Transfer switch

Heard from FR rep and also saw in a service notice that in August FR will start a recall on Berkshire on issues with the power transfer switch. You may want to get a hold of your dealer and find out if it's just a inspection or repair/replacement.
__________________
2011: 54 days, 2012: 218 days, 2013: 175 days, 2014: 196 days
2015: 188 days, 2016: 72 days, 2017: 185 days: 2018 182 days
2019: 156 days (2009 Berkshire, 390QS, and toad)
NO3putt is offline   Reply With Quote
Old 08-03-2012, 07:44 PM   #2
2011 Berkshire 390bh
 
wnytaxman's Avatar
 
Join Date: Jul 2009
Location: Western NY State
Posts: 688
Skip,

Do you know what year or years Berkshire this applies to? Mine is an '11 but purchased in '10.

Ed
__________________
2011 Berkshire 390bh
wnytaxman is offline   Reply With Quote
Old 08-03-2012, 08:16 PM   #3
Berkshire 390QS
 
NO3putt's Avatar
 
Join Date: Feb 2011
Location: Colorado
Posts: 1,470
Exclamation link to recall information

Transfer Switch recall, Berkshire and Charleston.

You can find the recall information at : safercar.gov. Type in the recall number 12V341000 and it will cover the years and models. It covers 850 unit made between 2005 - 2011 and says FR will replace the transfer switch free of change. The notice also provided a FR phone number to call. 574-295-8749

Hope this helps everyone.

Skip
__________________
2011: 54 days, 2012: 218 days, 2013: 175 days, 2014: 196 days
2015: 188 days, 2016: 72 days, 2017: 185 days: 2018 182 days
2019: 156 days (2009 Berkshire, 390QS, and toad)
NO3putt is offline   Reply With Quote
Old 08-04-2012, 08:29 AM   #4
410 QS 425 2011 Birkshire
 
Join Date: Aug 2011
Location: Mount Olive Shores North
Posts: 121
thanks for the information will be calling my dealer with my new address
malewis49 is offline   Reply With Quote
Old 08-04-2012, 07:24 PM   #5
2011 Berkshire 390bh
 
wnytaxman's Avatar
 
Join Date: Jul 2009
Location: Western NY State
Posts: 688
Skip, I called my dealer, Buffalo RV, and they had just pulled a Berkshire into service with a burnt out transfer switch. If you were closer to us, it would have made me think it was yours.
__________________
2011 Berkshire 390bh
wnytaxman is offline   Reply With Quote
Old 08-04-2012, 08:33 PM   #6
Berkshire 390QS
 
NO3putt's Avatar
 
Join Date: Feb 2011
Location: Colorado
Posts: 1,470
Ed,
Not ours, we had a burned up AC breaker panel that's under the bed. Too close to mess around with. Cause was one or more wires had come off the power bus and shorted. We were lucky for sure. I will be taking off the breaker panel every so often and checking to make sure all the wire are secure.

Skip
__________________
2011: 54 days, 2012: 218 days, 2013: 175 days, 2014: 196 days
2015: 188 days, 2016: 72 days, 2017: 185 days: 2018 182 days
2019: 156 days (2009 Berkshire, 390QS, and toad)
NO3putt is offline   Reply With Quote
Old 08-04-2012, 08:50 PM   #7
Senior Member
 
VinceU's Avatar
 
Join Date: Dec 2011
Posts: 3,568
Quote:
Originally Posted by NO3putt View Post
Ed,
Not ours, we had a burned up AC breaker panel that's under the bed. Too close to mess around with. Cause was one or more wires had come off the power bus and shorted. We were lucky for sure. I will be taking off the breaker panel every so often and checking to make sure all the wire are secure.

Skip
Boy that's scary! Some folks don't realize how dangerous this " low voltage " can be.......
VinceU is offline   Reply With Quote
Old 08-04-2012, 09:38 PM   #8
Berkshire 390QS
 
NO3putt's Avatar
 
Join Date: Feb 2011
Location: Colorado
Posts: 1,470
It was not the low voltage panel, it was the 50amp panel that has all the AC breakers in it.
__________________
2011: 54 days, 2012: 218 days, 2013: 175 days, 2014: 196 days
2015: 188 days, 2016: 72 days, 2017: 185 days: 2018 182 days
2019: 156 days (2009 Berkshire, 390QS, and toad)
NO3putt is offline   Reply With Quote
Old 08-05-2012, 09:18 AM   #9
Senior Member
 
