50 amp vs 30 amp?

Last min reservation this weekend, I was able to get 30 amp site. I have a Georgetown, 50 amp. Will I be able to use all the normal appliances or will I be limited on what I can use at the same time. Advice please....thanks
Leismom is offline   Reply With Quote
Old 08-17-2016, 09:02 AM   #2
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,924
Quote:
Originally Posted by Leismom View Post
Last min reservation this weekend, I was able to get 30 amp site. I have a Georgetown, 50 amp. Will I be able to use all the normal appliances or will I be limited on what I can use at the same time. Advice please....thanks
They will be all powered via the adapter but you are going to be limited to what you can use at the same time.

Simply put, when using a 120/240 volt 50 amp split phase service, your RV has TWO 50 amp legs powering it, each at 50 amps for a grand total of 100 amps of potential power.

A 30 amp single phase service has ONE leg at 30 amps for a grand total of 30 amps of potential power.

So, when you have to use an adapter and plug into the 30 amp service, you are actually moving from 100 amps of potential power, to 30 amps....and cannot use everything at the same time as you could when plugged into a 50 amp outlet. You need to remember that your power potential has dropped by over two/thirds when using a 30 amp outlet.

This link explains the differences and the last paragraph explains the adapter you are using:


Electrical Tutorial - Chapter 3 - 30 Amp versus 50 Amp
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is offline   Reply With Quote
Old 08-17-2016, 09:02 AM   #3
Senior Member
 
SeaDog's Avatar
 
Join Date: Jan 2016
Location: x
Posts: 12,423
You will be somewhat limited, your coach is designed for 50 amps to run all your equipment. What will happen is if you bring on to many appliances you may trip the 30 amp breaker. Make sure you have the 30 to 50 amp adapter before you leave.
__________________
Retired Navy
Jake my sidekick (yellow Lab) 10/04 - 05/20
2017 RAM 2500 CC 4X4 Cummins Diesel
2016 Flagstaff 26 FKWS
AF&AM & El Korah Shrine of Idaho
SeaDog is offline   Reply With Quote
Old 08-17-2016, 09:24 PM   #4
Senior Member
 
Join Date: Jul 2009
Location: Warsaw,NC
Posts: 7,184
Run your hot water heater on propane and if you have a RV refrigerator run that on gas. I would say than half of all campers have only 30amps and they get along fine


Sent from my iPhone using Forest River Forums
spock123 is offline   Reply With Quote
Old 08-18-2016, 12:56 AM   #5
Senior Member
 
kfd82's Avatar
 
Join Date: Jul 2016
Location: Madisonville, TX
Posts: 251
I'm still new to all this, but I was told I could run everything except my 2nd air conditioner.

May not be able to run the microwave and a hair dryer and the AC all at once, but you should be able to run everything you need.
kfd82 is offline   Reply With Quote
Old 08-18-2016, 03:50 AM   #6
Senior Member
 
Join Date: Mar 2016
Posts: 353
Quote:
Originally Posted by kfd82 View Post
I'm still new to all this, but I was told I could run everything except my 2nd air conditioner.

May not be able to run the microwave and a hair dryer and the AC all at once, but you should be able to run everything you need.
In a perfect world, unfortunately most campgrounds do not have perfect nor adequate services for the number of sites they have.

the electrical services per code is NOT required to handle the full load capacity of all the outlets. Most parks will be using all those outlets on a busy weekend, therefore your voltage will be on the low end causing your amperage to be on the high end.

You don't want to use the micro, water heater, a hair dryer and the Air conditioner at the same time. The starting load on the Air conditioner alone will be 20+ amps, water heater - 12 amps, 1000 watt microwave - 9 amps. 1500 watt hair dryer - 12 amps.

Then there is the power inverter that is running all the time that uses a share of the 30 amp capacity.

The only way you will be able to tell what you can run at the same time is by trial and error and most likely will not be the same at every location.

The DW found out the hard way a couple weekends ago. The campground was near capacity. She was running the microwave when the Air conditioner fired up causing our 30 Amp main to trip.

