Surburban 35K btu furnace shuts off

The furnace blower starts and shuts off at 30 seconds. Then, it does not try again even though the thermostat is calling for heat. If I shut off the thermostat and restart it, then the furnace does the same 30 second blower run and shuts off again. The gas water heater and all the stovetop burners are working fine.
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-01-2022, 08:00 AM   #2
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,074
How is your 12v system?
The furnace needs to get to a certain speed to evacuate the combustion chamber and to move the sail switch to allow ignition.

If the 12v system isn't working correctly, the fan will run slow and not allow the furnace to light.

Suburban has a good troubleshooting guide in the manual.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2017 Ford F-Series SCREW 4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=86
5picker is offline   Reply With Quote
Old 10-01-2022, 08:13 AM   #3
Senior Member
 
Join Date: Sep 2016
Location: WI
Posts: 324
The battery is showing full charge and no other 12V issues are noted. Do you have a link to the manual?
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-01-2022, 08:17 AM   #4
Site Team
 
Mr. Dan's Avatar
 
Join Date: Mar 2014
Location: Grayson County, Texas
Posts: 21,502
Quote:
Originally Posted by dcavaiani View Post
The battery is showing full charge and no other 12V issues are noted. Do you have a link to the manual?
Where are you seeing that the battery is showing full charge?
__________________
2015 FR Wildcat 295RSX / GMC Sierra

Nights Camped: '13 = 49/'14 = 74/'15 = 74/'16 = 85/'17 = 110/'18 = 111/'19 = 86/'20 =108/'21 = 115/'22 = 135/'23 = 78; Booked for 2024 = 69
Mr. Dan is offline   Reply With Quote
Old 10-01-2022, 08:31 AM   #5
Senior Member
 
Join Date: Sep 2016
Location: WI
Posts: 324
Quote:
Originally Posted by Mr. Dan View Post
Where are you seeing that the battery is showing full charge?
Just on the inside panel. Don't have my meter with me.
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-01-2022, 08:34 AM   #6
Senior Member
 
Join Date: Sep 2016
Location: WI
Posts: 324
Wondering about the propane regulator and don't know if the pressure dial on the regulator should be messed with? It is 924N model regulator.
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-01-2022, 08:52 AM   #7
Site Team
 
Mr. Dan's Avatar
 
Join Date: Mar 2014
Location: Grayson County, Texas
Posts: 21,502
Quote:
Originally Posted by dcavaiani View Post
Just on the inside panel. Don't have my meter with me.
If you're hooked up to shore power, the inside panel showing 4 lights does not indicate state of charge. It indicates the converter is charging the battery.
__________________
2015 FR Wildcat 295RSX / GMC Sierra

Nights Camped: '13 = 49/'14 = 74/'15 = 74/'16 = 85/'17 = 110/'18 = 111/'19 = 86/'20 =108/'21 = 115/'22 = 135/'23 = 78; Booked for 2024 = 69
Mr. Dan is offline   Reply With Quote
Old 10-01-2022, 09:13 AM   #8
Senior Member
 
Join Date: Sep 2016
Location: WI
Posts: 324
Quote:
Originally Posted by Mr. Dan View Post
If you're hooked up to shore power, the inside panel showing 4 lights does not indicate state of charge. It indicates the converter is charging the battery.
I am hooked up. All other devices in the camper are working fine.
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-01-2022, 09:24 AM   #9
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
Disconnect shore power and start furnace. Look at your panel at same time to see if still shows full charge.
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
fonzie is offline   Reply With Quote
Old 10-01-2022, 09:45 AM   #10
Senior Member
 
Join Date: Sep 2016
Location: WI
Posts: 324
Quote:
Originally Posted by fonzie View Post
Disconnect shore power and start furnace. Look at your panel at same time to see if still shows full charge.
Pulled shore power and battery still showed full charge and just slightly dimmed the fully charged light after about 5 minutes of inside lights being on.
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-01-2022, 10:30 AM   #11
Senior Member
 
Join Date: Sep 2016
Location: WI
Posts: 324
How can a DIY wannabe person such as me ever get at this inside accessed furnace to check/clean things without disconnecting everything and not knowing anything about the furnace? Seems to be daunting for sure and guess I will have to try to find a technician to come in and check it out. Again, the fan starts and blows loud, but there is no clicking/ignition, and it shuts off after about 30 seconds. A stuck sail switch ?
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-01-2022, 10:46 AM   #12
Site Team
 
