I have a number of outlets on a gfci circuit. The outlet in the bathroom has the reset button. The other outlets on the circuit were working, but now are not. The bathroom outlet still works. I have a plug that supposedly tells you what may be wrong with an outlet. It has 3 lights on it. When plugged into the bathroom outlet, it shows no light, then 2 green lights which means it is functioning correctly. When plugged into the other outlets on the circuit, it also has no light, and 2 greens. However, the middle green light is dim. Those outlets do not work, when you plug something in. Tripping and hitting the reset doesn't make any difference.
Any idea what's going on? Could the gfci outlet be bad? Is there another fuse or breaker for this?
Any help is appreciated.
|
|
|
02-09-2020, 03:37 AM
|
#2
|
Senior Member
Join Date: Nov 2019
Location: Mesa, AZ
Posts: 212
|
I am NOT an electrician. However, I did rewire my entire house …
It is my understanding that a GFCI outlet is essentially like a switch - it's either off, or it's on - there is no "in between".
If the other outlets are on the DOWNSTREAM side of the GFCI and the one in the bathroom is off, then they are also going to be off (by "off", I mean no power - dead circuit/outlet). If those other outlets are "upstream" - if they get power before the bathroom does then they could still be on and the bathroom could be off if the GFCI is tripped.
If any recent electrical work was done prior to this problem and everything worked previously whoever did the electrical work did something wrong.
If everything was fine, no repairs have been made and this suddenly popped up I would think there's probably a circuit breaker involved.
Take your tester and put it in your pocket. Grab a small table lamp (that you know works for sure) and plug it in.
It's possible that the GFCI is wired improperly (it's important that the downstream wiring is wired to the downstream side of the GFCI) or it's possible that the wires were somehow reversed on the other outlets.
Sorry, just thinking with my fingers on the keyboard - as I said, I'm not an electrician.
__________________
2012 Ram Laramie 2500 4x4 CC SB Cummins
2016 Flagstaff 8528RKWS
Patrick (order taker), Barbara (order giver) & Jasper (Dutch Shepherd) and now Jade (Boxer/Lab/Pointer hybrid) aka PB&JJ
|
|
|
02-09-2020, 07:48 AM
|
#3
|
Senior Member
Join Date: Dec 2017
Posts: 606
|
Get a volt meter and check for voltage. A volt meter is the best tool in finding out low or high voltage. Take out gfci and tie the blacks and then whites separately together. Then check other outlets. If they show proper voltage bad gfci. Not uncommon for them to go bad.
|
|
|
02-09-2020, 08:06 AM
|
#4
|
Site Team
Join Date: Mar 2008
Location: Southwest Alabama
Posts: 9,850
|
Reading your description I'd say you have a loose connection at or after the GFCI receptacle. A voltmeter will tell you if you have low voltage, but I think you're actually going to have to pull some receptacles to find the problem.
Since you don't have power at any of the downstream receptacles, I'd pull the GFCI first and check the "load" wires on the back of it.
NOTE: Be sure the power is off.
__________________
Salem 29RKSS Pushing a GMC Sierra 2500HD!
Gotta go campin!
|
|
|
02-09-2020, 08:19 AM
|
#5
|
Member
Join Date: Jun 2015
Location: LaGrange GA
Posts: 49
|
GFCI outlet
X2 on BamaRambler's reply
|
|
|
02-09-2020, 09:58 AM
|
#6
|
Senior Member
Join Date: Jan 2020
Posts: 233
|
Thanks everyone. Sounds like a plan.
__________________
2006 Dodge Ram 3500 diesel
2010 Coachmen Northridge 340DBQ
2006 FR wildcat 32qbbs
|
|
|
02-09-2020, 01:59 PM
|
#7
|
Member
Join Date: Nov 2015
Location: Surprise, AZ.
Posts: 96
|
I had a similar experience, when I pulled the outlet the white common wire was barley touching the terminal, made a good connection and problem solved.
