Furnace shutting off
Good morning,
We have a 2015 Sierra 357 TRIP, we have used the furnace many times in the past, however waking up this morning it was chilly inside and furnace not working. I have checked, propane (tank half full), plugged into 50 amp service (full power), battery (fully charged), inside temp is 12 degrees cooler than what furnace temp is set at. I have taken out fuse for 2 minutes and re-installed , furnace runs 90 seconds and shuts off. I have shut off thermostat and re-started, again runs 90 seconds and shuts off. What else can I try? How do I access furnace? We have had problems with thermostat in past where we have had to reset to run AC, could that be the problem?
We are camping near Prescott AZ, cold front moving in today and temperatures are expected to drop 15 degrees tonight and get windy. If we can get furnace working may need to pack up this evening.
Thanks,
Budwag
|
|
|
02-18-2018, 11:10 AM
|
#2
|
Senior Member
Join Date: Jun 2012
Posts: 10,907
|
Here's the service manual for many Suburbans. Pgs 27/28 have troubleshooting help.
Looking at a pic of your unit on-line, it looks like it's in your bathroom. Go outside and look for you intake/exhaust. It looks like this:
The furnace will be inside at that same location. You'll probably have to open a cabinet, unscrew a panel, or something like that to get to it.
Good luck.
__________________
1988 Coleman Sequoia - popup (1987-2009) - outlasted 3 Dodge Grand Caravans!
2012 Roo19 - hybrid (2012-2015)
2016 Mini Lite 2503S - tt (2015 - ???)
2011 Traverse LT, 3.6L, FWD
2009 Silverado 1500 Ext Cab, 5.3L, 4x4, 3.73
2016 Silverado 2500HD Dbl Cab, 6.0L 4x4, 4.10
|
|
|
02-18-2018, 11:39 AM
|
#3
|
Site Team
Join Date: Mar 2008
Location: Louisville, KY
Posts: 10,525
|
If you're on 50 amp service you should be using 2 electric heaters and saving LP although
that won't keep the belly warm and if it's below freezing your pipes could be in jeopardy.
Sometimes furnace control boards just go bad. Happened to me.
The flame sensor circuit in the board goes bonkers.
Does your igniter keep clicking after the furnace lights??
When you start the furace-
1st the blower starts to purge the burner.
2nd the gas valve opens and the spark igniter clicks to light the burner.
If the igniter keeps clicking after the burner lights it means it's not detecting the
flame and shutting down.
There are other things that could be wrong but that's my guess.
Good luck!
__________________
Peace!
Dan & Rita D
2017 Nissan Titan 5.6L King cab 4wd
2016 Evergreen Everlite 242RBS
29' empty nest model. Blue Ox WD hitch
(1 queen bed, large main cabin and huge bathroom)
Camping days 2010-53, 2011-47, 2012-41, 2013-41, 2014-31, 2015-40, 2016-44, 2017-63, 2018-75, 2019-32, 2020-41, 2021-49, 2022-43, 2023-66
|
|
|
02-18-2018, 12:38 PM
|
#4
|
Senior Member
Join Date: Jan 2017
Location: Kalamazoo
Posts: 2,139
|
kydan has a good point. I have two inexpensive electric heaters in my unit when I'm not paying the electric. ( I think they were $10 at lowes) My guess would be something blocking the exhaust vent or there is prob a low oxygen sensor that shuts the furnace when oxygen is low? Crack a door or window for a minute?
|
|
|
02-18-2018, 12:46 PM
|
#5
|
Senior Member
Join Date: Jun 2012
Posts: 10,907
|
Quote:
Originally Posted by Kimber45
kydan has a good point. I have two inexpensive electric heaters in my unit when I'm not paying the electric. ( I think they were $10 at lowes) My guess would be something blocking the exhaust vent or there is prob a low oxygen sensor that shuts the furnace when oxygen is low? Crack a door or window for a minute?
|
These furnaces don't have low O2 sensors. Combustion air and exhaust are kept out of the TT. Only way to have exhaust air in the unit is a cracked heat exchanger or leaking combustion air/exhaust connection, which is why you have a CO detector.
The only units I'm aware of that have low O2 sensors are catalytic heaters, where the combustion air and exhaust DOES come from/to inside the trailer.
__________________
1988 Coleman Sequoia - popup (1987-2009) - outlasted 3 Dodge Grand Caravans!
2012 Roo19 - hybrid (2012-2015)
2016 Mini Lite 2503S - tt (2015 - ???)
2011 Traverse LT, 3.6L, FWD
2009 Silverado 1500 Ext Cab, 5.3L, 4x4, 3.73
2016 Silverado 2500HD Dbl Cab, 6.0L 4x4, 4.10
|
|
|
02-18-2018, 01:35 PM
|
#6
|
Junior Member
Join Date: Sep 2017
Posts: 8
|
Thank you the manual helps.
|
|
|
02-18-2018, 01:36 PM
|
#7
|
Junior Member
Join Date: Sep 2017
Posts: 8
|
Thanks for information
|
|
|
02-18-2018, 01:38 PM
|
#8
|
Junior Member
Join Date: Sep 2017
Posts: 8
|
We appreciate everyones comments and suggestions! We will continue to work and try info provided. Have a great weekend!
|
|
|
02-18-2018, 05:06 PM
|
#9
|
Junior Member
Join Date: Sep 2017
Posts: 8
|
Got it working. Found access in pass through storage compartment, took off panel walls. Tried switching main switch on/off on unit a couple of times no success. Then took off ducted panel, found sensor inside and took off both wiring terminals, then pushed back on. Tried unit again and started working properly. Yup, with my big long body stuffed in the compartment it got hot quickly.
Before re-installing panel and walls, turn unit on 3 more times and it worked great. We are staying the night, we will take everyone's advice, by getting space heater, saving furnace owner manual, and using this forum again if another problem comes up.
Budwag
|
|
|
02-18-2018, 09:48 PM
|
#10
|
Senior Member
Join Date: Jan 2017
Location: Kalamazoo
Posts: 2,139
|
Glad you got it fixed and I learned something new. I have a vent free unit at home with a low oxygen sensor. I guess when a unit has a vent/exhaust the low oxygen sensor is not needed.
|
|
|
02-18-2018, 09:53 PM
|
#11
|
Site Team
Join Date: Mar 2014
Location: Grayson County, Texas
Posts: 21,578
|
Quote:
Originally Posted by Budwag
Got it working. Found access in pass through storage compartment, took off panel walls. Tried switching main switch on/off on unit a couple of times no success. Then took off ducted panel, found sensor inside and took off both wiring terminals, then pushed back on. Tried unit again and started working properly. Yup, with my big long body stuffed in the compartment it got hot quickly.
Before re-installing panel and walls, turn unit on 3 more times and it worked great. We are staying the night, we will take everyone's advice, by getting space heater, saving furnace owner manual, and using this forum again if another problem comes up.
Budwag
|
Thanks for reporting back with your resolution. Reporting back gives honor to the time spent by other members attempting to help PLUS this thread may help someone else who has similar issues.