Water heater relief valve.

Hi all
I have a Surveyor Legend. When I select electric hot water every time it trips the pressure relief valve and I get about a quarter of a cup of water that comes out. I do not have this problem when I use propane to heat the water. Any suggestions or thoughts would be greatly appreciated thank you.
Skypod is offline   Reply With Quote
Old 06-20-2019, 11:57 PM   #2
Senior Member
 
Join Date: Mar 2018
Posts: 825
You may get other opinions but if if only happens once per trip, I wouldn't give it a second thought..
Skip12 is offline   Reply With Quote
Old 06-21-2019, 12:12 AM   #3
Senior Member
 
Capt. Mike's Avatar
 
Join Date: Dec 2012
Location: Franklin County, MO
Posts: 2,652
I think what the OP is saying is that it happens every time he tries to run his water heater on electric, but does not happen when he runs the water heater on propane.

You don't say what year your Surveyor is. Did you buy it new or used? Maybe somebody before you put in the wrong heating element and it is overheating the water. That will make the pressure relief valve "pop".
__________________
Mike and Yvonne
and Sophie, the little white dog
2017 Columbus 320RSC
2021 Chevy Silverado 3500HD DRW 4X4 Duramax
“It's not how old you are, it's how you are old.”Jules Renard
"It's not the years...it's the mileage." - Indiana Jones
Capt. Mike is offline   Reply With Quote
Old 06-21-2019, 02:49 AM   #4
Senior Member
 
nomad297's Avatar
 
Join Date: Jul 2015
Posts: 7,053
Quote:
Originally Posted by Capt. Mike View Post
Maybe somebody before you put in the wrong heating element and it is overheating the water. That will make the pressure relief valve "pop".
Using the wrong element wouldn’t make a difference in this case. The thermostat will shut down the power to the element once it reaches temperature no matter which element is installed.

I would start by measuring the temperature of the hot water. If it gets up to 210 degrees, the T&P valve will open, as it should. This will tell you that you have a malfunctioning thermostat. If the T&P valve opens at less than 210 degrees, the T&P valve could be bad or the the water is getting hot enough to increase the tank (and system) pressure to above 150psi.

Since it is only happening when being heated with electricity, and not happening when being heated with propane, I would guess that the thermostat needs to be replaced. It sounds like the thermostat for the propane side is shutting down when it is supposed to and the thermostat for the electric side is not.

Bruce
__________________
2016 Rockwood Windjammer 3029W Diamond Edition
2015 Chevy 3500HD LTZ 6.0 Crew Cab 4x4 Long Bed 4.10:1 SRW
nomad297 is offline   Reply With Quote
Old 06-21-2019, 01:27 PM   #5
Old Engineer
 
FleckDreher's Avatar
 
Join Date: Feb 2018
Location: UP of Michigan
Posts: 216
You may have an air bubble in the heater tank at the relief valve.

Try manually burping the valve to release the air before turning on the electric heater element.

__________________
2019 Dynamax Isata 3 24RW
Smart Car Towed 4 Down
Quote: "When all else fails, read the manual!"
FleckDreher is offline   Reply With Quote
Old 06-21-2019, 01:56 PM   #6
Senior Member
 
nomad297's Avatar
 
Join Date: Jul 2015
Posts: 7,053
Quote:
Originally Posted by FleckDreher View Post
You may have an air bubble in the heater tank at the relief valve.

Try manually burping the valve to release the air before turning on the electric heater element.

No.

Bruce
__________________
2016 Rockwood Windjammer 3029W Diamond Edition
2015 Chevy 3500HD LTZ 6.0 Crew Cab 4x4 Long Bed 4.10:1 SRW
nomad297 is offline   Reply With Quote
Old 06-21-2019, 01:56 PM   #7
Member
 
Join Date: Apr 2017
Posts: 60
Quote:
Originally Posted by FleckDreher View Post
You may have an air bubble in the heater tank at the relief valve.

Try manually burping the valve to release the air before turning on the electric heater element.

This is actually backwards, an air pocket in the top of the tank is needed as an expansion area when the water heats. Dripping from the valve is fixed by opening when the tank is cold and releasing water reestablishing the air pocket. Read the manual.
Sealyn is offline   Reply With Quote
Old 06-21-2019, 08:15 PM   #8
Old Engineer
 
FleckDreher's Avatar
 
Join Date: Feb 2018
Location: UP of Michigan
Posts: 216
The thermal performance of the relief valve is based on "water" being present at the valves thermal element.

If no water is present the valve will not operate as designed.

It's designed thermal performance conditions will not be satisfied.

That is why it works after opening once.

Believe it or not.

__________________
2019 Dynamax Isata 3 24RW
Smart Car Towed 4 Down
Quote: "When all else fails, read the manual!"
FleckDreher is offline   Reply With Quote
Old 06-21-2019, 08:41 PM   #9
Member
 
Join Date: Apr 2017
Posts: 60
Water level is at the valve, but proper operation requires an air pocket in the tank. This is maintained by opening the valve and letting excess water drain from the tank, per the operating manual. Believe it or not.
Sealyn is offline   Reply With Quote
Old 06-21-2019, 08:56 PM   #10
Old Engineer
 
FleckDreher's Avatar
 
Join Date: Feb 2018
Location: UP of Michigan
Posts: 216
My explanation is correct.

