Old 03-30-2016, 04:40 AM   #21
Site Team
 
wmtire's Avatar
 
Join Date: Nov 2010
Location: Northeast Louisiana
Posts: 33,934
Quote:
Originally Posted by rogerkathy View Post
I have also noticed most of the testers are for regular 110/ 15 or 20 amp outlets. I am not (yet) convinced that just adding a 50 amp adapter would allow the tester to accurately test the outlet. Comments?
The link that Doug provided in post #10 shows how to build a plug-n-play tester for a 50 amp outlet.

You must first understand what a 50 amp RV is and how it utilizes a 120/240 volt split phase outlet. In basic terms, the 50 amp outlet is comprised of TWO separate 120 volt hot legs (called L1 and L2), each at 50 amps. The RV uses each of these legs separately so they always remain only at 120 volts. Everything in your RV is 120 volts whether on the L1 or L2 side of your RV.

If you combined the L1 and L2, you would have 240 volts, but your RV does not combine them and uses them separately.

You can use the 120 volt circuit testers to test the L1 side, and it's neutral and ground....and then use one to test the L2 side with it's shared neutral and ground........since they are being used only as 120 volt. This is what everyone is pointing out to you.

These links may help better than I can explain it:

Electrical Tutorial - Chapter 3 - 30 Amp versus 50 Amp

AC Electricity

This site below has a left hand tab on outlet testing, that shows how to build the one in post #10, as well as how to use a multimeter for same.

RV Electric

Once you understand how the 120/240 volt split phase service works, it'll be easy to see how the link in post #10 works.

Hope this helps
__________________
2011 Flagstaff 831 RLBSS

A 72 hour hold in a psych unit is beginning to intrigue me as a potential vacation opportunity.
wmtire is online now   Reply With Quote
Old 03-30-2016, 04:49 AM   #22
Senior Member
 
Oaklevel's Avatar
 
Join Date: Sep 2012
Location: Virginia
Posts: 9,904
Quote:
Originally Posted by boondocking View Post
Please be careful with these little testers they have limitations and have seen two of them (different brands) explode when the voltage was off......... .. They will not show high or low voltage they just show voltage is there. They will not show quality of a ground.......

Also they must be tested before use on a know proper source as the bulbs do burn out.

They are meant for home use standard 110V outlet only to show voltage, reversed polarity, and a ground . Will not show quality, quantity


__________________

2005 Dodge 3500 Cummins
2017 Wildwood Lodge 4092 BFL
1966 Mustang GT
1986 Mustang SVO
Lillie Spoiled Rotten Boxer Mix
Oaklevel is offline   Reply With Quote
Old 03-30-2016, 08:18 AM   #23
Senior Member
 
Join Date: Jan 2016
Posts: 187
Thanks for all your valuable input! I think I will just get a multimeter since it seems to be the most versatile, and a receptacle tester with the 3 lights that I can plug into the trailer outlets for a quick check on them also. I can purchase the receptacle tester at Harbor Freight for under $7, plus I have a 20% off ANY item purchased, AND a FREE multimeter with any purchase. Looks like a win win for me!
rogerkathy is offline   Reply With Quote
Old 03-30-2016, 09:56 AM   #24
Senior Member
 
Join Date: May 2015
Posts: 925
Quote:
Originally Posted by westom View Post
That outlet tester cannot report only report a few anomalies. It can even imply a good receptacle power when some defects exist. It cannot report defective earthing, excessive voltages, or other more common problems in a campground. In some cases, it cannot even report a floating neutral.

Even a digital meter for $5 or $14 provides more useful information.
Yes, if you know what you are doing. I am guessing the OP doesn't or he would not be asking this question.

He is looking for a cheap way to do what a good PSI surge protector can do. Without the good background there isn't one. Even with a good meter and a good background there isn't any way to constantly monitor the pole outlet, unless you want to stand there all day and night.

