DC Converter Fried on new TT

Hi All,

Just got our new Puma 26FBSS camper prior to Memorial day and went camping at a Campground in WV and during our stay the main transformer at the campground blew sending out 240+ volts to all the circuits at the campground last count there were over 40 campers damaged ranging from converters, Air conditioners, Microwaves, and LCD TVs. The campground stated that every camper signed a "camp at risk" clause and they will not cover any damages.

Our DC converter was blown (Parallex 7155) and its around 200.00 to replace, This is an important lesson to learn if we had a surge protector we would have been spared this problem. I have contacted my insurance company to see if they will pay for a replacement. Should I replace the unit with the same converter or look at an upgrade? Does anyone have any suggestions on a direct replacement upgrade?

Al
ALMcKinney is offline   Reply With Quote
Old 06-02-2011, 10:08 PM   #2
Senior Member
 
Join Date: Aug 2010
Location: Canandaigua,New York (The heart of the Finger Lakes)
Posts: 487
I know of a nice Surge Protector - Progressive Industries Electrical Management System EMS-PT30C (30amp) or the EMS-PT50C (50amp) -- Sorry for your loss....I'd have been PO'd. Every time I read one of these posts about fried coverters, I show the DW why I purchased the surge protector ! Not sure if I would have wanted to be a Camp ground owner when something like this happens! Sorry I can't help you on the up-grade, but thanks for posting so others (Campers) can see it really does happen !! So it is worth buying a Surge Protector !!
__________________

David & Annamarie & 2-Pugs (Fatty and Harley)
2011 Rockwood Windjammer 3065
2011 Ford F-250 6.2- V8
2011 Hensley Arrow "NO-SWAY" Hitch
BigRed is offline   Reply With Quote
Old 06-03-2011, 06:22 AM   #3
Site Team
 
KyDan's Avatar
 
Join Date: Mar 2008
Location: Louisville, KY
Posts: 10,518
Sorry about your bad luck!
I don't suppose this is covered by your insurance??

And I'm not trying to start a big discussion here but surge protectors
are made for voltage spikes.
These typically are only milliseconds long.
A transformer that puts out 240 volts when it should have only been
120 will probably go right thru the surge protector and fry any thing
that happens to be on at the time.

I'm not saying you shouldn't have one but in this case I wonder if
it would have made a difference.
__________________
Peace!
Dan & Rita D
2017 Nissan Titan 5.6L King cab 4wd
2016 Evergreen Everlite 242RBS
29' empty nest model. Blue Ox WD hitch
(1 queen bed, large main cabin and huge bathroom)
Camping days 2010-53, 2011-47, 2012-41, 2013-41, 2014-31, 2015-40, 2016-44, 2017-63, 2018-75, 2019-32, 2020-41, 2021-49, 2022-43, 2023-66
KyDan is online now   Reply With Quote
Old 06-03-2011, 09:04 AM   #4
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,268
Still wondering how that could happen.

What possible failure mode at the pole transformer could cause 240 to show up on one leg of a circuit? Sounds like a "cop out" by the campground to me. If their electrician made a mistake when reconnecting the wires of a burnt out transformer; can see how that would do it.
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
Herk7769 is offline   Reply With Quote
Old 06-03-2011, 09:40 AM   #5
Senior Member
 
Join Date: Aug 2010
Location: Canandaigua,New York (The heart of the Finger Lakes)
Posts: 487
Kydan...The EMC-30PTC from Progressive Industries will shut-off the power to the TT, If 240volts is detected, So for this type of surge protector it would have just shut the power off. Now will some cheaper surge protectors...not sure about. This protector IS pricey ! @ $230 if search the internet and find it on sale. It retails for around $370 I believe.
__________________

David & Annamarie & 2-Pugs (Fatty and Harley)
2011 Rockwood Windjammer 3065
2011 Ford F-250 6.2- V8
2011 Hensley Arrow "NO-SWAY" Hitch
BigRed is offline   Reply With Quote
Old 06-03-2011, 07:16 PM   #6
Junior Member
 
electromagn8's Avatar
 
Join Date: Apr 2011
Location: Duanesburg, NY
Posts: 15
Herk, I am thinking the same thing, unless the neutral conductor is lost at the x-frmr. The end result would be 240 L-N on both phases. I did have a situation about 2 years ago during a wind storm where a lineman mis-wired a x-frmr bank and I ended up losing $1,800.00 in household electronics. Many neighbors lost their much more including meter sockets, panels, etc. The utility company paid for repairs.
__________________
[/SIGPIC]


2011 Flagstaff 8528BHSS
2008 Toyota Tundra SR5
electromagn8 is offline   Reply With Quote
Old 06-03-2011, 07:22 PM   #7
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,268
Quote:
Originally Posted by electromagn8 View Post
Herk, I am thinking the same thing, unless the neutral conductor is lost at the x-frmr. The end result would be 240 L-N on both phases. I did have a situation about 2 years ago during a wind storm where a lineman mis-wired a x-frmr bank and I ended up losing $1,800.00 in household electronics. Many neighbors lost their much more including meter sockets, panels, etc. The utility company paid for repairs.
Correct me if I am wrong, but if the neutral was disconnected, you would only have 1/2 of a connection in a 110 outlet (the hot) and NO connection on the Neutral. Thus no power AT ALL. This should not even be an issue on the 50 amp service since even through there would be 220 across the "hots" without a neutral there would be NO current on any 110 VAC breaker.

