Old 05-30-2016, 02:23 PM   #21
larryandamy
 
Join Date: Apr 2016
Location: Escondido, CA
Posts: 143
30A / 50A

I wrote a long and detailed explanation post on this before detailing that there is very slight risk of doing this. My recommendation is that there is no issue doing this. I can't find the post so a quick summary is below.

For something bad to happen 2 to 3 simultaneous events have to occur for there to be a burning issue. There is no single point of failure that would not be covered.
Your trailer and all the internal wiring is protected with its own 30A circuit breaker. So that CB would have to fail and CB's almost never fail by not tripping. If they fail, they trip prematurely.
The only way to draw more current than your trailer 30A wiring can handle that would not be protected by your trailer 30A CB tripping is a short in the wiring from the trailer CB to the 50A hookup. This would due to insulation abrasion or wires getting crushed or cut. And these short circuit events usually draw very short duration extremely high currents (arcing and sparking) that would trip the 50A site hookup CB.

So I concur... Just do it!
larryandamy is offline   Reply With Quote
Old 05-30-2016, 02:32 PM   #22
Senior Member
 
raspivey's Avatar
 
Join Date: Jun 2013
Location: Brazoria County, Texas
Posts: 1,460
Quote:
Originally Posted by nephi007 View Post
So i have a Progresssive Industries SSP-30X Smart Surge Protector Q: If I use a 39 to 50 amp adaptor do I now need a 50 amp PI Surge Protector?
No, the wiring in the adapter will take care of that.
__________________
2015 Chevy Silverado LTZ - HD tow package
2017 Rockwood 2703WS Emerald Edition
raspivey is offline   Reply With Quote
Old 05-30-2016, 03:36 PM   #23
Senior Member
 
Join Date: Jul 2015
Posts: 113
Hey everybody thanks for the tip. So i will buy to 30 amp to 50 amp adaptor and use the Progressive Industries 30 amp protector and call it good.
nephi007 is offline   Reply With Quote
Old 05-30-2016, 05:13 PM   #24
Junior Member
 
Join Date: May 2016
Location: MS Gulf Coast
Posts: 16
I agree.
__________________
2016 Flagstaff 23 FB, GVWR 5385
Tundra, Double Cab, 5.7
TRD Off Road 4x4, GVWR 7200 lbs.
w/ tow package
MS Gulf Coast
Goff is offline   Reply With Quote
Old 05-30-2016, 10:30 PM   #25
Senior Member
 
Join Date: Dec 2014
Posts: 423
I always use the 50 amp plug when available, never had a problem. Most 30 amp breaker are so worn out they trip easy. Also, when it's hot with high humidity, run your a/c fan on high, not on auto. The fan will run all the time, the compressor will work when it's needed. In the evening, when it cools down, turn the fan control back to auto so it will cycle when you sleep.
tomrob1161 is offline   Reply With Quote
Old 06-01-2016, 10:29 PM   #26
Senior Member
 
Join Date: Apr 2015
Posts: 113
Talking 30 amp breaker

Don't think I saw this in any of the posts. You said your A/C kept popping breaker. One thing to remember, each time the breaker pops, that breaker weakens and eventually will fail. So at this point your breaker could be in a weaker condition and pop easily. So you might want to replace it.
texasbuckeye is offline   Reply With Quote
Old 06-01-2016, 10:54 PM   #27
Senior Member
 
Join Date: Apr 2015
Location: Orlando
Posts: 778
Quote:
Originally Posted by Iwannacamp View Post
I posted this one time before and got backlash...
I have a Progressive Industries EMS(had on a 30amp 5er) and had a warranty issue. While talking to the tech from PI he told me to always use the 50 amp plug(with adapter) when applicable, because it was cleaner power. FWIW
That's funny. Power "cleanliness", which I assume he was referring to the quality of the waveform, is a non issue with utility power. The only issue I can see is that with a 50 amp supply you are using 1 leg to supply a 30 amp plug. A 50 amp breaker is meant to supply 25 amps to each leg. Wire size at the panel breaker may also become an issue, not sure about that one as I don't recall if wire gauge is larger when increasing from 25 to 30 amps. If you are using a generator with a 220v outlet don't use a single leg of it to supply 30 amps, the breaker will kick. If you have access to a 30 amp plug for your 30 amp RV, use the 30 amp plugs.
Brewhedd is offline   Reply With Quote
Old 06-01-2016, 11:44 PM   #28
Senior Member
 
