Old 06-20-2021, 01:32 PM   #21
Senior Member
 
MNtraveler's Avatar
 
Join Date: Oct 2015
Posts: 2,404
Quote:
Originally Posted by Laredo294 View Post
Great wisdom. Information is priceless. My issue is quite similar, but the trailer only gets energized when plugged into power outlet. It is fine when it runs off the generator. Could this be the inverter giving me the grief, or just the outlet i am plugged into
Plug an EMS into the outlet and it will tell you immediately if the outlet is good or bad.

I don’t know how to say this without sounding preachy, but humans should not enter an energized trailer. Stay safe until fixed.
MNtraveler is offline  
Old 06-27-2021, 07:38 AM   #22
Member
 
Join Date: Jul 2020
Posts: 40
Great read. I’m having an issue as well with 45 volts hitting the ground. Also when unplugged with batteries having 1/2 volt to ground. Another symptom is a “pop” and a scorched prong on my main power cord adapter. Another issue is my brand new converter isn’t working correctly anymore charging my batteries.
I’ve volt meter tested the hell out of everything. I turned off all breakers, still shocked. DC the converter same. My guess it is between the main plug and the sun panel. I’ve inspected. No rate chew marks, nada. Totally perplexed. Puzzling is I can get power to ground AC and DC.
Also not sure if this is correct or not but when my tester is set for continuity, I have continuity with the ground in the main plug and the frame of the RV. Is this correct?
Secondmanup is offline  
Old 06-27-2021, 07:59 AM   #23
Senior Member
 
Join Date: Jan 2017
Posts: 3,290
I've had 'hot skin' issues from time to time over the years - it generally comes down to a Neutral and Hot wire being switched. Sometimes when a shore cord Male end is replaced, it may be that the wires are installed incorrectly, and while the wiring may seem to 'work', it can also work to sometimes provide a small 'tingle' or 'shock' when you touch both a metal surface and while standing on the ground, ESPECIALLY in damp or wet conditions. It could also be a 30amp campground outlet that has these wires switched.

It would have nothing to do with an Inverter.
__________________
The Turners...
'07 Rockwood Signature Ultralight...
two Campers and two Electric cars : )
formerFR is offline  
Old 06-27-2021, 08:02 AM   #24
Senior Member
 
Join Date: Jan 2017
Posts: 3,290
Exclamation

Quote:
Originally Posted by MNtraveler View Post
... humans should not enter an energized trailer. Stay safe until fixed.

while this may seem to be common-sense, the reality is that the RV's tires provide protection to the 'humans', which is why you typically don't have issues WHILE you are in the RV, usually only when outside standing on the ground and touching a metal surface, coax cable, etc.
formerFR is offline  
Old 06-27-2021, 08:15 AM   #25
Member
 
Join Date: Jul 2020
Posts: 40
This occurred at home with the same outlet, cord, etc. nothing has changed. Checked. No reversed wires. Def had my knee in water and my finger in the drain hole of the water tank and the tingle was low enough I thought I had a fiberglass splinter in my finger but I realized I became ground. Like I said earlier, I shutoff all the breakers and still have the issue. So it rules out the HW tank I presume.
Again seeming to isolate everything from the plug to sub panel. No changes that I’ve made have occurred between those points.
Getting DC to ground at 1/2 volt then says something but not sure if I had a hot AC touching something looking for ground, why is the DC side trying to find ground too?
Secondmanup is offline  
Old 06-27-2021, 09:19 AM   #26
Senior Member
 
MNtraveler's Avatar
 
Join Date: Oct 2015
Posts: 2,404
Quote:
Originally Posted by formerFR View Post
while this may seem to be common-sense, the reality is that the RV's tires provide protection to the 'humans', which is why you typically don't have issues WHILE you are in the RV, usually only when outside standing on the ground and touching a metal surface, coax cable, etc.
Thanks. That’s why I said “should not enter.” You can ground out at the metal door step. Also when connecting the power cable, hose line, etc. you are touching the ground. Not a safe situation.

