Sequence of events

So I'm plugged into 110 shore, since it's getting warm in SoCal, I wanted to run AC's for awhile and it gives me a chance to exercise my generator. My question is, do I have to always shut off the fridge, unplug the shore power and then start the generator and then turn the fridge back on?
__________________
Ben & Michelle
2015 Berkshire 38A
2005 Jeep Wrangler toad
tnbendr is offline   Reply With Quote
Old 05-29-2015, 01:35 PM   #2
Senior Member
 
bubbles's Avatar
 
Join Date: Dec 2012
Posts: 7,652
No.
bubbles is offline   Reply With Quote
Old 05-29-2015, 01:43 PM   #3
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
True "no"
But who told you that you should?

TURBS
08 duramax tuned n modded
2011 32bhok Sabre
2015 camping "9 nights"
TURBS is offline   Reply With Quote
Old 05-29-2015, 01:50 PM   #4
Senior Member
 
Join Date: Dec 2012
Posts: 1,255
If you are unplugging THEN starting your genset you don't need to do anything. It's only when you stay plugged in AND start up your genset that you want to shut off any heavy loads.

It minimizes the chance of arcing in your transfer switch when it flips over from shore to genset... or vica versa. If you're only applying power one at a time it's a moot point.
rana is offline   Reply With Quote
Old 05-29-2015, 02:06 PM   #5
Senior Member
 
tnbendr's Avatar
 
Join Date: May 2015
Location: In our coach
Posts: 232
Quote:
Originally Posted by Yarome View Post
If you are unplugging THEN starting your genset you don't need to do anything. It's only when you stay plugged in AND start up your genset that you want to shut off any heavy loads.

It minimizes the chance of arcing in your transfer switch when it flips over from shore to genset... or vica versa. If you're only applying power one at a time it's a moot point.
I am not unplugging the shore and the only thing on is fridge, is that considered a heavy load?
__________________
Ben & Michelle
2015 Berkshire 38A
2005 Jeep Wrangler toad
tnbendr is offline   Reply With Quote
Old 05-29-2015, 02:11 PM   #6
Senior Member
 
dan-nickie's Avatar
 
Join Date: Feb 2014
Location: Dallas TX
Posts: 1,675
Quote:
Originally Posted by tnbendr View Post
I am not unplugging the shore and the only thing on is fridge, is that considered a heavy load?
Not to me. I consider the fridge a low power draw item.
I just turn off the Air Conditioners, then start up the generator with the shore power plugged in.
__________________
Dan
2014 Berkshire 390RB-60
dan-nickie is offline   Reply With Quote
Old 05-29-2015, 02:15 PM   #7
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Fridge draws under 5 amps.
A/c, microwave and water heater on electric would be high draws amps

TURBS
08 duramax tuned n modded
2011 32bhok Sabre
2015 camping "9 nights"
TURBS is offline   Reply With Quote
Old 05-29-2015, 02:21 PM   #8
Senior Member
 
Join Date: Dec 2012
Posts: 1,255
Quote:
Originally Posted by tnbendr View Post
I am not unplugging the shore and the only thing on is fridge, is that considered a heavy load?
Oops.. sorry. Thought you were unplugging, but it was part of the question. My bad.

What Dan and Turbs said... but also consider cumulative loads when switching electrical sources.

rana is offline   Reply With Quote
Old 05-29-2015, 03:25 PM   #9
Berkshire 390QS
 
NO3putt's Avatar
 
Join Date: Feb 2011
Location: Colorado
Posts: 1,489
We always unplug from shore power when starting generator, easyier on the ATS and make sure ACs are off.
__________________
2011: 54 days, 2012: 218 days, 2013: 175 days, 2014: 196 days
2015: 188 days, 2016: 72 days, 2017: 185 days: 2018 182 days
2019: 156 days (2009 Berkshire, 390QS, and toad)
NO3putt is offline   Reply With Quote
Old 05-29-2015, 03:44 PM   #10
Senior Member
 
tnbendr's Avatar
 
Join Date: May 2015
Location: In our coach
Posts: 232
Thanks all! Just trying to get familiar with all the nuances...this forum and you guys have been a great help so far and one day I'll be able to advise a newbie!
__________________
Ben & Michelle
2015 Berkshire 38A
2005 Jeep Wrangler toad
tnbendr is offline   Reply With Quote
Old 05-29-2015, 05:08 PM   #11
Senior Member
 
Campin Cajun's Avatar
 
Join Date: Mar 2013
Location: Cut Off, La.
Posts: 1,830
It's also a good idea to let the generator run for a few minutes before putting a load on it. This allows any dampness to dry up before the load is applied. And also allows the gen to warm up.

This step isn't written in any book or manual. I live in the south in very humid conditions and it's the way I've been taught when bringing any genset online.
__________________
2013 Berkshire 390BH
Campin Cajun is offline   Reply With Quote
Old 05-29-2015, 05:31 PM   #12
Senior Member
 
Join Date: Apr 2012
Location: West Michigan/Fort Myers
Posts: 3,927
Quote:
Originally Posted by Campin Cajun View Post
It's also a good idea to let the generator run for a few minutes before putting a load on it. This allows any dampness to dry up before the load is applied. And also allows the gen to warm up.

