Old 11-04-2015, 11:15 AM   #1
Member
 
Motodad's Avatar
 
Join Date: Jul 2015
Posts: 50
Generator capabilities

Does anyone know if the Onan 8000 will safely run 2 -1500btu units and 1 -13500btu unit all at the same time? I am defiantly fixing to add a 3rd Ac to my 390bh berk.
Thanks
Motodad is offline   Reply With Quote
Old 11-04-2015, 05:24 PM   #2
Senior Member
 
gasman94's Avatar
 
Join Date: Oct 2012
Location: Southwestern Mi
Posts: 1,242
Don't really know the answer, but my guess would be no. Info that I found from dometic ac units called for minimum 3.5kw for one unit or 5kw for two. Logical ( or illogical) progression from this would seem to be minimum of 6.5-7kw for the third unit....although I don't know if it works this way. If that is the case, I think that you are not really leaving much reserve for the rest of the coach. Here is my reference
Dometic B59516 Brisk II RV Air Conditioner 15,000 BTU White

Also, what are the size generators in other coaches with 3 ac units?


Rich
gasman94 is offline   Reply With Quote
Old 11-04-2015, 05:41 PM   #3
Senior Member
 
Join Date: Feb 2015
Posts: 741
Charlestons have 10kw


Paul
Paulie Boy is offline   Reply With Quote
Old 11-04-2015, 05:57 PM   #4
Senior Member
 
Bluepill's Avatar
 
Join Date: Jun 2015
Location: Pensacola, FL
Posts: 1,645
The running watts of all three would be a bit under 6KW. The problem is the high starting current when they switch on. Really marginal, IMO.

Since you tow with a truck, maybe a nice Honda 3KW inverter genny in the bed of the truck. Just run one of the A/C units off of that. It also serves as a back-up if you Onan is out of service.

If Santa owes you a really swell present this year, you can always ask for the new Honda 7KW fuel injected baby.
__________________
2019 Coachmen Freedom Express 192RBS
2015 T12RBST Flagstaff Hardside

Disclaimer: The actual value of my "Two Cents" of advice varies just like a bitcoin.
Bluepill is offline   Reply With Quote
Old 11-04-2015, 06:28 PM   #5
Senior Member
 
B and B's Avatar
 
Join Date: Jun 2013
Posts: 10,833
Send a message via AIM to B and B
It is the start up current that will trip the breaker. Turn on 1, lock it on by setting temp really low, turn on the next one, lock it on as well then finally the third one. If they all stay running and don't cycle you have enough power to run them. The inrush, or start current is the issue. Shed other load like HW Heater for example and fridge if it can run on invertor or propane. Charge batteries when on shore power.
__________________
B and B
2022 Venture RV SportTrek STT 302 VRB Travel Trailer
2018 Heartland Landmark 365 Louisville 5th Wheel
2015 Heartland Bighorn 5th Wheel
2013 FR Rockwood 8289WS 5th Wheel
2012 FR Rockwood 2703 SS Travel Trailer
B and B is offline   Reply With Quote
Old 11-04-2015, 07:01 PM   #6
Senior Member
 
Join Date: Apr 2012
Location: West Michigan/Fort Myers
Posts: 3,927
Quote:
Originally Posted by Bluepill View Post
The running watts of all three would be a bit under 6KW. The problem is the high starting current when they switch on. Really marginal, IMO.

Since you tow with a truck, maybe a nice Honda 3KW inverter genny in the bed of the truck. Just run one of the A/C units off of that. It also serves as a back-up if you Onan is out of service.

If Santa owes you a really swell present this year, you can always ask for the new Honda 7KW fuel injected baby.

He drags the truck behind him. It's a Moho.



Phil57 is offline   Reply With Quote
Old 11-04-2015, 07:04 PM   #7
Senior Member
 
Join Date: Apr 2012
Location: West Michigan/Fort Myers
Posts: 3,927
I don't think you will have a propels with it. I'm sure someone will do the math but there have been people that have added a third A/C and had no issue. With no WH the biggest drain will be the microwave and the fridge. It should be fine.