Flybob's Avatar
 
Join Date: Oct 2014
Posts: 15,266
This may help.
Attached Files
File Type: pdf Suburban-Furnace-Master-Service-and-Training-Manual.pdf (3.62 MB, 56 views)
__________________

2015 Freedom Express 248RBS
TV 2015 Silverado HD2500 Duramax
TST Tire Monitors
Honda 2000I + Companion
2 100W solar panels
Flybob is offline   Reply With Quote
Old 10-01-2022, 11:41 AM   #13
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
I would buy a multimeter to check actual voltage at battery when furnace starts. If battery is low, sail switch might not close initiating igniter and gas valve opening.
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
fonzie is offline   Reply With Quote
Old 10-01-2022, 12:07 PM   #14
Senior Member
 
Join Date: Sep 2016
Location: WI
Posts: 324
Quote:
Originally Posted by fonzie View Post
I would buy a multimeter to check actual voltage at battery when furnace starts. If battery is low, sail switch might not close initiating igniter and gas valve opening.
I'll be checking that soon. I assume that the furnace issue will not affect the A/C units?
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-01-2022, 12:33 PM   #15
Senior Member
 
Join Date: Sep 2016
Location: WI
Posts: 324
When the battery voltage is checked, should the shore power be pulled? Also, is there any other indication that the battery may be low? All else seemed to work well when shore power was pulled. Battery is in its 6th year since newly installed.
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-01-2022, 03:19 PM   #16
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,458
Just a few things

There are a couple of checks the the furnace makes before igniting. The first one is to check that the impellers (firebox AND cabin air) are spinning at speed. That's why others have suggested to check your battery. They may be incorrect since this check happens pretty quickly in the sequence, not 30 seconds as you have stated.

The next thing that happens is that the impellers are allowed to run for 15 seconds to purge any fuel/air from prior attempts.

Then the gas valve opens and the electronics produce spark ignition. If you turn the heat on and promptly get your head down on the floor near the furnace, you will hear a clunk as the gas valve opens and then click-click-click for seven seconds. as the sparks are generated to ignite the fuel/air. If someone else stands outside with nose near the furnace inlet/outlet, they should smell the fuel at this point. When ignition occurs (hear "whoomp"), it is detected and the furnace runs.

If not, it will go through another purge cycle and ignition attempt. After three such attempts, it will give up and go into "lockout." As you have noted, you have to turn the thermostat to "off" and back to "heat" to reset the lockout.

There are several things that can break.
  1. Gas valve might not be opening (no clunk, can't smell gas at the inlet/outlet port)
  2. Electronics not producing spark (no click-click). Sometimes this is electronics, sometimes you just need to reset the spark gap.
  3. Ignition didn't occur (could be spider webs or mud dauber nests in the inlet/outlet ports)
  4. Furnace ignites but ignition not detected (detector or electronics bad)
  5. But the one that seems to happen most often is the propane regulator by the tanks is starting to fail. They only last 8-10 years. The furnace, because it is essentially turbo-charged, is much more sensitive to fuel pressure than the range or water heater. The range has a secondary regulator and the water heater is normally-aspirated.
I'm going to attach the service manual for the furnace. Don't ignore that line near the front that says to check the propane pressure. I wasted hours checking other things before doing that once. (first-time experience). You can build a manometer in an hour with $5 of parts.

Let us know what you find.
Attached Files
File Type: pdf Suburban Furnace_Service_Manual.pdf (4.92 MB, 60 views)
__________________
Larry
"Everybody's RV is not like your RV."
"Always take pictures with the button on the right."
"Always bypass the water heater before opening the low-point drains."
Sticks and Bricks: Raleigh, NC
2008 Cherokee 38P: at Ivor, VA permanently
Larry-NC is offline   Reply With Quote
Old 10-01-2022, 07:08 PM   #17
Senior Member
 
Join Date: Sep 2016
Location: WI
Posts: 324
Quote:
Originally Posted by Larry-NC View Post
There are a couple of checks the the furnace makes before igniting. The first one is to check that the impellers (firebox AND cabin air) are spinning at speed. That's why others have suggested to check your battery. They may be incorrect since this check happens pretty quickly in the sequence, not 30 seconds as you have stated.

