03-25-2019, 09:48 PM
|
#1
|
Junior Member
Join Date: Aug 2018
Posts: 15
|
7500 watt generator.
I have a 2014 Forest River Crusader 360BHS. Myself and two buddies are taking trip from Thursday to Sunday in a couple months. The place we are going is pretty much a parking lot they are allowing campers to park on so there are no hook ups. We do get a portajohn with our entrance fee so that is good. My question is will a 7500 watt generator run both my ac units at the same time. I think they will but if anyone has done it I would like to hear about it. Thanks.
__________________
2014 Crusader BHS360
|
|
|
03-25-2019, 11:08 PM
|
#2
|
Always Learning
Join Date: Nov 2011
Location: Four Corners, FL
Posts: 21,891
|
7500 watts / 120 volts = 62.5 amps.
Each A/C will pull less than 15 amps.
You’ll be fine.
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
|
|
|
03-26-2019, 12:35 AM
|
#3
|
Site Team
Join Date: Jan 2007
Location: Goodyear, Arizona
Posts: 33,845
|
I don't think you'll be be able to hear anything, with a generator that loud.[emoji33]
__________________
Dan-Retired California Firefighter/EMT
Shawn-Musician/Entrepreneur/Wine Expert
and Zoe the Wonder Dog(R.I.P.)
2016 PrimeTime TracerAIR 255, pushing a 2014 Ford F150 SCREW XTR 4x4 3.5 Ecoboost w/Max Tow Package
4pt Equal-i-zer WDH and 1828lbs of payload capacity
|
|
|
03-26-2019, 06:08 AM
|
#4
|
Junior Member
Join Date: Aug 2018
Posts: 15
|
It’s really not that loud. It’s loud but not as loud as you would think.
__________________
2014 Crusader BHS360
|
|
|
03-26-2019, 07:13 AM
|
#5
|
Trailer Park Supervisor
Join Date: Sep 2018
Location: Northern NJ
Posts: 8,626
|
My Briggs and Stratton home gasoline generator in that power range is about one degree less annoying than a leaf blower. When the power goes out at home, you can barely hear it inside though if doors/windows are all closed. On pavement through the thin walls of an RV....I think I would rather sweat than listen to that thing drone on and on.
__________________
2019 Rockwood Geo Pro G19FD w/off road package
2015 Ford F150 XLT Super Cab 4x4 V8
Yes, I drink the water!
|
|
|
03-26-2019, 08:26 AM
|
#6
|
Senior Member
Join Date: Jun 2015
Location: Payson, AZ
Posts: 3,874
|
theoretically yes it will run both. with two a/c's i'm assuming you have a 50 amp trailer. and it appears you have not connected the generator to the trailer before. if there was a concern it would be how the 50 amp rv cord connects to the generator. is there proper receptacle on the generator for the 50 amp cable? or are there a pair of 30 amp receptacles on the generator? you may be fine but hook it up at home before the trip and verify that it will run both a/c's.
__________________
2015 cardinal model 3825fl
2015 dodge ram 3500 dually
|
|
|
03-26-2019, 08:34 AM
|
#7
|
Pickin', Campin', Mason
Join Date: Aug 2015
Location: South Western PA
Posts: 19,146
|
A 50a shore power service is 6000w on EACH leg. (12,000w total)
A 7500w generator will be marginal but should be OK to run BOTH A/Cs at the same time with some power management.
Make sure you have the proper connection to utilize the full wattage of the generator.
Not all generator outlets are created the same and provide the full wattage.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA
Days Camped ☼ '19=118 ☼ '20=116 ☼ '21=123 ☼ '22=134 ☼ '23=118☼ '24=90
|
|
|
03-26-2019, 08:35 AM
|
#8
|
Senior Member
Join Date: Jan 2019
Location: Reno, NV
Posts: 1,713
|
A parking lot, with a porta-potti, with buddies, Thursday through Sunday, "in a few months", sounds like a NASCAR race fan RV lot.
Racing makes a lot of noise but be polite with your RV neighbors when running what sounds like a construction site generator.
__________________
2018 Ram 2500 Tradesman, CTD/CC/SB/4X4/Equalizer WDH
2019 Forest River Surveyor Legend 19BHLE
|
|
|
03-26-2019, 08:42 AM
|
#9
|
Site Team
Join Date: Oct 2014
Posts: 15,300
|
Sounds like a open frame construction generator. You will not have many friends if you plan to run more than a few hours during the day.
__________________
2015 Freedom Express 248RBS
TV 2015 Silverado HD2500 Duramax
TST Tire Monitors
Honda 2000I + Companion
2 100W solar panels
|
|
|
03-26-2019, 08:43 AM
|
#10
|
Senior Member
Join Date: Jan 2017
Location: KS
Posts: 2,369
|
I think you will be fine power wise if that is what you plan on running. You wont be able to run everything at the same time (electric water heater or microwave). The two ACs should be fine with that size as long as they both don't start at the same exact time and even then you may not have a problem.
