Old 07-14-2016, 02:12 PM   #1
Junior Member
 
Join Date: Mar 2013
Posts: 16
50 amp RV wiring?

I'm trying to wire a 50 amp plug for my 5th wheel at home for temporary use, but the wire from my 50 amp breaker only has 3 #4 wires. Can I loop the ground and common wire at the plug?
T- High is offline   Reply With Quote
Old 07-14-2016, 02:17 PM   #2
Senior Member
 
Join Date: Aug 2015
Location: Box elder
Posts: 730
http://www.janeandjohn.org/docs/50am...stallation.pdf
__________________
2015 silverback 31IK
2023 f350
kcmusa is offline   Reply With Quote
Old 07-14-2016, 02:28 PM   #3
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,952
You need to understand how a split phase 50 amp service works for your RV, or you are going to be one unhappy camper.

Please. Please. Please read these links.


Electrical Tutorial - Chapter 3 - 30 Amp versus 50 Amp

RV Electric

http://www.myrv.us/Imgs/PDF/50-amp%20Service.pdf

Is your 50 amp breaker, a double pole?
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 07-14-2016, 02:43 PM   #4
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,952
The way it sounds, you have a 50 amp 240 volt breaker, with only three wires (and are missing either a neutral or ground wire at the outlet, depending on what this outlet was powering beforehand). You are going to need to run new wires (at least one) to properly install a 50 amp 120/240 split phase service outlet that you are describing.

Now if you don't want to do this, you can adapt what you have in place. You can remove the 50 amp double pole breaker, and replace it with a single pole 30 amp breaker. You will use one of the hot wires and attach it to the breaker. Take the other unused hot wire and make it either the ground or neutral in your distribution panel. Then take the third wire and make it whichever one you need now (neutral or ground).

You now will connect it as a 30 amp RV outlet below and can use an 50/30 adapter on your RV's 50 amp cord so you can plug in. You will be limited though in what you can run to a total of 30 amps, but this should allow one air conditioner and several other things.

http://www.myrv.us/Imgs/PDF/30-amp%20Service.pdf

All of this is also explained in the second link I provided above, if you click on the appliance tabs to the left hand side of screen and it explains how to do these conversions.
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 07-14-2016, 03:01 PM   #5
Junior Member
 
Join Date: Mar 2013
Posts: 16
Yes. My breaker is 50amp 2 pole.
T- High is offline   Reply With Quote
Old 07-15-2016, 01:25 PM   #6
Member
 
Join Date: Mar 2015
Posts: 78
T-High, I believe the answer you are looking for is (unfortunately) no.

You spurred me into doing a bunch of research after reading this. And the info out there is very confusing. Your premise that Neutral and Ground are essentially the same is correct to a point, but ONLY in the service panel box (where your breaker is located) where they both connect to ground. But if you connect ground to Neutral in the outlet, you can't assume a short (unwanted voltage) that is trying/seeking ground will go take the path through your service panel. It may take the path back into your Neutral line back into the coach and fry something.

Next, I will clarify an assumption I'm making: I'm assuming you have three wires that are insulated in your receptacle (two hot and one neutral). If you only have two insulated, and one ground (un-insulated) wire, then it's time to run a new wire.

Now having said that, and if my assumption is correct that you have three insulated lines, you may be able to install a grounding rod near your outlet and run a new ground wire from the receptacle to make up for the missing ground wire. I would use an eight foot grounding rod you can buy at Depot/Lowes and some really heavy wire (insulated is probably better in this case, but it wouldn't have to be.

The big deal is the fact that RVs have DC and AC systems intermixed and you can't assume that Neutral and Ground are the same all the time (i.e. they aren't grounded the same because the RV uses the chassis or the batteries for ground when running disconnected/inverted).

That's my two cents and I'm NOT an electrician.

If you can, run a new four wire lead from you box to your receptacle.

If your wire is two insulated and one ground, you pretty much have no choice but to run a new wire IMHO. Or go 30A.
smo99 is offline   Reply With Quote
Old 07-15-2016, 02:30 PM   #7
Always Learning
 
ependydad's Avatar
 
Join Date: Nov 2011
Location: Four Corners, FL
Posts: 21,891
Whatever you do- make sure you check and triple check that it's wired appropriately before plugging your rig in. People can and do FRY THINGS IN THEIR RIGS when they wire something up that is wrong.
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
ependydad is offline   Reply With Quote
Old 07-15-2016, 02:48 PM   #8
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
Quote:
Originally Posted by T- High View Post
I'm trying to wire a 50 amp plug for my 5th wheel at home for temporary use, but the wire from my 50 amp breaker only has 3 #4 wires. Can I loop the ground and common wire at the plug?
Nope not really, best to pull new wire or just make it a 30 amp outlet with a 30/ 50 adapter....BE SAFE not SORRY..... PS: IF you use your uninsulated ground for a neutral and use a grounding rod, you are asking for problems, just my limited opinion... PS: the only thing I don't like is that you would be using a uninsulated neutral. If you use a grounding rod but it would work but that bare wire will be hot...
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 07-15-2016, 03:59 PM   #9
Member
 