Jim
__________________
07 Dodge 1500 crew cab with 20" wheels, 08 Forest River Rockwood Signature Ultra-lite 8280SS
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore, all progress depends on the unreasonable man."
George Bernard Shaw
oldtool2 is offline   Reply With Quote
Old 03-30-2016, 10:05 AM   #25
Member
 
Join Date: Oct 2012
Posts: 97
Quote:
Originally Posted by oldtool2 View Post
Even with a good meter and a good background there isn't any way to constantly monitor the pole outlet, unless you want to stand there all day and night.
And that is the point; isn't it. Does not matter what a three light tester reports when conditions change and nothing is done to avert potential damage. A protector not only detects an anomaly and reports it. It also makes an appropriate change to avert damage.

Meter is a powerful tool. But it cannot, for example report large voltage changes (L-N, L-G, N-G) that occurs later as campground loads change dynamically.
westom is offline   Reply With Quote
Old 03-30-2016, 10:37 AM   #26
Senior Member
 
Join Date: May 2015
Posts: 925
Originally Posted by oldtool2
Even with a good meter and a good background there isn't any way to constantly monitor the pole outlet, unless you want to stand there all day and night.


Quote:
Originally Posted by westom View Post
And that is the point; isn't it. Does not matter what a three light tester reports when conditions change and nothing is done to avert potential damage. A protector not only detects an anomaly and reports it. It also makes an appropriate change to avert damage.

Meter is a powerful tool. But it cannot, for example report large voltage changes (L-N, L-G, N-G) that occurs later as campground loads change dynamically.
And that is why the only recommendation I would make is a good surge protector. No they are not cheap, but can be much less expensive than the damage that can be caused by not using one. This is not to mention the ruined vacation or trip.

Jim
__________________
07 Dodge 1500 crew cab with 20" wheels, 08 Forest River Rockwood Signature Ultra-lite 8280SS
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore, all progress depends on the unreasonable man."
George Bernard Shaw
oldtool2 is offline   Reply With Quote
Old 03-30-2016, 10:38 AM   #27
Moderator Emeritus
 
Kaadk's Avatar
 
Join Date: Apr 2013
Posts: 5,173
While a good EMS is the way to protect yourself while you are plugged in, there is merit in using a tester/meter before you plug in.

I for one would like to know if the site's wired wrong before I back in and start setting up. Once I know it's wired ok and safe to setup, I then depend on the surge guard to handle changing conditions like voltage, etc...


Sent from my iPhone using Forest River Forums
__________________
There's no use crying over spilt milk... unless it's on your keyboard.
Kaadk is offline   Reply With Quote
Old 03-30-2016, 11:01 AM   #28
Senior Member
 
Join Date: Mar 2014
Location: Mountain Foothills of Southern Alberta
Posts: 2,004
Quote:
Originally Posted by oldtool2 View Post

He is looking for a cheap way to do what a good PSI surge protector can do. Without the good background there isn't one.

Jim
Not really, if you read the original post he is wanting to know if the pedestal is wired correctly before plugging in, he is not looking for voltage protection.
__________________

2007 Surveyor SV230
- 200 Watts Solar/MPPT Controller - 220 AH Battery Bank (Two-GC2) - 600 watt PSW Inverter - (2) 2000 watt Inverter Generators - LED Lighting
2009 F150 - 5.4 Litre with Tow Package

Boon Docking 99% of the time.
boondocking is online now   Reply With Quote
Old 03-30-2016, 11:05 AM   #29
Senior Member
 
Join Date: Feb 2016
Posts: 265
Quote:
Originally Posted by Kaadk View Post
While a good EMS is the way to protect yourself while you are plugged in, there is merit in using a tester/meter before you plug in.

//snip//
Seems you make a good argument for a PORTABLE device like the SurgeGuard versus a hard-wired one.

With the portables you can plug it in to the pole and test before plugging in your camper.

