30amp double pole breaker for 50amp camper?

I was parked at my in-laws and my father-in-law had a welder plug in the garage. It was wired for 240v with a double-pole breaker in the basement.

He changed out the breaker to be a single pole 30amp breaker. And then we changed out the outlet to be a 120v 30amp twist-lock welding outlet like my generator has. I converted that to my 30amp dog bone and then put my 50amp dog bone onto that and plugged in. Life was good.

His brother has owned campers for many years and said we could have wired it so that we could use 2 legs of 30amp service and put a 50amp outlet on the wall. He does it, and it works great. I've read enough here over the years to say, "yeah, that scares the heck out of me".

Everything I read about 50amp outlets, 4 wires were required: 2 hots, a ground, and a neutral. We only had 3 wires.

Could we have done what the brother suggested? Somehow wired it up so that I'd have 2 legs of 30amp service?
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
ependydad is offline   Reply With Quote
Old 07-05-2018, 07:47 AM   #2
Senior Member
 
Join Date: Jul 2010
Location: Waynesville
Posts: 14,428
Oh boy another "Pop Corn Post"! These always go into areas of "Bad Saftey Advice"! Youroo!!
__________________
youroo is offline   Reply With Quote
Old 07-05-2018, 07:50 AM   #3
Ret E-9 Anchor-clanker
 
donanddona's Avatar
 
Join Date: Jul 2012
Location: Genoa, ILL
Posts: 1,476
This is why we promote surge guards. Know when your smart enough to call an certified technician to do the job.
__________________
Don & Dona W/yorkies Gizmo, Master Chief, & Tali
2011 Flagstaff 8528 BHSS 2015 Ford 6.7 XLT
2010 Full Timers & Still Going
donanddona is offline   Reply With Quote
Old 07-05-2018, 08:04 AM   #4
Always Learning
 
ependydad's Avatar
 
Join Date: Nov 2011
Location: Four Corners, FL
Posts: 21,891
Quote:
Originally Posted by youroo View Post
Oh boy another "Pop Corn Post"! These always go into areas of "Bad Saftey Advice"! Youroo!!
Dang. I swear it's not my intention.

I just couldn't figure out how it could possibly work.


Quote:
Originally Posted by donanddona View Post
This is why we promote surge guards. Know when your smart enough to call an certified technician to do the job.
That's the thing. I have a buddy who IS a certified electrician and fulltime RVer. He had mentioned something similar about setting up a 50amp plug with 2 x 30amp legs at his in-law's house. I didn't ask for details then as it wasn't directly pertinent at the time.

Though, I agree. I do have a hard-wired EMS and strongly suggest them for everyone.
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
ependydad is offline   Reply With Quote
Old 07-05-2018, 08:17 AM   #5
Senior Member
 
Join Date: Oct 2016
Location: SW PA
Posts: 909
Well it could be made to work by using the existing ground wire as the neutral and ground. Of course the max power avaliable would be 7200 watts vs 12,000.
Would it work, yes. Would it be safe and make code NO. You made the right decision by doing what you did.

As you said you need 4 wires of the proper gauge for a 240 volt split phase outlet.
There is a possibility the ground wire in the exsisting run is a smaller gauge than the hot wires, that could turn out bad if used as the neutral.
__________________


2021 Newmar Baystar 3401
2019 Jeep Cherokee Trailhawk toad
2017.5 Forester 3051S Traded 7/2020
Steve-W is offline   Reply With Quote
Old 07-05-2018, 08:48 AM   #6
Always Learning
 
ependydad's Avatar
 
Join Date: Nov 2011
Location: Four Corners, FL
Posts: 21,891
Quote:
Originally Posted by Steve-W View Post
Well it could be made to work by using the existing ground wire as the neutral and ground. Of course the max power avaliable would be 7200 watts vs 12,000.
Would it work, yes. Would it be safe and make code NO. You made the right decision by doing what you did.

As you said you need 4 wires of the proper gauge for a 240 volt split phase outlet.
There is a possibility the ground wire in the exsisting run is a smaller gauge than the hot wires, that could turn out bad if used as the neutral.
I definitely understand the less watts available. No worries there.

And yes, we talked about the 3 vs. 4 wires. He did say you'd just bind the ground and neutral together. Wire-size is interesting, I hadn't thought about that. Any other reason why you wouldn't/shouldn't do this?
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
ependydad is offline   Reply With Quote
Old 07-05-2018, 09:02 AM   #7
Senior Member
 
Join Date: Oct 2016
Location: SW PA
Posts: 909
Quote:
Originally Posted by ependydad View Post
I definitely understand the less watts available. No worries there.

