Atwood furnace won't stay lit

Greetings, all.
I'm looking for a little bit of guidance on an issue I'm having. We've got a trailer with an Atwood furnace...AFMD30 I think it is. The furnace will ignite but won't stay lit. The blink codes on the control board indicate failure to detect the flame. I'd have to agree with the little blinkey light...I hear it ignite but I can also hear the igniter never stops trying to ignite. I'm pretty sure it's a defective control board. When I opened the access panel to the furnace the board was wet...several of the components on top are rusted/corroded, etc. In addition, it was working fine just a few months ago. I can just buy a board but most electronic components aren't returnable so I'm trying to verify the flame sensor. I found a youtube video with the guy using a capacitor and ammeter and I'm not afraid of doing that but capacitors are harder to come by since the Radio Shack closed its doors. So is that the only way to test the flame sensor? Or should I just quit worrying about it and get the control board?

Thanks in advance...
endothermic_biped is offline   Reply With Quote
Old 01-31-2018, 09:09 AM   #2
Senior Member
 
SeaDog's Avatar
 
Join Date: Jan 2016
Location: x
Posts: 12,423
I think the first thing I would do is take some emery cloth and clean the flame sensor then retry. Being an old HVAC guy I have done this many times on household furnaces.
__________________
Retired Navy
Jake my sidekick (yellow Lab) 10/04 - 05/20
2017 RAM 2500 CC 4X4 Cummins Diesel
2016 Flagstaff 26 FKWS
AF&AM & El Korah Shrine of Idaho
SeaDog is offline   Reply With Quote
Old 01-31-2018, 09:17 AM   #3
Senior Member
 
jeff64's Avatar
 
Join Date: Mar 2015
Location: N. Illinois
Posts: 2,371
Quote:
Originally Posted by SeaDog View Post
I think the first thing I would do is take some emery cloth and clean the flame sensor then retry. Being an old HVAC guy I have done this many times on household furnaces.
X2 seen this before as well. Flame presence sensor = ignitor! Sends a feedback to the board. I like brass brush myself but shouldn't make a difference. Clean off mounting connections and hardware at the same time. You can get a .pdf on line for the furnasty and pay attention to any install, inspection of electrode, clearance or orientation instruction on that igniter. Ya'd think as long as it sparks and lights the gas you'd be good...not necessarily so!
__________________
2016 Flagstaff 27VRL Emerald
14K Equalizer
2020 Silverado 2500HD CC 4X4 6.6L gas 3.73
jeff64 is offline   Reply With Quote
Old 02-09-2018, 10:34 PM   #4
Junior Member
 
Join Date: May 2015
Posts: 11
Thanks. I'll give it a try. Weather and work have kept me from fiddling with it. Hope to work on it tomorrow. It's just over a year old and we've only used the heat on maybe three trips so I wouldn't figure the flame sensor would be fouled with carbon yet but I'll definitely give it a look. If it wasn't so far to our dealer I'd just get it fixed under warranty but as it is it'll cost me more in diesel fuel to get to the dealer than it will to just buy a board (or flame sensor). I'll post the fix when I find it.
endothermic_biped is offline   Reply With Quote
Old 02-21-2018, 09:14 PM   #5
Junior Member
 
Join Date: May 2015
Posts: 11
Well, for what it's worth...my trouble turned out to be a defective control board. Since it is so new I skipped checking on the flame sensor. Instead I checked the current between the flame sensor and board. I was getting about 6 microamps so I replaced the board and I've got heat again.
endothermic_biped is offline   Reply With Quote
Old 02-21-2018, 09:36 PM   #6
Senior Member
 
SeaDog's Avatar
 
Join Date: Jan 2016
Location: x
Posts: 12,423
glad you got it fixed thanks for the pic I see what you were talking about.
__________________
Retired Navy
Jake my sidekick (yellow Lab) 10/04 - 05/20
2017 RAM 2500 CC 4X4 Cummins Diesel
2016 Flagstaff 26 FKWS
AF&AM & El Korah Shrine of Idaho
SeaDog is offline   Reply With Quote
Reply

Tags
furnace


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 11:09 AM.