VinceU's Avatar
 
Join Date: Dec 2011
Posts: 3,568
Quote:
Originally Posted by NO3putt
It was not the low voltage panel, it was the 50amp panel that has all the AC breakers in it.
Yes I understand, in the world of power distrbution, 117VAC and 440 VAC are termed low voltage. I've forgotten exactly but high voltage can be 12KV-24KV and much higher. Where K= thousands.
My point was even low power 117vac can be dangerous.
VinceU is offline   Reply With Quote
Old 08-06-2012, 03:34 PM   #10
2011 Berkshire 390BH
 
Join Date: Nov 2011
Location: NW Ohio
Posts: 36
We JUST returned from a 7,000 mile trip out West and our transfer switch started a small electrical fire half way through. Thank goodness it was contained to the switch box. I'll post pictures when I have a moment. We were going down the road in California and we started smelling that nasty fried electrical smell. The switch box was melted and the wires inside were toast. Little copper beads (from the melted wires) all over the place. The neutral (white) wire on the manufacturer's side of the switch had a poor connection or something. It arced and melted in two and then it began frying other wires together. Our bedroom smells pretty nasty now.

I rigged it to where I had to manually switch from shore power to generator power. This was just so we could limp home through the deserts, etc.

Good thread with recall links - I came on here just to see if anyone else had this same issue.
LiteEmUp is offline   Reply With Quote
Old 08-06-2012, 05:07 PM   #11
Senior Member
 
klucas's Avatar
 
Join Date: Sep 2010
Posts: 376
Please show a picture and where to find this switch. I just got my recall letter today and I want to check it ASAP.
klucas is offline   Reply With Quote
Old 08-06-2012, 05:20 PM   #12
Senior Member
 
tmmar's Avatar
 
Join Date: Apr 2008
Location: Long Island (Nassau County), NY
Posts: 4,325
It is the black box inside the electrical compartment where the shore power cord is located. What did your letter say?
__________________
Tom and Margaret
2014 Berkshire 390bh-60

tmmar is offline   Reply With Quote
Old 08-06-2012, 05:27 PM   #13
Berkshire 390QS
 
NO3putt's Avatar
 
Join Date: Feb 2011
Location: Colorado
Posts: 1,470
When I found out about thie issue, the FR rep had us open the transfer switch box (with power disconnected) and inspect the white and green wires for any signs of browning and that the wires were still flexable. The concern was with the wires on top, furthest in. MAKE SURE YOU ARE DISCONNECTED.
__________________
2011: 54 days, 2012: 218 days, 2013: 175 days, 2014: 196 days
2015: 188 days, 2016: 72 days, 2017: 185 days: 2018 182 days
2019: 156 days (2009 Berkshire, 390QS, and toad)
NO3putt is offline   Reply With Quote
Old 08-06-2012, 05:49 PM   #14
Senior Member
 
klucas's Avatar
 
Join Date: Sep 2010
Posts: 376
The envelope had saftey recall on it. Letter said to bring it to a dealer ASAP to get it fixed. Should take an hour and they will change a switch. No charge etc etc.
klucas is offline   Reply With Quote
Old 08-06-2012, 09:22 PM   #15
2011 Berkshire 390BH
 
Join Date: Nov 2011
Location: NW Ohio
Posts: 36
Here are 4 picts from my burnt out transfer switch. Sorry about them being so small but that's what I had to do to get them to fit within this forum.

My transfer switch is in the last comparment on the drivers side. One door past the location where the shore power line is stored. We have a 2011 Berkshire 390BH.

As for the inside of the switch box, the left side of the terminal block is the switch manufacturer's side. Where they run the various inputs to their relays/switches and then to the output which is the top four terminals. On the right side, the shore power coming in is on terminals 5, 6, 7, and 8 from the top. You can also tell by the thick black cord coming into the bottom of the box. The generator line input is the bottom conduit line on the right. It's wires run to terminals 9, 10, 11, and 12 from the top (or the bottom four terminals). The top conduit on the right runs to the breaker panel under the bed. This is the output and is terminal numbers 1-4 from top.

In our case, the white/neutral wire on the left on terminal 3 from top arced and melted away. The heat from this resulted in everything else surrounding it to begin melting and arcing. Notice the red and neutral wire running to the breaker panel on the top right (terminals 2 and 3) how they started arcing as well.

I didn't take a picture of the cover but it is badly wrapped and disfigured.