And yes, we talked about the 3 vs. 4 wires. He did say you'd just bind the ground and neutral together. Wire-size is interesting, I hadn't thought about that. Any other reason why you wouldn't/shouldn't do this?
“Binding” the neutral and ground together besides being against code big time is a very unsafe way of doing this. It leaves your rig witnout any dedicated grounding in case something goes wrong. There are ways around this but all are in violation of code. Assuming the ground wire is the same ga as the hot wires (10ga for 30 amps) you most likely would have no issues.
You can also run into issues depending on the other wiring in the building, single mailn panel, sub panels, etc all have different grounding schemes.
Personally I would never do this.
__________________


2021 Newmar Baystar 3401
2019 Jeep Cherokee Trailhawk toad
2017.5 Forester 3051S Traded 7/2020
Steve-W is offline   Reply With Quote
Old 07-05-2018, 09:20 AM   #8
Always Learning
 
ependydad's Avatar
 
Join Date: Nov 2011
Location: Four Corners, FL
Posts: 21,891
Sounds good. Thanks for the replies, Steve.

It didn't sound right to me, but I thought I'd throw it out there.
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
ependydad is offline   Reply With Quote
Old 07-05-2018, 12:59 PM   #9
Senior Member
 
Join Date: Sep 2015
Posts: 1,022
Quote:
Originally Posted by ependydad View Post
I definitely understand the less watts available. No worries there.

And yes, we talked about the 3 vs. 4 wires. He did say you'd just bind the ground and neutral together. Wire-size is interesting, I hadn't thought about that. Any other reason why you wouldn't/shouldn't do this?
I believe tying the ground and neutral together creates a "bootleg ground" that Mike Sokol describes in his RV electrical book.
Springerdad is offline   Reply With Quote
Old 07-05-2018, 01:18 PM   #10
ExNavy-Exphoneguy
 
Join Date: Sep 2015
Posts: 20
I have that at home. 30 amp breaker, 4 wire #10 wire to a 50 amp plug. Have used the AC a few times, no trouble.
mikebecker80 is offline   Reply With Quote
Old 07-05-2018, 01:39 PM   #11
Senior Member
 
SailorSam20500's Avatar
 
Join Date: Jun 2016
Posts: 5,059
My thought is that the only way to make use of the,existing wiring and have both hot legs, would be to add a properly sized wire to handle the nuetral.
__________________
Al
I am starting to think, that I will never be old enough--------to know better.
Tolerance will reach such a level that intelligent people will be banned from thinking so as not to offend the imbeciles. Fyodor Mikhailovich Dostoevsky, Russian Novelist
S.E. Mich. Flagstaff 26FKWS / 2022 F-150 3.5 EcoBoost SCrew Propride
SailorSam20500 is online now   Reply With Quote
Old 07-05-2018, 01:49 PM   #12
Senior Member
 
Join Date: Oct 2016
Location: SW PA
Posts: 909
Since you have 4 conductor wire that is a safe workable solution. Although it does violate NEC code. Not so with the 3 conductors ependydad has to work with.
__________________


2021 Newmar Baystar 3401
2019 Jeep Cherokee Trailhawk toad
2017.5 Forester 3051S Traded 7/2020
Steve-W is offline   Reply With Quote
Old 07-05-2018, 01:54 PM   #13
ExNavy-Exphoneguy
 
Join Date: Sep 2015
Posts: 20
I only have 30 amp box in garage. But wrote 30 amp on the 50 amp outlet.
mikebecker80 is offline   Reply With Quote
Old 07-05-2018, 02:14 PM   #14
Senior Member
 
Join Date: Oct 2016
Location: SW PA
Posts: 909
Quote:
Originally Posted by SailorSam20500 View Post
My thought is that the only way to make use of the,existing wiring and have both hot legs, would be to add a properly sized wire to handle the nuetral.
Would work if the existing wire is in conduit, with enough space for an additional conductor.
__________________


2021 Newmar Baystar 3401
2019 Jeep Cherokee Trailhawk toad
2017.5 Forester 3051S Traded 7/2020
Steve-W is offline   Reply With Quote
Old 07-05-2018, 03:17 PM   #15
Senior Member
 
Tom48's Avatar
 
Join Date: Apr 2015
Location: Ontario, California
Posts: 2,146
Quote:
Originally Posted by youroo View Post
Oh boy another "Pop Corn Post"! These always go into areas of "Bad Saftey Advice"! Youroo!!
If someone WHO UNDERSTANDS what they are doing wires a 50 amp type socket on only a double 30 amp circuit, as long as it is fused (breakered) correctly for the gage of wire in the run, there should no problem.

You would have twice as much current as if you wired a 30 outlet on just the one "hot" then ran a dog bone (plug adapter) to your coach. Just know that the "breaker on the pole" so to speak, will blow long before your 50 amp Mains in the coach, so plan accordingly.