Phil57 is offline   Reply With Quote
Old 11-04-2015, 09:09 PM   #8
Senior Member
 
Joker's Avatar
 
Join Date: Mar 2011
Location: Colorado
Posts: 192
I run a 15 and a 13.5 routinely. I have accidentally turned on the third and the breaker hasn't tripped. However, if three are running and are cycling and two try to come on at the same time, I'd bet the breaker will trip.

Also, that will be putting some 'hard time' on your generator...running at higher loads and thus RPMs like that.

I just close up the rear sleeping area and just run the front two plus the chassis A/C. It keeps us plenty cool on our June/July drives from Colorado to Florida and back.
Joker is offline   Reply With Quote
Old 11-04-2015, 09:51 PM   #9
Senior Member
 
Join Date: Apr 2012
Location: West Michigan/Fort Myers
Posts: 3,927
Quote:
Originally Posted by Joker View Post
I run a 15 and a 13.5 routinely. I have accidentally turned on the third and the breaker hasn't tripped. However, if three are running and are cycling and two try to come on at the same time, I'd bet the breaker will trip.

Also, that will be putting some 'hard time' on your generator...running at higher loads and thus RPMs like that.

I just close up the rear sleeping area and just run the front two plus the chassis A/C. It keeps us plenty cool on our June/July drives from Colorado to Florida and back.

Did you ever install a vent to replace the one you used for your third A/C?
Also how do you control the third AC? Is it run through the same thermostat? Also if hooked up to a campground do you ever have low voltage issues. Do you run a Auto Former? ( not sure that's correct or spelled right)



Phil57 is offline   Reply With Quote
Old 11-04-2015, 10:02 PM   #10
Senior Member
 
dan-nickie's Avatar
 
Join Date: Feb 2014
Location: Dallas TX
Posts: 1,675
Joker, did you add a third air conditioner after you bought the rig? If you did please tell us about it. There have been several discussions on if and how it would be done.
__________________
Dan
2014 Berkshire 390RB-60
dan-nickie is offline   Reply With Quote
Old 11-04-2015, 11:26 PM   #11
Member
 
Motodad's Avatar
 
Join Date: Jul 2015
Posts: 50
My dealer said it can be done. They will install a shed switch. It will go where the vent is in the kitchen area. It will have controls on the unit itself. I will post more as I learn. It's gonna be a few weeks before they can get to. Thanks guys for all the input. I will probably only run front 2 units most of the hot days and turn one off to turn the bedroom Ac on when it gets close to bed time. It's just really hard to keep the living room area cool durn tx Summer's with no shade. Thanks again
Motodad is offline   Reply With Quote
Old 11-04-2015, 11:57 PM   #12
Senior Member
 
Joker's Avatar
 
Join Date: Mar 2011
Location: Colorado
Posts: 192
Yes, I had a new vent installed over the kitchen area to make up for the one that was filled in by the AC. I believe it's a safety requirement to have a vent in there since we have propane stoves. If you're having a new vent installed there, see if they can use the existing control wires from the old vent to operate the unit from the wall. Also, they may be able to salvage the old vent.

Mine is controlled off the existing thermostat. It has ability to control up to 4 units.

If you're having it done, consider having them add a heat strip too. It's easy to do while they're already working on the unit. Although mostly I just use a little ceramic unit that keeps that area warm enough.

I have tripped the pedestal breaker at Fort Wilderness a couple of times trying to run three ACs or two ACs and the vacuum. Oops. I can't remember tripping it anywhere else.

I think you want to make sure the front two ACs are on separate 'legs' of your power system so that you can run both at once.

I don't know what an autoformer is.
Joker is offline   Reply With Quote
Old 11-05-2015, 07:59 AM   #13
Senior Member
 
gasman94's Avatar
 
Join Date: Oct 2012
Location: Southwestern Mi
Posts: 1,242
Quote:
Originally Posted by Phil57 View Post
Did you ever install a vent to replace the one you used for your third A/C?
Also how do you control the third AC? Is it run through the same thermostat? Also if hooked up to a campground do you ever have low voltage issues. Do you run a Auto Former? ( not sure that's correct or spelled right)

Phil, if we're talking about this issue in the context of whether the genny would be ok for 3 ac's, I see where you're going with the autoformer. But, at least with my setup, autoformer is connected to boost shore power only.



