Solar & Inverter Project
Here are my plans for my new solar and inverter installation. I will be installing a tri-metric meter for more precise monitoring.
.
.
.
__________________
2011 2902ss Rockwood Ultralight
2008 Grand Cherokee 3.0L Diesel (255 hp @ 2900 rpm / 430 lb-ft @ 1,400-2,800 rpm)
3P ProPride Hitch
RV Mods
Wandering RV Life
|
|
|
10-09-2014, 08:29 AM
|
#2
|
Senior Member
Join Date: Aug 2010
Location: Canada
Posts: 223
|
250 Watt Solar Panel installed
First 250 Watt Solar Panel installed
.
.
.
__________________
2011 2902ss Rockwood Ultralight
2008 Grand Cherokee 3.0L Diesel (255 hp @ 2900 rpm / 430 lb-ft @ 1,400-2,800 rpm)
3P ProPride Hitch
RV Mods
Wandering RV Life
|
|
|
10-09-2014, 11:57 AM
|
#3
|
CCRVOC
Join Date: Jan 2012
Location: Where ever we are parked
Posts: 516
|
Looks good. What type solar panel did you get?
__________________
2012 Dodge 3500, SLT Big Horn,CC,DRW,Cummins HO, EB, 4x4, 3:73, Retrax Pro, Q20, TST507, Garmin RV760, Sleek 4g
2014 Cedar Creek, 36CKTS, 1000w Solar, TriStar MPPT 60, Magnum 2000w, PI EMS, WiFi Ranger Elite, Sleek 4g, Wingard DTV Traveler
Retired Army in 1995, and now retired in 2016
|
|
|
10-09-2014, 12:21 PM
|
#4
|
Senior Member
Join Date: Sep 2014
Location: Southern New England
Posts: 862
|
Looking good. Campground rather tight there though. Reminds me most of our east coast campgrounds...can pass a morning cup of coffee to your neighbor without touching the ground.
__________________
2017 GMC Yukon
2018 Roo 23 ikss
|
|
|
10-09-2014, 12:29 PM
|
#5
|
Senior Member
Join Date: Mar 2014
Location: Lower Michigan
Posts: 1,471
|
Looks really good, please keep posting as you progress I would like to do something like this, so I'm going too follow this thread.
__________________
Bill & Pam
2014 Trilogy 3650RE
2015 F350 PSD
|
|
|
10-09-2014, 12:35 PM
|
#6
|
Senior Member
Join Date: Aug 2010
Location: Canada
Posts: 223
|
__________________
2011 2902ss Rockwood Ultralight
2008 Grand Cherokee 3.0L Diesel (255 hp @ 2900 rpm / 430 lb-ft @ 1,400-2,800 rpm)
3P ProPride Hitch
RV Mods
Wandering RV Life
|
|
|
10-13-2014, 06:11 PM
|
#7
|
Senior Member
Join Date: Aug 2010
Location: Canada
Posts: 223
|
40 AMP MPPT Charger installed
25 ft (8 AWG) Solar Panel -> MPPT Charger
6 ft (4 AWG) MPPT Charger -> Battery
.
.
.
__________________
2011 2902ss Rockwood Ultralight
2008 Grand Cherokee 3.0L Diesel (255 hp @ 2900 rpm / 430 lb-ft @ 1,400-2,800 rpm)
3P ProPride Hitch
RV Mods
Wandering RV Life
|
|
|
10-21-2014, 10:08 PM
|
#8
|
Senior Member
Join Date: Aug 2010
Location: Canada
Posts: 223
|
Inverter remote switch & MPPT remote monitor installed
.
.
.
__________________
2011 2902ss Rockwood Ultralight
2008 Grand Cherokee 3.0L Diesel (255 hp @ 2900 rpm / 430 lb-ft @ 1,400-2,800 rpm)
3P ProPride Hitch
RV Mods
Wandering RV Life
|
|
|
10-21-2014, 10:48 PM
|
#9
|
Senior Member
Join Date: Aug 2014
Location: Texas
Posts: 1,162
|
WOW nice I want to do something like that but not as big maybe half that would work for me. Nice set up I'm watching thanks for sharing.
__________________
2014 Palomino Columbus 3650TH
435AH 12V VMax Charge Tanks, 520 watt Monocrystilline Solar Array, Morningstar MPPT TS-60 CC,Morningstar Remote,Cotek True Sine Wave Inverter,Cotek Remote Controller,50amp Progressive Hardwire Surge Protector
2015 Dodge 3500 6.7L 4X4
2011 CanAm Commander XT 1000
|
|
|
10-22-2014, 12:32 AM
|
#10
|
Senior Member
Join Date: Dec 2012
Posts: 1,255
|
Not too shabby! If I might maybe make a couple of suggestions?
I would lose the GP watt meter and the MT-5 tracer meter and just use the Trimetric. Of course, with the appropriate shunt installed.
I would move your 250watt fuse and run it between the charge controller and your battery bank.
Lastly, I would isolate your invert from your converter. (by using a subpanel) If you're not on shore power, you'll end up using your batteries to attempt to charge themselves via the converter.