And as mentioned, always safer to good surge guard or Progressive Dynamics device for further protection of your valuable coach.
__________________
Tom48
In Sunny So Cal /w
Now in 2005 Holiday Rambler Ambassador DP and The Hot Air Balloon RESTLESS
NO MORE Tricked out
2017 Sandstorm 250 T.H.
Tom48 is offline   Reply With Quote
Old 07-05-2018, 03:19 PM   #16
Senior Member
 
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,584
Well...

Quote:
Originally Posted by Steve-W View Post
Would work if the existing wire is in conduit, with enough space for an additional conductor.
Well, if the existing wiring run is in conduit, the conduit serves as ground. Only three wires would be needed for the trailer outlet: two hots and a neutral.

But if a 240 VAC welder were wired in conduit, there would only be two wires present, the two hot sides of the 240 VAC, and three would be needed. One too few, again.

This would be #8 AWG wire, seriously heavy stuff. You might not be able to pull three wires through the existing conduit, even if you pulled the other two out and then tried to pull three at once. Three #8 conductors is the maximum allowed in 1/2" galvanized conduit (if I'm reading the chart right).

Larry
Larry-NC is offline   Reply With Quote
Old 07-05-2018, 03:20 PM   #17
Senior Member
 
Join Date: Sep 2015
Posts: 1,022
Quote:
Originally Posted by youroo View Post
Oh boy another "Pop Corn Post"! These always go into areas of "Bad Saftey Advice"! Youroo!!
Why would you want to say that?
Springerdad is offline   Reply With Quote
Old 07-05-2018, 03:30 PM   #18
Senior Member
 
Join Date: Oct 2016
Location: SW PA
Posts: 909
Quote:
Originally Posted by Larry-NC View Post
Well, if the existing wiring run is in conduit, the conduit serves as ground. Only three wires would be needed for the trailer outlet: two hots and a neutral.

But if a 240 VAC welder were wired in conduit, there would only be two wires present, the two hot sides of the 240 VAC, and three would be needed. One too few, again.

This would be #8 AWG wire, seriously heavy stuff. You might not be able to pull three wires through the existing conduit, even if you pulled the other two out and then tried to pull three at once. Three #8 conductors is the maximum allowed in 1/2" galvanized conduit (if I'm reading the chart right).

Larry
This is true assuming metallic conduit installed correctly. As always there are so many options. Some are good and some not so good.
__________________


2021 Newmar Baystar 3401
2019 Jeep Cherokee Trailhawk toad
2017.5 Forester 3051S Traded 7/2020
Steve-W is offline   Reply With Quote
Old 07-05-2018, 03:41 PM   #19
Senior Member
 
Join Date: Jun 2016
Posts: 597
I'm guessing what the FIL's brother was using is a 4 plug/wire outlet, I ran power to my garage, I used a 50 amp 240 volt four wire plug to plug my camper into, I then built an adapter for my 50 amp welder (no neutral) and plasma cutter and ran an extension box off the 50 amp service for the 30 amp 120 volt welder or a 30 amp camper, I have the 30 amp circuit breaker'd at 30 amps.
wildcatter is offline   Reply With Quote
Old 07-05-2018, 03:46 PM   #20
Senior Member
 
Join Date: Apr 2016
Location: Port Charlotte Fl/Hinsdale Ma
Posts: 4,823
Quote:
Originally Posted by ependydad View Post
I was parked at my in-laws and my father-in-law had a welder plug in the garage. It was wired for 240v with a double-pole breaker in the basement.

He changed out the breaker to be a single pole 30amp breaker. And then we changed out the outlet to be a 120v 30amp twist-lock welding outlet like my generator has. I converted that to my 30amp dog bone and then put my 50amp dog bone onto that and plugged in. Life was good.

His brother has owned campers for many years and said we could have wired it so that we could use 2 legs of 30amp service and put a 50amp outlet on the wall. He does it, and it works great. I've read enough here over the years to say, "yeah, that scares the heck out of me".

Everything I read about 50amp outlets, 4 wires were required: 2 hots, a ground, and a neutral. We only had 3 wires.

Could we have done what the brother suggested? Somehow wired it up so that I'd have 2 legs of 30amp service?
Bare grounds and insulated neutrals are 2 different things and do 2 different jobs. The neutral carries AC. The ground carries unintentional AC.

You cannot make it work! The white wire of the 30 amp cord is neutral. You cannot put 120 volts on the line as it is hooked up to the neutral bus. Sparks will fly. I wish people would leave electric to the professionals. Then again, I made a pretty good living for 45 years fixing amateurs screw ups.
cavie is offline   Reply With Quote
Reply

Tags
breaker, camper


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 12:36 PM.