FWI those main breakers in your electrical panel get weaker with each time they trip and after a while will either not trip or trip well below their rated capacity... to low is safe, too high is dangerous and can lead to fires.
ShermanD is offline   Reply With Quote
Old 08-18-2016, 02:17 PM   #7
Junior Member
 
fljl's Avatar
 
Join Date: Jan 2016
Posts: 17
Had same issue, lites, micro and AC would trip a 30 amp. Could have been weak breaker. 50 will do two AC and everything else.
__________________
2015 GMC SLT CC Reese 20K
fljl is offline   Reply With Quote
Old 08-18-2016, 02:34 PM   #8
Senior Member
 
Join Date: Jan 2016
Location: Benbrook, Tx
Posts: 508
A few weeks ago we went to a campground that only had 30 amps available. We tried it for about an hour. Got fed up with the power shutting down when ever we tried to run a couple of things and one ac just not doing it. We're spoiled with our 50 amp system and running whatever we want.
We ended up packing it in and moving to another campground that was about an hour north. 50 amp and ran whatever we wanted. Just not exactly where we wanted to be. But hey, we were camping right?


The first camp was pretty busy as well and with older looking boxes.
__________________
Dwayne and Susan
Jiro and Phoebe-4 legged family members
Mike and Dana - Traveling buddies
2016 Ford F350 XLT 6.7 Powerstroke DRW 4X4
2016 Brookstone 395RL
dwayneb236 is offline   Reply With Quote
Old 08-18-2016, 03:19 PM   #9
Senior Member
 
Kenny kustom's Avatar
 
Join Date: Sep 2015
Posts: 3,464
Quote:
Originally Posted by dwayneb236 View Post
A few weeks ago we went to a campground that only had 30 amps available. We tried it for about an hour. Got fed up with the power shutting down when ever we tried to run a couple of things and one ac just not doing it. We're spoiled with our 50 amp system and running whatever we want.
We ended up packing it in and moving to another campground that was about an hour north. 50 amp and ran whatever we wanted. Just not exactly where we wanted to be. But hey, we were camping right?


The first camp was pretty busy as well and with older looking boxes.

We are in the same boat.
Except, no option to move to 50A.

That's why I put in a hybrid inverter.
I can run whatever I want off 30A.
Well worth the cost of the inverter.


2016 Sabre 36QBOK
2015 Ram 3500 CUMMINS
Bring Back The Search!
__________________
2017 Dynamax Isata 4
Kenny kustom is offline   Reply With Quote
Old 08-18-2016, 03:38 PM   #10
Some guy in back...
 
Join Date: Sep 2011
Posts: 218
A hybrid Inverter?

Quote:
Originally Posted by Kenny kustom View Post
We are in the same boat.
Except, no option to move to 50A.

That's why I put in a hybrid inverter.
I can run whatever I want off 30A.
Well worth the cost of the inverter.


2016 Sabre 36QBOK
2015 Ram 3500 CUMMINS
Bring Back The Search!
Kenny, what is a "hybrid inverter"? What Make & model did you put in?
__________________
ChateauV10
St. Charles, MO
Ex-SF Bay Area
'99 Ford E350 V10
'16 Rockwood 8329SS
ChateauV10 is offline   Reply With Quote
Old 08-18-2016, 06:14 PM   #11
Member
 
Join Date: Jun 2016
Posts: 80
Quote:
Originally Posted by wmtire View Post
They will be all powered via the adapter but you are going to be limited to what you can use at the same time.

Simply put, when using a 120/240 volt 50 amp split phase service, your RV has TWO 50 amp legs powering it, each at 50 amps for a grand total of 100 amps of potential power.

A 30 amp single phase service has ONE leg at 30 amps for a grand total of 30 amps of potential power.

So, when you have to use an adapter and plug into the 30 amp service, you are actually moving from 100 amps of potential power, to 30 amps....and cannot use everything at the same time as you could when plugged into a 50 amp outlet. You need to remember that your power potential has dropped by over two/thirds when using a 30 amp outlet.

