Drop in Solar output after 4 years

I installed 3 100 watt Renogy solar panels and their 30 amp MTTP controller. I was getting around 14 amps to my BB lithium batteries. Now I am getting only 10-11 amps. I am taking a reading at noon on clear sunny days. My first check was on the summer solstace. The volts from the panels shows 19.7v output on the controller disconnected from the batteries and only 16.5v when connected. Also the Renogy battery monitor shows only 145-147 watts coming from the 300 watt panels. My panel cables are joined with connectors and the 2 cables are routed to the fridge vent, down the side of the fridge and under the cabinets to the raise area at trhe rear of the MH. From there it continues under the floor across the the passenger side and forward to the controller. It's 25 feet and another 30" to the batteries. The cable is 10 awg as 8 awg was too stiff for fishing thru. I would expect some line voltage loss but not that much. Any thoughts?
__________________
2004 Winnebago Minnie 22e(went to a nice family Oct 3, 2015)
2016 Forester 2701DS (Aug 31, 2015)
2017 Camping 12 trips 38 nights
2018 Camping 10 trips 38 nights
2019 Camping 6 trips 19 nights
2020 Camping 0 trips Cancellations 6
Sagecoachdriver is offline   Reply With Quote
Old 08-11-2021, 09:37 AM   #2
Senior Member
 
rsdata's Avatar
 
Join Date: Aug 2014
Location: Northern KY
Posts: 5,725
I suspect you have cleaned the panels before making these measurements?

Wire does not deteriorate so that part of the equation should not change, but what about corrosion on the terminals and those terminal connections?

I use the stuff below on all electrical connections to clean and prevent oxidation...
Attached Thumbnails
Click image for larger version

Name:	deoxit02.jpg
Views:	154
Size:	28.8 KB
ID:	260831  
__________________
"nothing can now be believed which is seen in a newspaper. Truth itself becomes suspicious by being put into that polluted vehicle."
Thomas Jefferson to John Norvell pg. 2, June 11, 1807

2014 Shamrock 183
2014 RAM 1500 Bighorn Crew Cab, HEMI, 3.21 gears, 8 Spd, 4X4 TST TPMS
rsdata is offline   Reply With Quote
Old 08-11-2021, 09:46 AM   #3
Senior Member
 
Join Date: Jul 2017
Location: North of Seattle, WA
Posts: 17,362
Quote:
Originally Posted by Sagecoachdriver View Post
I installed 3 100 watt Renogy solar panels and their 30 amp MTTP controller. I was getting around 14 amps to my BB lithium batteries. Now I am getting only 10-11 amps. I am taking a reading at noon on clear sunny days. My first check was on the summer solstace. The volts from the panels shows 19.7v output on the controller disconnected from the batteries and only 16.5v when connected. Also the Renogy battery monitor shows only 145-147 watts coming from the 300 watt panels. My panel cables are joined with connectors and the 2 cables are routed to the fridge vent, down the side of the fridge and under the cabinets to the raise area at trhe rear of the MH. From there it continues under the floor across the the passenger side and forward to the controller. It's 25 feet and another 30" to the batteries. The cable is 10 awg as 8 awg was too stiff for fishing thru. I would expect some line voltage loss but not that much. Any thoughts?
I would check connections. Are panels connected in series as they should for the MPPT controller? Or are they wired in parallel. Regardless, loose or faulty connections can greatly reduce power output.

I pull 14 amp from two 100 watt panels at full sun wired in series. With three panels you should see just over 20 amps if wired in series. Output from solar panels should read around 50-55 volts.

I would isolate each panel and check individual outputs. Open Circuit Voltage in full sun should be ~22 volts (it's on the spec sticker on the back) for each panel.

Of course the obvious question has to be asked, "How clean are the panels?" An accumulation of dust and "pollution scum" can drastically reduce output. If sun can reach the silicon cells, power can't be produced.
__________________
"A wise man can change his mind. A fool never will." (Japanese Proverb)

"You only grow old when you run out of new things to do"

2018 Flagstaff Micro Lite 25BDS
2023 f-150 SCREW XLT 3.5 Ecoboost (The result of a $68,000 oil change)
TitanMike is offline   Reply With Quote
Old 08-11-2021, 09:57 AM   #4
Senior Member
 
Sagecoachdriver's Avatar
 
Join Date: Jun 2015
Location: Southern California
Posts: 2,087
Quote:
Originally Posted by rsdata View Post
I suspect you have cleaned the panels before making these measurements?

Wire does not deteriorate so that part of the equation should not change, but what about corrosion on the terminals and those terminal connections?

