Old 02-02-2018, 07:09 PM   #81
Senior Member
 
Join Date: Apr 2016
Location: Port Charlotte Fl/Hinsdale Ma
Posts: 4,824
Quote:
Originally Posted by Witch Doctor View Post
This is very interesting, I just talked to progressive, they said I either have to make a grounding plug or put my hard wired EMS in by-pass mode. They said that they feel it would be okay to do that, but you won't be protected on spikes. All this talk about generators on here and it has never been mentioned, now this is for a invertor generator potable generator only, so thanks aquenichet for this info, now they use to make this plug and said they stopped, you have to make your own, so back to ytube. A good y-tube on this is called testing and bonding a floating nuterial generator. how do other members handle this?..
We don't. Just forget about the grounding lug on the portable generator.

45 year Licensed Master Electrician here.
cavie is offline   Reply With Quote
Old 02-02-2018, 07:13 PM   #82
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,277
Quote:
Originally Posted by TitanMike View Post
I wouldn't obsess over the ground lug on a portable generator. For years and years these small gensets didn't have them but if they are used on a construction site, often the "OSHA" inspector will demand that the units be grounded. A jumper cable to a cold water pipe or ground rod was enough for many in days past but now some inspectors want to see a specified "ground point".

The reason to use the "jumper plug" is to provide the same ground/neutral bond that occurs in power panels for electrical equipment that requires continuity between ground and neutral. My home furnace is picky like this so when powering it during power outages I need to use my "cheater plug".

If campground posts are wired correctly the ground and neutral meet up back at the distribution panel.

On that last note, it's not a bad idea to carry a test plug that tells you if the hot and neutral are reversed or if the ground connection is bad. Considering the number of different people that plug into those posts in just a year's period of time, can you imagine the wear, tear, and abuse they get. They don't always get replaced correctly either.
Yes I have a test plug, my only thing is I want it to be line with my EMS, can t do it without, a ground or jumper, as I said only on the invertor models, no problem with open frame they are grounded to the frame. I want to know how safe it is combining a neutral bar and ground bar together, you are really taking the neutral out at that point. Also no problems with built in units they use a transfer switch that creates the ground, this is only invertor type closed generators and using your hard wired EMS. There benefits in using your EMS in line. Thanks for your help did const for 25 years understand what you are saying, but those were never invertor generators.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 02-02-2018, 07:16 PM   #83
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,277
Quote:
Originally Posted by cavie View Post
We don't. Just forget about the grounding lug on the portable generator.

45 year Licensed Master Electrician here.
Is your generator in line with a EMS? OR is it a invertor type, not apple and oranges , but thanks, my EMS will not work without the ground.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 02-02-2018, 07:47 PM   #84
Senior Member
 
Join Date: Jul 2017
Location: North of Seattle, WA
Posts: 9,835
Quote:
Originally Posted by Witch Doctor View Post
no problem with open frame they are grounded to the frame. I want to know how safe it is combining a neutral bar and ground bar together, you are really taking the neutral out at that point.

First off, I use the jumper with my inverter and no problems.

As for open frame gensets having neutral bonded, it depends. My champion 3500/4000 watt did not. Wouldn't run my high efficiency furnace in my house. A quickly applied jumper in the box at the end of my extension cord, neutral(silver) screw to ground (green) solved the problem and we had heat.

The "jumpered plug" is just a quicker way to do what I did inside the box I put on the end of my 10-3 w/ground SO cord I made an extension out of.

For all practical purposes, "neutral" is also "ground". Here in the US gensets don't seem to have their neutral's bonded while in other countries it's required.

Next time I have my inverter running (Champion 3500 watt) I'll plug in my jumper plug and see if there's any potential on exposed metal parts to an earth ground. My guess is that there won't be any more than if I was to hold the voltmeter leads, one in left and one in right hand.
__________________
"A wise man can change his mind. A fool never will."