Join Date: Mar 2015
Posts: 78
Just to clarify my point and AGREE with Witch Doctor, I wouldn't use a line with two hots and one UN-INSULATED line for the neutral. As I said above, i would only use the existing lines IF and ONLY IF all three are insulated and then run a new ground line (insulated or un-insulated) to the grounding rod.
__________________
______________________
Mark & Karla + 2 Kitties
2008 Berkshire 390-QS
Bigfork, Montana
smo99 is offline   Reply With Quote
Old 07-15-2016, 04:18 PM   #10
Senior Member
 
Iwannacamp's Avatar
 
Join Date: Aug 2013
Posts: 7,916
I am not an electrician... I am thinking these are same wiring diagrams as you would use on a mobile home or a metal shop. It requires an "extra" ground. 2 @ 120V, one box to box ground and one neutral(from pole) and the normal box to earth ground. Isn't this correct?
__________________
2017 Puma 297RLSS
2005 Ram 2500 4X4 diesel SMOKER!!
I love puns, irony and tasteless jokes...
born in Texas.... live in Arkansas
Iwannacamp is offline   Reply With Quote
Old 07-15-2016, 04:40 PM   #11
Senior Member
 
DouglasReid's Avatar
 
Join Date: Jun 2016
Location: Maurice, LA
Posts: 4,095
Bad Advice

You are getting some bad advice from some here who do not understand wiring. You CANNOT bond the Neutral and ground in an electrical panel Except at the "Service Entrance". To do otherwise is to risk back feeding electricity where you do not want it if you have a short. This can be DEADLY!

If you don't know what you are doing, CALL AN ELECTRICIAN. They make their living dealing with this dangerous resource. You may not like the expense, but it is better than a lifetime of regret should someone be injured or killed.
__________________
2012 Wildcat Sterling 32RL, Gladiator Qr35 ST235/85R16 Load rating G, TST 507 TPMS w/ Flow-thru Sensors & Repeater, Reese Sidewinder 16K Pin Box, PI EMS HW50C
2009 Chevy Silverado 2500HD CCSB LTZ Diesel, Fumoto Oil Drain Valve, Turbo Brake activated, 39 gal Aux Tank W/ Fuel Pump transfer, Air Lift Loadlifter 5000 air bags.
DouglasReid is offline   Reply With Quote
Old 07-15-2016, 04:48 PM   #12
Senior Member
 
Join Date: Sep 2012
Posts: 361
50 AMP

Get on line and look at a wiring diagram as suggested in the thread! Your house neutral and ground are tied together. RV wiring has separate frame ground also used for 12 DC ground and 120 VAC return/neutral above ground connected to outlets neutrals and converter neutral not ground. RV grounded outlets are frame ground not tied to neutral. 50 AMP service is two (2) 120 VAC supplies only thing in common is a neutral and a ground pin on the plug to ground the trailer. That's why you can see one 120 VAC drawing 15 AMPS and the other 120 VAC line at 2 AMPS on a Progressive 50 surge protector.
Home Dryer plugs aren't wired with a neutral, just two (2) 120 VAC and ground. Internally timers and motors run on one 120 VAC line and ground, that's why it is important to ground your dryer.
__________________
DJsFolly
D. J. Schuler is offline   Reply With Quote
Old 07-15-2016, 06:01 PM   #13
Senior Member
 
DouglasReid's Avatar
 
Join Date: Jun 2016
Location: Maurice, LA
Posts: 4,095
[QUOTE=D. J. Schuler;
Home Dryer plugs aren't wired with a neutral, just two (2) 120 VAC and ground. Internally timers and motors run on one 120 VAC line and ground, that's why it is important to ground your dryer.[/QUOTE]

That used to be true. Today's modern codes REQUIRE a separate Neutral and Ground as well as the two hot wires for the Dryer, Range and Oven. This code change was made for safety purposes.

I cannot stress enough, WHY take a chance? Get an Electrician if you do not know what you are doing!
__________________
2012 Wildcat Sterling 32RL, Gladiator Qr35 ST235/85R16 Load rating G, TST 507 TPMS w/ Flow-thru Sensors & Repeater, Reese Sidewinder 16K Pin Box, PI EMS HW50C
2009 Chevy Silverado 2500HD CCSB LTZ Diesel, Fumoto Oil Drain Valve, Turbo Brake activated, 39 gal Aux Tank W/ Fuel Pump transfer, Air Lift Loadlifter 5000 air bags.
DouglasReid is offline   Reply With Quote
Old 07-15-2016, 06:16 PM   #14
jkoenig24
 
Join Date: Apr 2015
Location: Box Elder, SD (formerly NY)
Posts: 953
Buy and read Mike Sokol's ebook "No Shock Zone". It is a WEALTH of electrical information for RVs. I bought my copy at Amazon; less than $10.

https://www.amazon.com/No~Shock~Zone...=No+Shock+Zone

Mike has a YouTube channel too.