Then it will continue to protect while camping.
__________________
Family of six, camping in a Grey Wolf 26DBH LTD pushing a 2010 Armada via 10k/1k HaulMaster WDH stopped by a Prodigy P2 brake controller

Tug: 2010 2wd Nissan Armada Titanium with tow package.
Specs: Max Trailer Weight 9,100, Tongue Load: 910, GCWR: 15,100, GVWR: 7,150, Payload: 1,592
DadOfTwo is offline   Reply With Quote
Old 03-30-2016, 11:10 AM   #30
Moderator Emeritus
 
Kaadk's Avatar
 
Join Date: Apr 2013
Posts: 5,173
Quote:
Originally Posted by DadOfTwo View Post
Seems you make a good argument for a PORTABLE device like the SurgeGuard versus a hard-wired one.



With the portables you can plug it in to the pole and test before plugging in your camper.



Then it will continue to protect while camping.

That's exactly what I do, since I have a portable. But for those with the hardwired, which provides it's own benefits in both theft protection and the ability of inside monitoring, an additional check of the pole before accepting the site is usually a good idea.


Sent from my iPhone using Forest River Forums
__________________
There's no use crying over spilt milk... unless it's on your keyboard.
Kaadk is offline   Reply With Quote
Old 03-30-2016, 11:36 AM   #31
Senior Member
 
Join Date: Jan 2016
Posts: 187
I have a hardwired Progressive EMS surge protector for the RV after plugging in. I just wanted a quick test for the site itself BEFORE I go to the trouble of setting up camp so I can move to a different location if needed.
rogerkathy is offline   Reply With Quote
Old 03-30-2016, 11:43 AM   #32
Always Learning
 
ependydad's Avatar
 
Join Date: Nov 2011
Location: Four Corners, FL
Posts: 21,891
Quote:
Originally Posted by rogerkathy View Post
I have a hardwired Progressive EMS surge protector for the RV after plugging in. I just wanted a quick test for the site itself BEFORE I go to the trouble of setting up camp so I can move to a different location if needed.


Yep, exactly the same here.
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
ependydad is offline   Reply With Quote
Old 03-30-2016, 01:14 PM   #33
Senior Member
 
Join Date: Jan 2016
Posts: 187
Ok, just got back from purchasing a 3 light receptacle tester. Decided to try it out in my home. Boy, was I surprised when it showed the hot and neutral were reversed on the first outlet I checked! Other outlets tested OK. I guess I better check ALL my house outlets.
rogerkathy is offline   Reply With Quote
Old 03-30-2016, 05:53 PM   #34
Senior Member
 
Join Date: Dec 2015
Location: West Hills, CA
Posts: 200
I recommend Michael Sokol's book "No-Shock-Zone". It is an easy read and will point out some very important and potentially deadly situations to be aware of. He covers the use of inexpensive test tools, and which ones to get. Explains some of the Do's and Don't's of troubleshooting the pedestal and your rig. I plan to laminate the provided charts in the appendix, include a simple step-by-step process w/meter settings along with the test tools into a bag and it should be just a 5-10 minute test ...before dropping the landing gear.

For example, a 3 light tester nor an EMS will detect a RPBG (Reverse Polarity Bootleg Ground).
__________________
2015 Rockwood 8289WS
2003 Dodge Cummins w/Banks 3:73
CraigBean7672 is offline   Reply With Quote
Old 03-30-2016, 07:51 PM   #35
Member
 
Join Date: Oct 2012
Posts: 97
Quote:
Originally Posted by rogerkathy View Post
I guess I better check ALL my house outlets.
Appreciate what was discovered. Polarity is one of many 'layers' for human protection. Polarity is irrelevant to appliance protection; is only one of many features for human protection.

Other human safety defects can exist - a three light tester cannot detect them.

Back to the camper. Some (first) faults will not be apparent when using a meter. Others become apparent after drawing power from a pedestal. A properly designed protector will not connect power until first checking for those (first) faults. And will continue checking when other (second) faults can be detected - after a camper draws power. Checking (ie with a meter) before connecting power dies not detect all anomalies since some may only be apparent after a camper consumes power.

Best protector disconnects when either (first or second) anomaly is detected. Meter only detects a fault. As oldtool2 so accurately notes, human cannot disconnect fast enough.