"You only grow old when you run out of new things to do"

2018 Flagstaff Micro Lite 25BDS
2004 Nissan Titan
TitanMike is online now   Reply With Quote
Old 02-02-2018, 08:08 PM   #85
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,277
Thanks, I'm just going to make the plug up, if my voltage drops because I'm running out of gas I want the power to trailer to also stop at that point. The manual states that the connection needs to be turned off before running out of gas or damage COULD occur not covered, just good practice and safe being grounded. Thanks for your post


Sent from my SM-N920V using Forest River Forums mobile app
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 02-02-2018, 08:16 PM   #86
Senior Member
 
Join Date: Jul 2017
Location: North of Seattle, WA
Posts: 9,835
Quote:
Originally Posted by Witch Doctor View Post
Thanks, I'm just going to make the plug up, if my voltage drops because I'm running out of gas I want the power to trailer to also stop at that point. The manual states that the connection needs to be turned off before running out of gas or damage COULD occur not covered, just good practice and safe being grounded. Thanks for your post


Sent from my SM-N920V using Forest River Forums mobile app
The problems caused by running out of gas are caused by the voltage regulator in the genset/inverter having to "hunt" during that period where the motor speed drops then rises as the fuel runs out.

To prevent this I just pay more attention to my fuel consumption and time running. I'm not averse to shutting down the unit and refueling after 4-5 hours on gas (10 hours on 20# propane tank). That said, having an automatic load shutoff do the job as soon as voltage fluctuates is great.

Strangely enough, my old Champion generator had a switch that I could use to shut off the power output without shutting off the motor.

My Inverter does not. Only way to shed load is to pull the plug.
__________________
"A wise man can change his mind. A fool never will."

"You only grow old when you run out of new things to do"

2018 Flagstaff Micro Lite 25BDS
2004 Nissan Titan
TitanMike is online now   Reply With Quote
Old 04-23-2018, 08:42 PM   #87
Senior Member
 
stormer's Avatar
 
Join Date: Apr 2018
Posts: 228
Ok, I've read 9 pages of post here about generators. Thank you all for contributing. But I am still green at RVing and only had my Rockwood 2906 for a "week" as of this post.

My TT has...
50amp but runs on 30amp with adapter.
1 15k btu A/C.
1 electric/propane 9cf fridge
1 43" furion and entertainment system.
1 microwave.
multiple ipads/iphones plugged in charging.
1 appleTV
1 blueray player
1 laptop plugged in and probably an external monitor. (work)
My wife wants an electric can opener lol!
Electric / Propane water heater.
Wifi ranger

Will 2 Honda 2200 generators running parallel run everything??

Obviously the microwave will only run when needed. Shutting off A/C for a min or so is not a problem. I was almost joking about the can opener. But am I going to have any problems running the rest??



Thank you!

James
__________________
James & Aimee
----------------------------
2018 Rockwood 2906WS
2012 Ram 2500HD 6.7L Cummins
Equal-i-zer 4 Point Hitch
stormer is offline   Reply With Quote
Old 04-23-2018, 09:36 PM   #88
Senior Member
 
NMWildcat's Avatar
 
Join Date: Jun 2012
Location: Southern NM
Posts: 6,416
Quote:
Originally Posted by stormer View Post
Will 2 Honda 2200 generators running parallel run everything??

Obviously the microwave will only run when needed. Shutting off A/C for a min or so is not a problem. I was almost joking about the can opener. But am I going to have any problems running the rest??



Thank you!

James
We have 2 EU2000is that run everything just fine in our 50amp RV.

Of course there are a few caveats.

When on generator you will run everything that can be run on propane or electric, on propane. If you run the microwave/coffee pot with A/C, if the compressor kicks in, you might have a brown out or overload the gennies. So when running something like the microwave and a/c, we will put the a/c on fan only until done with the other device.

When not running the a/c, we usually only run one generator at a time and just watch what we run simultaneously.

You will be very happy with two 2200s and will learn very fast what the best practices are.
__________________
Scott and Liz - Southern NM
2012 Wildcat Sterling 32RL - w/level up (best option ever)
2007 Chevy 2500HD 4dr short bed Duramax w/allison
Reese Fifth Airborne air ride king pin coupler with Sidewinder
NMWildcat is online now   Reply With Quote
Old 04-23-2018, 11:03 PM   #89
Senior Member
 
stormer's Avatar
 
Join Date: Apr 2018
Posts: 228
Quote:
Originally Posted by NMWildcat View Post
We have 2 EU2000is that run everything just fine in our 50amp RV.
Thank you! That's what I was hoping to hear!