The life and RV you save may be your own.
jkoenig24 is offline   Reply With Quote
Old 07-15-2016, 08:56 PM   #15
Senior Member
 
Join Date: Dec 2015
Posts: 294
Quote:
Originally Posted by smo99 View Post
T-High, I believe the answer you are looking for is (unfortunately) no.

You spurred me into doing a bunch of research after reading this. And the info out there is very confusing. Your premise that Neutral and Ground are essentially the same is correct to a point, but ONLY in the service panel box (where your breaker is located) where they both connect to ground. But if you connect ground to Neutral in the outlet, you can't assume a short (unwanted voltage) that is trying/seeking ground will go take the path through your service panel. It may take the path back into your Neutral line back into the coach and fry something.

Next, I will clarify an assumption I'm making: I'm assuming you have three wires that are insulated in your receptacle (two hot and one neutral). If you only have two insulated, and one ground (un-insulated) wire, then it's time to run a new wire.

Now having said that, and if my assumption is correct that you have three insulated lines, you may be able to install a grounding rod near your outlet and run a new ground wire from the receptacle to make up for the missing ground wire. I would use an eight foot grounding rod you can buy at Depot/Lowes and some really heavy wire (insulated is probably better in this case, but it wouldn't have to be.

The big deal is the fact that RVs have DC and AC systems intermixed and you can't assume that Neutral and Ground are the same all the time (i.e. they aren't grounded the same because the RV uses the chassis or the batteries for ground when running disconnected/inverted).

That's my two cents and I'm NOT an electrician.

If you can, run a new four wire lead from you box to your receptacle.

If your wire is two insulated and one ground, you pretty much have no choice but to run a new wire IMHO. Or go 30A.
Good explanation and advice here, but one word of caution. If a second grounding rod is used, it MUST be bonded to the existing ground in the main breaker box. This is due to variance in resistance of the soil. Remember, not all grounds are created equal.

That being said, it is a viable option. The ground wire does not need to be in the same conduit as the two hots and neutral. As stated else where, if you are unsure, seek the help of a qualified electrician.
tkarper14 is offline   Reply With Quote
Old 07-15-2016, 09:04 PM   #16
Senior Member
 
Forbes's Avatar
 
Join Date: Jan 2012
Location: Tennessee
Posts: 813
Find an electrician is best advice given. After 40 plus years of work in the field I would not try and explain how to anyone unless I was looking at it and had hands on. Get some professional help to be safe.
__________________
Roger & Mary Forbes
WB4FSN
Little Lady (Dog)
2014 F350 / 2015 CC 36 CKTS
Forbes is offline   Reply With Quote
Old 07-15-2016, 09:05 PM   #17
Senior Member
 
Join Date: Sep 2012
Posts: 361
I totally agree with "Get the right INFO", old house old wiring, new house new wiring get an electrician who has/knows RV wiring (experience) too.
Also suggest Progressive Industries EMS PT50C, protects/turns off when missing/reversed ground/neutral and high/low voltage either leg and surges are detected. Three years ago watched a guy plug into neutral connected to ground on the post and no ground connection, he touched the side of his TT and knew something was wrong, thank goodness it was dry weather.
__________________
DJsFolly
D. J. Schuler is offline   Reply With Quote
Old 07-15-2016, 09:17 PM   #18
Senior Member
 
Join Date: Jul 2010
Location: Waynesville
Posts: 14,428
Quote:
Originally Posted by Forbes View Post
Find an electrician is best advice given. After 40 plus years of work in the field I would not try and explain how to anyone unless I was looking at it and had hands on. Get some professional help to be safe.
This is a Very True Statement that should be Followed!^^^ It is the same as going to a BAR and asking a Drunk Electrician "How do I wire My House"! Youroo!!
__________________
youroo is offline   Reply With Quote
Old 07-16-2016, 08:35 AM   #19
Member
 
Join Date: Feb 2011
Posts: 56
Anyone doing electrical with a RV needs to read Mike Sokol's book, "No~Shock~Zone - RV Electrical Safety".

It's a great tool to have.
menekaunee is offline   Reply With Quote
Old 07-16-2016, 08:43 AM   #20
Senior Member
 
BandJCarm's Avatar
 
Join Date: Jun 2013
Location: Between Pickles Gap and Toad Suck, AR
Posts: 6,070
Quote:
Originally Posted by menekaunee View Post
Anyone doing electrical with a RV needs to read Mike Sokol's book, "No~Shock~Zone - RV Electrical Safety".

It's a great tool to have.
I don't doubt it, and I am glad there are those here that would benefit from reading it.

But for ME? I want my electrician to read it.........
__________________
"Next to prayer, fishing is the most personal relationship of man" Herbert Hoover
"American by Birth, Southern by the Grace of God"Lewis Grizzard

FROG AR-0019-242
2016 GMC Denali 3500Dually--2017 CC 36CKTS
BandJCarm is offline   Reply With Quote
Reply

Tags
50 amp, wiring


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 07:55 AM.