Certainly anyone with a pacemaker, defibrillator or heart condition should be quite cautious. That’s not to say the rest of us are invincible to electrical shocks either.

For those wondering how to know, a non-contact voltage tester available at hardware stores will tell you if your frame is hot.
MNtraveler is offline  
Old 06-27-2021, 09:22 AM   #27
Senior Member
 
MNtraveler's Avatar
 
Join Date: Oct 2015
Posts: 2,404
Quote:
Originally Posted by Secondmanup View Post
This occurred at home with the same outlet, cord, etc. nothing has changed. Checked. No reversed wires. Def had my knee in water and my finger in the drain hole of the water tank and the tingle was low enough I thought I had a fiberglass splinter in my finger but I realized I became ground. Like I said earlier, I shutoff all the breakers and still have the issue. So it rules out the HW tank I presume.
Again seeming to isolate everything from the plug to sub panel. No changes that I’ve made have occurred between those points.
Getting DC to ground at 1/2 volt then says something but not sure if I had a hot AC touching something looking for ground, why is the DC side trying to find ground too?
An EMS plugged into your outlet and the adapter you are using will tell you if your base circuit is good or bad. If good, then you can plug the EMS into the receiving end of the RV power cord (in place of the RV) and check your power cord. After that, it’s inside. Good luck!
MNtraveler is offline  
Old 06-27-2021, 10:31 AM   #28
Senior Member
 
Join Date: Aug 2019
Posts: 1,042
the test gun is known by the name " buck rogers gun" to some telephone repair men. it will keep you alive.
Thomas ho is offline  
Old 06-27-2021, 01:39 PM   #29
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,203
Quote:
Originally Posted by Laredo294 View Post
Great wisdom. Information is priceless. My issue is quite similar, but the trailer only gets energized when plugged into power outlet. It is fine when it runs off the generator. Could this be the inverter giving me the grief, or just the outlet i am plugged into
Quote:
Originally Posted by Secondmanup View Post
Great read. I’m having an issue as well with 45 volts hitting the ground. Also when unplugged with batteries having 1/2 volt to ground. Another symptom is a “pop” and a scorched prong on my main power cord adapter. Another issue is my brand new converter isn’t working correctly anymore charging my batteries.
I’ve volt meter tested the hell out of everything. I turned off all breakers, still shocked. DC the converter same. My guess it is between the main plug and the sun panel. I’ve inspected. No rate chew marks, nada. Totally perplexed. Puzzling is I can get power to ground AC and DC.
Also not sure if this is correct or not but when my tester is set for continuity, I have continuity with the ground in the main plug and the frame of the RV. Is this correct?

Mike Sokol is the de facto expert on these hot skin chassis events. If you both will please read the OP of this thread above, Mike explains the causes and what to search for to find the problem.


He also explains how reverse polarity will NOT be the cause of this unless you have another wiring problem like someone who bonded the neutral and ground wires together at any place besides the electrical service entrance. The Service entrance will NOT be anywhere in the RV (it's a subpanel) and usually will not even be at the pedestal outlet.



After rereading the OP you will know you are most likely looking for a safety grounding issue and it could be in the shore power cord, any electric adapters, the shore power outlet, the inlet in your RV. etc.
__________________
2011 Flagstaff 831 RLBSS

In order to be number 1, you have to be odd.
wmtire is online now  
Old 08-30-2021, 01:35 PM   #30
Member
 
Join Date: Jul 2020
Posts: 40
An update. Please help. So here’s what I’ve found.
1)with all breakers off I lose 45 volts to ground if my knee is in water. I backtracked the outlet, extension cord. 120 to 30 amp converter plug, and the 30amp cord that plugs into my rig. I checked continuity with each piece. All wires independent check out.
2) I used a plug in device that indicates up to the end of the 120 extension cord is wired cord is wired correctly.
3) However the outlet on rig says there is an open neutral.
4) I took apart the outlet on the rig. Tested each wire input separately for continuity. All good.
5) I have eyes on the 120 that goes from the plug, 24” run under the cabinet, and unde the floor where it’s got spray insulation around. No room for a rat and no sign of poop or pee or shredded stuff.
6) The wire emerges in the sub panel. I ran a wire from the ground to the sub panel. I checked continuity and all is good.
7) I am totally puzzled. It doesn’t appear open.