Quote:
Originally Posted by NMWildcat View Post
When on generator you will run everything that can be run on propane or electric, on propane.
check!

Quote:
Originally Posted by NMWildcat View Post
If you run the microwave/coffee pot with A/C, if the compressor kicks in, you might have a brown out or overload the gennies. So when running something like the microwave and a/c, we will put the a/c on fan only until done with the other device.
Makes total sense. We are ditching the coffee pot for a kerug. We only drink maybe a few cups of coffee each a day. Hadn't thought about that. I suspect since it only runs a little bit it might not be a problem, but maybe it jacks the watts also?

Quote:
Originally Posted by NMWildcat View Post
When not running the a/c, we usually only run one generator at a time and just watch what we run simultaneously.

You will be very happy with two 2200s and will learn very fast what the best practices are.
Thank you Wildcat for your reply. I'm feeling a lot better about it. I went back and forth between other brands, I'd check them out on homedepot, see they were a LOT less then I'd read the reviews and many horror stories. I looked at 7k watt gens and so on... back and forth.

I just want something that is going to work and last a long time and I don't have to give it too much thought. Maybe that is what I am paying extra for?

James
__________________
James & Aimee
----------------------------
2018 Rockwood 2906WS
2012 Ram 2500HD 6.7L Cummins
Equal-i-zer 4 Point Hitch
stormer is offline   Reply With Quote
Old 04-24-2018, 06:16 AM   #90
Senior Member
 
NMWildcat's Avatar
 
Join Date: Jun 2012
Location: Southern NM
Posts: 6,416
Quote:
Originally Posted by stormer View Post
Thank you Wildcat for your reply. I'm feeling a lot better about it. I went back and forth between other brands, I'd check them out on homedepot, see they were a LOT less then I'd read the reviews and many horror stories. I looked at 7k watt gens and so on... back and forth.

I just want something that is going to work and last a long time and I don't have to give it too much thought. Maybe that is what I am paying extra for?

James
Our two Honda Eu2000is are 11 years old. All I do is change the synthetic oil and spark plug every year. I also clean the air filter and spark arrestor screen when needed. I only use high octane fuel with StaBil added. I never worry about draining the fuel. I also ensure they are started at least once a month. We use ours frequently for weeks at a time and 24 hours a day at times during the summer. Since the Hondas have a fuel pump, it makes using our 6 gallon nurse tank easy.

Our friends that buy the cheaper options buy new generators on the average of every 2 to 3 years.

Enjoy your Honda generators!!!
Attached Thumbnails
Click image for larger version

Name:	IMG_20170307_094448.jpeg
Views:	59
Size:	142.7 KB
ID:	169411  
__________________
Scott and Liz - Southern NM
2012 Wildcat Sterling 32RL - w/level up (best option ever)
2007 Chevy 2500HD 4dr short bed Duramax w/allison
Reese Fifth Airborne air ride king pin coupler with Sidewinder
NMWildcat is online now   Reply With Quote
Old 04-24-2018, 06:40 AM   #91
Wolfpup owner
 
Join Date: Feb 2017
Location: Hendersonville,tn
Posts: 56
Thanks for asking and answering this question. I had the exact question as well but everything I ready was really complicated. Why I donít know.
nlparrott1212 is offline   Reply With Quote
Old 04-24-2018, 07:33 AM   #92
Member
 
Join Date: Apr 2018
Posts: 80
Quote:
Originally Posted by NMWildcat View Post
Since the Hondas have a fuel pump, it makes using our 6 gallon nurse tank easy.
Where did you get the nurse tank and fuel hose set up?
__________________
"Never forget the trip is as important as the destination"

