|
08-09-2022, 07:51 PM
|
#1
|
Junior Member
Join Date: Oct 2019
Posts: 22
|
circuit breaker overheat 34HD
2020 34 HD rear a/c unit tripping breaker
weather very hot
this breaker is a double unit with the dryer on 1 side
front ac has a larger single unit breaker
I proped the c/b box door open and put a small fan blowing in to cool the box
worked for 3 days @ 108 degrees
made it to cooler weather
will invent blower for this area
|
|
|
08-09-2022, 08:49 PM
|
#2
|
Senior Member
Join Date: Jan 2019
Posts: 1,165
|
Quote:
Originally Posted by Joe B
2020 34 HD rear a/c unit tripping breaker
weather very hot
this breaker is a double unit with the dryer on 1 side
front ac has a larger single unit breaker
I proped the c/b box door open and put a small fan blowing in to cool the box
worked for 3 days @ 108 degrees
made it to cooler weather
will invent blower for this area
|
Please turn of shore power then Check and make sure the wire is tightly screwed into. A loose screw or wire will cause it to get hot. Also make sure the breaker is seated in the panel.. if it still gets hot I would replace the breaker.
|
|
|
08-09-2022, 09:39 PM
|
#3
|
Senior Member
Join Date: Jan 2020
Posts: 4,846
|
Quote:
Originally Posted by Joe B
will invent blower for this area
|
You are treating the symptom of the problem and not the problem itself. Circuit breakers normally don't get hot on their own, there is a problem causing them to get hot.
|
|
|
08-09-2022, 09:42 PM
|
#4
|
Site Team
Join Date: Jan 2007
Location: Goodyear, Arizona
Posts: 33,551
|
Quote:
Originally Posted by Joe B
2020 34 HD rear a/c unit tripping breaker
weather very hot
this breaker is a double unit with the dryer on 1 side
front ac has a larger single unit breaker
I proped the c/b box door open and put a small fan blowing in to cool the box
worked for 3 days @ 108 degrees
made it to cooler weather
will invent blower for this area
|
What RV brand is a 34HD?
__________________
Dan-Retired California Firefighter/EMT
Shawn-Musician/Entrepreneur/Wine Expert
and Zoe the Wonder Dog(R.I.P.)
2016 PrimeTime TracerAIR 255, pushing a 2014 Ford F150 SCREW XTR 4x4 3.5 Ecoboost w/Max Tow Package
4pt Equal-i-zer WDH and 1828lbs of payload capacity
|
|
|
08-10-2022, 04:37 PM
|
#5
|
Senior Member
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,412
|
A little heat is normal
Quote:
Originally Posted by NavyLCDR
You are treating the symptom of the problem and not the problem itself. Circuit breakers normally don't get hot on their own, there is a problem causing them to get hot.
|
Umm, little heat when operating near the rated load will normally cause a breaker to get warm or hot. I spent a summer designing building wiring and part of the job was to specify breaker to be used.
These breakers are designed with two distinct trip mechanisms for two distinct conditions in order to provide protection while minimizing nuisance tripping. - Moderate overcurrent (e.g., 110-150% of rating): The breaker includes a series resistance which warms a thermal release (bi-metallic?) which trips the breaker. Specifications may include details like "several minutes at 110%, 10 seconds at 200%). This prevents tripping from motor-starting currents (A/C, refrigerator) that momentarily exceed rating. This resistance warms the breaker and its case.
- Severe overload (short circuit or nearly so): The breaker also includes a series electromagnet. Its strength under moderate currents is not sufficient to trip the breaker, but under a heavy overload the electromagnet will trip the breaker.
Now, Commander, it's obvious that one would be able to feel the warmth of any breaker operated near rated load. (Try it on your water heater breaker.) And it's also obvious that the trip point is affected by the cumulative effect of internally generated heat and ambient temperature. The OP's breaker could be old and have a reduced thermal trip point, but when you consider the effect of an additional 40°F temperature, it might be performing to specification.
(Last Wednesday, we opened up the trailer. Outside air temperature was 90°F. Inside the trailer it was 109°F. When you consider that the breaker was probably spec'd at 20°C (68°F), a difference of 41°F. The internals of the breaker were probably hot enough to burn me after the A/C ran for a while--and this is NORMAL operation. There's a reason why breakers are packaged in Bakelite. When I think about it, I'm actually pleased that the air conditioner started.)
__________________
Larry
"Everybody's RV is not like your RV."
"Always take pictures with the button on the right."
"Always bypass the water heater before opening the low-point drains."
Sticks and Bricks: Raleigh, NC
2008 Cherokee 38P: at Ivor, VA permanently
|
|
|
08-10-2022, 06:08 PM
|
#6
|
Senior Member
Join Date: Jan 2020
Posts: 4,846
|
Quote:
Originally Posted by Larry-NC
Umm, little heat when operating near the rated load will normally cause a breaker to get warm or hot. I spent a summer designing building wiring and part of the job was to specify breaker to be used.