This link explains the differences and the last paragraph explains the adapter you are using:


Electrical Tutorial - Chapter 3 - 30 Amp versus 50 Amp
How is 100 amps possible with a 50 amp breaker? If you tried to se 100 amps wouldn't the breaker trip?
Steve29rlx is offline   Reply With Quote
Old 08-18-2016, 06:35 PM   #12
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,924
Quote:
Originally Posted by Steve29rlx View Post
How is 100 amps possible with a 50 amp breaker? If you tried to se 100 amps wouldn't the breaker trip?
A 120/240 volt split phase service is really simple once you understand it, but it can take a bit to get your head wrapped around it. The biggest confusion is people thinking that 120/240 split phase works like 120 volt single phase.....which it doesn't.

The main thing to understand is that a 50 amp service is 50 amps at 240 volts or 100 amps at 120 volts. Both produce 12000 watts. Watts= amps X volts

A double pole 50 amp circuit breaker grabs 50 amps from one pole/leg (L1) at 120 volts and another 50 amps from another pole/leg (L2) at 120 volts.

To get 240 volts, you have to have an item connected to both L1 and L2.

The RV doesn't have items connected to both L1 and L2...but instead uses the L1 and L2 separately, so L1 provides 50 amps at 120 volts and L2 provides another 50 amps at 120 volts....... for a total of 100 amps at 120 volts.

Now the L1 and L2 share a common neutral wire (you have to have a neutral when using 120 volts), which is also only rated to carry 50 amps. However, the way the split phase service works is called load balancing as power shuttles back and forth between L1 and L2. The neutral only carries the imbalance.

If you are using 45 amps on L1 and 40 amps on L2...then the imbalance is 5 amps, and this is what the neutral wire carries.

At the extreme, say you are using the max on L1 of 50 amps (as per its circuit breaker max). Then say you are using 0 amps on L2. Then the neutral carries the imbalance of 50 amps (which it is rated for). If something were to happen on either L1 or the L2 and the amps were exceeded on either, then since a double pole breaker is in essence two breakers tied together, if one side trips, then the other side has to trip too. This also protects the shared neutral wire so neither L1 or L2 can make it carry any possible imbalance of over 50 amps.

It's explained a lot better in this link. it takes a little to wrap your head around it, but you will.

Electrical Tutorial - Chapter 3 - 30 Amp versus 50 Amp

More reading;

http://www.rv-motorhome-answers.com/AC-Electricity.html

http://www.myrv.us/electric/

http://www.nojolt.com/Understanding_...circuits.shtml
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is offline   Reply With Quote
Old 08-18-2016, 06:59 PM   #13
Senior Member
 
Kenny kustom's Avatar
 
Join Date: Sep 2015
Posts: 3,464
Quote:
Originally Posted by ChateauV10 View Post
Kenny, what is a "hybrid inverter"? What Make & model did you put in?

Magnum msh3012m

It's a 3k watt inverter than can use battery power to support the shore power. I split most of the rig ac circuits into the sub panel.
I tell the inverter to use 14 amps from the shore power. Any more draw, and the inverter will pull from the batteries.

I also run both fridges on electric while on the road.

Click image for larger version

Name:	ImageUploadedByForest River Forums1471564524.419017.jpg
Views:	165
Size:	244.0 KB
ID:	117740

I did some testing the other day.
Ran the front ac right off the batteries. Click image for larger version

Name:	ImageUploadedByForest River Forums1471564744.394893.jpg
Views:	142
Size:	101.9 KB
ID:	117741

After an hour, the batteries were still at 85% SOC.


2016 Sabre 36QBOK
2015 Ram 3500 CUMMINS
Bring Back The Search!
__________________
2017 Dynamax Isata 4
Kenny kustom is offline   Reply With Quote
Old 08-18-2016, 08:00 PM   #14
Senior Member
 
Evereddie's Avatar
 
Join Date: Feb 2013
Location: Pfafftown NC
Posts: 2,353
I think 50 amp service should be called 100 amp service. That is what it is and it would eliminate much of the confusion. Ya, it's split between 2 legs but it is still 100 amps for the rig.
__________________
There are 10 types of people in the world.
Those that know binary, and those that don't.

