Old 12-26-2015, 10:41 PM   #21
Senior Member
 
Join Date: Jun 2012
Posts: 10,907
The GFCI is most likely in the receptacle in the bathroom.
__________________
1988 Coleman Sequoia - popup (1987-2009) - outlasted 3 Dodge Grand Caravans!
2012 Roo19 - hybrid (2012-2015)

2016 Mini Lite 2503S - tt (2015 - ???)
2011 Traverse LT, 3.6L, FWD
2009 Silverado 1500 Ext Cab, 5.3L, 4x4, 3.73
2016 Silverado 2500HD Dbl Cab, 6.0L 4x4, 4.10
rockfordroo is offline   Reply With Quote
Old 12-26-2015, 10:44 PM   #22
Senior Member
 
Join Date: Apr 2014
Posts: 643
You keep saying there is no neutral. There will always be a neutral. The main power from the power company is two hot and one neutral. The voltage measured from each hot to the neutral will be 110V and from hot to hot 220V (actually a range for both but the same relationships). The ground is derived at the box where the main breaker is by driving a conductive rod into the ground and attaching it to the ground buss. The neutral to ground bond is done here too. The hot wires go through the breaker and the neutrals are fed from the neutral buss. The power provided to a 110V outlet will have one hot, one neutral and one ground wire. If one of these these doesn't exist then you are not conforming to code.

As I asked and Flybob asked above do you have some type power protection or surge protection device it could be detecting a fault condition and not allowing the trailer to power up. It is possible you converter also has AC fault detection and will not power up either. If this is the case unless you are an electrician or electrical engineer I think it is time you get an electrician involved. The risk of shock or fire it too high if you don't know what you are doing.
keith_h is offline   Reply With Quote
Old 12-26-2015, 11:31 PM   #23
Senior Member
 
Scubanut's Avatar
 
Join Date: Mar 2013
Location: Canada
Posts: 436
Quote:
Originally Posted by keith_h View Post
You keep saying there is no neutral. There will always be a neutral. The main power from the power company is two hot and one neutral. The voltage measured from each hot to the neutral will be 110V and from hot to hot 220V (actually a range for both but the same relationships). The ground is derived at the box where the main breaker is by driving a conductive rod into the ground and attaching it to the ground buss. The neutral to ground bond is done here too. The hot wires go through the breaker and the neutrals are fed from the neutral buss. The power provided to a 110V outlet will have one hot, one neutral and one ground wire. If one of these these doesn't exist then you are not conforming to code.

As I asked and Flybob asked above do you have some type power protection or surge protection device it could be detecting a fault condition and not allowing the trailer to power up. It is possible you converter also has AC fault detection and will not power up either. If this is the case unless you are an electrician or electrical engineer I think it is time you get an electrician involved. The risk of shock or fire it too high if you don't know what you are doing.

X2 on that. Something seems not right on the electrical side and a licensed electrician should evaluate it.


2012 F150 FX4 Crew 5.0 3.73

2012Coachman Freedom Express 292BHDS (outdoor Kitchen)
Scubanut is offline   Reply With Quote
Old 12-27-2015, 08:22 AM   #24
Senior Member
 
TimVWulp's Avatar
 
Join Date: Jan 2015
Location: West Michigan
Posts: 629
Quote:
Originally Posted by llawson2 View Post
I moved my camper to another location and everything worked when i plug in my 30 amp plug. I left and came back a few days later and now the 120 volt system is not working. Any suggestions?
Hi Remove plug on side of TT. Check for power at the end of the power cord that plugs into the TT if no power look for a problem from plug to the beaker that supply's power to the plug end. Inspect the power plug cord end and the TT plug for damage. When you plug the power cord back into the TT make sure to twist the power cord to the right just a little bit and tighten the lock ring on power cord to TT. If the power cord connection is not tight it may result in damage to the connection.

