Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×


Reply
 
Thread Tools Display Modes
Old 01-16-2013, 09:51 PM   #41
Senior Member
 
caper's Avatar
 
Join Date: Jul 2010
Posts: 2,031
If your 15 amp breaker in the house was to fail you would not be drawing 200 amp. If you are on a 50 amp service and your 30 amp main breaker did not trip you are then able to put up to 50 amps on the main wire of the TT.
__________________
Terry and Janet
2008 3001W Windjammer
2007 Ford F150
caper is offline   Reply With Quote
Old 01-16-2013, 09:55 PM   #42
Senior Member
 
jimh's Avatar
 
Join Date: Jul 2010
Location: Lake Charles, La.
Posts: 1,536
i may be getting ready to answer why not the change the 30 amp main in the trailer to 50 A. the main protects the buss in the breaker box. the individual breakers in the box protect the individual wires they are assigned to.

my other suggestion to change out the cable and the 50 amp main may not work if the breaker box (buss) isn't rated above 30A. it may be worth a check but i suspect the manufacture has this sized right.

the voltage drops in the original cable and connections isn't going to be improved by adding another connection unless the problem is in the 30 amp socket at the pedistal. ur still contending with the same supply voltage with more resistance (2 more connections by adding the adapter).

adapting from 50 a to 30 a is a way to get around a pedestal breaker tripping and the main in the trailer not.
jimh is offline   Reply With Quote
Old 01-16-2013, 09:57 PM   #43
Oklahoma Proud
 
MillerTime's Avatar
 
Join Date: Jul 2012
Location: central OK
Posts: 2,784
Ok, if the impossible happens, call your insurance and make a claim, then your lawyer to handle the claim about breaker failing (which is not going to fail in the closed position), then to camco for offering an adapter, the campground for having electric......
MillerTime is offline   Reply With Quote
Old 01-16-2013, 10:13 PM   #44
Senior Member
 
jimh's Avatar
 
Join Date: Jul 2010
Location: Lake Charles, La.
Posts: 1,536
i'm thinking the 50 amp at the pedestal would trip before u got enough for a fire. i believe u can put 30a thru #12, i don't know what u can put thru 10. these numbers may be in free space which u don't have in a cable.

personally, i wouldn't have a problem adapting from 50 to 30. it wouldn't keep me awake at night. Several yrs ago, i camped in a park in Ky that only offered 50 and 20. the campground had adapters for use. i always thought that if they offered 50 there would be a 30 in there as well. that was a first.
jimh is offline   Reply With Quote
Old 01-16-2013, 10:19 PM   #45
Oklahoma Proud
 
MillerTime's Avatar
 
Join Date: Jul 2012
Location: central OK
Posts: 2,784
Jim
14 gauge =15 amp
12. =20 amp
10. =30 amp
8. =40 amp
6. =60 amp

This is the american wire gauge system-Awg, straight from the book
MillerTime is offline   Reply With Quote
Old 01-16-2013, 10:31 PM   #46
Senior Member
 
jimh's Avatar
 
Join Date: Jul 2010
Location: Lake Charles, La.
Posts: 1,536
Quote:
Originally Posted by MillerTime View Post
Jim
14 gauge =15 amp
12. =20 amp
10. =30 amp
8. =40 amp
6. =60 amp

This is the american wire gauge system-Awg, straight from the book
agree.
that is below what the wire is capable of. that overload factor is why i wouldn't be concerned abt the remote possibility that i could overload the wire outside. even though the inside main is not meant to protect the outside cable, it would in most cases. i wouldn't even think of putting too large a breaker on one of the inside circuits.
jimh is offline   Reply With Quote
Old 01-16-2013, 10:58 PM   #47
Senior Member
 
caper's Avatar
 
Join Date: Jul 2010
Posts: 2,031
You can purchase a 50 to 30 amp adapter so you can use a CG that does not have 30 amp service. They are not to be used to try to get extra power to the TT when you are overloading the draw. The gauge of wire used to go from the plug on the side of the TT to the control panel will be the weak link in this whole setup.
__________________
Terry and Janet
2008 3001W Windjammer
2007 Ford F150
caper is offline   Reply With Quote
Old 01-16-2013, 11:03 PM   #48
Senior Member
 