Doesn’t open mean…a break?
With that…would an open ground be causing me to get shocked with my hand on the frame and my knee to ground?
Secondmanup is offline  
Old 08-30-2021, 02:07 PM   #31
Member
 
Join Date: Jul 2015
Posts: 62
I don't whether you mentioned that you actually checked the OUTLET and Main Panel where you are plugged in - the outlet could have a loose neutral wire, or it could be loose at the Main Panel.
Yes, the loss of the Neutral can certainly mean that YOU become the Neutral when it is otherwise not functioning properly, which is why the 'tingle'...
MrPalazzo is offline  
Old 08-30-2021, 02:44 PM   #32
Senior Member
 
MNtraveler's Avatar
 
Join Date: Oct 2015
Posts: 2,404
Why are you using an extension cord with your 30 A line? That’s a bit of a red flag.. Is it an outdoor rated extension? If so, it may be ok within rated current capacity.

Also, there is no 120V to 30A converter or adapter. The 30A line is still 120V. You may have a 15A to 30A adapter. the terminology worries me.
__________________
2016 FR Forester 2401R
Towing 2014 Honda CR-V
MNtraveler is offline  
Old 08-30-2021, 03:01 PM   #33
Member
 
Join Date: Jul 2020
Posts: 40
It’s a heavy outdoor rated cord. I’m not pulling heavy amps. I know better than to run an ac or a heavy load. It’s for the converter.
My household rated cord goes into the 30 amp supplied cord for the rig. It is down stream of the household cord.
Secondmanup is offline  
Old 08-30-2021, 03:04 PM   #34
Member
 
Join Date: Jul 2020
Posts: 40
Another update in trouble shooting.
1) all receptacles report an open ground.
2) With all breakers shut off I get an 8v leak to ground.
3) As I turn on breakers individually I get varying amounts from 9, 11, 14, and the biggest 24 when I flip the AC breaker on
Essentially power is getting past all the breakers.

Question. If the rig is unpowered should there be continuity between ground and neutral in the panel? I don’t.
Secondmanup is offline  
Old 08-31-2021, 10:11 AM   #35
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,203
Quote:
Originally Posted by Secondmanup View Post
Another update in trouble shooting.
1) all receptacles report an open ground.
2) With all breakers shut off I get an 8v leak to ground.
3) As I turn on breakers individually I get varying amounts from 9, 11, 14, and the biggest 24 when I flip the AC breaker on
Essentially power is getting past all the breakers.

Question. If the rig is unpowered should there be continuity between ground and neutral in the panel? I don’t.
You should not have continuity between the neutral and safety ground in the RV if the power cord is disconnected. The RV's panel should have the two unbonded.....as its treated as a subpanel.

As explained by Mike Sokol above the only place these two are bonded is at the very main shore power panel...and not at subpanels.
__________________
2011 Flagstaff 831 RLBSS

In order to be number 1, you have to be odd.
wmtire is online now  
Old 12-24-2021, 11:34 AM   #36
Member
 
Join Date: Nov 2021
Posts: 30
Sounds like a bad ground. Sounds like a high resistance short to ground. If you were pluged into a ground fault breaker it would trip preventing you from getting a shock.
This could be very dangerous.
JoeFanzo
Actec is offline  
Old 01-04-2022, 09:31 AM   #37
Member
 
Join Date: Nov 2019
Posts: 58
peripherally related.....I store my TT in a field with high tension wires running overhead. With the TT completely unplugged (battery disconnected, no shore power), depending on the level of humidity, I get a pretty good tingle if I touch anything metallic on the TT.
Heatheroo is offline  
Closed Thread

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 02:51 PM.