I use the stuff below on all electrical connections to clean and prevent oxidation...
Panels are clean and I did spray each connection with contact cleaner. I am replacing the connectors and the 30 amp fuses. Only thing left would be the cables.
__________________
2004 Winnebago Minnie 22e(went to a nice family Oct 3, 2015)
2016 Forester 2701DS (Aug 31, 2015)
2017 Camping 12 trips 38 nights
2018 Camping 10 trips 38 nights
2019 Camping 6 trips 19 nights
2020 Camping 0 trips Cancellations 6
Sagecoachdriver is offline   Reply With Quote
Old 08-11-2021, 10:01 AM   #5
Senior Member
 
Join Date: Jul 2017
Location: North of Seattle, WA
Posts: 17,362
Quote:
Originally Posted by Sagecoachdriver View Post
Panels are clean and I did spray each connection with contact cleaner. I am replacing the connectors and the 30 amp fuses. Only thing left would be the cables.
Save yourself some time and check output from each panel. Panel output can impacted if there is a bypass diode failure. Start with the source (panels) and make sure you have proper output before chasing wire or connector problems.
__________________
"A wise man can change his mind. A fool never will." (Japanese Proverb)

"You only grow old when you run out of new things to do"

2018 Flagstaff Micro Lite 25BDS
2023 f-150 SCREW XLT 3.5 Ecoboost (The result of a $68,000 oil change)
TitanMike is offline   Reply With Quote
Old 08-11-2021, 10:12 AM   #6
Senior Member
 
rsdata's Avatar
 
Join Date: Aug 2014
Location: Northern KY
Posts: 5,725
Quote:
Only thing left would be the cables.
Wires don't fail... connections do...

I think the panel testing as TitanMike suggested would be the ticket... Panels do age and cells deteriorate...
__________________
"nothing can now be believed which is seen in a newspaper. Truth itself becomes suspicious by being put into that polluted vehicle."
Thomas Jefferson to John Norvell pg. 2, June 11, 1807

2014 Shamrock 183
2014 RAM 1500 Bighorn Crew Cab, HEMI, 3.21 gears, 8 Spd, 4X4 TST TPMS
rsdata is offline   Reply With Quote
Old 08-11-2021, 11:49 AM   #7
Senior Member
 
GravelRider's Avatar
 
Join Date: Jul 2020
Posts: 907
Quote:
Originally Posted by Sagecoachdriver View Post
I installed 3 100 watt Renogy solar panels and their 30 amp MTTP controller. I was getting around 14 amps to my BB lithium batteries. Now I am getting only 10-11 amps. I am taking a reading at noon on clear sunny days. My first check was on the summer solstace. The volts from the panels shows 19.7v output on the controller disconnected from the batteries and only 16.5v when connected. Also the Renogy battery monitor shows only 145-147 watts coming from the 300 watt panels. My panel cables are joined with connectors and the 2 cables are routed to the fridge vent, down the side of the fridge and under the cabinets to the raise area at trhe rear of the MH. From there it continues under the floor across the the passenger side and forward to the controller. It's 25 feet and another 30" to the batteries. The cable is 10 awg as 8 awg was too stiff for fishing thru. I would expect some line voltage loss but not that much. Any thoughts?
Are these rigid or flexible solar panels? The flexible ones are notorious for developing a bit of a glaze over them over time, thus decreasing output.
__________________
GravelRider is offline   Reply With Quote
Old 08-11-2021, 11:58 AM   #8
Senior Member
 
Sagecoachdriver's Avatar
 
Join Date: Jun 2015
Location: Southern California
Posts: 2,087
These are ridged panels. Good idea to check each panels output. I have new connectors arriving today and will check each panels output. Thanks
__________________
2004 Winnebago Minnie 22e(went to a nice family Oct 3, 2015)
2016 Forester 2701DS (Aug 31, 2015)
2017 Camping 12 trips 38 nights
2018 Camping 10 trips 38 nights
2019 Camping 6 trips 19 nights
2020 Camping 0 trips Cancellations 6
Sagecoachdriver is offline   Reply With Quote
Old 08-11-2021, 02:22 PM   #9
Junior Member
 
Join Date: May 2015
Location: Muskegon MI
Posts: 14
Is the battery state of charge similar between the two readings?
__________________
Retired Piston Ring Engineer
Auto Industry Supplier
BSME U of M 1978
2014 F150 SCREW 5.0L
2016 Mini-Lite 2506S
sytsmasj is offline   Reply With Quote
Old 08-11-2021, 08:57 PM   #10
Senior Member
 