__________________
Forest River Lexington Grand Touring.
|
|
|
02-09-2020, 02:18 PM
|
#8
|
Senior Member
Join Date: Jan 2018
Location: Raleigh, NC
Posts: 9,584
|
Yes
Quote:
Originally Posted by Bama Rambler
Reading your description I'd say you have a loose connection at or after the GFCI receptacle. A voltmeter will tell you if you have low voltage, but I think you're actually going to have to pull some receptacles to find the problem.
Since you don't have power at any of the downstream receptacles, I'd pull the GFCI first and check the "load" wires on the back of it.
NOTE: Be sure the power is off.
|
Yes! Given that all the downstream outlets are insulation-displacement outlets (no terminal screws), the most likely source of the problem is the Load (downstream) connection at the GFCI outlet.
Next most likely is a failed GFCI outlet.
__________________
Larry
"Everybody's RV is not like your RV."
"Always take pictures with the button on the right."
"Always bypass the water heater before opening the low-point drains."
Sticks and Bricks: Raleigh, NC
2008 Cherokee 38P: at Ivor, VA permanently
|
|
|
02-09-2020, 02:27 PM
|
#9
|
Site Team
Join Date: Oct 2014
Posts: 15,292
|
If you recently used any high current devices ( heater, coffee maker) on that circuit, check the outlet you used first.
__________________
2015 Freedom Express 248RBS
TV 2015 Silverado HD2500 Duramax
TST Tire Monitors
Honda 2000I + Companion
2 100W solar panels
|
|
|
02-09-2020, 02:33 PM
|
#10
|
Senior Member
Join Date: Nov 2017
Posts: 1,754
|
Originally gfci was incorporated in breaker, then they started building them into an outlet, small place for the parts. They go bad frequently, now throw in China made. I never do anything electrical without a meter, but there are times where the meter shows voltage because and like another said it could be a bad connection so you may consider load testing also, like a hair drier or a corded tool. The meter load is very minimal.
|
|
|
02-09-2020, 07:55 PM
|
#11
|
Senior Member
Join Date: Jun 2013
Posts: 1,114
|
Quote:
Originally Posted by tandem54
I had a similar experience, when I pulled the outlet the white common wire was barley touching the terminal, made a good connection and problem solved.
|
I've seen this type of thing before. There's enough of a connection that you get a voltage reading but not enough to pass any appreciable amount of power (potential).
If all the outlets "downstream" of the GFCI are the same I'd check the first in the line, that is if you can figure out how it was wired. Shouldn't be too hard to check them all though, front cover pops off and screws are quarter turn with little flags that hold them in place. Actually pretty cheesy.
|
|
|
02-09-2020, 08:12 PM
|
#12
|
Member
Join Date: Jul 2016
Posts: 37
|
It could be that reset in your Bathroom GFCI has not been reset properly or all the way. You can still have power at your Bathroom Receptacle, but all the other outlets downstream from it are relying on the GFCI to close the circuit internally within the GFCI providing there are no Ground Faults causing the electronics to not reset. I would shut the circuit breaker off for that circuit at your main panel, reset the GFCI by pressing the reset button using a firm push on the reset, then resetting the main circuit breaker and testing all the Receptacles for power. I have seen GFCI Receptacles that don't work once they have been triggered by a ground fault . In that case you may have to replace it with a new one.
|
|
|
02-09-2020, 10:21 PM
|
#13
|
Senior Member
Join Date: Jun 2016
Posts: 130
|
Check the GFI connections. Could be a piggy back wire that is loose.
|
|
|
02-09-2020, 10:54 PM
|
#14
|
Senior Member
Join Date: Feb 2018
Posts: 160
|
Junk receptacles
Be aware that when you pull the receptacles to check them that they're special "trailer receptacles" that absolutely suck. There is a special tool that is used to seat the wires. When I had to replace several wires, including the main 10/2 wire because I drilled into them installing my Solid Steps, I replaced all of the receptacles with regular residential receptacles in old work boxes.
