12 volt wire size & type
I want to run wire for a 12 volt recepticle, and don't know what type of wire would be appropiate for this. The other 12 volt recepticle that I have in my trailer is 15 amp, so I would probably want this 1 to be also. I presume that 14 ga. wire would be the proper size, but what type of wire do I need ??
Thanks in advance.
|
|
|
02-24-2009, 05:38 PM
|
#2
|
Senior Member
Join Date: Jun 2008
Location: Chelsea, Alabama
Posts: 331
|
I would think that a 14 ga. Automotive type wire from an auto parts store would be fine.
|
|
|
02-24-2009, 05:48 PM
|
#3
|
Moderator Emeritus
Join Date: Sep 2008
Location: Shenandoah Valley of Virginia
Posts: 9,280
|
Quote:
Originally Posted by cat1956
I would think that a 14 ga. Automotive type wire from an auto parts store would be fine.
|
That was kinda what I was thinking, also. I intend to run it through the flexible automotive wiring harness conduit to protect it from rubbing on things that I can't see along it's path.
Thanks.
|
|
|
02-24-2009, 08:24 PM
|
#4
|
Senior Member
Join Date: Aug 2006
Location: Prairieville, Louisiana
Posts: 1,923
|
mtnguy,
This might help.
Click here and scroll to the bottom of the page, to WIRE GAUGE SELECTION TABLE.
|
|
|
02-24-2009, 09:37 PM
|
#5
|
Site Team
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
|
While 14 ga is correct for 15 amps but personally I'd run at least 12 and probably 10 awg. voltage drop is the biggest issue especially if your several feet from the batteries. Besides, if you run bigger than the minimum, you'll alleviate any future problems with loading.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
|
|
|
02-24-2009, 11:34 PM
|
#6
|
Senior Member
Join Date: Aug 2008
Location: Enumclaw, WA
Posts: 2,615
|
Quote:
Originally Posted by milzat
mtnguy,
This might help.
Click here and scroll to the bottom of the page, to WIRE GAUGE SELECTION TABLE.
|
AMEN and dito to this. Take a look at the table. 14ga wire is good for up to 20' of run and 18amps.
I have wired both my houses and installed a solar system, inverter and other items on our RV and have never subscribed to the "more is better" philosophy of anything, especially with wiring. Keep in mind that wires are de-rated to some extent for safety. The idea that if 14 ga is suitable then 10 must be better is just a waste of money and in a lot of cases just a really big pain in the arse as the thicker the wire the harder it is to run, both in home and automotive instances. I am also a firm believer in using the wire loom to run the wiring in on the cars and RV. It drives me nuts to see under the hood of some of my friends rigs and see wires unprotected running willie nilliy all over the place and rolled up because there was too much of it. It doesn't take all that much time to do things right.
Per the tables listed in the link above you will be fine with 14ga wire....
Good luck on your project.
|
|
|
02-25-2009, 08:36 AM
|
#7
|
CLASS "A" Senior Member
Join Date: Nov 2008
Location: Upperco, Maryland
Posts: 3,136
|
[QUOTE=NWJeeper;24894]
I am also a firm believer in using the wire loom to run the wiring in on the cars and RV. It drives me nuts to see under the hood of some of my friends rigs and see wires unprotected running willie nilliy all over the place and rolled up because there was too much of it. It doesn't take all that much time to do things right.
I couldn't agree more with you. The other thing I do is tag the wire I run so in case there's ever a problem I know exactly what I'm looking at. It eliminates quite a bit of time when you're troubleshooting a problem. I really wished the manufacturers took that extra time & effort.
__________________
2007 Georgetown 370TS
aka - RAYNMKR
Driver: Charlie
Navigator: Sheri
|
|
|
02-25-2009, 08:55 AM
|
#8
|
Moderator Emeritus
Join Date: Sep 2008
Location: Shenandoah Valley of Virginia
Posts: 9,280
|
Thanks to all for the replies. I see according to the chart for my short ~10-15 foot run that the 14 ga. should be OK, but I might just run 12 ga. as a precaution to help any voltage loss.
|
|
|
02-25-2009, 10:45 AM
|
#9
|
Senior Member
Join Date: Aug 2008
Location: Enumclaw, WA
Posts: 2,615
|
Quote:
Originally Posted by mtnguy
Thanks to all for the replies. I see according to the chart for my short ~10-15 foot run that the 14 ga. should be OK, but I might just run 12 ga. as a precaution to help any voltage loss.
|
These charts already take voltage drop into account, thus the 20ft max run for the 14ga wire at 18amps.
Cfsoistman: Good idea on the taging, it would at least be usefull to know what a particular bundle contained as far as wiring. I don't usually tend to forget my own wiring but as I get older I find myself forgetting what I got up off the couch and walked into the kitchen for so I suppose it wouldn't hurt to label my wiring jobs. With Romex it's easy, just write on the casing with a sharpie marker but 12v wiring is just too small for that.
|
|
|
|