2014 Ram 3500 Laramie 4X4 CTD
2011 Dutchmen Denali 262 RLX
DRogers is offline   Reply With Quote
Old 04-24-2018, 08:34 AM   #93
Senior Member
 
stormer's Avatar
 
Join Date: Apr 2018
Posts: 228
Quote:
Originally Posted by NMWildcat View Post
Our two Honda Eu2000is are 11 years old. All I do is change the synthetic oil and spark plug every year. I also clean the air filter and spark arrestor screen when needed. I only use high octane fuel with StaBil added. I never worry about draining the fuel. I also ensure they are started at least once a month. We use ours frequently for weeks at a time and 24 hours a day at times during the summer. Since the Hondas have a fuel pump, it makes using our 6 gallon nurse tank easy.

Our friends that buy the cheaper options buy new generators on the average of every 2 to 3 years.

Enjoy your Honda generators!!!
Wow, that is a sweat setup! Thanks again, bookmarking this page.

The longevity testimonials/reviews I have read is what pushed me to the hondas over the others.

James
__________________
James & Aimee
----------------------------
2018 Rockwood 2906WS
2012 Ram 2500HD 6.7L Cummins
Equal-i-zer 4 Point Hitch
stormer is offline   Reply With Quote
Old 04-24-2018, 09:58 AM   #94
Senior Member
 
NMWildcat's Avatar
 
Join Date: Jun 2012
Location: Southern NM
Posts: 6,416
Quote:
Originally Posted by DRogers View Post
Where did you get the nurse tank and fuel hose set up?
You can buy them from several places similar to this one: http://www.genxdirect.com/b-e-r-g-s/...t-hnd1-2000id/

Or you can do I like I did and just buy a marine tank, a kit that has parts to replace the vent in the generator fuel caps with a straight through nipple, some 1/8" fuel line, and valves to shut off one side or the other. I just use little drip irrigation valves. Much cheaper route. I do have to replace the fuel line and valves about every three years due to wear and tear from connecting/disconnecting.
__________________
Scott and Liz - Southern NM
2012 Wildcat Sterling 32RL - w/level up (best option ever)
2007 Chevy 2500HD 4dr short bed Duramax w/allison
Reese Fifth Airborne air ride king pin coupler with Sidewinder
NMWildcat is online now   Reply With Quote
Old 04-24-2018, 09:58 AM   #95
Senior Member
 
Join Date: Oct 2015
Posts: 1,502
The only benefit I see with two generators is less weight. However, most 3kw generators have handles and wheels and are fairly easy to move around.

2 generators in parallel

Pros:
Weight
You can run one genny when you need less power which is basically anytime air conditioning isn't running
If a genny fails, you have a backup.
At same load, I think parallel gennies are running slightly quieter in parallel then a single larger genny.

Cons:
Smaller ones do not have remote control for remote electric start/shutdown
Pull start-I have a bad shoulder
Twice the maintenance. Oil changes on some of these smaller gennies are messy
Need to refuel two gennies instead of one


Yes, we get it Honda and Yamaha are the gold standard.

With that said, not everybody has a budget for a "Mercedes" but a Hyundai is in their budget.

Champion generators have a great initial warranty and have a solid reputation. Predator generators appear to have a very good initial reputation and are simply rebadged generators that are very common.


My much maligned Boliy generator ran perfectly fine until a fuel line popped loose or split (not 100% sure) which lead to a nasty fire. I'll be replacing my fuel lines every 5 years and checking fuel clamps regularly especially when I replace the fuel filter annually (or install one if there isn't one). My Boliy was about 7 years old with over 2000 hours of use on it. I track my generator usage hours for maintenance and longeivity. Saying my Honda is 11 years old tells me nothing if it is only used 2-3 times a summer for a couple of hours a day.

A tip I found that really helps extend the life of air cooled "splash" lubricated 4 stroke engines is to add about 1.5 oz of low ash 2 stroke oil per gallon of fuel. This is particularly important if you use a gasoline with ethanol. This improves cylinder wall lubricity a tad and should extend service life. Don't worry, spark plugs won't foul with such little oil.

