Location: Brookings
Posts: 502
Had that same problem on a previous 5ver. I checked everything and everybody told me it was the gas valve. $70.00 later....it was doing the same thing. I checked for 12 volys on the brown wire from the module board the the water heater.....only had about 7 volts. Was enough to make it click but enough to open the gas solenoids. Borrowed a friends board....plugged it in and the water heater fired right up. So...bought a new board and all the problems are solved except I have a brand new gas valve that I do not need!!
__________________
cpaulsen is offline   Reply With Quote
Old 01-06-2013, 08:42 AM   #14
Member
 
Join Date: Sep 2011
Posts: 42
had the same problom with mine just put the elecrtic sparker closer to the end of the tube and it worked fine since that it would make a big bang to light it before i moved it in closer
__________________
jkklops is offline   Reply With Quote
Old 01-06-2013, 10:21 AM   #15
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 21,158
As almost everyone stated, check for a broken or out of adjustment electrode.
I would add that the flue could be blocked with a nest of some kind (spider or wasp) causing an over rich mixture at the burner inlet.
__________________

__________________

Lou and Laura with Bella - German Short Hair Pointer
2008 GMC Sierra 2500HD Crewcab SB Allison Duramax
2010 Flagstaff 8526RLWS - Superglide 3300
HAM CALLSIGN - KC3FFW
Herk7769 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Virginia Campgrounds

Reviews provided by




ForestRiverForums.com is not in any way associated with Forest River, Inc. or its associated RV manufacturing divisions.


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -5. The time now is 02:23 PM.