Cost should always be secondary to solving an unacceptable problem Especially when a properly designed protector is so inexpensive.
westom is offline   Reply With Quote
Old 03-31-2016, 08:38 AM   #36
Senior Member
 
WolfWhistle's Avatar
 
Join Date: Apr 2012
Posts: 3,275
I know first hand the danger of faulty wiring (RPBG, but didn't know it had a name). I dodged the bullet and could have been killed. What got me was a situation where only when the water heater was on, was the skin or frame at a 120 VAC potential.

It is important to be aware that surge protectors and simple testers cannot determine faulty in some cases. Earth ground is expected to be 0 volts, but it might not be.

After dodging the bullet I made it a practice of testing a trailer frame to actual earth (dirt - with screw driver) with a good meter set to read high ohms. If I read anything, I don't touch it. If it is mine, more testing and a fix would be necessary.

Maybe we should test our trailer skin (frame) before assuming we are safe.

For you DIYers out there, understand that if a device has a ground lug, run a separate wire to frame ground and don't be tempted to strap neutral to it; neutral is the return path functionality and protection ground is there to protect us so when something goes wrong the skin or housing isn't at the potential of the supply or hot.
WW
__________________
Hyper Lite was sold

2017 F-250 4x4 6.2L Gas
I can't fix everything, but I can make it so nobody else can
WolfWhistle is offline   Reply With Quote
Old 03-31-2016, 02:24 PM   #37
Senior Member
 
Join Date: Dec 2015
Location: West Hills, CA
Posts: 200
Yep, it's more than just frying your electronics when all it takes is 10 to 20 milliamperes (=very small amount) to stop your heart. Doing things like opening a mis-wired pedestal with one hand and while plugging in the cord with the other (breaker on) or something else like touching your metal step frame while standing on wet ground can be do it. Awareness of this is important.

Happy and safe camping to all.
__________________
2015 Rockwood 8289WS
2003 Dodge Cummins w/Banks 3:73
CraigBean7672 is offline   Reply With Quote
Old 04-03-2016, 09:08 AM   #38
Senior Member
 
Join Date: May 2015
Posts: 925
Quote:
Originally Posted by boondocking View Post
Not really, if you read the original post he is wanting to know if the pedestal is wired correctly before plugging in, he is not looking for voltage protection.
The OP asks "Is there a simple item you can just plug into the campground electrical boxes to test if they are good or bad without using a meter or an expensive surge protector? ". The simplest way is an inexpensive meter. You can get one for under ten bucks. I do think the best way though is to plug in a PSI portable surge protector and use a meter, then you can cover everything.

I know many prefer the hardwired unit because of theft protection but you are going to need a very good set of bolt cutters to cut the lock and chain I use to fasten my portable unit to the post.

Jim
__________________
07 Dodge 1500 crew cab with 20" wheels, 08 Forest River Rockwood Signature Ultra-lite 8280SS
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore, all progress depends on the unreasonable man."
George Bernard Shaw
oldtool2 is offline   Reply With Quote
Old 04-04-2016, 11:24 AM   #39
Always Learning
 
ependydad's Avatar
 
Join Date: Nov 2011
Location: Four Corners, FL
Posts: 21,891
Quote:
Originally Posted by oldtool2 View Post
he simplest way is an inexpensive meter. You can get one for under ten bucks.
The problem is- many of us aren't comfortable with a meter and stuffing probes in dangerous sockets. The idea scares the beejeebees out of me.
__________________
Officially a SOB with a 2022 Jayco Precept 36C
Checkout my site for RVing tips, tricks, and info | Was a Fulltime Family for 5 years, now we're part-timing on long trips
ependydad is offline   Reply With Quote
Old 04-04-2016, 11:54 PM   #40
Junior Member
 
Join Date: Mar 2016
Posts: 8
I use this when I'm at campgrounds.




Sent from my iPhone 6 using Tapatalk
Bill1957 is offline   Reply With Quote
Reply

Tags
electric, electrical


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Forest River, Inc. or any of its affiliates. This is an independent, unofficial site.



All times are GMT -5. The time now is 08:14 PM.