Join Date: Jan 2013
Location: Space Coast of Florida
Posts: 3,967
Quote:
Originally Posted by Brewhedd View Post
That's funny. Power "cleanliness", which I assume he was referring to the quality of the waveform, is a non issue with utility power. The only issue I can see is that with a 50 amp supply you are using 1 leg to supply a 30 amp plug. A 50 amp breaker is meant to supply 25 amps to each leg. Wire size at the panel breaker may also become an issue, not sure about that one as I don't recall if wire gauge is larger when increasing from 25 to 30 amps. If you are using a generator with a 220v outlet don't use a single leg of it to supply 30 amps, the breaker will kick. If you have access to a 30 amp plug for your 30 amp RV, use the 30 amp plugs.
I believe a 50 amp, 220 volt circuit supplies 50 amps to each leg. Check the breaker at the pedestal or in your RV and you will see double 50 amp breakers ganged together...
__________________


2016 Siverback 33IK, Towed 50K+ mile
2018 Ford F-350 Lariat 6.7L V8 Diesel 4WD Crew Cab

"If you don't know where you are going, any road will get you there."
dalford is online now   Reply With Quote
Old 06-02-2016, 04:47 AM   #29
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,739
Quote:
Originally Posted by Brewhedd View Post
That's funny. Power "cleanliness", which I assume he was referring to the quality of the waveform, is a non issue with utility power. The only issue I can see is that with a 50 amp supply you are using 1 leg to supply a 30 amp plug. A 50 amp breaker is meant to supply 25 amps to each leg. Wire size at the panel breaker may also become an issue, not sure about that one as I don't recall if wire gauge is larger when increasing from 25 to 30 amps. If you are using a generator with a 220v outlet don't use a single leg of it to supply 30 amps, the breaker will kick. If you have access to a 30 amp plug for your 30 amp RV, use the 30 amp plugs.
Quote:
Originally Posted by dalford View Post
I believe a 50 amp, 220 volt circuit supplies 50 amps to each leg. Check the breaker at the pedestal or in your RV and you will see double 50 amp breakers ganged together...
Dalford is correct. A 50 amp 120/240 volt split phase service is TWO 50 amp hot legs with TWO 50 amp breakers ganged together in essence.....which provides 100 amps total.

The double pole breakers are tied together because they share a common neutral wire between them, which carries the return load imbalance between the two sides.

These links will explain it better:

Electrical Tutorial - Chapter 3 - 30 Amp versus 50 Amp

RV Electric

and this pic helps:

__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 06-02-2016, 07:52 AM   #30
Senior Member
 
Join Date: Apr 2015
Location: Orlando
Posts: 778
Quote:
Originally Posted by dalford View Post
I believe a 50 amp, 220 volt circuit supplies 50 amps to each leg. Check the breaker at the pedestal or in your RV and you will see double 50 amp breakers ganged together...
That would be the first time I've heard of that. A 50 amp breaker in a supply panel, say the one in your home, is rated for 50 amps total not 100. There seems to be a large misconception that because a 50 amp breaker is marked 50 amps on each leg it can carry 100 amps. That is not the case, it is a 50 amp breaker.


Here's a 50 amp breaker, as you can see it's rated @ 50 amps.
New Cutler Hammer BR 2 Pole 50 Amp Breaker Free Shipping | eBay
Brewhedd is offline   Reply With Quote
Old 06-02-2016, 08:00 AM   #31
Senior Member
 
bubbles's Avatar
 
Join Date: Dec 2012
Posts: 7,645
Quote:
Originally Posted by Brewhedd View Post
That would be the first time I've heard of that. A 50 amp breaker in a supply panel, say the one in your home, is rated for 50 amps total not 100. There seems to be a large misconception that because a 50 amp breaker is marked 50 amps on each leg it can carry 100 amps. That is not the case, it is a 50 amp breaker.


Here's a 50 amp breaker, as you can see it's rated @ 50 amps.
New Cutler Hammer BR 2 Pole 50 Amp Breaker Free Shipping | eBay
There are 2, 50 amp breakers ganged together at all power panels for rv hook up. There are 2 power busses in the rv and each one has 50 amps available to it. You do the math.
bubbles is offline   Reply With Quote
Old 06-02-2016, 08:09 AM   #32
Site Team
 
Flybob's Avatar
 
Join Date: Oct 2014
Posts: 15,266
Be careful, you want a 50A to 30A adapter as shown below. There is also a 30A to 50A which you do not want.


