Exclamation Both A/c's won't always run on generator especially when hot (when needed most!)

Hello! new to forum and itt seems others have had similar issues but wanted to know the latest on this issue if anyone knows. My dealer is having issues narrowing down the problem, I have a 2013 329 Georgetown with a Onan 5.5 and 2 Dometic A/C's.

Often, not always, when I try to turn on the 2nd A/C, the generator shuts off power to both. I have to then wait a few minutes, restart the a/c 's again. They may fail 1 out of 4 attempts. This problems never happens on shore power. The dealer seems to think it might be a heat factor on the a/c 's because he asked me when it happened more and I said when it's hot outside. Isn't that when you need an a/c i said! It rarely fails for them in their much cooler service bays. However, I'm asking them why couldn't this be a generator issue???

The R/V is only a year old and has approx 200 hours on generator, so it's fairly new. I'm asking if they can't run diagnostics or monitor the amperage draw on both generators and/or the a/c units. They appear to be hesitant because it doesn't fail often and they are not being paid for "diagnostic time". So, they are motivated to have it get worse(at my expense and frustration) before identifying issues because they are more likely to get paid for an identified failed component that is covered under warranty. It has failed in their presence although the mechanic appears to be skeptical. Any ideas would be appreciated.
Thanks jerry!
Reyco50 is offline   Reply With Quote
Old 09-04-2014, 02:04 PM   #2
Senior Member
 
bubbles's Avatar
 
Join Date: Dec 2012
Posts: 7,652
Quote:
Originally Posted by Reyco50 View Post
Hello! new to forum and itt seems others have had similar issues but wanted to know the latest on this issue if anyone knows. My dealer is having issues narrowing down the problem, I have a 2013 329 Georgetown with a Onan 5.5 and 2 Dometic A/C's.

Often, not always, when I try to turn on the 2nd A/C, the generator shuts off power to both. I have to then wait a few minutes, restart the a/c 's again. They may fail 1 out of 4 attempts. This problems never happens on shore power. The dealer seems to think it might be a heat factor on the a/c 's because he asked me when it happened more and I said when it's hot outside. Isn't that when you need an a/c i said! It rarely fails for them in their much cooler service bays. However, I'm asking them why couldn't this be a generator issue???

The R/V is only a year old and has approx 200 hours on generator, so it's fairly new. I'm asking if they can't run diagnostics or monitor the amperage draw on both generators and/or the a/c units. They appear to be hesitant because it doesn't fail often and they are not being paid for "diagnostic time". So, they are motivated to have it get worse(at my expense and frustration) before identifying issues because they are more likely to get paid for an identified failed component that is covered under warranty. It has failed in their presence although the mechanic appears to be skeptical. Any ideas would be appreciated.
Thanks jerry!
Well, a major difference between shore power and gen power is that shore power is 50 amps 2 phase (100 amps total) delivered to 2 load busses (50 amps to each bus). The gen delivers about 49 amps 1 phase (49 amps total) to those 2 busses. The A/C's typically are wired with 1 A/C on bus 1 and the other on bus 2. 5500 watts (gen output) is probably right on the edge of sufficient power in your situation (with everything else powered and both A/C's happen to start up together). JMO.
bubbles is offline   Reply With Quote
Old 09-04-2014, 03:24 PM   #3
Senior Member
 
fonzie's Avatar
 
Join Date: Sep 2010
Location: Eastern Ontario
Posts: 4,167
When running the generator for the AC's, make sure your water heater is on propane only, fridge on propane if possible, reducing current consumption from other appliances might work......
__________________
Fonzie
2011 Rockwood 8319SS with ProPride 3P hitch/GoodYear Marathons/TST TPMS 507
2019 F350 Ruby Red 6.7l diesel 3.31 axle electronic locker
Yamaha 3000iseb generator:Progressive Ind. EMS-HW30C : Eastern Ontario
Nights Camped: 2014 (18) 2015 (18) 2016 (36) 2017 (32) 2018 (42) 2019 (28) 2020 (35)
fonzie is offline   Reply With Quote
Old 09-04-2014, 03:37 PM   #4
Member
 
Join Date: May 2014
Posts: 53
I have the same issue on my 2015 351DS. I'm just guessing too much power needed from the generator. Mine happens when I drive and use the generator to power the fridge, tv, whatever else plugged in such as phone, etc. It would turn on for a bit and eventually trip the breaker on the generator. I learn to live with just using the back one and the fronts being cooled by the front cab A/C from the RV itself.
sithc is offline   Reply With Quote
Old 09-04-2014, 05:07 PM   #5
Grape Escape
 
Join Date: Sep 2006
Location: Southern Ontario
Posts: 774
That is why 7KW is offered as option which will run everything.
__________________
2008 Cardinal 30RKLE 5th wheel sold
2006 Rockwood 2607, 2001 Traillite
55 nights 2009, 53 for 2010
44 for 2011, 38 for 2012, 35 for 2013, 51 for 2014
dezolen is offline   Reply With Quote
Old 09-04-2014, 05:50 PM   #6
Senior Member
 
