01-04-2018, 10:48 AM
|
#1
|
Member
Join Date: Jul 2017
Location: Mendocino CA
Posts: 67
|
Predator 3500 Inverter Generator: Need a ground strap?
I just purchased Harbor Freight Predator 3500 inverter Generator. I haven’t put the oil in it yet, still reading the manual. The manual says that I must install a 4 gauge wire from the generator inverter to a copper ground rod.
The inverter is marketed to RV owners. How is it possible to have a ground cable when the inverter is mounted in the bed of my tow vehicle (Ram 2500 pickup)?
Thanks in advance,
Rennie
__________________
Rennie
2017 F.R. Sonoma 220RBS Explorer Edition
|
|
|
01-04-2018, 11:06 AM
|
#2
|
Pickin', Campin', Mason
Join Date: Aug 2015
Location: South Western PA
Posts: 19,144
|
That is a CYA (cover your butt) statement from OSHA and intended IF the portable generator is used to supply power to a building via a transfer switch.
From OSHA...
"Grounding Requirements for Portable
and Vehicle-mounted Generators
Under the following conditions, OSHA
directs (29 CFR 1926.404(f)(3)(i)) that the
frame of a portable generator need not be
grounded (connected to earth) and that the
frame may serve as the ground (in place of
the earth)
• The generator supplies only equipment
mounted on the generator and/or cordand
plug-connected equipment through
receptacles mounted on the generator,
§ 1926.404(f)(3)(i)(A), and
• The noncurrent-carrying metal parts of
equipment (such as the fuel tank, the internal
combustion engine, and the generator’s
housing) are bonded to the generator
frame, and the equipment grounding conductor
terminals (of the power receptacles
that are a part of [mounted on] the generator)
are bonded to the generator frame,
§ 1926.404(f)(3)(i)(B).
Thus, rather than connect to a grounding
electrode system, such as a driven ground
rod, the generator’s frame replaces the
grounding electrode.
If these conditions do not exist, then a
grounding electrode, such as a ground rod,
is required.
If the portable generator is providing electric
power to a structure by connection via a
transfer switch to a structure (home, office,
shop, trailer, or similar) it must be connected
to a grounding electrode system, such as a
driven ground rod. The transfer switch must
be approved for the use and installed in
accordance with the manufacturer’s installation
instructions by a qualified electrician."
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA
Days Camped ☼ '19=118 ☼ '20=116 ☼ '21=123 ☼ '22=134 ☼ '23=118☼ '24=90
|
|
|
01-04-2018, 11:16 AM
|
#3
|
Member
Join Date: Jul 2017
Location: Mendocino CA
Posts: 67
|
Perfect! Thanks so much for confirming !
__________________
Rennie
2017 F.R. Sonoma 220RBS Explorer Edition
|
|
|
01-06-2018, 04:19 AM
|
#4
|
Member
Join Date: Mar 2017
Location: Wyoming
Posts: 92
|
Go to YouTube and look at the reviews, don't see anyone with a ground strap. For $659.99 it was a good price. At 35* outside it starts right up. This thing is quit, we will be happy camper now.
__________________
Got are first TT, a 2017 2506S. TV, 2016 GMC Canyon Duramax Diesel Loving it!
|
|
|
01-06-2018, 02:53 PM
|
#5
|
Senior Member
Join Date: Jul 2017
Location: Michigan/Rosarito, MX
Posts: 146
|
bought a Predator 3500 last fall - secured it to a custom installed 5th wheel hitch - towed it from MI to S CA and on into MX - Never grounded to anything and runs and powers my 5er just great. I will note however I have two cousins who bought Champions and both have problems with the ground faults on their campers - even when grounded to a ground rod.
__________________
Steve & Cody the Wonder Dog (he wonders if he is a dog or not)
Forest River - Rockwood
2018 Ultra Lite 2040WS 5th wh
2020 Ram 1500 Eco Diesel Curt Hitch - 392 rear end
|
|
|
01-06-2018, 02:57 PM
|
#6
|
Senior Member
Join Date: Apr 2016
Location: Port Charlotte Fl/Hinsdale Ma
Posts: 4,823
|
It's called legalez
|
|
|
01-06-2018, 09:49 PM
|
#7
|
Senior Member
Join Date: Apr 2017
Posts: 106
|
Have a champion 3500 duel fuel, runs a CC 36 ckts 5er no problem. FYI
|
|
|
03-22-2018, 11:51 AM
|
#8
|
Senior Member
Join Date: Feb 2012
Location: Clarksville Va.
Posts: 10,422
|
Quote:
Originally Posted by Boatdude62
Have a champion 3500 duel fuel, runs a CC 36 ckts 5er no problem. FYI
|
Do you also have a EMS system in line?