The next thing that happens is that the impellers are allowed to run for 15 seconds to purge any fuel/air from prior attempts.

Then the gas valve opens and the electronics produce spark ignition. If you turn the heat on and promptly get your head down on the floor near the furnace, you will hear a clunk as the gas valve opens and then click-click-click for seven seconds. as the sparks are generated to ignite the fuel/air. If someone else stands outside with nose near the furnace inlet/outlet, they should smell the fuel at this point. When ignition occurs (hear "whoomp"), it is detected and the furnace runs.

If not, it will go through another purge cycle and ignition attempt. After three such attempts, it will give up and go into "lockout." As you have noted, you have to turn the thermostat to "off" and back to "heat" to reset the lockout.

There are several things that can break.
  1. Gas valve might not be opening (no clunk, can't smell gas at the inlet/outlet port)
  2. Electronics not producing spark (no click-click). Sometimes this is electronics, sometimes you just need to reset the spark gap.
  3. Ignition didn't occur (could be spider webs or mud dauber nests in the inlet/outlet ports)
  4. Furnace ignites but ignition not detected (detector or electronics bad)
  5. But the one that seems to happen most often is the propane regulator by the tanks is starting to fail. They only last 8-10 years. The furnace, because it is essentially turbo-charged, is much more sensitive to fuel pressure than the range or water heater. The range has a secondary regulator and the water heater is normally-aspirated.
I'm going to attach the service manual for the furnace. Don't ignore that line near the front that says to check the propane pressure. I wasted hours checking other things before doing that once. (first-time experience). You can build a manometer in an hour with $5 of parts.

Let us know what you find.
Awesome response!
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-02-2022, 01:21 PM   #18
Junior Member
 
TimLG's Avatar
 
Join Date: Jul 2018
Location: Indiana
Posts: 23
Furnace shutting off

I've had the same problem twice. First time it was a sticking sail switch, I temporarily jumpered the sail switch to confirm the problem. Don't run the furnace without a good sail switch. The 2nd time, found a mud dauber (wasp) nest and a stinkbug in the heat exchanger tube, restricting the flow of the combustion gas. Removed both and used an air hose to blow out the heat exchanger to restore normal operation. I had to disconnect the gas line and remove the igniter assembly to get access to the combustion chamber. I also installed insect screens for the furnace, water heater and refrigerator.
TimLG is offline   Reply With Quote
Old 10-02-2022, 03:42 PM   #19
Senior Member
 
Join Date: Sep 2016
Location: WI
Posts: 324
I love what the DIY'ers know! I fall short of that, but for now I have ordered a new regulator which I can install, and I suppose I can check my battery while the shore power is disconnected and while the camper lights are turned on ?
__________________
Sierra Destination Camper - 2017 401 FLX
dcavaiani is offline   Reply With Quote
Old 10-02-2022, 05:44 PM   #20
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,458
Let us know?

Quote:
Originally Posted by dcavaiani View Post
I love what the DIY'ers know! I fall short of that, but for now I have ordered a new regulator which I can install, and I suppose I can check my battery while the shore power is disconnected and while the camper lights are turned on ?
Keep us posted with your progress.
  • Did you do the sound checks I suggested? The fans blow, right. Did you hear the gas valve open? Did you hear the click-click?
  • Did you look into the furnace intake and exhaust ports on the outside of the trailer, using a flashlight? Did you probe them with a straightened coat hanger? Did you smell the outside exhaust port while running a trial?
  • When you turned the furnace on, how long did it run before the fans stopped? Did you get the three cycles before lockout? The fan would have run continuously, but you would hear three separate gas valve open/closes and click-click cycles.
The regulator is a high-failure rate item, but I don't favor replacing things by guessing--we used to call it Easter-egging. Sometimes it introduces a second problem. Answering some of these questions will rule out other causes.
__________________
Larry
"Everybody's RV is not like your RV."
"Always take pictures with the button on the right."
"Always bypass the water heater before opening the low-point drains."
Sticks and Bricks: Raleigh, NC
2008 Cherokee 38P: at Ivor, VA permanently
Larry-NC is offline   Reply With Quote
Reply

Tags
furnace

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 11:38 PM.