Old 09-19-2020, 06:02 PM   #1
Member
 
Join Date: Sep 2020
Posts: 52
Unhappy Low voltage into ATS

We have not used our 2019 GT5 since May and started the process of checking out systems before planned trip in October. So, we hooked to shore power to run refrig, then when satisfied, unhooked from shore and turned on generator (onan 5500), refrig operated, then turned on on Air Conditioner unit, it came on; then attempted to turn 2nd unit on and click noise occurred and all shut off.

We then ensured all electrical draws were off and checked all circuit brearkers. No tripped breakers found. Turned on generator and this time auto transfer did not occur. No voltage increase noted on readout.

So, did some reading then went to ATS (auto transfer switch) pulled cover and performed voltage measurements (as indicated in troubleshooting section of manufacturers paperwork). Both input voltage and switch output voltage. Input voltage read 55 volts AC (should be 105 to 130) and 0 output volts (should be 105 to 130 if switched).

Question is: what faulted between generator and input to ATS to result in odd voltage? What did we do to cause this type of failure? I would think that if we caused a voltage overload a breaker would have tripped?

Help me!

Thanks for any insight!

Scott
__________________
Go Poly

2019 Georgetown GT5 31R5
Go Poly is offline   Reply With Quote
Old 09-19-2020, 08:14 PM   #2
Member
 
Join Date: Sep 2020
Posts: 52
I.e. Generator is not charging batteries or providing 120. V

120 v AC
__________________
Go Poly

2019 Georgetown GT5 31R5
Go Poly is offline   Reply With Quote
Old 09-19-2020, 08:25 PM   #3
Junior Member
 
Join Date: Jul 2015
Posts: 15
I believe mine has a breaker on the generator itself
mercury9 is offline   Reply With Quote
Old 09-19-2020, 08:34 PM   #4
Senior Member
 
Join Date: Jan 2020
Posts: 4,866
Check the circuit breakers on the generator itself.
NavyLCDR is offline   Reply With Quote
Old 09-19-2020, 09:28 PM   #5
Member
 
Join Date: Sep 2020
Posts: 52
There are two breakers on the generator. Neither were tripped, but a switched on and off just in case. No change.
__________________
Go Poly

2019 Georgetown GT5 31R5
Go Poly is offline   Reply With Quote
Old 09-19-2020, 10:50 PM   #6
Senior Member
 
Join Date: Jan 2020
Posts: 4,866
I would check generator output voltage at the connections of the cables to the output of the generator breakers.
NavyLCDR is offline   Reply With Quote
Old 09-20-2020, 01:28 PM   #7
Member
 
Join Date: Sep 2020
Posts: 52
Voltage measurements

Generator output:

1). Both breakers switched on: 50 to 55 VAC
2). Both breakers switched off: 0 VAC
3). Upper breaker off, lower on: 50 to 55 VAC
4). Upper breaker on, lower off: 22 to 27 VAC
__________________
Go Poly

2019 Georgetown GT5 31R5
Go Poly is offline   Reply With Quote
Old 09-20-2020, 06:30 PM   #8
Member
 
Join Date: Sep 2020
Posts: 52
Generator did not shutdown

Therefore there were no fault codes.
__________________
Go Poly

2019 Georgetown GT5 31R5
Go Poly is offline   Reply With Quote
Old 09-21-2020, 09:13 PM   #9
Member
 
Join Date: Sep 2020
Posts: 52
Status

No conclusion, yet. Talked to many experts......either wiring from gen to ATS (makes no sense to me since it worked fine prior to event), faulty brushes (makes no sense due to some output voltages measured as reported above) to the final, and most likely culprit, the gen control board.

I will report back once final fix implemented.
__________________
Go Poly

2019 Georgetown GT5 31R5
Go Poly is offline   Reply With Quote
Old 10-09-2020, 04:44 PM   #10
Member
 
Join Date: Sep 2020
Posts: 52
Solved!

Ok, so I figured I would report back once my predicament was solved.

Recall I left this forum thread regarding an odd generator output voltage, as measured at the transfer switch. I thought it best to take rig to authorized Cummins/Onan repair/dealer in case this could be a warranty item (less than 2 years since purchase).

The technician promptly measured generator output voltage AT THE GENERATOR and determined that there was no issue with the generator. I.E. proper 118VAC out. So, issue must be between generator and transfer switch. Upon further investigation they discovered a junction box not far from the generator underneath the rig. Upon removing the cover the technician discovered a melted wire nut. The large gauge wire from the transfer switch was attached to the smallish wire from the generator using wire nuts! OMG! Apparently the high resistance of this less than robust connection created a perfect storm when I attempted to start both AC units simultaneously.

Lesson learned in my specific case (per wife): Do not attempt to power up both AC units simultaneously.

Additional lesson learned: measure voltage at generator proper, as recommended by NAVYLCDR.

Recommendation to manufacturer: Consider using some type of "high current" terminal block with screw or lug thread type connections. I would think this would be much lower contact resistance and therefore lower electrical resistance (and less variation from connection to connection than wire nuts, perhaps less susceptible to corrosion as well)
__________________
Go Poly

2019 Georgetown GT5 31R5
Go Poly is offline   Reply With Quote
Reply

Tags
voltage


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 02:54 PM.