Sagecoachdriver's Avatar
 
Join Date: Jun 2015
Location: Southern California
Posts: 2,087
Quote:
Originally Posted by sytsmasj View Post
Is the battery state of charge similar between the two readings?
The Renogy battery monitor is off as there is a parasitic drain of .2amps that is not reflected on the monitor. I have the batteries disconnected and have a 10-15 amp drain after a week or two. Not reflected on battery monitor still showing 100% and 200 amps. Voltage is the same or within .2 amps and voltage. on the controller and the battery monitor.
I received the new set of connectors and installed them. I found 2 connectors that needed replacing which I did. Do to overcast skies and late hour I was unable to see any real improvement or test each individual panel with voltage, amps and watts. Maybe tomorrow, heading out to the beach for 2 days.
I did order a 4 cable connector so I can add another panel if needed.
__________________
2004 Winnebago Minnie 22e(went to a nice family Oct 3, 2015)
2016 Forester 2701DS (Aug 31, 2015)
2017 Camping 12 trips 38 nights
2018 Camping 10 trips 38 nights
2019 Camping 6 trips 19 nights
2020 Camping 0 trips Cancellations 6
Sagecoachdriver is offline   Reply With Quote
Old 08-11-2021, 09:31 PM   #11
Senior Member
 
Join Date: Jul 2017
Location: North of Seattle, WA
Posts: 17,362
Quote:
Originally Posted by Sagecoachdriver View Post
The Renogy battery monitor is off as there is a parasitic drain of .2amps that is not reflected on the monitor. I have the batteries disconnected and have a 10-15 amp drain after a week or two. Not reflected on battery monitor still showing 100% and 200 amps. Voltage is the same or within .2 amps and voltage. on the controller and the battery monitor.
I received the new set of connectors and installed them. I found 2 connectors that needed replacing which I did. Do to overcast skies and late hour I was unable to see any real improvement or test each individual panel with voltage, amps and watts. Maybe tomorrow, heading out to the beach for 2 days.
I did order a 4 cable connector so I can add another panel if needed.
If you add another panel just like others it would be beneficial to connect them all in a series/parallel configuration. Connect pairs of two, in parallel, In series and utilize the MPPT controller to maximize efficiency. Earlier start of charging, later end of charging as sun goes down.
__________________
"A wise man can change his mind. A fool never will." (Japanese Proverb)

"You only grow old when you run out of new things to do"

2018 Flagstaff Micro Lite 25BDS
2023 f-150 SCREW XLT 3.5 Ecoboost (The result of a $68,000 oil change)
TitanMike is offline   Reply With Quote
Old 08-11-2021, 09:31 PM   #12
Senior Member
 
Join Date: May 2020
Posts: 212
Solar panel output

Solar panel output is much like a battery, the voltage output depends on the draw, that is the battery state of charge plus other items in RV drawing power, for me too difficult on a day to day basis while camping to compare the solar output readings. The short circuit voltage test on each panel would verify panel output.
Daniel.mullins4 is offline   Reply With Quote
Old 08-11-2021, 09:59 PM   #13
Senior Member
 
Sagecoachdriver's Avatar
 
Join Date: Jun 2015
Location: Southern California
Posts: 2,087
Quote:
Originally Posted by TitanMike View Post
If you add another panel just like others it would be beneficial to connect them all in a series/parallel configuration. Connect pairs of two, in parallel, In series and utilize the MPPT controller to maximize efficiency. Earlier start of charging, later end of charging as sun goes down.
So you are saying rather than have them in parallel or all 3 or 4 going into one connector, have 2 go into one connector and the other 2 go into another connecter and then have the 2 cables go into another connector. Then do the same for the other cables. It's still in parallel right?
__________________
2004 Winnebago Minnie 22e(went to a nice family Oct 3, 2015)
2016 Forester 2701DS (Aug 31, 2015)
2017 Camping 12 trips 38 nights
2018 Camping 10 trips 38 nights
2019 Camping 6 trips 19 nights
2020 Camping 0 trips Cancellations 6
Sagecoachdriver is offline   Reply With Quote
Old 08-11-2021, 10:06 PM   #14
Senior Member
 
Sagecoachdriver's Avatar
 
Join Date: Jun 2015
Location: Southern California
Posts: 2,087
I originally used the branch connectors and they were dried out and one was missing the locking piece. I replaced them with the wire ones.
Attached Thumbnails
Click image for larger version

Name:	61bgkXoXItL._AC_SX466_.jpg
Views:	53
Size:	21.9 KB
ID:	260897   Click image for larger version

