Originally Posted by Yarome
Reverse polarity. If your plugged into shore power, your outlet needs to be rewired. If you're on battery then go flip flop the battery cables.
This is Mike Sokol from the no~Shock~Zone and I just received a private message from the forum moderator that I was needed here, sort of like the Batman Signal, I guess....
OK, let's get to the bottom of this quickly, since this is a simple thing. But first, let me detail what is is NOT!!!
It's NOT reversed or flipped battery cables. And you certainly don't want to be swapping battery cables at any time since that really DOES reverse polarity and could easily destroy electronics such as your inverters, televisions, stereo systems, etc... That's because a battery has a positive and a negative pole, so reversing the cables actually reverses the polarity, and electronics are VERY sensitive to polarity reversal and can be destroyed by in in a few milliseconds (a millisecond is 1/1000 of a second).
It's NOT reversed polarity on the AC shore power plug, unless something else is miswired at the same time. That's loosely defined as the Hot and Neutral wires being swapped or "reversed" in the extension cord or outlet. But the White Neutral wire is supposed to be isolated from the frame/skin of your RV according to the NEC and RVIA build codes. If you've accidentally bonded (connected) the Neutral and Chassis Ground together, then it's possible that a Reversed Polarity Outlet could energize the RV chassis/skin, but if the ground wires is intact it should trip the circuit breaker immediately.
It's definitely some sort of compromised EGC (Equipment Grounding Conductor) more commonly called a safety ground, or simply "ground" by most consumers. This "ground" is supposed to drain away any small ground fault currents and trip a circuit breaker for any large ground fault currents.
By definition, a ground fault current is any sort of leakage between the incoming hot wires and the chassis of an appliance or your RV itself. There will ALWAYS be some ground fault current available in ANYTHING plugged into a power outlet, but it's normally very small, typically less than 1 mA (1 milliamp or 1/1000 of an ampere). Most of the time there will be a balancing act between the hot and neutral leakage impedance which the open ground hot-skin voltage biasing to around 1/2 of the line voltage. So if your EGC (ground) wire is compromised without anything else being wrong in your RV, you'll often measure 40 to 80 volts between the RV frame and a screwdriver stuck in the earth. While this sort of low-current ground fault may not be immediately deadly, you still need to take it seriously since it can turn into a high current ground fault in a heartbeat, and there will be nothing to stop it from killing you or a loved one.
OK, now let's consider what can compromise your RV's grounding system. There needs to be a solid connection between the frame/chassis of your RV all the way back to the electrical service panel feeding your home or the campground. So everywhere there's a connection, it's possible for a failure to occur. So that means that it could be caused a broken or loose or corroded connection in your shore power cable, extension cord, dog-bone adapter, pedestal outlet, or even the AC power feeding the pedestal or outlet itself. I've seen loose grounding screws inside of the RV's circuit breaker box cause this, and even a broken ground screw on the back of the RV's shore power jack on the side of vehicle. To be code compliant, this EGC (ground) needs to have less than 1 ohm impedance back to the service panel's G-N-E bonding point.
Also, a ground rod connected to the frame of your RV does NOT "ground" your RV. Lot's of reasons for this, but an earthed ground rod can often measure up to 100 ohms to the earth, so while it might drain away a low-current ground fault, it certainly CAN'T drain away a high-current ground fault. That can be caused by a screw being driven though a wire in the wall, or insulation worn through by rubbing on the frame, or even a failed transformer in your microwave oven. As a side note, jacks on the ground do nothing to "ground" your RV, so don't get me started on that subject.
Finally, there's one really dangerous outlet miswinrg condition I sometimes find in old garages and church outlets. I call it an RPBG (Reverse Polarity Bootleg Ground) and it can't be detected by any standard tests including 3-outlet testers or even metering between H-N, H-G and N-G. You must have an external reference to earth to find it. See my article on it at
Failures in Outlet Testing Exposed | Contractor content from Electrical Construction & Maintenance (EC&M) Magazine and my video on how you can use a NCVT (Non Contact Voltage Tester) to easily find a hot-skin condition at
So, please take any felt shocks as a sign that something is seriously wrong with your RV's ground system, which could be anywhere from the outlet itself, dog-bone adapter, extension cord, shore power cord, or even the ground bonding point inside your RV itself. I get all the police and inspector reports whenever someone is electrocuted (killed) by an RV or guitar on stage, and most every instance was preceded by someone noticing they were feeling a shock for a few days or even weeks. Modern code requires that RVs and appliances are designed so that you NEVER feel a shock. If you do, then the grounding system has failed. It's as simple as that.
Also, at the risk of self promoting, I think that all of you, especially the ones who are giving out incorrect electrical advice, need to get and read a copy of my book - No~Shock~Zone RV Electrical Safety. This is a must-read before doing any electrical work on your RV, and will certainly give you enough information to discuss electrical problems with a trained technician or licensed electrician.
ATTN MODERATOR - Feel free to delete the book info above if that violates forum self-promotion policy. But I think that everyone who plugs an RV into an electrical outlet needs to understand the basics of electricity for their own safety.
Let's play safe out there...
Mike Sokol
No Shock Zone