Explain to me how a 50 amp connection works.

This may be a stupid question but I’m tired and trying to answer A question for my father.

So a 30 amp Rv plug is a standard 110 v connection 1 hot, 1 Neutral, 1
Ground.

A 50 amp adds in an additional hot.

So in a house application 110 v circuits pull off of either hot. You loose a hot wire and half the 110 b will not work. 220 v gets nasty when you loose a hot.

So when you plug in a 50 amp Rv into a 30 amp plug using an adapter why does everything still work?


We are by no means in familiar with residential and commercial wiring. I am very familiar with automotive wiring.

We are looking at adding a small 30 amp inverter generator to his 42foot fifth wheel that has the wires ran for the generator but no transfer
Switch. All the transfer switches I am
Seeing are listed as 240v. So I am just trying to understand the system to see if this will work.

He wants the small generator to be able to stop and use the inside of the trailer to cook and eat lunch and one 1 of his 3 Ac units while on the road. Trying to make it as simple as can be for him to just fire the greater up and go inside the turn it off and get back in the road.
quicky06 is offline   Reply With Quote
Old 03-12-2020, 09:48 PM   #2
Senior Member
 
Join Date: Apr 2016
Location: Cedar Creek Lake, TX
Posts: 3,484
What exactly is your question?
By the way it is when you loose the neutral, not a hot leg, that causes problems in an RV. An adapter takes the single 120 volt leg and branches it to feed both legs in a 50 amp RV.
__________________
Cedar Creek Lake, Texas
2019 Keystone Loredo 290SRL
2019 Ram 2500 4x4 Cummins crew cab
Andersen hitch
CedarCreekWoody is offline   Reply With Quote
Old 03-12-2020, 10:11 PM   #3
Senior Member
 
Join Date: Aug 2016
Posts: 420
Quote:
Originally Posted by CedarCreekWoody View Post
What exactly is your question?
By the way it is when you loose the neutral, not a hot leg, that causes problems in an RV. An adapter takes the single 120 volt leg and branches it to feed both legs in a 50 amp RV.

Does the Rv only use of of the 50 amp hot legs?
If it uses both I can’t figure out how.
quicky06 is offline   Reply With Quote
Old 03-12-2020, 10:49 PM   #4
Senior Member
 
Join Date: Apr 2016
Location: Cedar Creek Lake, TX
Posts: 3,484
It uses both legs, each leg feeding one half of the electrical buss with 50 amp at 120 volts. Total amperage in the box is 100 amps at 120 volts when connected to 50 amp RV service. When connected to a 30 amp adapter one 30 amp leg feeds both sides of the buss bar for 30 amps total in the box.
__________________
Cedar Creek Lake, Texas
2019 Keystone Loredo 290SRL
2019 Ram 2500 4x4 Cummins crew cab
Andersen hitch
CedarCreekWoody is offline   Reply With Quote
Old 03-12-2020, 11:14 PM   #5
Senior Member
 
Join Date: Aug 2016
Posts: 420
So does someone make a transfer switch that can handle the 50 amp Service from shore power and 110v 30 amp generator input.

I would like at ovoid anything wfco
quicky06 is offline   Reply With Quote
Old 03-12-2020, 11:49 PM   #6
Senior Member
 
Join Date: Apr 2016
Location: Port Charlotte Fl/Hinsdale Ma
Posts: 4,823
A 50 amp service in in fact 240 volts to the RV main breaker. That is where 240 stops. Most, except very high end MH, cannot access 240 volts.

50 to 30 dog bone picks just one leg of 240 and puts in on the hot wire of the 30 amp adapter.

By the same token a 30 to 50 adapter puts the hot leg of the 30 amps on both wires going to the RV 50 amp service.

RV generator will feed 2 30 amp circuits to a 50 amp service.
cavie is offline   Reply With Quote
Old 03-12-2020, 11:52 PM   #7
Senior Member
 
Join Date: Jul 2017
Location: California
Posts: 7,616
Quote:
Originally Posted by quicky06 View Post
So does someone make a transfer switch that can handle the 50 amp Service from shore power and 110v 30 amp generator input.

I would like at ovoid anything wfco
You just use a 30A to 50A adapter from your generator and a regular 50A transfer switch. The transfer switch doesn't care.
babock is offline   Reply With Quote
Old 03-13-2020, 06:58 AM   #8
Senior Member
 
Join Date: Dec 2017
Posts: 606
Hope this helps a littleClick image for larger version

Name:	Screenshot_20180602-142014.jpg
Views:	1932
Size:	31.8 KB
ID:	225081
cmysstailights is offline   Reply With Quote
Old 03-13-2020, 07:02 AM   #9
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,934
This is always the link I refer to, to help memberS understand how 30 and 50 amp service work....including the adapter which will jump the ONE 30 amp hot leg over onto the other hot leg of the 50 amp RV, so both legs are powered by the one leg. THE LINK WILL FULLY EXPLAIN EVERYTHING


https://www.rvtechmag.com/electrical/chapter3.php





__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is offline   Reply With Quote
Old 03-13-2020, 07:26 AM   #10
Senior Member
 
mjbenedict's Avatar
 
Join Date: Oct 2015
Posts: 433
Explain to me how a 50 amp connection works.