Not only is the switch toast, but the wires going to our panel (and possibly the green ground from shore power) are now bad and need to be replaced.

Also, look at the bottom of the box. Little beads of molten metal piled up there. I picked most of them out.

This occurred while running the generator traveling down the interstate in the morning hours. We were running our two A/C units - nothing else. So this was not the result of excessive load or excessive outside temperatures. I'm wondering if there was a poor connection to begin with. But what do I know other than we almost lost our motorhome to a fire!
Attached Images
    
LiteEmUp is offline   Reply With Quote
Old 08-06-2012, 10:42 PM   #16
Berkshire 390QS
 
NO3putt's Avatar
 
Join Date: Feb 2011
Location: Colorado
Posts: 1,470
Looks bad for sure. Glad no one got hurt. Suggest while your unit is in the shop that they pop off the AC breaker panel cover and make sure all the wires are secure on the bus bars. We had one or more wires come off and it melted the box and burned up many wires and could have lost the MH.

Skip, if I knew how to post pictures on here would show the mess
__________________
2011: 54 days, 2012: 218 days, 2013: 175 days, 2014: 196 days
2015: 188 days, 2016: 72 days, 2017: 185 days: 2018 182 days
2019: 156 days (2009 Berkshire, 390QS, and toad)
NO3putt is offline   Reply With Quote
Old 08-07-2012, 03:38 AM   #17
Senior Member
 
Iggy's Avatar
 
Join Date: Jul 2010
Posts: 7,884
That was from loose connections. I have a 2012 Georgetown and on my final inspection opened the transfer switch and noticed the wires were discolored from being loose while energized. FR approved replacment of the 50 AMP transfer switch to a different brand.


Top Picture -
The Light manufactured one with the white and gold label was the bad one.


Bottom Picture -
The new transfer switch is above my Progessive Industires Electrical Managment System that monitors power. (Model EMS-LCHW50)
It monitors high and low volatges, high and low cycles, plus more. If anything is wrong it will not energize or it will shut down if already powered up. Nice optional toy I bought.

Here is a link to Progressive Industries and my power managment box if you are interested.
http://www.progressiveindustries.net/ems_lchw50.htm
Attached Thumbnails
Click image for larger version

Name:	April_17_2012 011.jpg
Views:	124
Size:	50.6 KB
ID:	17624   Click image for larger version

Name:	new 001.jpg
Views:	120
Size:	53.9 KB
ID:	17626  
Iggy is offline   Reply With Quote
Old 08-07-2012, 11:41 AM   #18
Senior Member
 
klucas's Avatar
 
Join Date: Sep 2010
Posts: 376
Here are some photos of mine. It looks like mine is a little different. It is in a metal box. All the wires look ok. What do you guys think?
Attached Thumbnails
Click image for larger version

Name:	image-3967885481.jpg
Views:	95
Size:	49.0 KB
ID:	17635   Click image for larger version

Name:	image-2406036693.jpg
Views:	113
Size:	49.0 KB
ID:	17636  
klucas is offline   Reply With Quote
Old 08-07-2012, 11:57 AM   #19
CLASS "A" Senior Member
 
cfsoistman's Avatar
 
Join Date: Nov 2008
Location: Upperco, Maryland
Posts: 3,136
Quote:
Originally Posted by NO3putt View Post
Ed,
Not ours, we had a burned up AC breaker panel that's under the bed. Too close to mess around with. Cause was one or more wires had come off the power bus and shorted. We were lucky for sure. I will be taking off the breaker panel every so often and checking to make sure all the wire are secure.

Skip
Seems FR has a bit of a problem with their, excuse the title, Electricians! I've had more than my fair share of electrical issues involving bad connections. First the power cord fried the neutral lug in the transfer switch from not being tightened properly. I cut the original cord back about 6 inches and connected to the spare neutral lug. Also had problems with wiring in a junction box where the AC units and front Receptacles all meet. Numerous fried wires due to questionable use of wirenuts without twisting the wires together.
__________________

2007 Georgetown 370TS
aka - RAYNMKR

Driver: Charlie
Navigator: Sheri
cfsoistman is offline   Reply With Quote
Old 08-07-2012, 05:54 PM   #20
410 QS 425 2011 Birkshire
 
Join Date: Aug 2011
Location: Mount Olive Shores North
Posts: 121
talked to Lazydays got one story, then talked to Forestriver got another story, but now have appointment to have it replaced on the 21th of the month ? only one day to fix it, will see when that happens!
malewis49 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 09:47 AM.