Rich
gasman94 is offline   Reply With Quote
Old 11-05-2015, 08:03 AM   #14
Senior Member
 
OntarioFireFighter's Avatar
 
Join Date: Jan 2015
Location: Ontario, Canada
Posts: 175
Adding soft-start capacitors (sometimes called a hard-start kit) would really drop the inrush current; and that's where your biggest issue would be...

Since they'll be working on the unit, adding the cap's should be no big deal.
__________________
2014 Grey Wolf 28BH, behind a 2015 F350 Diesel Crew Cab

Nights Camped 2016: 44

Nights Booked 2017: 11
Nights Camped 2017: 6
OntarioFireFighter is offline   Reply With Quote
Old 11-06-2015, 07:30 PM   #15
Senior Member
 
JTN8's Avatar
 
Join Date: May 2013
Location: Virginia
Posts: 619
I have two 15k's and plugged my buddy's RV into the engine block heater outlet in the electrical bay while dry camping at NASCAR races and ran both my AC's and he ran his while plugged into my coach and I've never had an issue blowing any CB's. We also had the TV's going, lights etc...

Jason
JTN8 is offline   Reply With Quote
Old 11-06-2015, 10:47 PM   #16
Senior Member
 
Join Date: Oct 2011
Location: Alberta Canada
Posts: 440
I would check the the engineers at FR before installing a third AC unit. I had talked to them a few years ago when I looked a pitting a third on our 2012 390BH60. I was told in no uncertain terms that the unit was not designed for 3 AC both from a power and structural perspective.

You are much better off spending some time to limit heat coming into the unit.

Insulated and reflective covering on windshield. Awning and vertical covers to name a couple.

Over cooling at night will also make a huge difference. 2 15s will maintain the cool over the course of the day but they may struggle to drop temperature if the ambient temp is high.
lefaivre is offline   Reply With Quote
Old 11-06-2015, 11:21 PM   #17
Senior Member
 
Join Date: Apr 2012
Location: West Michigan/Fort Myers
Posts: 3,927
Quote:
Originally Posted by lefaivre View Post
I would check the the engineers at FR before installing a third AC unit. I had talked to them a few years ago when I looked a pitting a third on our 2012 390BH60. I was told in no uncertain terms that the unit was not designed for 3 AC both from a power and structural perspective.

You are much better off spending some time to limit heat coming into the unit.

Insulated and reflective covering on windshield. Awning and vertical covers to name a couple.

Over cooling at night will also make a huge difference. 2 15s will maintain the cool over the course of the day but they may struggle to drop temperature if the ambient temp is high.

I don't disagree and I'm not ready to add a third yet. I will say after the last few weeks in South Florida in 90 degree plus that two 13.5 AC's are falling short. I can get the Moho cool to a point. When it's 95 and the sun is out I can get the inside down to about 78-80. It's better than 95 but still a bit warm. With out the sun I do better. I do have a windshield cover a driver side window cover. A door cover. All slide out windows have covers as well as window awnings on the two living room windows and the bedroom window. The covers a Magna Shade and are of excellent material.
The heat transfer in the front is bad. It's amazing how hot the cupboards are. The insulation in the front and rear caps is not working. I would love to see what is in there.



Phil57 is offline   Reply With Quote
Old 11-07-2015, 12:09 PM   #18
Junior Member
 
Join Date: Jun 2011
Posts: 17
For anyone interested I have a 13,500 heat pump in a box on a pallet ready to ship. It will be a steal to get it out of my garage.
Just thought I would give it a shot since it was on topic :-)
JMosley33 is offline   Reply With Quote
Old 11-07-2015, 05:39 PM   #19
Senior Member
 
Join Date: Mar 2014
Posts: 277
In Arizona the heat is bad... I have (2) 13.5's and all the magnashades etc. I added a standalone 8k Ac that ducts to the exterior out the drivers window. Still not enough in my option for Az. Also looking to add 3rd Ac but still thinking of it...


Sent from my iPhone using Forest River Forums
__________________
Jc
2014 400BH-60
jcowles3 is offline   Reply With Quote
Old 11-07-2015, 06:11 PM   #20
Junior Member
 
Join Date: Jun 2011
Posts: 17
Well I have a near new (used less than 5 times) Penguin II 13,500 btu A/C heatpump in the factory box ready to ship and for sale.
JMosley33 is offline   Reply With Quote
Reply

Tags
generator

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 10:36 AM.