Quote:
Originally Posted by nephi007 View Post
Hey everybody thanks for the tip. So i will buy to 30 amp to 50 amp adaptor and use the Progressive Industries 30 amp protector and call it good.
Attached Thumbnails
Click image for larger version

Name:	50A to 30A adapter.jpg
Views:	111
Size:	137.4 KB
ID:	109848  
__________________

2015 Freedom Express 248RBS
TV 2015 Silverado HD2500 Duramax
TST Tire Monitors
Honda 2000I + Companion
2 100W solar panels
Flybob is online now   Reply With Quote
Old 06-02-2016, 08:25 AM   #33
Senior Member
 
Oaklevel's Avatar
 
Join Date: Sep 2012
Location: Virginia
Posts: 9,740
But the bottom line is if you are tripping your 30A breaker now.... using an adapter on the 50A outlet is not going to change anything. You will still be tripping your 30A breaker on the trailer.

Using the adapter is fine though.

__________________

2005 Dodge 3500 Cummins
2017 Wildwood Lodge 4092 BFL
1966 Mustang GT
1986 Mustang SVO
Lillie Spoiled Rotten Boxer Mix
Oaklevel is offline   Reply With Quote
Old 06-02-2016, 08:33 AM   #34
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,739
Quote:
Originally Posted by Brewhedd View Post
That would be the first time I've heard of that. A 50 amp breaker in a supply panel, say the one in your home, is rated for 50 amps total not 100. There seems to be a large misconception that because a 50 amp breaker is marked 50 amps on each leg it can carry 100 amps. That is not the case, it is a 50 amp breaker.


Here's a 50 amp breaker, as you can see it's rated @ 50 amps.
New Cutler Hammer BR 2 Pole 50 Amp Breaker Free Shipping | eBay
It's all explained in the links I provided in post #29. It's 50 amps total at 240 volts..... or 100 amps total at 120 volts (which is how the RV's utilize it). The links will help explain it all, as I know it's hard to sometimes get a understanding of it.

The double pole breaker you have linked is just that, a double pole breaker. Each pole is 50 amps at 120 volts.

When a 120/240 split phase service is used as 120 volts only (both legs separate), then the total amps available are added together (50 amps on L1 + 50 amps on L2).

Another thing that may help get a handle on it, is to look up RV power cords. You will see that a 50 amp power cord, utilizes larger wires (the L1, L2, and neutral), since they have to be rated to handle 50 amps of 120 volt power on each wire..... as opposed to a 30 amp cord having to handle 30 amps on each wire.

You should find that your typical 25' cord utilizes #6 wire for the L1, L2, and neutral in a 50 amp cord.......... whereas a 30 amp cord utilizes #10 wire.
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 06-14-2016, 10:33 PM   #35
Rivnut
 
Rivnut's Avatar
 
Join Date: Feb 2014
Location: Monterey, TN cumberland Plateau
Posts: 170
adapters 30 to 50 amp

Can we talk about getting 30 or 50 amps from the dryer plug, my son has no spare circuits or anything else to supply us with power to the trailer when we visit. Looks like the second picture dogbone would fit the dryer plug. Can I do this???
thanks
Rivnut

Quote:
Originally Posted by wmtire View Post
They make adapters to go both ways. The 50 amp male to 30 amp female adapter just terminates the L2 leg inside the adapter so there is no second 120 volt leg (L2), which a 30 amp RV doesn't need.



12" Adapter 50 Amp Male to 30 Amp Female Dogbone Adapter



The 30 amp male to 50 amp female jumps the L1 leg over onto the L2 side, to provide power to both legs inside a 50 amp RV, albeit you are limited to 30 amps total power between both legs.

Rivnut is offline   Reply With Quote
Old 06-14-2016, 11:12 PM   #36
Senior Member
 
Join Date: Jul 2012
Posts: 236
Along the same lines, my garage outlets and the driveway lighting are on a 30 amp circuit. I have an outlet box wired in line with the mercury vapor driveway light that I plug my Hauler into with the 30 amp RV cord with the plug adaptor. With this in mind my question is, am I asking for trouble if I run my Haulers AC off of this?
rblack22 is offline   Reply With Quote
Old 06-14-2016, 11:37 PM   #37
Senior Member
 
raspivey's Avatar
 
Join Date: Jun 2013
Location: Brazoria County, Texas
Posts: 1,460
Quote:
Originally Posted by Rivnut View Post
Can we talk about getting 30 or 50 amps from the dryer plug, my son has no spare circuits or anything else to supply us with power to the trailer when we visit. Looks like the second picture dogbone would fit the dryer plug. Can I do this???
thanks
Rivnut
You could do this...and fry everything. That dryer plug is wired for 240V. Stay away from it.
__________________
2015 Chevy Silverado LTZ - HD tow package
2017 Rockwood 2703WS Emerald Edition
raspivey is offline   Reply With Quote
Old 06-15-2016, 01:22 AM   #38
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,739
Quote:
Originally Posted by Rivnut View Post
Can we talk about getting 30 or 50 amps from the dryer plug, my son has no spare circuits or anything else to supply us with power to the trailer when we visit. Looks like the second picture dogbone would fit the dryer plug. Can I do this???
thanks
Rivnut
Probably not. The dryer is most likely 240 volts without a separate ground wire....which any RV has to have the ground whether 30 amps or 50 amps.