The reason a 30A feeding both legs of a 50A breaker box works in a RV is most all RVs don’t have 240V appliances. If they do, you cannot run them when connected to the adapter and I would suggest shutting off that dual-pole breaker while using the dogbone adapter.
__________________
2020 Dynamax Isata 5 36DS 4X4 (Super C)
2020 Ram 1500 Limited
Sold: 2015 Rockwood Ultralite 2604WS
No longer mine: 2006 Rockwood Roo 23SS
All pop-up and tent camping before...
mjbenedict is offline   Reply With Quote
Old 03-13-2020, 02:07 PM   #11
Senior Member
 
Join Date: Apr 2016
Location: Cedar Creek Lake, TX
Posts: 3,484
Quote:
Originally Posted by mjbenedict View Post
The reason a 30A feeding both legs of a 50A breaker box works in a RV is most all RVs don’t have 240V appliances. If they do, you cannot run them when connected to the adapter and I would suggest shutting off that dual-pole breaker while using the dogbone adapter.
This makes no sense. What double pole breaker are you referring to? The one on the camper circuit breaker box has to be on for power to flow to the buss.
CedarCreekWoody is offline   Reply With Quote
Old 03-13-2020, 02:08 PM   #12
Senior Member
 
Swampy's Avatar
 
Join Date: Dec 2015
Posts: 241
Quote:
Originally Posted by quicky06 View Post
This may be a stupid question but I’m tired and trying to answer A question for my father.

So a 30 amp Rv plug is a standard 110 v connection 1 hot, 1 Neutral, 1
Ground.

A 50 amp adds in an additional hot.

So in a house application 110 v circuits pull off of either hot. You loose a hot wire and half the 110 b will not work. 220 v gets nasty when you loose a hot.

So when you plug in a 50 amp Rv into a 30 amp plug using an adapter why does everything still work?


We are by no means in familiar with residential and commercial wiring. I am very familiar with automotive wiring.

We are looking at adding a small 30 amp inverter generator to his 42foot fifth wheel that has the wires ran for the generator but no transfer
Switch. All the transfer switches I am
Seeing are listed as 240v. So I am just trying to understand the system to see if this will work.

He wants the small generator to be able to stop and use the inside of the trailer to cook and eat lunch and one 1 of his 3 Ac units while on the road. Trying to make it as simple as can be for him to just fire the greater up and go inside the turn it off and get back in the road.
quicky06, If I am understanding what you are asking, you want to hook up a 30A, 120V inverter generator to a 50A, double 120V RV.

If my interpretation is correct, then simply test to determine which of the 2 hot legs at the main RV panel go to the generator pre-wire Hot and Neutral ... once identified, mark with tape on both ends. Next, determine which half of the RV the A/C and microwave are fed from. That one will be the side of the mains you want to connect to the generator output. As far as the transfer switch goes, use a 50A, 240V model with a 120V control to sense the land power source as primary feed. be sure to verify the neutral wire is connected to the panel near the main bus as it must carry the full return current from the generator output.
Let us know how the project goes and be sure to ask more questions if you get confused. Above all, be careful while playing with electricity! Swampy
__________________
Jim (Swampy), Susie, Jimmy & The Chihuahua Crew
2008 Chevy Silverado LS, 4.3L, V6, 2WD, 3.23:1

2014 287 BHBE; 1981 JayRaven: Predator 3500i - Call Home Pearl River, Louisiana. on The Honey Island Swamp
https://www.forestriverforums.com/at...pic81807_1.gif
Swampy is offline   Reply With Quote
Old 03-13-2020, 02:22 PM   #13
Senior Member
 
Join Date: Jul 2017
Location: California
Posts: 7,616
Quote:
Originally Posted by CedarCreekWoody View Post
This makes no sense. What double pole breaker are you referring to? The one on the camper circuit breaker box has to be on for power to flow to the buss.
He was saying if the RV happened to have a 240V appliance. In that case, you want to turn the double pole breaker for that appliance. It's rare to have one of those but some large RVs do have them.
babock is offline   Reply With Quote
Old 03-13-2020, 02:22 PM   #14
Member
 
