Using 50A vs 30A on a 30A trailer
Trailer is a 30A setup, 2017 Grey Wolf 26DBH. Is there any advantage/disadvantage to using the adapter and plugging into the 50A receptacle on the pole vs the 30A when both are available? I am sure it has been talked about before but my google search power must be weak, all I come up with are discussions using 30A power on 50A rigs. BTW will be using an EMS-pt30x as well.....or possibly hard wired if there looks like a decent place to do it. I know the breakers in the trailer are on the opposite side from electric in so not sure which route I will end up going.
Thanks!
|
|
|
03-19-2017, 07:45 PM
|
#2
|
Director, FROG
Join Date: Sep 2011
Location: Middlebury, IN
Posts: 3,518
|
Even if you plug your 30-amp trailer into a 50-amp outlet with an adapter, you'll still have only 30 amps. A 30-amp outlet is wired to provide 120 volts on one side, and none on the other. That will provide you with 3,600 watts 30 x 120).
A 50-amp outlet is wired with 120 volts on each side for a total of 12,000 watts (50 x 120 x 2), but your trailer is wired to accept the voltage from only one side to prevent overloading your system, making the other side effectively dead.
There's no advantage or disadvantage to plugging into a 50-amp plug, so you might as well not bother with the adapter.
There's a pretty good non-technical explanation at
|
|
|
03-19-2017, 07:49 PM
|
#3
|
Senior Member
Join Date: Nov 2013
Posts: 1,947
|
Except that it was discussed in a thread here not long ago that the vast majority of times people are using 30 amp, and with the constant flicking on and off of the 30 amp breakers that in some parks the 30 amp breaker becomes weaker and is more susceptible to tripping. So for that reason many prefer using the 50...seems to make sense.
__________________
2016 Chevy Silverado 2500 Duramax
2016 Rockwood 8289WS, Diamond Pkg.
|
|
|
03-19-2017, 07:51 PM
|
#4
|
Director, FROG
Join Date: Sep 2011
Location: Middlebury, IN
Posts: 3,518
|
If you find the situation of a weak 30-amp breaker, it won't hurt to use the 50-amp side, but I'd quickly report the breaker to the park manager as well.
|
|
|
03-19-2017, 07:55 PM
|
#5
|
Senior Member
Join Date: Nov 2013
Location: Seaford, De
Posts: 2,377
|
amps are drawn, not forced. You will never get more in than your rig can handle
__________________
David & Lynn 2014 Coachmen Chaparral Signature 327 RLKS 2016 Ford F350 Lariat CC Dually
|
|
|
03-19-2017, 07:58 PM
|
#6
|
Senior Member
Join Date: Sep 2016
Location: Concord, NC
Posts: 443
|
I like to use the adapter because it seems that many of the 30 amp plugs at parks have a burnt ground terminal at the post. I have been told a few different reasons why that is but the 50 amps connections always look good. So I plug in my 50 to 30 adapter and go with it. I had to replace the end on my trailer one time because of the bad connection at the park. It melted my plug because of the high resistance.
|
|
|
03-19-2017, 08:22 PM
|
#7
|
Canadian Member
Join Date: Feb 2012
Location: Eastern GTA, Ontario, Canada
Posts: 6,235
|
How are the power posts wired? Is the 50A receptacle fed from an entirely different circuit than the 30A receptacle? I understand that the 50A receptacle has 2 legs of 50A at 120VAC with a double 50A breaker, so plugging a 30A trailer into the 50A receptacle means that your power cable is not protected at 30A but aside from that, I just wonder if the 50A circuits would have better, more reliable power since at most campgrounds the majority of trailers connect to the 30A circuit. In the heat of the summer, the 30A circuits tend to have lower voltage because of all the high loads.
I have a 50 to 30 dog bone but try to use the 30A receptacle unless I'm have power issues with the 30A supply.
__________________
2023 Rockwood Signature 8262RBS
2016 Ford F-250 XLT SuperCrew, 6.2L, 4x4, 6'9" bed
2019 Rockwood Signature 8290BS (2019 - 2022)
2011 Rockwood Signature 8293SS (2015 - 2018)
2010 Rockwood Roo 23SS (2012 - 2014)
|
|
|
03-19-2017, 08:38 PM
|
#8
|
Senior Member
Join Date: Sep 2016
Location: Concord, NC
Posts: 443
|
You are right about the breaker being 50 amps. This summer we were hooked up through the 50 to 30 connector and we were using the a/c, water heater on electric, tvs and everything. When we turned on the microwave the main breaker in the trailer tripped. Upside to that though was that we didn't have to go out in the rain to reset it.
|
|
|
03-20-2017, 03:28 PM
|
#10
|
Senior Member
Join Date: Feb 2015
Location: Ohio
Posts: 220
|
Be Careful
Even though your 30 amp breaker in your power center SHOULD trip, your cable is only rated for 30 amps. It will melt before the 50 amp breaker will trip. I wouldn't think that would be very likely, but just wanted to point it out in case you had a dead short before the load center (critter eating the insulation and wires on your incoming power feed).
__________________
2023 Silverado 3500HD CC Long Bed Diesel DRW
2016 Silverback 33IK
|
|
|
03-20-2017, 04:28 PM
|
#11
|
Senior Member
Join Date: Apr 2015
Location: Ontario, California
Posts: 2,146
|
Quote:
Originally Posted by F.R.O.G.;1449214
There's no advantage or disadvantage to plugging into a 50-amp plug, so you might as well not bother with the adapter.
