Quote:
Originally Posted by TitanMike
If your furnace is anything like the one in my 25BDS you may not be able to access electric connections and circuit board without actually removing unit.
I think mine is an NT-20 ? And wiring goes to vent/exhaust end which is against the outer wall.
Gas is the easiest to disconnect as it's right in front of you when you open return air grille (again, on mine).
I looked mine over for the likelihood of future service needs. It will be difficult to remove.
|
If the NT-20 is like the Suburban SF series (lots of illustrated installation and repair manuasl readily found online), it's much easier to access than it looks.
For an SF-series,
--Turn off the propane
--Take off the grille
--Turn off the propane (check again)
--Disconnect propane at the furnace flare nut. (May need to use a crowfoot socket)
--Remove the plenum front cover (one or two sheet metal screws at the top)
--Remove the firebox anchor screw at the bottom center
--There are four wires going to the furnace. Either they will be long enough to allow you to pull it out, or there's a plug-jack to unplug
--Pull the firebox out of the plenum
--All of the circuit boards, motor, sail switch, etc. are accessible
--You can even run the furnace (without propane) when it's out.