This link helps explain it better. Click on the appliance links to the left.

RV Electric

You'll also probably find out the dogbone adapter does not fit the dryer plug, as the ground terminal plug on the adapter is not the same as neutral terminal on the dryer outlet. Even if you made it fit, you would be sending one leg of of 120 volts onto the neutral wire of your RV, and burn something up.

DO NOT attempt this

As from the link:
No adapter is made or available to plug your RV into the OLD 50-amp 120/240-volt 3 pole 3 wire (10-50R) OR a 30-amp 120/240-volt 3 pole 3 wire (10-30R) APPLIANCE service.


Is using a generator out of the question at your son's home?

If so, there is a way to convert his dryer outlet to at least a 120 volt 30 amp service using the existing wiring. You'll have to change the breaker (remove the double pole dryer breaker and install a single pole 30 amp breaker) and wire connection in his electrical box. You'll just make one of the currently used hot wires into a ground. Then you will remove his dryer outlet and wire in a TT-30R like this:

http://www.myrv.us/Imgs/PDF/30-amp%20Service.pdf

If you want to make it a 120/240 volt 50 amp split phase service though, you'll have to get someone to pull a new ground wire.

It's explained in the appliance tab of the link above. However I would caution against doing this yourself as you don't seem to be very familiar with this (no insult intended), and may be best to hire an electrician to do it for you. You can show him the diagrams.

But if you do this, then you may likely be taking his clothes dryer out of the picture, which I assume he uses.
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 06-15-2016, 05:20 AM   #39
Member
 
Join Date: Sep 2014
Posts: 297
Quote:
Originally Posted by raspivey View Post
You could do this...and fry everything. That dryer plug is wired for 240V. Stay away from it.
so are 50 amp rv plugs... what's the difference?
__________________
2016 Flagstaff 27VRL with overloaded tires from factory
2015 Chevy Silverado
Paul GA is offline   Reply With Quote
Old 06-15-2016, 05:22 AM   #40
Member
 
Join Date: Sep 2014
Posts: 297
Quote:
Originally Posted by wmtire View Post
Probably not. The dryer is most likely 240 volts without a separate ground wire....which any RV has to have the ground whether 30 amps or 50 amps.

This link helps explain it better. Click on the appliance links to the left.

RV Electric

You'll also probably find out the dogbone adapter does not fit the dryer plug, as the ground terminal plug on the adapter is not the same as neutral terminal on the dryer outlet. Even if you made it fit, you would be sending one leg of of 120 volts onto the neutral wire of your RV, and burn something up.

DO NOT attempt this

As from the link:
No adapter is made or available to plug your RV into the OLD 50-amp 120/240-volt 3 pole 3 wire (10-50R) OR a 30-amp 120/240-volt 3 pole 3 wire (10-30R) APPLIANCE service.


Is using a generator out of the question at your son's home?

If so, there is a way to convert his dryer outlet to at least a 120 volt 30 amp service using the existing wiring. You'll have to change the breaker (remove the double pole dryer breaker and install a single pole 30 amp breaker) and wire connection in his electrical box. You'll just make one of the currently used hot wires into a ground. Then you will remove his dryer outlet and wire in a TT-30R like this:

http://www.myrv.us/Imgs/PDF/30-amp%20Service.pdf

If you want to make it a 120/240 volt 50 amp split phase service though, you'll have to get someone to pull a new ground wire.

It's explained in the appliance tab of the link above. However I would caution against doing this yourself as you don't seem to be very familiar with this (no insult intended), and may be best to hire an electrician to do it for you. You can show him the diagrams.

But if you do this, then you may likely be taking his clothes dryer out of the picture, which I assume he uses.
Any dryer plug wired in the last 20 years must have ground separate from the neutral. 4 prongs he's good to go, 3 he's not.
__________________
2016 Flagstaff 27VRL with overloaded tires from factory
2015 Chevy Silverado
Paul GA is offline   Reply With Quote
Reply

Tags
50 amp

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 10:19 AM.