Join Date: Sep 2013
Posts: 216
Maybe fr should have installed the bigger one so no problems huh


Sent from my iPad using Forest River Forums
rwehba is offline   Reply With Quote
Old 09-04-2014, 05:55 PM   #7
Senior Member
 
Join Date: May 2013
Location: Whitehouse, Texas
Posts: 1,275
I have a 2013 378XL
5500 watt generator
Both a/c running and can still run the microwave. Even when it is very hot.
I'm not a certified mechanic but sounds like a generator inverter problem
Let us know if you find out


Sent from my iPad using Forest River Forums
__________________
2013 Georgetown XL 378
2008 Honda CR-V
wrapperman is offline   Reply With Quote
Old 09-04-2014, 05:58 PM   #8
Senior Member
 
Cypressloser's Avatar
 
Join Date: May 2014
Location: Alberta - East of the Rockies, West of the Rest
Posts: 1,785
The key here is the power draw most aren't aware off and that is the battery charger.
Depending on generator type and setup (btw. the same applies to shore power) the power is either fed directly to the batteries and the AC's or fed through the RV's converter/charger and then shared. This draw can be as much as 15 Amp AC on larger chargers. One option is to let the batteries charge for a couple of hours before starting the AC that shares the circuit with the charger.
__________________
2018 RAM 5500 Laramie CC
Sold: Riverstone Legacy 38RE, 960 Watt Solar, 6x6 Volt AGM Battery Bank, Freedom SW 3012 Inv/Charger
Ordered: 2021....
Cypressloser is offline   Reply With Quote
Old 09-04-2014, 06:08 PM   #9
Junior Member
 
Join Date: Jan 2014
Location: Tucson
Posts: 27
Quote:
Originally Posted by bubbles View Post
Well, a major difference between shore power and gen power is that shore power is 50 amps 2 phase (100 amps total) delivered to 2 load busses (50 amps to each bus). The gen delivers about 49 amps 1 phase (49 amps total) to those 2 busses. The A/C's typically are wired with 1 A/C on bus 1 and the other on bus 2. 5500 watts (gen output) is probably right on the edge of sufficient power in your situation (with everything else powered and both A/C's happen to start up together). JMO.
Thank you for yur response JMO. Yes, your absolutely correct based on what my Tech said also. However, it fails with only the 2 a/c's and nothing else on since I've been very careful not to overload. Pls let me know if you know of anything else that might need checking. thank you…jerry
Reyco50 is offline   Reply With Quote
Old 09-04-2014, 06:59 PM   #10
Senior Member
 
bubbles's Avatar
 
Join Date: Dec 2012
Posts: 7,652
Quote:
Originally Posted by Reyco50 View Post
Thank you for yur response JMO. Yes, your absolutely correct based on what my Tech said also. However, it fails with only the 2 a/c's and nothing else on since I've been very careful not to overload. Pls let me know if you know of anything else that might need checking. thank you…jerry
Since it does operate normally otherwise (Im assuming it is) all I can possibly think of is to let an authorized gen repair facility connect a load bank to the unit and check that the advertised output load is being produced. Could possibly be a 60Hz issue also because of speed controls. There are numerous adjustements the repair facility can make. It's kind of difficult to try and come up with just one reason for these gen issues, such as your's because it evidently functions just fine in all other scenarios. I'm sorry I could not be of further assistance to your questions. There are very knowledgeable individuals on this forum and maybe one will chime in. I have always had a 70kva gen and this issue has never happened to me. Good luck. JMO
bubbles is offline   Reply With Quote
Old 09-04-2014, 07:12 PM   #11
Senior Member
 
Join Date: Aug 2014
Posts: 259
I have a 5500 gen.. And run two 13k AC units in Fl heat with out a problem.... I also run my microwave convection oven at the same time without issue... I will mention..when I went to pickup my unit during the PDI the gen trip the breaker when both units fired up... ( didn't happen when my inspector checked it).. They had a Cummings Gen specialist there ... He checked a few things.. Had dealer change the plug for the 50amp cord ( it was loose) where it plugged into the gen.. Then he replaced the board on the gen....it's been running everything without issue... Even making the newbie mistake of firing up generator with both AC on....
__________________
2010 Georgetown 300FWSSouth Florida
speedjester is offline   Reply With Quote
Old 09-04-2014, 07:56 PM   #12
Senior Member
 
