Almost had a fire

I had my TT hooked up to a 20amp gfci outlet in my garage with a Surge Guard 44260 power protector, to run the a/c and refrigerator. It was running for about an hour when I smelled something burning. I checked the power cord and noticed the surge protector was smoking from the end attached to the trailer 30 amp power cord. The 30 amp cord was also very hot but the 15 amp wall adapter was not. I have no idea why the breaker didn’t trip or what could have caused the short in the surge protector?
Attached Thumbnails
Click image for larger version

Name:	BEECFB41-36E2-40CC-86EE-F8DD944DC4E4.jpg
Views:	194
Size:	278.0 KB
ID:	233897   Click image for larger version

Name:	0E54D760-BD15-47D8-9027-5297FA3832ED.jpg
Views:	221
Size:	545.0 KB
ID:	233898  
Attached Images
 
Spkittrick1 is offline   Reply With Quote
Old 07-14-2020, 11:47 AM   #2
llr
Senior Member
 
Join Date: Feb 2017
Location: SW Ohio
Posts: 1,680
A bad connection or corroded plug or socket. I highly doubt if it was over the 30A rating especially since you are in a 20A outlet.

FYI, you a pushing it to run the fridge and AC on the 20A circuit but that was not an issue here.
__________________
2024 Artic Fox 3018 5th Wheel
Grand Design 2800BH TT 2021 - for sale
Prior TT 2017 Flagstaff 831CLBSS Classic Ultra lite - SOLD 5/21
TV 2024 F350 DRW - on order
Prior TV 2017 F150 6.5' bed 3.5 Eco-boost Max tow 1800lbs payload
llr is offline   Reply With Quote
Old 07-14-2020, 11:58 AM   #3
Site Team
 
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
A burnt connection is a more common occurrence than it should be, but we see them here pretty often.

A burned connection like that doesn't increase the amperage so the breaker won't trip unless it burns badly enough to encompass the hot and neutral or ground.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
Bama Rambler is offline   Reply With Quote
Old 07-14-2020, 12:32 PM   #4
Senior Member
 
ceedog's Avatar
 
Join Date: Sep 2013
Posts: 380
If the connection between the cord & surge protector isn't real tight it can cause arcing which could have caused your problem.


Arcing might not trip the breaker.
__________________
It ain't easy being me...I've tried.

ceedog is offline   Reply With Quote
Old 07-14-2020, 12:56 PM   #5
Pickin', Campin', Mason
 
5picker's Avatar
 
Join Date: Aug 2015
Location: South Western PA
Posts: 19,074
I'll agree with a loose/poor blade connection.

I have gotten into the habit of spreading the tangs periodically on the plug side (shore power and surge guard) and squeezing the blades on the receptacle side. (surge guard/outlet with power off!)
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2017 Ford F-Series SCREW 4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA

Days Camped '19=118 '20=116 '21=123 '22=134 '23=118 '24=86
5picker is offline   Reply With Quote
Old 07-14-2020, 01:03 PM   #6
Senior Member
 
rsdata's Avatar
 
Join Date: Aug 2014
Location: Northern KY
Posts: 5,724
I squirt all outside metal connections periodically with this stuff...

helps keep bad connections under control
Attached Thumbnails
Click image for larger version

Name:	deoxit02.jpg
Views:	472
Size:	28.8 KB
ID:	233904  
__________________
"nothing can now be believed which is seen in a newspaper. Truth itself becomes suspicious by being put into that polluted vehicle."
Thomas Jefferson to John Norvell pg. 2, June 11, 1807

2014 Shamrock 183
2014 RAM 1500 Bighorn Crew Cab, HEMI, 3.21 gears, 8 Spd, 4X4 TST TPMS
rsdata is offline   Reply With Quote
Old 07-14-2020, 01:09 PM   #7
Senior Member
 
dbledan's Avatar
 
Join Date: Jan 2017
Location: KS
Posts: 2,369
Quote:
Originally Posted by rsdata View Post
I squirt all outside metal connections periodically with this stuff...

helps keep bad connections under control
X2 great stuff. I also adjust the blades as necessary as well.
dbledan is offline   Reply With Quote
Old 07-14-2020, 03:01 PM   #8
Senior Member
 
Join Date: Sep 2016
Location: Colorado
Posts: 1,306
As discussed here on a number of other occasions be sure to turn off the breaker before connecting your cords, and EMS units. Arcing over time, will cause the ends to burn/ corrode and eventually creat a high resistance connection causing heat. The prongs may not fail at that time, but down the road when put under heavier load. My experience with burned prongs on my adapters and cords all came under similar load situations to yours. 20 amp outlet with the AC on. If you see any heat signs on any of your cords, toss em.
__________________
2003 Duramax
2017 Crusader 315

2016 Boston Whaler Montauk 150
Former Montana owner
Colorado Cruiser, Over the Pass and Down the Hill
Comanchecreek is offline   Reply With Quote
Old 07-14-2020, 03:09 PM   #9
Senior Member
 
Join Date: Jun 2017
Location: British Columbia Canada
Posts: 556
I clean the blades often, actually every other time i plug in. I carry a piece of emery cloth in my electrical bay If you continue to use a 20 amp circuit for your A/C you should periodically feel the electrical connections for heat. If you have a long run they could easily heat up.
__________________
2017 FR3 28 DS
cariboo camper is offline   Reply With Quote
Old 07-14-2020, 03:10 PM   #10
jkoenig24
 
Join Date: Apr 2015
Location: Box Elder, SD (formerly NY)
Posts: 953
"FYI, you a pushing it to run the fridge and AC on the 20A circuit but that was not an issue here."

