furnace short cycling , poor heat

I noticed the other night the furnace in our grey wolf was short cycling. Good hot air for about 5 mins and then the burner would cut out and only run fan and as the furnace cooled down it would relight the burner. Classic short cycle. I pulled the air return panel under the stove and the first thing I noticed was I thought the frame of the furnace itself was very warm. I pulled the access panel off the burner compartment and there is a heat overload limit right there. I was able to determine that particular limit is taking the furnace out and then cooling off and allowing the furnace to re light.


Here is the good stuff...

The burner box has provisions for up to six 4inch supply air taps to be ducted into the living space for hot air. This application is only using two. I'm suspecting that there simply is not enough air flow over the heat exchanger to allow the furnace to operate correctly with out short cycling.... I am considering trying to install at least two more taps into the living space to help achieve enough airflow across the heat exchanger to prevent the short cycling....

Any thoughts/suggestions??
__________________
Allen Stegall - Upstate SC
2014 Greywolf 26BDH
2004 Suburban 2500 496 , Curt XD, main tow rig, LBZ candidate
15,000 pounds of fun rolling down the road!
Back up rigs : 01 Yukon XL 1500, 07 Yukon 1500, 04 Sierra 2500
only1stegall is offline   Reply With Quote
Old 11-19-2013, 10:19 AM   #2
Senior Member
 
jtstromsburg's Avatar
 
Join Date: Jul 2011
Location: Stromsburg, Nebraska
Posts: 1,682
Quote:
Originally Posted by only1stegall View Post
I noticed the other night the furnace in our grey wolf was short cycling. Good hot air for about 5 mins and then the burner would cut out and only run fan and as the furnace cooled down it would relight the burner. Classic short cycle. I pulled the air return panel under the stove and the first thing I noticed was I thought the frame of the furnace itself was very warm. I pulled the access panel off the burner compartment and there is a heat overload limit right there. I was able to determine that particular limit is taking the furnace out and then cooling off and allowing the furnace to re light.

Here is the good stuff...

The burner box has provisions for up to six 4inch supply air taps to be ducted into the living space for hot air. This application is only using two. I'm suspecting that there simply is not enough air flow over the heat exchanger to allow the furnace to operate correctly with out short cycling.... I am considering trying to install at least two more taps into the living space to help achieve enough airflow across the heat exchanger to prevent the short cycling....

Any thoughts/suggestions??
This is exactly what I did on my '12 28BH. Added another duct right by the door. It was a bit of work, but helped distribute heat better. I never had any problems with short cycling. Not sure about yours, but mine had completely exposed underbelly, so I heated with electric mostly. In my new fiver, I must use the furnace some to keep the underbelly tanks and piping heated, unless I don't plan to use water.
__________________
Joel and Teresa
2016 Sabre 34TBOK
2006 GMC 3500 CC LB DRW 4X4
jtstromsburg is offline   Reply With Quote
Old 11-19-2013, 10:50 AM   #3
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
Another thought: Do you have a bug screen in the outside intake/exhaust? The manufacturer says not to use those. That might be restricting your flow too much as well.
BarryD0706 is offline   Reply With Quote
Old 11-19-2013, 10:55 AM   #4
Junior Member
 
only1stegall's Avatar
 
Join Date: Nov 2013
Location: upstate SC
Posts: 7
Quote:
Originally Posted by BarryD0706 View Post
Another thought: Do you have a bug screen in the outside intake/exhaust? The manufacturer says not to use those. That might be restricting your flow too much as well.
Actually I do..... does suburban say that or forest river?

I will try the furnace with the wasp guards off and see what happens
__________________
Allen Stegall - Upstate SC
2014 Greywolf 26BDH
2004 Suburban 2500 496 , Curt XD, main tow rig, LBZ candidate
15,000 pounds of fun rolling down the road!
Back up rigs : 01 Yukon XL 1500, 07 Yukon 1500, 04 Sierra 2500
only1stegall is offline   Reply With Quote
Old 11-19-2013, 11:58 AM   #5
Senior Member
 
Join Date: Nov 2012
Location: X
Posts: 2,781
Quote:
Originally Posted by only1stegall View Post
Actually I do..... does suburban say that or forest river?
It's in the Suburban book, at least for my heater. I leave them on except when I'm going to use the heater.
BarryD0706 is offline   Reply With Quote
Old 11-19-2013, 12:01 PM   #6
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Quote:
Originally Posted by only1stegall View Post
I noticed the other night the furnace in our grey wolf was short cycling. Good hot air for about 5 mins and then the burner would cut out and only run fan and as the furnace cooled down it would relight the burner. Classic short cycle. I pulled the air return panel under the stove and the first thing I noticed was I thought the frame of the furnace itself was very warm. I pulled the access panel off the burner compartment and there is a heat overload limit right there. I was able to determine that particular limit is taking the furnace out and then cooling off and allowing the furnace to re light.


Here is the good stuff...

The burner box has provisions for up to six 4inch supply air taps to be ducted into the living space for hot air. This application is only using two. I'm suspecting that there simply is not enough air flow over the heat exchanger to allow the furnace to operate correctly with out short cycling.... I am considering trying to install at least two more taps into the living space to help achieve enough airflow across the heat exchanger to prevent the short cycling....