Hope This Helps Tim
TimVWulp is offline   Reply With Quote
Old 12-27-2015, 09:55 AM   #25
Usually Confused Member
 
emm-dee's Avatar
 
Join Date: Nov 2015
Location: Georgia
Posts: 3,767
My power cord has a little red indicator that comes on when power is available from the source. I assume it shows any power but is it possible that if there is not correct power (i.e., only one lug powered on the 50 amp hot sides) that the light would give some indication of that?
__________________
2018 Forester 3051S (aka Clyde, the rolling roadblock)

2015 Wrangler Toad (aka Bonnie)

At some point during every day you suddenly realize nothing else productive is going to happen the rest of that day. For me, it usually occurs around 9 am.
emm-dee is online now   Reply With Quote
Old 12-27-2015, 12:50 PM   #26
Senior Member
 
Anders's Avatar
 
Join Date: Apr 2010
Location: Campbell River, BC
Posts: 178
Quote:
Originally Posted by llawson2 View Post
I moved my camper to another location and everything worked when i plug in my 30 amp plug. I left and came back a few days later and now the 120 volt system is not working. Any suggestions?
I have two GFI plug ins.... check the buttons, might be it..

Cheers,
__________________
Anders Campbell River,
BC. Canada
Pony: 2017 Dodge 3500 Longhorn 4x4, Quad Cab Chuckwagon: 2020 GD Solitude 310 GK
My RV Cookbook now on Amazon! USA or Canada
Travel Blog
Cooking Blog
Anders is online now   Reply With Quote
Old 12-27-2015, 02:21 PM   #27
Senior Member
 
Join Date: Nov 2014
Posts: 591
You will have systematically troubleshoot work downstream from pole receptacle with your meter. Check input to main breaker if nothing check cord plug and wiring and so on. Could be a bad connection
Harkerr is offline   Reply With Quote
Old 12-27-2015, 04:53 PM   #28
Senior Member
 
derek6669's Avatar
 
Join Date: Sep 2014
Location: Lindsay, Ontario, Canada
Posts: 156
had a very similar problem in Nova Scotia this summer. Turned out the solenoid for the gennie was partially tripped. Start the gennie what until the microwave powers up. Stop the gennie and then try shore power. Solved my problem.

The GFI is another one to check , normally located in the bathroom .
derek6669 is offline   Reply With Quote
Old 12-27-2015, 06:02 PM   #29
Site Team
 
Mr. Dan's Avatar
 
Join Date: Mar 2014
Location: Grayson County, Texas
Posts: 16,587
GFCI outlets inside the trailer do not normally affect microwave and TV outlets and the OP said neither of these devices work.
__________________
FR Wildcat 295RSX / GMC Sierra

Nights Camped: '13 = 49/'14 = 74/'15 = 74/'16 = 85/'17 = 110/'18 = 111/'19 = 86/'20 =108/'21 = 28; Booked = 50
Mr. Dan is online now   Reply With Quote
Old 12-27-2015, 08:55 PM   #30
Senior Member
 
Join Date: Sep 2012
Posts: 361
No 120V

Two years watched a guy with an older TT (no GFI) plug in and touch the TT - he jumped a few feet. The neutral and ground were tied together, the ground was not grounded. in fact it was about 60v above ground. The park gave the guy an extension to get to another post. In order for a GFI to function correctly you need Ground separate so it sees a voltage differential to neutral.
Get a Progressive EMS box, it checks incoming power connections, it has saved me and my electronics several times.
__________________
DJsFolly
D. J. Schuler is offline   Reply With Quote
Old 12-27-2015, 09:10 PM   #31
Junior Member
 
Join Date: Dec 2015
Posts: 8
UPDATE!!! Found a burnt wire where my power cable connects inside the camper. I cut the burnt wires and reattached and now everything works. Thanks for everybody's help...
llawson2 is offline   Reply With Quote
Old 12-27-2015, 09:27 PM   #32
Site Team
 
Mr. Dan's Avatar
 
Join Date: Mar 2014
Location: Grayson County, Texas
Posts: 16,587
Quote:
Originally Posted by llawson2 View Post
UPDATE!!! Found a burnt wire where my power cable connects inside the camper. I cut the burnt wires and reattached and now everything works. Thanks for everybody's help...
Great news!
Thanks for reporting back.
__________________
FR Wildcat 295RSX / GMC Sierra

Nights Camped: '13 = 49/'14 = 74/'15 = 74/'16 = 85/'17 = 110/'18 = 111/'19 = 86/'20 =108/'21 = 28; Booked = 50
Mr. Dan is online now   Reply With Quote
Old 12-27-2015, 09:31 PM   #33
Senior Member
 
Wobbles's Avatar
 
Join Date: Feb 2015
Location: Southern, IL
Posts: 3,272
Quote:
Originally Posted by llawson2 View Post
UPDATE!!! Found a burnt wire where my power cable connects inside the camper. I cut the burnt wires and reattached and now everything works. Thanks for everybody's help...
Glad you are back online. Now find why it burnt.