If you have a hardwired EMS you will want to test before you get there or learn how to bypass it. Most generators require an N-G plug to function and some generate an irregular sine wave that will trip the EMS.
|
|
|
03-26-2019, 08:48 AM
|
#11
|
Recently new!
Join Date: Dec 2014
Location: Arizona, in The Land of Scorch!
Posts: 1,206
|
If that is a contractor/construction type generator, you need to verify the outlet is an RV type dual 120 volt, not 220/240 volts!
__________________
1987 Starcraft Nova tent trailer, purch. '87, sold 8.14
2013 Crusader 290RLT bought new, 8.14 lotsa mods!
2001 Ford F-250 7.3
Loving wife, R.I.P., 6/6/19
and Mason the always dirty dog! R.I.P, 2/19
|
|
|
03-26-2019, 10:58 AM
|
#12
|
Junior Member
Join Date: Aug 2018
Posts: 15
|
Close but not a race. It’s a motorcycle rally at a drag strip. I have a 30 amp to 50 amp plug. Seen below. My plan was to start one ac at a time. The only other thing being run would be a few lights. No water heater. Might try the fridge but we got coolers
__________________
2014 Crusader BHS360
|
|
|
03-26-2019, 11:42 AM
|
#13
|
Pickin', Campin', Mason
Join Date: Aug 2015
Location: South Western PA
Posts: 19,146
|
Quote:
Originally Posted by 14Crusader
Close but not a race. It’s a motorcycle rally at a drag strip. I have a 30 amp to 50 amp plug. Seen below. My plan was to start one ac at a time. The only other thing being run would be a few lights. No water heater. Might try the fridge but we got coolers
Attachment 199868
|
If that is the adapter you plan to use and the generator twist-lock outlet is only rated at 30a then you will be hard pressed to run BOTH A/C units at one time since you are now going to be limited by the 30a outlet.
That's the thing with the ratings on most open frame/contractor type generators... they may have a 30a plug rated for 3600w and a couple 15a plugs rated at 1800w each and COMBINED they will give the generator a 7500w rating... BUT... you are not getting it ALL out of one plug.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA
Days Camped ☼ '19=118 ☼ '20=116 ☼ '21=123 ☼ '22=134 ☼ '23=118☼ '24=90
|
|
|
03-27-2019, 12:46 AM
|
#14
|
Senior Member
Join Date: Jan 2011
Location: Part Timing It Now
Posts: 3,457
|
Quote:
Originally Posted by 14Crusader
Close but not a race. It’s a motorcycle rally at a drag strip. I have a 30 amp to 50 amp plug. Seen below. My plan was to start one ac at a time. The only other thing being run would be a few lights. No water heater. Might try the fridge but we got coolers
Attachment 199868
|
Quote:
Originally Posted by 5picker
If that is the adapter you plan to use and the generator twist-lock outlet is only rated at 30a then you will be hard pressed to run BOTH A/C units at one time since you are now going to be limited by the 30a outlet.
That's the thing with the ratings on most open frame/contractor type generators... they may have a 30a plug rated for 3600w and a couple 15a plugs rated at 1800w each and COMBINED they will give the generator a 7500w rating... BUT... you are not getting it ALL out of one plug.
|
X2! That's a 30a to 50a adapter. The business side (generator side) is still only 30a & that's all you're going to get.
Also, you should be using an inverter style generator for "clean pure sine wave" power. This is preferred to protect the electronics in the RV such as sound systems, fridge circuitry, microwave circuitry, converter etc. Most open frame "contractor style" generators are not inverter generators. They're fine for running power tools & such but, not meant for delicate electronics.
__________________
"PT Crew Members Since 9/2010"
2011 RAM 2500 HD 6.7L CTD Crew
2014 Prime Time Sanibel 3250
|
|
|
03-28-2019, 12:04 PM
|
#15
|
Junior Member
Join Date: Aug 2018
Posts: 15
|
The generator is a dual 120/240. I and sitting in the camper with both AC’s running good and cold with all the lights on inside the camper. I am using the 50 to 30 amp adapter for the generator. It has been running for 30 min and is not even at 50% load on the generator.
__________________
2014 Crusader BHS360
|
|
|
03-28-2019, 03:07 PM
|
#16
|
Senior Member
Join Date: Apr 2016
Posts: 1,011
|
Looking at your adapter, it appears that it is a 4 prong at the male end. If that. Is the case, I’m pretty sure you have 2 30 amp hot legs that could be used as a 240 volt with the right kind of connector. The adapter lets it work as 2 120 volt legs for the rv. Jay
|
|
|
03-29-2019, 06:13 PM
|
#17
|
Junior Member
Join Date: Aug 2018
Posts: 15
|
Thanks for the help!
__________________
2014 Crusader BHS360
|
|
|
03-29-2019, 06:35 PM
|
#18
|
Senior Member
Join Date: Jul 2017
Location: California
Posts: 7,616
|
Quote:
Originally Posted by Paulie1138
If that is a contractor/construction type generator, you need to verify the outlet is an RV type dual 120 volt, not 220/240 volts!
|
RV types are also 240V with a neutral. Its just the configuration of the outlet that will be the issue. They typically are different.
|
|
|
|