__________________
Coachmen M/H
Concord
2018 / 300 DSC
|
|
|
03-22-2018, 12:11 PM
|
#9
|
Senior Member
Join Date: Dec 2015
Posts: 241
|
Grounding Plug
Most if not all inverter generators have no electrical connection between Neutral and Ground. In order for your EMS to function properly, you will need to bond the Neutral to the Ground. This is easy to accomplish with a replacement125V, 20A 3 pole male plug and an inch of #12 Cu wire. You can plug the grounding plug into any unused outlet on the generator and the EMS will function as it should. you contain the jumper totally inside the plug and run it from the round spade (Ground) to the larger flat spade (Neutral). Make sure you keep any wiring connections away from the smaller spade (Hot wire).
Good Camping ..... Swampy
__________________
Jim (Swampy), Susie, Jimmy & The Chihuahua Crew
2008 Chevy Silverado LS, 4.3L, V6, 2WD, 3.23:1
2014 287 BHBE; 1981 JayRaven: Predator 3500i - Call Home Pearl River, Louisiana. on The Honey Island Swamp
https://www.forestriverforums.com/at...pic81807_1.gif
|
|
|
03-22-2018, 12:35 PM
|
#10
|
Frog-Toberfest Organizer
Join Date: Aug 2012
Location: Iowa
Posts: 1,335
|
Would this generator fit and/or work in the stock generator spot in the nose of a fifth wheel? I didn't get one with my Vengeance and now I wish I had one.
__________________
2016 Vengeance 320A
2015 Chevy 2500HD LT 6.6L 4x4 ccsb Z71 trim
2012 HD Electra Glide
Andersen Ultimate Aluminum fifth wheel hitch V2
Days camped '16=43, '17=47, '18=57 '19=47 '20=47 '21=64 '22=62 '23=72 '24=0
|
|
|
03-22-2018, 01:23 PM
|
#11
|
Senior Member
Join Date: Dec 2015
Posts: 241
|
Specifications
I am not familiar with the available space in your camper, but here are the listed specifications for the 3500i :
Product Height
20 in. Product Length 22.75 in. Product Weight 99.2 lbs. Product Width 17.3 in.
__________________
Jim (Swampy), Susie, Jimmy & The Chihuahua Crew
2008 Chevy Silverado LS, 4.3L, V6, 2WD, 3.23:1
2014 287 BHBE; 1981 JayRaven: Predator 3500i - Call Home Pearl River, Louisiana. on The Honey Island Swamp
https://www.forestriverforums.com/at...pic81807_1.gif
|
|
|
03-22-2018, 01:37 PM
|
#12
|
Pickin', Campin', Mason
Join Date: Aug 2015
Location: South Western PA
Posts: 19,144
|
Quote:
Originally Posted by Electra glide
Would this generator fit and/or work in the stock generator spot in the nose of a fifth wheel? I didn't get one with my Vengeance and now I wish I had one.
|
It might... but built in generators are designed to have cooling and also exit the exhaust in such a way that it doesn't infiltrate the camper.
I wouldn't just sit one in there and run it.
__________________
2022 Cedar Creek 345IK 5th Wheel•Solar & Inverter•2024 Ford F-Series SCREW•7.3L•4x4•Factory Puck•B&W Companion•TST Tire Monitor w/Repeater•Sinemate 3500w Gen.
F&AM Lodge 358 Somerset, PA - JAFFA Shrine - Altoona, PA
Days Camped ☼ '19=118 ☼ '20=116 ☼ '21=123 ☼ '22=134 ☼ '23=118☼ '24=90
|
|
|
03-22-2018, 01:40 PM
|
#13
|
Frog-Toberfest Organizer
Join Date: Aug 2012
Location: Iowa
Posts: 1,335
|
Quote:
Originally Posted by 5picker
It might... but built in generators are designed to have cooling and also exit the exhaust in such a way that it doesn't infiltrate the camper.
I wouldn't just sit one in there and run it.
|
I was thinking I would route the exhaust out. I might just keep checking craigslist and see if a used gas Onan ever pops up.
__________________
2016 Vengeance 320A
2015 Chevy 2500HD LT 6.6L 4x4 ccsb Z71 trim
2012 HD Electra Glide
Andersen Ultimate Aluminum fifth wheel hitch V2
Days camped '16=43, '17=47, '18=57 '19=47 '20=47 '21=64 '22=62 '23=72 '24=0
|
|
|
03-22-2018, 02:29 PM
|
#14
|
Senior Member
Join Date: May 2015
Location: Minnesota, St. Paul suburb
Posts: 335
|
Quote:
Originally Posted by Electra glide
I was thinking I would route the exhaust out. I might just keep checking craigslist and see if a used gas Onan ever pops up.
|
Probably a better, safer idea if installing inside a camper that it be the same type one using the same type connections.
__________________
2018 Cedar Creek Silverback 29IK
18 Silverado 3500 HD Dually 6.6 Duramax 4X4
Ultimate Aluminum 5th Wheel Hitch, TST tire monitors w/repeater
Semi-Retired February 3, 2014