Keep the faith and keep sharing. We all learn from these conversations. Oh yah, post pictures for people like me that have not seen the components and condition.

If you want, add your rig age and model to your signature. Might help folks with ideas as to a resolution or place to start.
__________________
Bob & Michelle
2016 Ford F-250 Lariat 4x4
2017 Flagstaff Super Lite 526RLWS
Wobbles is offline   Reply With Quote
Old 12-27-2015, 09:39 PM   #34
Site Team
 
Flybob's Avatar
 
Join Date: Oct 2014
Posts: 12,654
A burnt wire at a connection usually means that the connection was loose which results in a high resistance connection ( generates heat). I would check the remaining connections in the area to insure they were secure as well. Poor connections usually reveal themselves when the current draw is high. Glad you found it and shared your resolution.
__________________

2015 Freedom Express 248RBS
TV 2015 Silverado HD2500 Duramax
TST Tire Monitors
Honda 2000I + Companion
2 100W solar panels
Flybob is online now   Reply With Quote
Old 12-27-2015, 10:32 PM   #35
Senior Member
 
Join Date: Jun 2012
Posts: 10,907
You're lucky it didn't burn the camper, too! Maybe you should buy a lottery ticket!
__________________
1988 Coleman Sequoia - popup (1987-2009) - outlasted 3 Dodge Grand Caravans!
2012 Roo19 - hybrid (2012-2015)

2016 Mini Lite 2503S - tt (2015 - ???)
2011 Traverse LT, 3.6L, FWD
2009 Silverado 1500 Ext Cab, 5.3L, 4x4, 3.73
2016 Silverado 2500HD Dbl Cab, 6.0L 4x4, 4.10
rockfordroo is offline   Reply With Quote
Old 12-28-2015, 08:05 AM   #36
Senior Member
 
derek6669's Avatar
 
Join Date: Sep 2014
Location: Lindsay, Ontario, Canada
Posts: 156
llawson2, Bravo Zulu
derek6669 is offline   Reply With Quote
Old 12-28-2015, 08:26 AM   #37
Member
 
Join Date: May 2015
Location: Louisiana
Posts: 37
I agree with D.J. Schuler about getting a Progressive EMS Box. It saved my electronics as well!
hardoiler is offline   Reply With Quote
Old 12-28-2015, 11:53 AM   #38
Member
 
Join Date: Dec 2015
Posts: 37
FWIW The ground and neutral went to the same buss for years. When GFI's became common the code was changed to split ground from neutral.

FWIW 2 if you look at the spec for a camper outlet it specifies bonding ground and neutral at the box on the pole/wall/whatever. It is not a shock hazard.
nothermark is offline   Reply With Quote
Old 12-28-2015, 11:56 AM   #39
TGR
Senior Member
 
TGR's Avatar
 
Join Date: Apr 2014
Location: Twin Cities, Minnesota
Posts: 287
Iím glad to see your loss of power was discovered and fixed. However, I am concerned that you still havenít added a proper ground circuit to your wiring.

An electrician can quickly add a ground circuit to your setup and make sure your wiring is safe. There are too many possible variables in your setup to give a specific solution; therefore, an electrician is the best way to get it done properly.
__________________
2015 Wildcat 282 RKX
2011 F350 Lariat, 6.7 L. Diesel, 8 ft., SRW, Reese R20
TGR is offline   Reply With Quote
Old 12-28-2015, 09:02 PM   #40
Member
 
Join Date: Dec 2015
Posts: 37
Quote:
Originally Posted by TGR View Post
Iím glad to see your loss of power was discovered and fixed. However, I am concerned that you still havenít added a proper ground circuit to your wiring.

An electrician can quickly add a ground circuit to your setup and make sure your wiring is safe. There are too many possible variables in your setup to give a specific solution; therefore, an electrician is the best way to get it done properly.

What is wrong with his system and why?
nothermark is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 06:11 PM.