LaydBack's Avatar
 
Join Date: Dec 2012
Posts: 322
I done the 50A conversion on my last trailer. Most expensive part was the cord and that was maybe $120-$140. Actually, the most expensive part was the new hardwired Surge Guard. I used the original converter, as I was not needing anymore DC power, so no need to replace it. There's pics and details in the link in my sig. I'd say I was maybe at $500 including the surge guard, cord, 50A panel, and new hatch door.
__________________
LINK TO MY MODS

2012 F350 King Ranch DRW 6.7L
2013 Sabre 36QBOK-7 Platinum Package
LaydBack is offline   Reply With Quote
Old 01-16-2013, 11:42 PM   #49
Senior Member
 
Join Date: Oct 2012
Location: Northern Calif.
Posts: 412
After reading this post I realized I do not know where my breakers are at. If I were to trip the breaker, I would not know where to even look. 2012 XLR 27 HFS. During the walk through no mention was made and nothing in the manual.

Thanks, sorry if this is a off the topic
Kaboom is offline   Reply With Quote
Old 01-17-2013, 06:09 AM   #50
Senior Member
 
Witch Doctor's Avatar
 
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
On my Trailer the fireplace, water heater and GFI are on their own breakers. The first thing I would do is put a amp probe on each and see what they are pulling each one. I could see plugging in a coffee maker and hair drier and a space heater to trip your GFI that's all 1 breaker. Breakers get weak and wires get loose. If you are not tripping the 30 amp main it is not a power problem coming in to the unit. I use to trip my AC breaker when I put the fan on high. Changed the breaker and the problem was solved. The real problem is finding out what is wired were. I tried to get a wiring diagram from FR and they said they do not have one, it depends on who installed it on the line when being made. Changing to 50 amp will not help if you are not tripping the main. I run a coffee maker, water heater and fireplace and never trip and my main is 30 amp.
__________________
Coachmen M/H
Concord
2018 / 300 DSC

Witch Doctor is offline   Reply With Quote
Old 01-17-2013, 07:06 AM   #51
White River Powersports Dealership
 
powertrader's Avatar
 
Join Date: Jan 2013
Posts: 20
Cool

Quote:
Originally Posted by jeeplj8 View Post
It is interesting to see how quickly you exceed the 15 amps available with just a few appliances. It sounds like 50 amp service is going to cost more than I want to spend. My original plan to have one of them shower at night. I like that plan better now.

But Miller a idea at least makes sure I have 30 amps on the right side of the box.
The simple inexpensive solution is the Coleman stove-top (gas) coffee maker. That will eliminate the 10amp draw.
powertrader is offline   Reply With Quote
Old 01-17-2013, 08:24 AM   #52
Senior Member
 
Dave Lyon's Avatar
 
Join Date: Aug 2012
Location: Oshawa, ON
Posts: 983
As several have mentioned - managing the power consumption is probably your wisest option. I run a separte extension cord to the pedistal when I need to power ceramic heater etc. You've paid for the power - why not use it.

There is no way I would spend in excess of $500 to convert to 50 amp, when power consumption can be managed through common sense.

my two cents!
__________________
Dave, Southern,ON



2017 GMC SLT HD All Terrain Crew Cab (6' 6" Box) 2012 Roo 23SS
E2 Trunnion WDH (1,000 lb / 10,000 lb)
Dave Lyon is offline   Reply With Quote
Old 01-17-2013, 12:03 PM   #53
Senior Member
 
Join Date: Feb 2012
Location: Midland, MI
Posts: 954
I don't think I saw anyone here mention yet that a 50Amp RV upgrade would require a 4 wire hook-up (2 hots, a Neutual & a ground.) So you'd have to pull a lot of heavy wire between your converter and the outside plug.
__________________
Cathy & Jeff
Midland, Michigan
2020 Cedar Creek 34IK / 2019 Ram3500 CID
SimchaSabre is offline   Reply With Quote
Old 01-17-2013, 12:46 PM   #54
Junior Member
 
Join Date: Oct 2011
Posts: 7
If the trailer has a 55 amp converter what is the harm in using the 30 / 50 adapter?
tnpopr is offline   Reply With Quote
Old 01-17-2013, 01:08 PM   #55
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Quote:
Originally Posted by tnpopr View Post
If the trailer has a 55 amp converter what is the harm in using the 30 / 50 adapter?
Even tho you'd have 50 amps available your load center still will have a max of 30 amps before breakee trips.