2013:31 / 2014:51 / 2015:58 / 2016:37 / 2017:46
2018:16
Total 239
Evereddie is offline   Reply With Quote
Old 08-18-2016, 08:29 PM   #15
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,143
Quote:
Originally Posted by Evereddie View Post
I think 50 amp service should be called 100 amp service. That is what it is and it would eliminate much of the confusion. Ya, it's split between 2 legs but it is still 100 amps for the rig.
I disagree. It is NOT a 100 amp service. Any draw of more than 50 amps per phase, will trip the breaker. A more appropriate name might be 'Dual 50 Amp' but not 100 amp.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=90
5picker is offline   Reply With Quote
Old 08-18-2016, 09:46 PM   #16
Senior Member
 
Evereddie's Avatar
 
Join Date: Feb 2013
Location: Pfafftown NC
Posts: 2,353
Quote:
Originally Posted by 5picker View Post
I disagree....
Here, someone always will.
Let's try this,...the sky is blue.
__________________
There are 10 types of people in the world.
Those that know binary, and those that don't.

2013:31 / 2014:51 / 2015:58 / 2016:37 / 2017:46
2018:16
Total 239
Evereddie is offline   Reply With Quote
Old 08-18-2016, 10:14 PM   #17
Senior Member
 
B and B's Avatar
 
Join Date: Jun 2013
Posts: 10,833
Send a message via AIM to B and B
If North America abandoned 120 v and went 240 volt for RV's the anacondas we have to carry would have the size. Just 100 amps at 240 volt or 30 amp 120.
__________________
B and B
2022 Venture RV SportTrek STT 302 VRB Travel Trailer
2018 Heartland Landmark 365 Louisville 5th Wheel
2015 Heartland Bighorn 5th Wheel
2013 FR Rockwood 8289WS 5th Wheel
2012 FR Rockwood 2703 SS Travel Trailer
B and B is offline   Reply With Quote
Old 08-19-2016, 07:25 AM   #18
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,143
Quote:
Originally Posted by Evereddie View Post
Here, someone always will.
Let's try this,...the sky is blue.
Nope... not today. Cloudy & grey.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=90
5picker is offline   Reply With Quote
Old 08-19-2016, 07:30 AM   #19
Senior Member
 
Join Date: Mar 2016
Posts: 353
Quote:
Originally Posted by 5picker View Post
I disagree. It is NOT a 100 amp service. Any draw of more than 50 amps per phase, will trip the breaker. A more appropriate name might be 'Dual 50 Amp' but not 100 amp.
X2

A 100 amp 120/240 volt residential service provides 100 amps of 120 volt power on each of two hot legs with the neutral wire capable of carrying an unbalanced load of 100 amps.

A 50 amp 120/240 volt RV service provides 50 amps of 120 volt power on each of two hot legs with the neutral wire capable of carrying an unbalanced load of 50 amps.

A 30 amp 120 volt RV service provides 30 amps of 120 volts power on one hot leg with the neutral wire capable of carrying the entire load of 30 amps.

A 20 amp 120 volt RV service, used on older popups and ?, provides 20 amps of power on one hot leg with the neutral wire capable of carrying the entire 20 amp load.

It takes two hot wires with a shared neutral in order to have an unbalanced load.

It is my understanding that most RV's do not use any 240 volt appliances, although there is no reason they couldn't. An instant hot water heater would draw half the amps if wired straight 220. Unfortunately the instant hot water heater would be useless without a 50 amp 120/240 volt shore power or generator, which is probably the reasoning for wiring everything 120 volts.
45 year member IBEW retired
ShermanD is offline   Reply With Quote
Old 08-20-2016, 09:09 AM   #20
Senior Member
 
Join Date: May 2016
Posts: 1,363
Quote:
Originally Posted by 5picker View Post
I disagree. It is NOT a 100 amp service. Any draw of more than 50 amps per phase, will trip the breaker. A more appropriate name might be 'Dual 50 Amp' but not 100 amp.


You are correct, more than 50 amps on either leg and the double breaker will trip. You can however pull 50 amps on each leg, which is the 100 amps.




Sent from my iPhone using Tapatalk
325BH is offline   Reply With Quote
Reply

Tags
50 amp


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 04:21 AM.