There's a pretty good non-technical explanation at [URL
|
|
|
03-20-2017, 04:48 PM
|
#12
|
Senior Member
Join Date: Jan 2015
Location: Englewood FL
Posts: 2,797
|
There is really only one reason to use a 30 to 50 amp adapter on a 30 amp RV and that is to avoid a tired 30 amp receptacle and a worn 30 amp pedestal breaker. I have a 50 amp coach that really only needs 30 amps most of the time (single A/C). The cable, however, is wired for 50 amps and I generally use it when available.
__________________
2015 335DS
|
|
|
03-20-2017, 06:18 PM
|
#13
|
Senior Member
Join Date: Aug 2015
Location: Sierra Nevada foothills
Posts: 236
|
Quote:
Originally Posted by F.R.O.G.
If you find the situation of a weak 30-amp breaker, it won't hurt to use the 50-amp side, but I'd quickly report the breaker to the park manager as well.
|
Yeah, good luck with that. We were at a park at Big Bear Lake, CA where the 30A receptacle was worn so that it was open ground. No 50A at this spot and the park management was clueless. They have to call an electrician for this so I got by with the 20A and an adapter. Not a big deal.
__________________
2015 Microlite 21 DS
2012 Silverado extended cab Z71
|
|
|
03-20-2017, 07:00 PM
|
#14
|
Senior Member
Join Date: Feb 2016
Posts: 103
|
A few times camping with my ac and water heater running I kept tripped the 30 amp breaker on the pedistol. I plugged in my 50 amp adapter and never tripped the 30 in the camper. I would have to say there is an advantage to running off of 50 amps.
__________________
2016 Coachmen Apex 288BHS
2015 F150 Sport 4x4 3.5 Eco Boost
|
|
|
03-20-2017, 07:09 PM
|
#15
|
Senior Member
Join Date: Jan 2015
Location: Englewood FL
Posts: 2,797
|
Quote:
Originally Posted by 4B11T
A few times camping with my ac and water heater running I kept tripped the 30 amp breaker on the pedistol. I plugged in my 50 amp adapter and never tripped the 30 in the camper. I would have to say there is an advantage to running off of 50 amps.
|
the only explanation for that would be a weak breaker in the pedestal and/or a bad pedestal receptacle that generated a large voltage drop when both were running. You weren't drawing much more that 30 amps or the breaker in your AC panel in the RV would have tripped.
__________________
2015 335DS
|
|
|
03-20-2017, 07:12 PM
|
#16
|
Site Team - Lou
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,269
|
Quote:
Originally Posted by NCBBA11043
Even though your 30 amp breaker in your power center SHOULD trip, your cable is only rated for 30 amps. It will melt before the 50 amp breaker will trip. I wouldn't think that would be very likely, but just wanted to point it out in case you had a dead short before the load center (critter eating the insulation and wires on your incoming power feed).
|
I agree.
Here is a photo of a camper that was using a 30 amp extension cord in addition to the OEM cord. It kept tripping the 30 amp breaker on the pedestal. They moved the extension cord with an adapter to the 50 amp service and the camper was "happy" not seeing more than 30 amps; the 50 amp breakers were "happy"; but the connection between the cord and the extension cord was not "happy".
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
|
|
|
03-20-2017, 07:15 PM
|
#17
|
Senior Member
Join Date: Jan 2016
Location: x
Posts: 12,423
|
This just may be me but I have found at times the 50 amp side of things seems to be more stable when allot of folks are running things like ACs. I always use a surge guard at the pedestal so there is no way I will overload my 30 amp cord.
__________________
Retired Navy
Jake my sidekick (yellow Lab) 10/04 - 05/20
2017 RAM 2500 CC 4X4 Cummins Diesel
2016 Flagstaff 26 FKWS
AF&AM & El Korah Shrine of Idaho
|
|
|
03-20-2017, 07:18 PM
|
#18
|
Senior Member
Join Date: Jun 2013
Posts: 10,833
|
I used to use the 50 amp to 30 amp all of the time. The 30 amp plugs at Goshen for example are loose and will cause the end of your plug to either weld into the outlet or fall out. Resistance in a connection will cause heating. My 30 amp breaker in my trailer was replaced due to tripping with a higher curve model. I do check all connections for heating and also clean them often. I also carry a temp gun and Fluke clamp on ammeter.
__________________
B and B
2022 Venture RV SportTrek STT 302 VRB Travel Trailer
2018 Heartland Landmark 365 Louisville 5th Wheel
2015 Heartland Bighorn 5th Wheel
2013 FR Rockwood 8289WS 5th Wheel
2012 FR Rockwood 2703 SS Travel Trailer
|
|
|
03-20-2017, 07:24 PM
|
#19
|
Senior Member
Join Date: Apr 2016
Location: Cedar Creek Lake, TX
Posts: 3,484
|
Quote:
Originally Posted by SeaDog
This just may be me but I have found at times the 50 amp side of things seems to be more stable when allot of folks are running things like ACs. I always use a surge guard at the pedestal so there is no way I will overload my 30 amp cord.
|
The surge guard is not a breaker. It prevents voltage spikes, it will not prevent an overload. Only the pedestal breaker or RV breaker protects for overload.
|
|
|
03-20-2017, 07:31 PM
|
#20
|
Senior Member
Join Date: Jan 2016
Location: x
Posts: 12,423
|
I do have to check mine I though it also had over amperage and voltage features in it.
__________________
Retired Navy
Jake my sidekick (yellow Lab) 10/04 - 05/20
2017 RAM 2500 CC 4X4 Cummins Diesel
2016 Flagstaff 26 FKWS
AF&AM & El Korah Shrine of Idaho
|
|
|
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
Disclaimer:
This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.
All times are GMT -5. The time now is 01:09 AM.
|