Old 11-10-2015, 07:05 AM   #1
Member
 
Join Date: Oct 2015
Posts: 45
FR Toyhauler 377v furnace ?

Not sure what model furnace I have -- not sure where to find that yet, but it doesn't appear to be working properly.

It's pretty cold here in Colorado, and it was freezing in the RV last night -- and this morning! It just doesn't seem to be kicking on. I turned the heat off and back on and it came on and then went back off.

Hubby thought he would "kickstart" it by turning it to Fan mode and then to heat, but now it appears to be stuck in Fan mode, I think, because when I turn it to Furnace, cool air comes out both heater and a/c vents.

In either case, and as an added note, when it's gotten cold before and the heater doesn't kick on at night, something seems to happen around mid morning when it warms up a bit because it will typically kick on with warm air.

Any suggestions on what I could be looking at here as a problem?

TIA!
whisperwhillow is offline   Reply With Quote
Old 11-10-2015, 11:48 AM   #2
Member
 
Join Date: Oct 2015
Posts: 45
So I filled up on propane; hooked it up and turned it on, of course; turned on the stove to bleed the lines a bit and make sure I had propane going through the lines; turned on the heat again. While heat comes out of the heater vents now, it's still pumping air (not sure if it's a/c or not because the air is chilly as it is) through the a/c vents.

I have turned it off and on many times; I have even taken the fuse out to reset the furnace. Still doing the same thing.

Suggestions?
whisperwhillow is offline   Reply With Quote
Old 11-10-2015, 11:59 AM   #3
Member
 
Join Date: Oct 2015
Posts: 45
Well, this is embarrassing... Not a problem that I'm the only one responding to my inquiry lol, but I figured it out! The fan setting on the thermostat has to be set to auto to only run the furnace.

Whoever powers that be can mark this as closed.

Thanks for being a sounding board, FR forums! Till next time, happy (and warm!) camping!
whisperwhillow is offline   Reply With Quote
Old 11-10-2015, 12:08 PM   #4
Senior Member
 
knockando's Avatar
 
Join Date: May 2015
Posts: 105
We've nearly had this exact issue all Fall on a Suburban furnace.

As for the air coming out of the AC vents make sure the Fan mode is turned to Auto. That should stop the air from coming out of the AC vents.

Our furnace seems to stop igniting (kicks on, fan runs for about 20-30 sec and then shuts off) when it gets a bit colder out. From what I can tell around < 38 deg F. When it warms up mid-morning > 38 the furnace operates properly. I believe I've isolated the issue to either the LP tank or the dual-stage regulator. I replaced the dual-stage regulator and we still had the issue.

From additional reading we think our LP tank tank has moisture in it causing the regulator to "freeze" up when it gets to a lower temperature. I have not gone any further but two things I've read:
- Have an LP company perform a purge of the tank to rid the moisture
- Someone suggested putting a heating blanket or something similar on the tank/regulator to prevent the freezing.

These comments come from experience and not an expertise so take them as you wish.
knockando is offline   Reply With Quote
Old 11-10-2015, 12:18 PM   #5
Member
 
Join Date: Oct 2015
Posts: 45
Wow, a lot of trial and error it seems! Thank you for the tips. If this continues, I'll definitely look into the purge or the blanket to see if it helps. Best of luck!
whisperwhillow is offline   Reply With Quote
Old 11-10-2015, 02:37 PM   #6
Senior Member
 
knockando's Avatar
 
Join Date: May 2015
Posts: 105
Yes, 6 month old doesn't sleep to well when it's 50 in the camper

The piece that doesn't make sense is that the gas stove seems to be working fine during the issues with the furnace. I've also tried shutting off the gas at the tank, bleeding the line through the stove and then SLOWLY turning the gas back on. This only works sometimes. I've heard the furnaces are much more picky with gas pressure, etc. when attempting to ignite than stoves/fridges.
knockando is offline   Reply With Quote
Old 11-10-2015, 06:10 PM   #7
TGR
Senior Member
 
TGR's Avatar
 
Join Date: Apr 2014
Location: Twin Cities, Minnesota
Posts: 320
I too had furnace issues this weekend. My problem appears to be one of the LP tank regulators. I fixed my problem by moving my full tank to the other side of the RV, replacing the empty tank on that side and selecting the relocated tank for propane.


My stove worked and so did my water heater but the furnace would cycle through the 3-strike futility circuit and shut down. I could feel and hear the burners start but then go out. I also noticed a problem when I tried my water heater. The flame roared like I expected but I also heard some sputtering of the flame. When I exchanged my LP tanks all was well.


Apparently, there was enough gas pressure to run the water heater, albeit, with a sputtering sound, but not enough volume to run the furnace. If you are still having furnace problems, consider trying the fix I needed to get through the weekend.
__________________
2015 Wildcat 282 RKX
2011 F350 Lariat, 6.7 L. Diesel, 8 ft., SRW, Reese R20
TGR is offline   Reply With Quote
Old 11-16-2015, 05:22 PM   #8
Summer2Go
 
Summer2Go's Avatar
 
Join Date: May 2014
Location: NW New Jersey
Posts: 652
I have not really used the furnace yet. I tried to warm up the camper to clean, turned on a burner, and turned on the thermostat. Got cold air blowing like crazy. Then I smelled gas, so I turned it all off. Do you smell gas?


Sent from my iPad using Forest River Forums
Summer2Go is offline   Reply With Quote
Old 11-16-2015, 06:07 PM   #9
TGR
Senior Member
 
TGR's Avatar
 
Join Date: Apr 2014
Location: Twin Cities, Minnesota
Posts: 320
Standing outside, next to the furnace, I could hear the igniter clicking and the flame start. There was also heat coming from the furnace exhaust for a brief time but then the heat stopped and only cold air came from the furnace exhaust. I could smell propane but only slightly.


Again, moving the full bottle to the other side fixed my problem for he night. I haven't investigated further.
__________________
2015 Wildcat 282 RKX
2011 F350 Lariat, 6.7 L. Diesel, 8 ft., SRW, Reese R20
TGR is offline   Reply With Quote
Old 11-19-2015, 03:45 PM   #10
TGR
Senior Member
 
TGR's Avatar
 
Join Date: Apr 2014
Location: Twin Cities, Minnesota
Posts: 320
I filled my empty tank and with warmer weather, my furnace works fine from either thank.

My guess is that one of my regulators was malfunctioning because water vapor froze and messed up my LP regulator or partially clogged my line from the one tank. The warmer weather melted the frost and all seems normal now.

I won't be using my trailer any more this year but if the problem reoccurs, I'll try purging my tanks or have methanol added.
__________________
2015 Wildcat 282 RKX
2011 F350 Lariat, 6.7 L. Diesel, 8 ft., SRW, Reese R20
TGR is offline   Reply With Quote
Reply

Tags
furnace


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 11:04 PM.