Ummmm, I disagree. A PROPERLY WIRED receptacle can CONTINUOUSLY deliver ONLY 80% of its' rating (20A x 80% = 16A CONTINUOUSLY; there is supposed to be a 20% safety factor to cover BRIEF usage above the 80% rule) An air conditioner and a refrigerator together could easily exceed those 16A. Throw in the SURGE drawn when a compressor kicks in and, you have a disaster waiting to happen. Now consider that the circuit breaker has probably seen "better days" and there may well be corroded connections so, it's surprising that we don't see more overheated plugs and receptacles.
jkoenig24 is offline   Reply With Quote
Old 07-14-2020, 06:22 PM   #11
Senior Member
 
Villagerjjm's Avatar
 
Join Date: Aug 2017
Posts: 852
I connect my 30 amp trailer landline to a 20 amp outdoor outlet controlled by a GFCI breaker. I had one adapter that got hot after a few uses and it was on the verge of melting when I took it out of service. I run the AC while plugged in, and I will run other appliances for testing them. I always check the cord, connection and breaker for heat. I use a thermometer to do this... like what they use at the door of a doctors office when they check you. Always monitor!!!! Always !!!
Villagerjjm is offline   Reply With Quote
Old 07-14-2020, 06:37 PM   #12
Senior Member
 
Join Date: Apr 2017
Posts: 175
Never heard of an 80% rule. I HAVE heard of a rated capacity. Also professionally speaking, for whatever reason, the connectors were not making good contact OR the connector was poorly made and the contactor and wire within cable were improperly bonded/crimped.
BigRockr is offline   Reply With Quote
Old 07-14-2020, 08:00 PM   #13
Senior Member
 
Join Date: Aug 2013
Location: Edmonton, Alberta
Posts: 112
Quote:
Originally Posted by BigRockr View Post
Never heard of an 80% rule. I ...........
‘This is true. A 15 amp breaker should not carry a CONTINOUS load exceeding 12 amp. A 20 amp breaker at 16 amps etc. This is an electrical code requirement in Canada and, I might assume, also in the US. (NEC)

As has been discussed multiple times, a motor under start-up (AC unit) can see an inrush current of up to 300% over a short duration. The circuit breaker is a slow reacting device and the inrush is over such a short time, the breaker does not have time to react to the surge.
dnicoll is offline   Reply With Quote
Old 07-14-2020, 08:26 PM   #14
Senior Member
 
Join Date: Aug 2015
Location: Box elder
Posts: 724
https://blog.se.com/datacenter/power...cuit-breakers/
__________________
2015 silverback 31IK
2023 f350
kcmusa is offline   Reply With Quote
Old 07-14-2020, 10:09 PM   #15
Senior Member
 
Join Date: May 2020
Posts: 212
additional amp draw from converter charging batteries

The converter is also increasing the amp draw when plugged into shore power, install a battery disconnect if connected to a 20 amp circuit while running the AC, or even the microwave.
Daniel.mullins4 is offline   Reply With Quote
Old 07-15-2020, 10:04 PM   #16
Senior Member
 
Join Date: Feb 2018
Posts: 160
Trying to draw too many amps through the 15 amp adapter. Very common when trying to run a 30 amp unit with a 15 amp receptacle
__________________
2016 Rockwood Windjammer 3001W
2016 F150 SCREW 3.5 EB
ProPride 3P 1400
Oafdawg is offline   Reply With Quote
Old 07-23-2020, 06:42 PM   #17
Senior Member
 
Join Date: Oct 2018
Posts: 161
I have seen where the problem is the manufacture process. The method of how the fine strand wires are attached to the blade is a trouble spot. Some times after use, or defect in manufacturing, some of the fine wires break off where they attach to the blade. Then instead of a 30 amp connection it is reduced to a lower capacity while heating up the blade. In the case of a molded plug, there is nothing you can do!! But what I do is to buy a cap at the hardware store that screws on. Then you can form the strands and tin them, or use solder to make a solid wire for screwing to the plug. Cut one of these molded plugs apart to see the connections!
wanderer44 is offline   Reply With Quote
Old 07-23-2020, 07:06 PM   #18
Senior Member
 
Join Date: Aug 2016
Posts: 135
The heat is where the high resistance connection is. You clearly had a poor connection where the trailer 30 amp plug connects to the surge protector. Both parts are damaged, I cannot tell you which one started the problem. I can tell you, it had nothing to do with the 20 amp outlet you were plugged into, Again, the heat is where the poor connection is.
__________________
2018 Shadow Cruiser 265RLS
2018 Chevy Silverado 1500 with 5.3 max tow package
Shiawassee County, Michigan
Tacky is offline   Reply With Quote
Old 07-23-2020, 10:55 PM   #19
Senior Member
 
Join Date: Jan 2020
Posts: 4,854
Quote:
Originally Posted by Oafdawg View Post
Trying to draw too many amps through the 15 amp adapter. Very common when trying to run a 30 amp unit with a 15 amp receptacle
I might agree if it was the 15 amp connection point that melted. But look at the photos. It was a 30 amp plug and receptacle that melted.
NavyLCDR is offline   Reply With Quote
Old 07-24-2020, 05:28 AM   #20
Senior Member
 
Papadave's Avatar
 
Join Date: Sep 2018
Location: Murphy NC
Posts: 300
Arrow Breakers go bad too

I would recommend testing the breaker as well. I had one explode and start a fire in the service entrance panel when I reset it. Echo the advice to only attach plugs with the power off. Many marina fires from not bothering to do so.
Papadave is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 06:38 AM.