Join Date: Aug 2014
Posts: 496
If you have 2-15k btu Ac units then forget it. Too much power draw. If 2-13,5k then it should work fine. I have the same genny and it will run everything and 1-15k btu Ac no problem.
__________________
Doc
____________________________________
2014 V-Cross Platinum 365VTSB (Bought Labor Day 2014)
TV: 2016 GMC 3500 Denali - Motor Ops Tuned
Days Camped 2016: 28
Days Camped 2017: 25 so far
DocGTO is offline   Reply With Quote
Old 09-04-2014, 10:15 PM   #13
Senior Member
 
Join Date: Oct 2013
Location: Tigard, Oregon
Posts: 472
We have 2 15 AC units and I run them on the genny no problem when driving. Have even used th microwave. 351Ds.
ChrisAndGarren is offline   Reply With Quote
Old 09-05-2014, 07:25 AM   #14
Senior Member
 
Dijoeboss's Avatar
 
Join Date: May 2013
Posts: 532
Been dealing with this very issue since Feb. 2013 on XL, no fix other than to consider a larger generator! Installed hard start capictors, no help, changed out transfer switch, no help, I've just learned to accept the fact that it would have been nice to have gotten the larger generator from the start!!


2013 Georgetown XL 350
Bunkhouse
2002 F250 4X4 CC
2012 Jeep Liberty
Dijoeboss is offline   Reply With Quote
Old 09-05-2014, 02:46 PM   #15
Senior Member
 
Join Date: May 2013
Location: Whitehouse, Texas
Posts: 1,275
I don't understand why it doesn't provide enough power for everything on your coach.
My 5500 watt generator powers everything on my 378 xl. Including 2 heats strips (1500 watts each)( A/C's are 1500 watts each), fireplace heater (1500 watts refrigerator, microwave and all lights with no trouble.
If it is still under warranty take it to a certified Onan dealer and have them put it under a load test.
Let us know how things turn out.
Good luck



Sent from my iPad using Forest River Forums
__________________
2013 Georgetown XL 378
2008 Honda CR-V
wrapperman is offline   Reply With Quote
Old 09-05-2014, 08:47 PM   #16
Tim & Lisa Trempert
 
Join Date: Sep 2008
Posts: 458
I run 2 A/C all the time and whatever else I want including the water heater (on electric) and never once have I blown a breaker. 3+ years.....something is wrong with the generator. I would start by checking the voltage output by starting the generator without load and checking the voltage at one of the outlets. I would say ideal is 115-120V with a preference of 120V. Then start the A/C's one by one and see if the voltage is maintained at the outlet. As voltage drops, more current is drawn and that will blow the breaker every time. I'm guessing the generator voltage is either set too low or is not being maintained with a load. One trick is to have the voltage set 2-3 volts higher than the specs. It won't hurt anything and will lower the current draw.
__________________
Tim & Lisa
2011 Georgetown 350
Trempert is offline   Reply With Quote
Old 09-06-2014, 01:18 AM   #17
Senior Member
 
Dijoeboss's Avatar
 
Join Date: May 2013
Posts: 532
Both A/c's won't always run on generator especially when hot (when needed most!)

How do you set the voltage? I didn't know it was adjustable???

I have been fightin tryin to run 2 a/c's all day-- it ain't happenin!!!!

2013 Georgetown XL 350
Bunkhouse
2002 F250 4X4 CC
2012 Jeep Liberty
Dijoeboss is offline   Reply With Quote
Old 09-06-2014, 08:04 PM   #18
Tim & Lisa Trempert
 
Join Date: Sep 2008
Posts: 458
Sorry, I now realize the voltage is electronically controlled at 120 volts. I don't think the Onan 5500 has an adjustment. Check the voltage as described earlier. It should stay right at 120v.


Sent from my iPhone using Forest River Forums
__________________
Tim & Lisa
2011 Georgetown 350
Trempert is offline   Reply With Quote
Old 09-08-2014, 08:01 AM   #19
Junior Member
 
Join Date: Jan 2010
Location: Louisville, Ky.
Posts: 19
Both AC's

My 2011 378 has the same 5500 onan. Runs everything at the same time with no problem. 2-13.5s in my unit. The only problem I have is that with both ac's on, traveling down the road, the transfer switch shuts off power to everything especially during drive over very rough roads.
Called Parallax and asked about the ATS 501 transfer switch in my unit, and the gentleman said that this switch was not designed for a moving vehicle such as a motorhome. For fixed installations it was fine, but extreme vibration would cause it to turn off power. If that is the case, G-town needs to look at another brand that is up to the task!
We are still extremely happy with our unit, and April Conner has helped get all the problems fixed. I only wish the overhead front drop down bed had been available when we bought our unit from Lazy Days.
Happy camping!
__________________
Paul and Rosemary
2011 Georgetown 378 Firemist
2010 Jeep Liberty Limited 4X4
Maddog378 is offline   Reply With Quote
Old 09-08-2014, 10:45 AM   #20
Member
 
Join Date: May 2014
Posts: 53
That could possibly be the case. As the only time I use the generator is when I'm driving.
sithc is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 03:52 AM.