Join Date: Feb 2017
Posts: 45
A 30a plug has 1 hot 30a 120v wire and 1 neutral 30a wire plus a ground. For RV 50a you effectively have 1 hot line off of phase 1, 1 hot off of phase 2, 1 neutral and ground. If you measure the voltage from phase 1 to phase 2 it is 240v. But you are not going from phase to phase. You are using 2 separate legs of 120v to the neutral. So essentially you get 2 legs of 25a 120v hot combined for 50a on your neutral. You can tie those two hot lines together and run 1 50a hot 120v line to get the same results.
__________________
2020 GMC Sierra 3500 SRW L5P
2021 Vengeance Rogue Armored 351A13

Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety.
Benjamin Franklin
Bigruh36 is offline   Reply With Quote
Old 03-13-2020, 02:24 PM   #15
Senior Member
 
Join Date: Jul 2017
Location: California
Posts: 7,616
Quote:
Originally Posted by Bigruh36 View Post
So essentially you get 2 legs of 25a 120v hot combined for 50a on your neutral.
Wrong! Each leg is 50A. The most you would ever have on the neutral is 50A if only one leg was drawing 50A. If the other leg is also drawing 50A, the current in the neutral would be zero.

You are really an HVAC service technician?
babock is offline   Reply With Quote
Old 03-13-2020, 02:36 PM   #16
Member
 
Join Date: Feb 2017
Posts: 45
Quote:
Originally Posted by babock View Post
Wrong! Each leg is 50A. The most you would ever have on the neutral is 50A if only one leg was drawing 50A. If the other leg is also drawing 50A, the current in the neutral would be zero.

You are really an HVAC service technician?
If it was a 240v circuit you would be correct. But it is 2 50a 120v circuits. The neutral can only handle 50a, so the total amount of current flowing through both legs cannot exceed 50a.
The current could be divided between 1 or both legs however It cannot exceed 50a total. the neutral is the return leg.
__________________
2020 GMC Sierra 3500 SRW L5P
2021 Vengeance Rogue Armored 351A13

Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety.
Benjamin Franklin
Bigruh36 is offline   Reply With Quote
Old 03-13-2020, 02:50 PM   #17
Senior Member
 
Join Date: Jul 2017
Location: California
Posts: 7,616
Quote:
Originally Posted by Bigruh36 View Post
If it was a 240v circuit you would be correct. But it is 2 50a 120v circuits. The neutral can only handle 50a, so the total amount of current flowing through both legs cannot exceed 50a.
The current could be divided between 1 or both legs however It cannot exceed 50a total. the neutral is the return leg.
We ARE talking about a 240V service. That is what a 50A RV service is....240V split phase. You can have 50A flowing through both legs!
babock is offline   Reply With Quote
Old 03-13-2020, 02:52 PM   #18
Senior Member
 
Join Date: Jun 2012
Posts: 10,907
One more pic that might help:
Attached Thumbnails
Click image for larger version

Name:	30amp vs 50amp vs dogleg.gif
Views:	9306
Size:	66.1 KB
ID:	225110  
__________________
1988 Coleman Sequoia - popup (1987-2009) - outlasted 3 Dodge Grand Caravans!
2012 Roo19 - hybrid (2012-2015)

2016 Mini Lite 2503S - tt (2015 - ???)
2011 Traverse LT, 3.6L, FWD
2009 Silverado 1500 Ext Cab, 5.3L, 4x4, 3.73
2016 Silverado 2500HD Dbl Cab, 6.0L 4x4, 4.10
rockfordroo is offline   Reply With Quote
Old 03-13-2020, 02:58 PM   #19
Canadian Member
 
Join Date: Feb 2012
Location: Eastern GTA, Ontario, Canada
Posts: 6,235
Bigruh36, to clarify, the "split phase" part means that the 2 legs both can have 50A running through them but never simultaneously. When Leg 1 is energized, Leg 2 is not and vice versa. Therefore the shared neutral will never have more the 50A running through it.

I'm sure the electricians here will correct me if I'm wrong!
__________________
2023 Rockwood Signature 8262RBS
2016 Ford F-250 XLT SuperCrew, 6.2L, 4x4, 6'9" bed
2019 Rockwood Signature 8290BS (2019 - 2022)
2011 Rockwood Signature 8293SS (2015 - 2018)
2010 Rockwood Roo 23SS (2012 - 2014)

itat is offline   Reply With Quote
Old 03-13-2020, 03:01 PM   #20
Member
 
Join Date: Feb 2017
Posts: 45
Quote:
Originally Posted by itat View Post
Bigruh36, to clarify, the "split phase" part means that the 2 legs both can have 50A running through them but never simultaneously. When Leg 1 is energized, Leg 2 is not and vice versa. Therefore the shared neutral will never have more the 50A running through it.

I'm sure the electricians here will correct me if I'm wrong!
That is what I was trying to say.... sorry I am not a good writer
__________________
2020 GMC Sierra 3500 SRW L5P
2021 Vengeance Rogue Armored 351A13

Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety.
Benjamin Franklin
Bigruh36 is offline   Reply With Quote
Reply

Tags
50 amp


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 10:59 PM.