Ps the 55 amp converter is output amps not input.

Turbs
TURBS is offline   Reply With Quote
Old 01-17-2013, 01:11 PM   #56
Phat Phrog Stunt Team
 
AquaMan's Avatar
 
Join Date: Apr 2012
Location: Tipp City, OH
Posts: 7,154
Ok, from what I understand, you are using your HW on gas AND electric for faster recovery. Do you have a 6 or 10 gal HW heater? If you have a 6 gal, a more simple approach might be to move to a 10 gal HW and use on gas only in the morning. Electric problem solved. Wife and daughter happy.
__________________
2016 Georgetown 364TS
2017 Jeep Rubicon Recon toad
Nights Camped 2019 - 17
AquaMan is offline   Reply With Quote
Old 01-17-2013, 01:16 PM   #57
Junior Member
 
Join Date: Oct 2011
Posts: 7
Thanks, my understanding of electrical things doesn't go much past pushing in the plug. I've always wondered why my trailer has a 30 amp cable and sticker on the side but the converter is 55 amp.
tnpopr is offline   Reply With Quote
Old 01-17-2013, 01:17 PM   #58
Phat Phrog Stunt Team
 
TURBS's Avatar
 
Join Date: Aug 2011
Location: Iowa
Posts: 34,507
Quote:
Originally Posted by tnpopr View Post
Thanks, my understanding of electrical things doesn't go much past pushing in the plug. I've always wondered why my trailer has a 30 amp cable and sticker on the side but the converter is 55 amp.
No problem
TURBS is offline   Reply With Quote
Old 01-17-2013, 03:05 PM   #59
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,952
Quote:
Originally Posted by tnpopr View Post
Thanks, my understanding of electrical things doesn't go much past pushing in the plug. I've always wondered why my trailer has a 30 amp cable and sticker on the side but the converter is 55 amp.
Your converter is doing as it name says, and "converting" AC voltage into DC voltage......in able to provide power to the things in your trailer that run off of DC power. Your trailer has a 30 amp 120 Volt AC cable. Your converter is capable of outputting 55 amps of 12 volt DC power.

120 volt AC is not the same as 12 volt DC.

For example (and this is just a guess), your converter might use 8 amps of AC power to output 55 amps of 12 volt DC power.

The basic function of a converter, as the name suggests, is to convert 120 volts AC electricity into 12 volts DC power.

This article may help understand it better:

http://rvservices.koa.com/rvinformat...d-amp-draw.asp
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is offline   Reply With Quote
Old 01-17-2013, 04:05 PM   #60
Senior Member
 
jimh's Avatar
 
Join Date: Jul 2010
Location: Lake Charles, La.
Posts: 1,536
Quote:
Originally Posted by SimchaSabre View Post
I don't think I saw anyone here mention yet that a 50Amp RV upgrade would require a 4 wire hook-up (2 hots, a Neutual & a ground.) So you'd have to pull a lot of heavy wire between your converter and the outside plug.
you r correct. what i was suggesting earlier was to use only one leg of the 50 amp supply. i would upgrade the connecting cable from #10 to #6. then change the main in the trailer from 30 to 50. i would still keep the pedestal side with a 30 amp (3 prong) plug (wired 1 hot, 1 neutral, and 1 ground). that would give u 20 more amps to play with (when u plugged into a 50 at the pedestal using an adapter). the extra 20 may be all u need.

only problem i see doing this is that the breaker box may not be able to take the extra amperage...ie buss may be too small.
also once u go thru this much expense, u might as well replace the breaker box and do the full upgrade.
jimh is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 11:29 AM.