I can totally understand a mis-wire causing this problem. If the other hot was wired to the neutral grid at the campground, then there would be 220 across the 110 outlets.
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
Herk7769 is offline   Reply With Quote
Old 06-03-2011, 07:29 PM   #8
Junior Member
 
electromagn8's Avatar
 
Join Date: Apr 2011
Location: Duanesburg, NY
Posts: 15
If the neutral is lost at the point (or close to) the secondary of the x-frmr, then it basically connects the phases together at the next distribution point. This then essentially makes the 120v circuit 240v, when loads are connected to both phases to complete the path.
__________________
[/SIGPIC]


2011 Flagstaff 8528BHSS
2008 Toyota Tundra SR5
electromagn8 is offline   Reply With Quote
Old 06-03-2011, 07:39 PM   #9
Site Team - Lou
 
Herk7769's Avatar
 
Join Date: Oct 2009
Location: South Eastern PA
Posts: 23,268
Quote:
Originally Posted by electromagn8 View Post
If the neutral is lost at the point (or close to) the secondary of the x-frmr, then it basically connects the phases together at the next distribution point. This then essentially makes the 120v circuit 240v, when loads are connected to both phases to complete the path.
OH! Duh! I think I get it!

This could only happen in a 50 amp camper though since both phases are only used in a two buss system (50 amp camper). The neutral buss in the panel (with no neutral to drain off the return current to maintain 120 VAC) would carry that current to the "other side" through components used on that leg, like the second AC making everything "see" 220 VAC.

In a single phase unit (30 amp) there would be no second phase to carry the current "back home" so there would be no power.

Did I get that right?
__________________
Lou & Freya the wonder dog
2008 GMC Sierra 3000HD Allison Duramax
2019 Flagstaff 8529FL
Herk7769 is offline   Reply With Quote
Old 06-03-2011, 11:06 PM   #10
Senior Member
 
Join Date: Mar 2011
Posts: 108
Quote:
Originally Posted by herk7769 View Post
OH! Duh! I think I get it!

This could only happen in a 50 amp camper though since both phases are only used in a two buss system (50 amp camper). The neutral buss in the panel (with no neutral to drain off the return current to maintain 120 VAC) would carry that current to the "other side" through components used on that leg, like the second AC making everything "see" 220 VAC.

In a single phase unit (30 amp) there would be no second phase to carry the current "back home" so there would be no power.

Did I get that right?

I think you got it.

I got a call from the camp ground and the power company gave them a claim number for us to use to be compensated for any loss. So it seems it may have been a power company issue. The campground stated the lineman did something wrong which caused this problem to begin with.

Also my insurance company stated the damage would be covered as well.

So all well that ends well.

I am going to purchase a surge protector this weekend.

Regards,
Al
ALMcKinney is offline   Reply With Quote
Old 06-05-2011, 08:57 PM   #11
Senior Member
 
Join Date: Mar 2011
Posts: 108
Quote:
Originally Posted by ALMcKinney View Post
I think you got it.

I got a call from the camp ground and the power company gave them a claim number for us to use to be compensated for any loss. So it seems it may have been a power company issue. The campground stated the lineman did something wrong which caused this problem to begin with.

Also my insurance company stated the damage would be covered as well.

So all well that ends well.

I am going to purchase a surge protector this weekend.

Regards,
Al
Just an update,

Looks like I will have to contact my insurance company, power company will not pay for any damages per campground.

Take care,
Al
ALMcKinney is offline   Reply With Quote
Old 06-05-2011, 10:11 PM   #12
Senior Member
 
Join Date: Aug 2010
Location: Manitoba
Posts: 1,283
At least you didn't do it yourself!
A "buddy" of mine forced his camper's 50 amp 120V plug into a 240V welding receptacle in his shop. Needless to say, the guy is a dufus.
But he did get it repaired for about $50. Only one component blew, but it did leak some nasty-looking oil.
But if there is a "surge" protector that stops 240V, it might be a good thing to have.
crocus is offline   Reply With Quote
Old 06-05-2011, 10:39 PM   #13
Senior Member
 
Join Date: Aug 2010
Location: Canandaigua,New York (The heart of the Finger Lakes)
Posts: 487
Progressive Industries EMS-PT50C surge protector will stop a 240V shot ! Its worth the cost !!
__________________

David & Annamarie & 2-Pugs (Fatty and Harley)
2011 Rockwood Windjammer 3065
2011 Ford F-250 6.2- V8
2011 Hensley Arrow "NO-SWAY" Hitch
BigRed is offline   Reply With Quote
Old 06-05-2011, 11:23 PM   #14
Senior Member
 
jimh's Avatar
 
Join Date: Jul 2010
Location: Lake Charles, La.
Posts: 1,536
i understand the floating neutral, i've seen it happen in someone's home. they must have had several problems at the campground.
here, they tie the neutral to ground at each pole and at the home. the one above had a poor connection from the utility (had to be re crimped). the ground from the meter base had also been cut (from trimming grass with a solid blade).
i'm wondering if a surge suppressor would have prevented ur problem.
jimh is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 03:39 PM.