This step isn't written in any book or manual. I live in the south in very humid conditions and it's the way I've been taught when bringing any genset online.

Great advice. I've had mine stall out by putting a load in it before it's warmed up. It restarts with a big puff of black smoke. It can't be good for it. I learned to wait.



Phil57 is offline   Reply With Quote
Old 05-29-2015, 05:42 PM   #13
Senior Member
 
tnbendr's Avatar
 
Join Date: May 2015
Location: In our coach
Posts: 232
Quote:
Originally Posted by Campin Cajun View Post
It's also a good idea to let the generator run for a few minutes before putting a load on it. This allows any dampness to dry up before the load is applied. And also allows the gen to warm up.

This step isn't written in any book or manual. I live in the south in very humid conditions and it's the way I've been taught when bringing any genset online.
I did consciously wait (either common sense or dumb luck) before turning the AC's on.
__________________
Ben & Michelle
2015 Berkshire 38A
2005 Jeep Wrangler toad
tnbendr is offline   Reply With Quote
Old 05-30-2015, 07:42 AM   #14
Senior Member
 
I-RV's Avatar
 
Join Date: Jun 2013
Location: Mount Laurel, NJ
Posts: 1,024
tnbendr If your shore line has enough amperage to run your AC's, then why start the generator. If your shoreline is insufficient, then it makes sense to start the generator. But once the generator is running, everything will be on the generator. The shoreline will be not used. X2 to the suggestions of shedding the load when the generator is started.
__________________
Gale & Hank- 2012 Berkshire 390BH
I-RV is offline   Reply With Quote
Old 05-30-2015, 11:55 AM   #15
Senior Member
 
dan-nickie's Avatar
 
Join Date: Feb 2014
Location: Dallas TX
Posts: 1,675
I believe he said because he wants to exercise his generator while parked.
__________________
Dan
2014 Berkshire 390RB-60
dan-nickie is offline   Reply With Quote
Old 05-30-2015, 12:37 PM   #16
Senior Member
 
ernest917's Avatar
 
Join Date: Jun 2011
Location: On Another Adventure
Posts: 2,563
I always turn off AC then UNPLUG, start gen and wait for the " beep " then fire up AC 's.... Rather be safe than sorry ... Have had multiple techs tell me that's the safest way....


Sent from my iPhone using Forest River Forums
ernest917 is offline   Reply With Quote
Old 05-30-2015, 01:00 PM   #17
Senior Member
 
dan-nickie's Avatar
 
Join Date: Feb 2014
Location: Dallas TX
Posts: 1,675
Actually sometimes on hot days when I'm leaving a campground, I will start the generator with the air conditioner on. Everything keeps right on working when I unplug the power cord and I pull out of the campground with a cool coach. I know some of you are going to say its bad, but I do it anyway at my own risk.
__________________
Dan
2014 Berkshire 390RB-60
dan-nickie is offline   Reply With Quote
Old 05-30-2015, 03:02 PM   #18
Senior Member
 
Join Date: Apr 2012
Location: West Michigan/Fort Myers
Posts: 3,927
Dan I do the same thing. I never knew it was a bad thing to do. I know not to hit either side with a load but it never occurred to me that this would harm the transfer switch.



Phil57 is offline   Reply With Quote
Old 05-30-2015, 03:27 PM   #19
Senior Member
 
tnbendr's Avatar
 
Join Date: May 2015
Location: In our coach
Posts: 232
Quote:
Originally Posted by I-RV View Post
tnbendr If your shore line has enough amperage to run your AC's, then why start the generator. If your shoreline is insufficient, then it makes sense to start the generator. But once the generator is running, everything will be on the generator. The shoreline will be not used. X2 to the suggestions of shedding the load when the generator is started.
I am only plugged into a 15 amp 110 circuit, so I don't even want to try the AC. I wanted to run the AC and exercise the gen, especially now that I've learned it "needs" to run. It was a little dirty on the exhaust for awhile at first but I ran it for about 2 1/2 hrs...it's clean now!
__________________
Ben & Michelle
2015 Berkshire 38A
2005 Jeep Wrangler toad
tnbendr is offline   Reply With Quote
Old 05-30-2015, 07:16 PM   #20
Senior Member
 
15berkxl's Avatar
 
Join Date: Mar 2015
Location: Mishawaka
Posts: 576
The transfer switch is designed to disconnect the shore power and connect to generator power without causing harm. There is a break in power seconds in duration that no power is sent to anything in the coach. Otherwise the coach would attempt to sync with the local utility company and that would not go well. The a/c compressor will turn off during the transfer and by design will not restart for 5 minutes max. This prevents power surges to the a/c units and generator.
__________________
Wayne
15berkxl is offline   Reply With Quote
Reply

Tags
vent


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 10:26 AM.