Lpg gas Onan Generator

2401r air works perfect under dockside power, but not working under generator only power, and yes batteries are on, help please. Thanks!
BEMR is offline   Reply With Quote
Old 08-19-2017, 08:27 PM   #2
2012 Solera
 
Join Date: May 2012
Posts: 1,823
Our 2012 Solera runs the 13.5K air-con okay on the propane generator. Which air-con do you have? 13.5K or 15K? Saw some posts a while ago reporting problems running the 15K air-con on the diesel generator (which has less rated output power than the propane generator).

Also, what other 120 volt items are turned on? I believe, other than air-con, the biggest 120 volt power users are the water heater and the microwave. Next, I think, are the refrigerator and the converter. Easy to turn off the microwave and switch both the water heater and the refrigerator to propane.
__________________
JLeising
2012 Solera "S"
Calif SF Bay Area
JLeising is online now   Reply With Quote
Old 08-19-2017, 08:29 PM   #3
Senior Member
 
Join Date: May 2013
Location: Missouri
Posts: 908
Quote:
Originally Posted by BALLZITCH View Post
2401r air works perfect under dockside power, but not working under generator only power, and yes batteries are on, help please. Thanks!
What size generator is it?
What are you trying to run on it?
__________________
Mark B.
2021 GMC 1500
Anderson WDH
markb5900 is offline   Reply With Quote
Old 08-19-2017, 08:44 PM   #4
Member
 
Join Date: Sep 2016
Location: Canyon Hills CA
Posts: 53
Quote:
Originally Posted by markb5900 View Post
What size generator is it?
What are you trying to run on it?
RV. QG 3600 ONAN L.P. just trying to run air only.
BEMR is offline   Reply With Quote
Old 08-19-2017, 08:45 PM   #5
Senior Member
 
Join Date: May 2013
Location: Missouri
Posts: 908
Quote:
Originally Posted by BALLZITCH View Post
RV. QG 3600 ONAN L.P. just trying to run air only.
I honestly don't know if a 3600 will run your AC or not.
I never had less than a 4K and it would run the AC.
__________________
Mark B.
2021 GMC 1500
Anderson WDH
markb5900 is offline   Reply With Quote
Old 08-19-2017, 08:48 PM   #6
Member
 
Join Date: Sep 2016
Location: Canyon Hills CA
Posts: 53
Yes it has worked on many occasions just air conditioner as your driving, but air won't kick on now unless dockside pwr.
BEMR is offline   Reply With Quote
Old 08-19-2017, 09:01 PM   #7
Member
 
Join Date: Jun 2017
Posts: 68
Do any other ac items work on the genny.
__________________
David & Teresa
2017 Silverado 3500 HD Duramax 4X4 Crewcab Dully
2017 Cedar Creak Silverback 37MBH
K4DCF is offline   Reply With Quote
Old 08-19-2017, 09:03 PM   #8
Member
 
Join Date: Sep 2016
Location: Canyon Hills CA
Posts: 53
Just noticed 28 hours on generator we used it for 4 hours at the most since new, from factory to California 24 hours use from delivery company? Seems it also could need service too?
BEMR is offline   Reply With Quote
Old 08-19-2017, 09:18 PM   #9
Member
 
Join Date: Sep 2016
Location: Canyon Hills CA
Posts: 53
Quote:
Originally Posted by K4DCF View Post
Do any other ac items work on the genny.
Funny you should ask, NO. Tv and lights but they run with just house batteries right? Microwave not coming on either
BEMR is offline   Reply With Quote
Old 08-19-2017, 09:19 PM   #10
2012 Solera
 
Join Date: May 2012
Posts: 1,823
Do your other 120 volt appliances work (e.g. microwave)? Does the generator stall when you try to start the air-con? From your post, sounds like nothing happens when you try to start the aircon - correct?
If microwave works okay on generator, generator is working and transfer switch has properly engaged. Don't understand in that case why air-con would do nothing but work on shore power. Check the aircon circuit breaker - maybe it kicked off after you ran it on shore power.
If the microwave won't run either, there is likely no 120 volt from the generator getting to the coach. Check some outlets to confirm. There is a circuit breaker on the baseplate of the generator that occasionally kicks off on our Solera. Generator runs, but no output when that happens. Easy to reset, but somewhat difficult to find (open the generator door and search the baseplate). If that breaker isn't it, I would suspect the transfer switch.
__________________
JLeising
2012 Solera "S"
Calif SF Bay Area
JLeising is online now   Reply With Quote
Old 08-19-2017, 09:23 PM   #11
2012 Solera
 
Join Date: May 2012
Posts: 1,823
Was typing when the other posts came in. I suspect the breaker on the generator- by open the generator door I mean both the hatch door and the panel on the front of the generator. The breaker is on the baseplate behind the generator service panel.
__________________
JLeising
2012 Solera "S"
Calif SF Bay Area
JLeising is online now   Reply With Quote
Old 08-19-2017, 09:40 PM   #12
Member
 
Join Date: Sep 2016
Location: Canyon Hills CA
Posts: 53
Duh the breaker inside the genny was tripped for some reason, flipped on all works perfect now. Thanks for those who tried to help.
BEMR is offline   Reply With Quote
Old 08-20-2017, 01:10 PM   #13
Senior Member
 
Telstar's Avatar
 
Join Date: May 2013
Location: La Mirada, CA
Posts: 528
If your fridge is set on automatic it will switch to AC when the gen starts up. Make sure fridge and WH are set to propane only. We have the same gen as you and have no problem running a 15k air unless micro is turned on. If you overload it the breaker at the gen will switch off.
__________________
Gary and Donna
2005 Cardinal 33TS-LX
Trail Air pin box
Center Point suspension
2018 Ram Laramie 3500 6'4" box 2WD
Demco AutoSlide 18k
Telstar is offline   Reply With Quote
Old 08-20-2017, 04:13 PM   #14
Junior Member
 
Join Date: Jun 2017
Posts: 19
Onan gen + air con

In my 2014 Solera 24R I have a 3600 Onan LP gen. I can run Refrigerator, Air Con (15000) and television. Haven't tried the Microwave/convection. I bought mine used a month ago and am learning a lot from this forum. My Gen has 800 hrs on it and it was services when I bought the MH.
Supersprink is offline   Reply With Quote
Old 08-21-2017, 05:06 AM   #15
Junior Member
 
Join Date: Aug 2017
Posts: 7
Quote:
Originally Posted by BALLZITCH View Post
2401r air works perfect under dockside power, but not working under generator only power, and yes batteries are on, help please. Thanks!
Check the breaker on the. Generator next to the start switch. I had the same thing happen on my 2401r.
djb2400r is offline   Reply With Quote
Old 09-12-2017, 05:41 PM   #16
Member
 
Join Date: Sep 2017
Posts: 54
Cool

On my new rig, 2401, the breaker was off when I picked it up. Of course everything worked fine on shore power during PDI, but I went to break the generator in and had no battery charging, A/C, microwave, etc.

Called the PDI guy and he led me to the breaker and all's well.

John C
JOhn_R_C is offline   Reply With Quote
Reply

Tags
gas, generator

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 12:33 AM.