Name:	71LuMOef3LL._AC_SX466_.jpg
Views:	43
Size:	14.3 KB
ID:	260898  
__________________
2004 Winnebago Minnie 22e(went to a nice family Oct 3, 2015)
2016 Forester 2701DS (Aug 31, 2015)
2017 Camping 12 trips 38 nights
2018 Camping 10 trips 38 nights
2019 Camping 6 trips 19 nights
2020 Camping 0 trips Cancellations 6
Sagecoachdriver is offline   Reply With Quote
Old 08-11-2021, 11:09 PM   #15
Senior Member
 
Join Date: Aug 2015
Location: Box elder
Posts: 730
Last note, panels do deteriorate over time. Many have a spec sheet about how much output over how many years.
__________________
2015 silverback 31IK
2023 f350
kcmusa is offline   Reply With Quote
Old 08-11-2021, 11:12 PM   #16
Senior Member
 
Join Date: Jul 2017
Location: North of Seattle, WA
Posts: 17,362
Quote:
Originally Posted by kcmusa View Post
Last note, panels do deteriorate over time. Many have a spec sheet about how much output over how many years.
Most panels built in the last few years have LONG warranties for power output.
__________________
"A wise man can change his mind. A fool never will." (Japanese Proverb)

"You only grow old when you run out of new things to do"

2018 Flagstaff Micro Lite 25BDS
2023 f-150 SCREW XLT 3.5 Ecoboost (The result of a $68,000 oil change)
TitanMike is offline   Reply With Quote
Old 08-11-2021, 11:16 PM   #17
Senior Member
 
Sagecoachdriver's Avatar
 
Join Date: Jun 2015
Location: Southern California
Posts: 2,087
Quote:
Originally Posted by TitanMike View Post
Most panels built in the last few years have LONG warranties for power output.
Yes,
25-year power output warranty: 5 year/95% efficiency rate, 10 year/90% efficiency rate, 25-year/80% efficiency rate.

At 4 years they should have lost maybe 5% not 30%+.
__________________
2004 Winnebago Minnie 22e(went to a nice family Oct 3, 2015)
2016 Forester 2701DS (Aug 31, 2015)
2017 Camping 12 trips 38 nights
2018 Camping 10 trips 38 nights
2019 Camping 6 trips 19 nights
2020 Camping 0 trips Cancellations 6
Sagecoachdriver is offline   Reply With Quote
Old 08-11-2021, 11:17 PM   #18
Senior Member
 
Join Date: Jul 2017
Location: North of Seattle, WA
Posts: 17,362
Quote:
Originally Posted by Sagecoachdriver View Post
So you are saying rather than have them in parallel or all 3 or 4 going into one connector, have 2 go into one connector and the other 2 go into another connecter and then have the 2 cables go into another connector. Then do the same for the other cables. It's still in parallel right?
Connect like this. Ignore voltages shown, your panels are more like 18-22 volts each and around 5 amp output. Just use the Diagram for cable connections.Click image for larger version

Name:	Screenshot_20210811-211440_Edge.jpg
Views:	123
Size:	28.3 KB
ID:	260901
__________________
"A wise man can change his mind. A fool never will." (Japanese Proverb)

"You only grow old when you run out of new things to do"

2018 Flagstaff Micro Lite 25BDS
2023 f-150 SCREW XLT 3.5 Ecoboost (The result of a $68,000 oil change)
TitanMike is offline   Reply With Quote
Old 08-11-2021, 11:47 PM   #19
Senior Member
 
Join Date: Sep 2020
Posts: 742
And series-parallel let's you keep the smaller sized wire and fuse.
__________________
2021 Flagstaff 21DS
2015 Silverado 2500HD (overkill but convenient)

Renogy bits: 3000W Inverter/Charger, 400Ah LiFePo4, 40A DC-to-DC
Rich Solar bits: 400W of panels, 40A MPPT
Misc bits: LevelMatePro+, SolidRemote based wireless controlled LED storage lighting
jbflag21ds is offline   Reply With Quote
Old 08-12-2021, 12:09 AM   #20
Senior Member
 
Sagecoachdriver's Avatar
 
Join Date: Jun 2015
Location: Southern California
Posts: 2,087
So the 24v 8 amps going into the controller brings itdown to 12v and how many amps? What would the controller be set at?
__________________
2004 Winnebago Minnie 22e(went to a nice family Oct 3, 2015)
2016 Forester 2701DS (Aug 31, 2015)
2017 Camping 12 trips 38 nights
2018 Camping 10 trips 38 nights
2019 Camping 6 trips 19 nights
2020 Camping 0 trips Cancellations 6
Sagecoachdriver is offline   Reply With Quote
Reply

Tags
solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 04:48 AM.