These breakers are designed with two distinct trip mechanisms for two distinct conditions in order to provide protection while minimizing nuisance tripping. - Moderate overcurrent (e.g., 110-150% of rating): The breaker includes a series resistance which warms a thermal release (bi-metallic?) which trips the breaker. Specifications may include details like "several minutes at 110%, 10 seconds at 200%). This prevents tripping from motor-starting currents (A/C, refrigerator) that momentarily exceed rating. This resistance warms the breaker and its case.
- Severe overload (short circuit or nearly so): The breaker also includes a series electromagnet. Its strength under moderate currents is not sufficient to trip the breaker, but under a heavy overload the electromagnet will trip the breaker.
Now, Commander, it's obvious that one would be able to feel the warmth of any breaker operated near rated load. (Try it on your water heater breaker.) And it's also obvious that the trip point is affected by the cumulative effect of internally generated heat and ambient temperature. The OP's breaker could be old and have a reduced thermal trip point, but when you consider the effect of an additional 40°F temperature, it might be performing to specification.
(Last Wednesday, we opened up the trailer. Outside air temperature was 90°F. Inside the trailer it was 109°F. When you consider that the breaker was probably spec'd at 20°C (68°F), a difference of 41°F. The internals of the breaker were probably hot enough to burn me after the A/C ran for a while--and this is NORMAL operation. There's a reason why breakers are packaged in Bakelite. When I think about it, I'm actually pleased that the air conditioner started.)
|
Well, put a fan on it then, I guess. I've never heard of a standard AC distribution panel with nothing but circuit breakers in it require a cooling fan.
|
|
|
08-10-2022, 07:04 PM
|
#7
|
Senior Member
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,412
|
Keep cool
Quote:
Originally Posted by NavyLCDR
Well, put a fan on it then, I guess. I've never heard of a standard AC distribution panel with nothing but circuit breakers in it require a cooling fan.
|
Standard panels don't usually operate at close to rated load at 109 degrees F.
If this happened to me in the field, I would turn off everything else (to minimize current through the breaker), then run the A/C until the interior cooled down.
__________________
Larry
"Everybody's RV is not like your RV."
"Always take pictures with the button on the right."
"Always bypass the water heater before opening the low-point drains."
Sticks and Bricks: Raleigh, NC
2008 Cherokee 38P: at Ivor, VA permanently
|
|
|
08-10-2022, 08:23 PM
|
#8
|
Senior Member
Join Date: Jan 2020
Posts: 4,846
|
Quote:
Originally Posted by Larry-NC
Standard panels don't usually operate at close to rated load at 109 degrees F.
If this happened to me in the field, I would turn off everything else (to minimize current through the breaker), then run the A/C until the interior cooled down.
|
Thank you for the information. From some research it looks like circuit breaker rated capacities are based upon 104F ambient temperature. Lower than 104F and the tripping point goes up. Higher than 104F and the tripping point does indeed go lower than what the circuit breaker is rated for. And then on top of that, there is the allowed tolerance.
|
|
|
08-10-2022, 09:01 PM
|
#9
|
Senior Member
Join Date: Apr 2021
Posts: 2,216
|
Hot Breaker
I use an Infra Red heat gun to locate the hot breaker. The Infra-Red measures temperature without touching.
Bob
|
|
|
08-10-2022, 09:32 PM
|
#10
|
Senior Member
Join Date: Sep 2018
Location: Milwaukee
Posts: 175
|
I have a simple diagnostic, what is he Amp rating of the circuitbreaker, what is the actual circut voltage and Amp draw.
I learned alot from this posting. Oh by the way, Bob I like to test the temperature with my tongue :-]
|
|
|
08-15-2022, 06:42 AM
|
#11
|
Junior Member
Join Date: Oct 2019
Posts: 22
|
Circuit breaker
Connections have been checked nothing loose
|
|
|
08-15-2022, 06:45 AM
|
#12
|
Junior Member
Join Date: Oct 2019
Posts: 22
|
Dynamax super C
|
|
|
08-15-2022, 07:14 AM
|
#13
|
Senior Member
Join Date: Apr 2022
Location: Tarpon Springs FL
Posts: 3,280
|
did anyone measure the actual voltage and amps.... start from the post
at the power post
at breaker box input
at breaker box individual breakers.
at the a/c input
at the a/c individual components (especially the compressor)
Multi meters are a great tool, last forever and are great in tracking down problems without paying big $$$ replacing parts that you think may be faulty
Lots of videos on google on how to use a multi meter
you can also google individual problems .. test air conditioner compressor voltage with multi meter
even if a tutorial is NOT based on a RV .... the principle is the same so 99% of the info out there can be used in a RV situation
__________________
Tarpon Springs FL
2022 Salem 24RLXL
|
|
|
08-15-2022, 07:23 AM
|
#14
|
Senior Member
Join Date: Nov 2017
Location: Dayton Ohio
Posts: 3,566
|
Probably the breaker. Not expensive. Not hard to change.
Running like this is not a good plan.
|
|
|
|
Thread Tools |
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|