Any thoughts/suggestions??
If your unit is short cycling, for the reason you stated you should put a meter on the limit to see if that is opening when it shuts down. Where is your stat located compared to a heating duct? If you turn your stat up to 80 will the unit stay on? You can also just open 1 of the area without a duct and see if that helps and if it stays on, unless you really want to add more ducts anyway. But you need to find the reason out first. How many total registers do you have in the floor 2 or do you have more in the sidewall or floors somewhere?
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 11-19-2013, 01:04 PM   #7
Mod free 5er
 
Join Date: Mar 2008
Location: Concord, NC
Posts: 24,702
Have had a wire hornet/wasp guard on our last 2 units and never had a problem with the furnace. Don't use them that much, but when we do, the furnaces worked fine. We normally use only the EdenPure elec. heater and if it is going to be below freezing, I just turn the furnace blower on. Had to do this for 3 nights last week. Ran the blower from about 9pm to 9am the 3 nights.
__________________
OldCoot is offline   Reply With Quote
Old 11-19-2013, 01:20 PM   #8
Junior Member
 
only1stegall's Avatar
 
Join Date: Nov 2013
Location: upstate SC
Posts: 7
Quote:
Originally Posted by gljurczyk View Post
If your unit is short cycling, for the reason you stated you should put a meter on the limit to see if that is opening when it shuts down. Where is your stat located compared to a heating duct? If you turn your stat up to 80 will the unit stay on? You can also just open 1 of the area without a duct and see if that helps and if it stays on, unless you really want to add more ducts anyway. But you need to find the reason out first. How many total registers do you have in the floor 2 or do you have more in the sidewall or floors somewhere?
Yes I watched the limit open with my meter.

Two registers total, as stated in original post.

Thermostat is on side wall in front of bunks, factory location.

The furnace is not cycling on the thermostat , but rather the limit as I stated before.
__________________
Allen Stegall - Upstate SC
2014 Greywolf 26BDH
2004 Suburban 2500 496 , Curt XD, main tow rig, LBZ candidate
15,000 pounds of fun rolling down the road!
Back up rigs : 01 Yukon XL 1500, 07 Yukon 1500, 04 Sierra 2500
only1stegall is offline   Reply With Quote
Old 11-19-2013, 01:57 PM   #9
Mod free 5er
 
Join Date: Mar 2008
Location: Concord, NC
Posts: 24,702
Quote:
Originally Posted by only1stegall View Post
Yes I watched the limit open with my meter.

Two registers total, as stated in original post.

Thermostat is on side wall in front of bunks, factory location.

The furnace is not cycling on the thermostat , but rather the limit as I stated before.
Strictly as an experiment, remove the limit from the furnace and try it.
__________________
OldCoot is offline   Reply With Quote
Old 11-19-2013, 04:21 PM   #10
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Quote:
Originally Posted by only1stegall View Post
Yes I watched the limit open with my meter.

Two registers total, as stated in original post.

Thermostat is on side wall in front of bunks, factory location.

The furnace is not cycling on the thermostat , but rather the limit as I stated before.
Well now you need to find out if the limit is good by temp at the limit location. I find it hard to understand how a 26' unit has only two ducts in it. Not that I doubt you. I'm just not familiar with your unit and this is the first time I heard about only 2 ducts. A 4" duct will only carry about 80 cfm depending on the static pressure. Do you have a return air? I ask you that because mine did not have one when I bought it. they seemed to forgot to install it. I had to take it back to the dealer to have them cut one in. Sorry I didn't catch the part that you had a meter on the limit when it opened and broke the circuit to the valve. You might want to also call Suburban and ask what temp the high limit is set for. Or as OC said jumper it out and see if it stays on. You must be getting heat out of registers thats pretty hot to open your upper limit.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 11-19-2013, 07:30 PM   #11
Junior Member
 
only1stegall's Avatar
 
Join Date: Nov 2013
Location: upstate SC
Posts: 7
Quote:
Originally Posted by gljurczyk View Post
Well now you need to find out if the limit is good by temp at the limit location. I find it hard to understand how a 26' unit has only two ducts in it. Not that I doubt you. I'm just not familiar with your unit and this is the first time I heard about only 2 ducts. A 4" duct will only carry about 80 cfm depending on the static pressure. Do you have a return air? I ask you that because mine did not have one when I bought it. they seemed to forgot to install it. I had to take it back to the dealer to have them cut one in. Sorry I didn't catch the part that you had a meter on the limit when it opened and broke the circuit to the valve. You might want to also call Suburban and ask what temp the high limit is set for. Or as OC said jumper it out and see if it stays on. You must be getting heat out of registers thats pretty hot to open your upper limit.
Yes it has return. I spent a little time today. The limit opens at around 170.. seems legit to me. Im going to go ahead with the add some vents plan.... I agree, 180 cfms or less isn't enough for a 20k BTU furnace.

Grey wolf is a value brand.... get what you pay for I guess!
__________________
Allen Stegall - Upstate SC
2014 Greywolf 26BDH
2004 Suburban 2500 496 , Curt XD, main tow rig, LBZ candidate
15,000 pounds of fun rolling down the road!
Back up rigs : 01 Yukon XL 1500, 07 Yukon 1500, 04 Sierra 2500
only1stegall is offline   Reply With Quote
Reply

Tags
furnace

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 11:23 AM.