I'm a strong advocate of Champion generators. Mine has been rock solid since I bought it last year. However, in the interest of full disclosure, it doesn't get run very much as my solar takes care of everything but air conditioning and ac use is minimal where we camp. I use my champion more at home in my garage when I don't want to dig out and unroll a long extension cord to power my air compressor for filling my RV tires on the street.
Skyliner is offline   Reply With Quote
Old 04-24-2018, 03:19 PM   #96
Junior Member
 
Join Date: Jan 2018
Location: Greenville, IL
Posts: 5
Thanks so much for taking the time to answer my question so completely.
__________________
2013 Flagstaff 27RLWS
2014 Lincoln Navigator
Husky Centerline WDH
Cary649 is offline   Reply With Quote
Old 04-24-2018, 03:38 PM   #97
...far N Georgia!
 
formerFR's Avatar
 
Join Date: Jan 2017
Location: Hiawassee, GA!
Posts: 3,179
since you're a 'newbie'... or so, here's some additional questions for all your 'lectrical needs : )

- how many batteries does the coach come with, and are they 6v or 12v?

- does your coach come with an Inverter? (provides 120v power from the batteries)
formerFR is offline   Reply With Quote
Old 04-25-2018, 07:01 AM   #98
Member
 
Join Date: Apr 2018
Posts: 80
Quote:
Originally Posted by Skyliner View Post
Saying my Honda is 11 years old tells me nothing if it is only used 2-3 times a summer for a couple of hours a day.

Quote:
Originally Posted by NMWildcat View Post
Our two Honda Eu2000is are 11 years old. We use ours frequently for weeks at a time and 24 hours a day at times during the summer. Since the Hondas have a fuel pump, it makes using our 6 gallon nurse tank easy.


I think he did say how much he used them in those eleven years, just didn't give actual total hours
__________________
"Never forget the trip is as important as the destination"

2014 Ram 3500 Laramie 4X4 CTD
2011 Dutchmen Denali 262 RLX
DRogers is offline   Reply With Quote
Old 04-25-2018, 07:21 AM   #99
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,277
Quote:
Originally Posted by DRogers View Post
I think he did say how much he used them in those eleven years, just didn't give actual total hours
I agree 24/7 for weeks at a time tells me something
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 04-25-2018, 09:46 AM   #100
Senior Member
 
NMWildcat's Avatar
 
Join Date: Jun 2012
Location: Southern NM
Posts: 6,416
Quote:
Originally Posted by Skyliner View Post
My Boliy was about 7 years old with over 2000 hours of use on it. I track my generator usage hours for maintenance and longeivity. Saying my Honda is 11 years old tells me nothing if it is only used 2-3 times a summer for a couple of hours a day.
Ah. Ok. Unless folks install an hour meter on these smaller inverter generators, any hour usage statement is a SWAG.

But seeing as how you are so interested, I'll give it a shot

We boondock most of the time, and in the Southwest we RV every month of the year. AVG run time per day is 5 hours unless it's summer. We try to use hookups in the summer due to the heat, but always have at least a couple of trips where we run both generators 24 hours a day.

Before retirement, estimating only boondock trips, I get about 400 hours a year for 8 years. Now most of that is split between the 2 EU2000is, so roughly 1600 hours per generator.

After retirement, it has at least doubled, so 800 hours for 3 years is about 1200 hours per generator.

Grand total of an estimated 2800 hours per generator over 11 years. Again.... a SWAG.

After playing with these numbers, appears I change the oil/plugs about every 200 hours which is double the recommended, but it is synthetic so I figure I'm good. Plus the oil always looks good coming out (not too dark and smells ok). Spark plugs are always clean.

I was getting concerned about the lifetime of Honda 2000s until I read posts of folks in Alaska and on sail boats, using them for 10,000 to 20,000 hours. So I should easily have at least another 11 years on these!
__________________
Scott and Liz - Southern NM
2012 Wildcat Sterling 32RL - w/level up (best option ever)
2007 Chevy 2500HD 4dr short bed Duramax w/allison
Reese Fifth Airborne air ride king pin coupler with Sidewinder
NMWildcat is online now   Reply With Quote
Reply

Tags
inverter, service

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 10:29 PM.