You may not understand it.

__________________
2019 Dynamax Isata 3 24RW
Smart Car Towed 4 Down
Quote: "When all else fails, read the manual!"
FleckDreher is offline   Reply With Quote
Old 06-21-2019, 09:00 PM   #11
Senior Member
 
Join Date: Jun 2012
Posts: 10,907
Assuming you have a Suburban WH (you never said who made it), you have two thermostats; one for the 120VAC electric element and a 12VDC one for the gas. Never of of it before, but it's POSSIBLE that the T-stat for your electric has drifted high somehow. However, the standard T-stat is set to 130F, but they also make a 140F T-stat, so it seems doubtful that could be your problem.

In the past, I've found the Suburban part numbers below.

The first 2 are what you should have as standard. The next two are the hotter ones. I could only find one lower one; I THINK 120VAC, but not certain.

Standard
232306, 130 deg, 120VAC
232282, 130 deg, 12VDC

Higher
232319, 140 deg, 12VDC
232317, 140 deg, 120VAC

Lower
520788, 120 deg, 120VAC??

You could also try replacing the TP valve.
__________________
1988 Coleman Sequoia - popup (1987-2009) - outlasted 3 Dodge Grand Caravans!
2012 Roo19 - hybrid (2012-2015)

2016 Mini Lite 2503S - tt (2015 - ???)
2011 Traverse LT, 3.6L, FWD
2009 Silverado 1500 Ext Cab, 5.3L, 4x4, 3.73
2016 Silverado 2500HD Dbl Cab, 6.0L 4x4, 4.10
rockfordroo is offline   Reply With Quote
Old 06-21-2019, 09:19 PM   #12
Senior Member
 
Join Date: Jul 2017
Posts: 4,056
Quote:
Originally Posted by FleckDreher View Post
You may have an air bubble in the heater tank at the relief valve.

Try manually burping the valve to release the air before turning on the electric heater element.

If there was a air bubble as you put it . T&P valve not immersed in water then how does he lose water out of it when on electric ?
MR.M is offline   Reply With Quote
Old 06-21-2019, 09:42 PM   #13
Member
 
Join Date: Apr 2017
Posts: 60
Quote:
Originally Posted by FleckDreher View Post
My explanation is correct.

You may not understand it.

It seems that several others here are also so dense that we realize you are the one that is wrong. As in your signature, read the manual, by design, the water level will be above the valve and opening it is to let excess water (not air) out of the tank.
Sealyn is offline   Reply With Quote
Old 06-21-2019, 09:47 PM   #14
Site Team
 
Mr. Dan's Avatar
 
Join Date: Mar 2014
Location: Grayson County, Texas
Posts: 21,578
The site team has closed this thread while we review several guidelines violations.
__________________
2015 FR Wildcat 295RSX / GMC Sierra

Nights Camped: '13 = 49/'14 = 74/'15 = 74/'16 = 85/'17 = 110/'18 = 111/'19 = 86/'20 =108/'21 = 115/'22 = 135/'23 = 78; Booked for 2024 = 69
Mr. Dan is offline   Reply With Quote
Old 06-22-2019, 07:11 AM   #15
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,952
OK, the T&P valve (which stands for Temperature AND Pressure) will open if the temperature and/or the pressure gets too high. Higher temperatures will also result in higher pressures.

There may be some confusion, but it appears some are talking about temperature and some are talking about pressure. I think everyone is correct in their own way.

Suburban/Aircel sent us over some great videos awhile back on the operation and use of their brand of tank type water heaters. If the OP has an Atwood/Dometic brand I would feel they would operate in a similar fashion. We keep all 5 of the Suburban videos as a sticky in the FAQ subsection at this link.

http://www.forestriverforums.com/for...es-135977.html

Mark Polk explains the function/use of the T&P valve, as well as the valve dripping. Here it is again below:

Water Heater Series 01: Video 02 – Pressure Relief Valve Function


The fact it is doing it only on electric is kind of interesting. The thermostat and the hi-limit/ECO thermostat would both have to fail for the temp to get over 165 degrees (but this could happen easily if the thermostat assembly was not snug against the tank wall and ASSUMING the OP has a Suburban). I would think the OP would notice if the water was that hot as it would be unbearable.

Anyhow, we are going to reopen this thread. Please remember that this is a friendly forum, and we are all here to share collective wisdom. You may disagree with someone else's opinion, but it's 'HOW" you express this disagreement that's key.
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 06-23-2019, 12:27 PM   #16
Junior Member
 
Join Date: Apr 2019
Posts: 4
Thank you all for your replies. I will work this tomorrow. It’s a new 2019 Survey legend. I’ll test the water temperature. I always felt that it is very hot. Has anyone changed out the temp limit switch?
Thanks
Skypod is offline   Reply With Quote
Reply

Tags
heater, valve, water, water heater


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 05:18 AM.