__________________
2016 Rockwood Windjammer 3001W
2016 F150 SCREW 3.5 EB
ProPride 3P 1400
|
|
|
02-10-2020, 09:39 AM
|
#15
|
Senior Member
Join Date: Apr 2015
Location: Ontario, California
Posts: 2,146
|
Quote:
Originally Posted by aircommuter
Originally gfci was incorporated in breaker, then they started building them into an outlet, small place for the parts. They go bad frequently, now throw in China made. I never do anything electrical without a meter, but there are times where the meter shows voltage because and like another said it could be a bad connection so you may consider load testing also, like a hair drier or a corded tool. The meter load is very minimal.
|
X2
A voltmeter is not necessarily enough load to test a loose but still touching, connection.
|
|
|
02-10-2020, 09:49 AM
|
#16
|
Senior Member
Join Date: Jun 2013
Posts: 10,833
|
Quote:
Originally Posted by Sparkyone
It could be that reset in your Bathroom GFCI has not been reset properly or all the way. You can still have power at your Bathroom Receptacle, but all the other outlets downstream from it are relying on the GFCI to close the circuit internally within the GFCI providing there are no Ground Faults causing the electronics to not reset. I would shut the circuit breaker off for that circuit at your main panel, reset the GFCI by pressing the reset button using a firm push on the reset, then resetting the main circuit breaker and testing all the Receptacles for power. I have seen GFCI Receptacles that don't work once they have been triggered by a ground fault . In that case you may have to replace it with a new one.
|
The Local outlets and load output feeding other outlets are both effect by the 1 GFCI circuit in the outlet.
|
|
|
02-17-2020, 07:42 PM
|
#17
|
Senior Member
Join Date: Jan 2020
Posts: 233
|
I finally got a chance to check out the wiring. Here's what I found. The gfci plug had a loose neutral going downstream. The downstream outlets still weren't getting full power, so I pulled the next outlet. These outlets are really weird. They have the wires between two contacts that are supposed to cut through the insulation to make contact. Again a neutral was loose, but the insulating was hardly cut on any of the wires, and the grounds still had the paper wrap around them. I have seen this kind of connections in auto wiring, but never with 110v outlets. I removed the outlet and wired hot wires together and neutrals together and the rest of the downstream outlets work. I am replacing it with a shallow outlet box and standard household outlet. However, my confidence in the rest of those rv outlets is very low. I will replace them as necessary.
I appreciate everyone's help.
Oh, also, there was a burn mark inside of the outlet where the loose neutral wire was.
__________________
2006 Dodge Ram 3500 diesel
2010 Coachmen Northridge 340DBQ
2006 FR wildcat 32qbbs
|
|
|
02-17-2020, 07:58 PM
|
#18
|
Senior Member
Join Date: Nov 2017
Posts: 1,754
|
Lots of RVs have those kind. Bad idea, cheap and fast and dangerous. That is why I suggested lied testing. Best of success on changing them.
|
|
|
02-17-2020, 08:00 PM
|
#19
|
Member
Join Date: Feb 2019
Posts: 50
|
My husband replaced all of ours. Those RV outlets suck big time. Warning the walls are too shallow for a standard box. My husband had to cut the back off the household electric box by about a 1/2 inch. He then cut away the back wall of the box part that he had cut off and glued it back on to the box. I suggest you drill a 1/2 inch hole into the top and bottom of the alter box for the wires to enter the box, so you may wire a house outlet. It took the better part of a day to replace all the outlets. That isn't counting the time to alter the electrical boxes for those shallow walls.
|
|
|
02-17-2020, 08:06 PM
|
#20
|
Senior Member
Join Date: Apr 2017
Posts: 153
|
Pocket tester will detect any voltage, a multi meter will be the best tool to tell you what voltage you are actually getting. As a couple people have mentioned I think you definitely have a loose wire. WITH THE POWER OFF to the unit, I would start at the GFI and check all electrical connections. It probably would not be a bad thing to go all the way back to the panel and check those connections as well, THIS TIME MAKE SURE YOUR UNIT IS UNPLUGGED FROM THE SHORE POWER.
|
|
|
|
|