Just some smansy additions... you might consider adding a 40amp fused cutoff switch between the Charge controller and batteries.. and another 60amp fused disconnect between the batteries and your convert... then move the red stand alone disconnect between the inverter and your relay switch. For the cost, you might appreciate the additional protections, and it's nice to be able to isolate the main system components for maintenance purposes.
You might consider using 10/2 coming down from you panels and 2/0 between your charge controller and batteries... but that's a personal choice. It's just with the little difference in price it's an inexpensive way to help increase the efficiency of your system.
Just suggestions....
|
|
|
10-22-2014, 09:15 AM
|
#11
|
Senior Member
Join Date: Oct 2013
Location: Iowa
Posts: 449
|
Quote:
Originally Posted by Yarome
Lastly, I would isolate your invert from your converter. (by using a subpanel) If you're not on shore power, you'll end up using your batteries to attempt to charge themselves via the converter.
.......
Just suggestions....
|
Solved this issue as per my earlier post. No need for a sub-panel. See the following link.
http://www.forestriverforums.com/for...dea-70207.html
..Marty
|
|
|
10-22-2014, 11:38 AM
|
#12
|
Senior Member
Join Date: Aug 2010
Location: Canada
Posts: 223
|
Updated Diagram
Updated diagram:
1. Removed GP Watt meter
2. Added TriMetric 2030 monitor (Will removed MT-5 Tracer once installed)
3. Added wire gauge for [solar->controller, controller->battery]
The 250 watt fuse is to protect the Sine wave inverter. My understanding is that needs to be there and within 18" of battery. Since my solar panels should be able to keep the batteries totally charged, I was planning on turning off the built-in charger at the breaker panel. The wire gauge I used [solar->controller 8AWG 25ft and controller->battery 4AWG 6ft] are below the 3% loss recommended.
thanks for the suggestions. Will look into getting a 40-60AMP fuse between controller and batteries with a cut-off switch.
.
Quote:
Originally Posted by Yarome
Not too shabby! If I might maybe make a couple of suggestions?
I would lose the GP watt meter and the MT-5 tracer meter and just use the Trimetric. Of course, with the appropriate shunt installed.
I would move your 250watt fuse and run it between the charge controller and your battery bank.
Lastly, I would isolate your invert from your converter. (by using a subpanel) If you're not on shore power, you'll end up using your batteries to attempt to charge themselves via the converter.
Just some smansy additions... you might consider adding a 40amp fused cutoff switch between the Charge controller and batteries.. and another 60amp fused disconnect between the batteries and your convert... then move the red stand alone disconnect between the inverter and your relay switch. For the cost, you might appreciate the additional protections, and it's nice to be able to isolate the main system components for maintenance purposes.
You might consider using 10/2 coming down from you panels and 2/0 between your charge controller and batteries... but that's a personal choice. It's just with the little difference in price it's an inexpensive way to help increase the efficiency of your system.
Just suggestions....
|
__________________
2011 2902ss Rockwood Ultralight
2008 Grand Cherokee 3.0L Diesel (255 hp @ 2900 rpm / 430 lb-ft @ 1,400-2,800 rpm)
3P ProPride Hitch
RV Mods
Wandering RV Life
|
|
|
10-22-2014, 02:55 PM
|
#13
|
Senior Member
Join Date: Dec 2012
Posts: 1,255
|
Quote:
Originally Posted by WestCoastRV'er
The 250 watt fuse is to protect the Sine wave inverter. My understanding is that needs to be there and within 18" of battery. Since my solar panels should be able to keep the batteries totally charged, I was planning on turning off the built-in charger at the breaker panel. The wire gauge I used [solar->controller 8AWG 25ft and controller->battery 4AWG 6ft] are below the 3% loss recommended.
thanks for the suggestions. Will look into getting a 40-60AMP fuse between controller and batteries with a cut-off switch.
.
|
Oh yes. You're right about the fuse. I wasn't paying attention to your inverter. Most of the ones I see and have used are fused internally. You might still want to add a 300watt between the solar controller and the batteries.
Must have been late when I typed that. LOL Flip flop the fused cutoffs... a 60amp feeding into the controller, standard disconnect between the controller and batteries, then a 40amp feeding into the house 12v system.
I'll stick a picture of the ones I use. You can pick them up just about anywhere.
There is a lot of opinions when it comes to wiring. The gauges you plan on using certainly meet the standard minimums. Some potential bottlenecks can be avoided (increasing efficiency) by moving up a few gauges over the minimums. Such at the cable connectors. Larger gauge, larger connector surfaces, less heat, longer wear. A lot depends on your budget. When you start getting up into the $.80 an inch stuff.. it can get real spendy in a heartbeat.
Of course, if you're just looking to supplement your power needs for a couple 2 or 3 days of dry camping, you don't really need to go to the added expense to irk out a few more percentage points on the efficiency scale.
I know some fellas that use 4/0 for a 3 foot run. I'm in the "bigger is better.. but let's not get ridiculous" camp. Ever tried attempting to get 4/0 to go where you want it and stay there?
All in all it looks like you know what you're doing and should be really happy with the results. Nothing better than free energy.
|
|
|
10-22-2014, 05:27 PM
|
#14
|
Senior Member
Join Date: Aug 2010
Location: Canada
Posts: 223
|
WoW. Very clean installation.
.
.
.
__________________
2011 2902ss Rockwood Ultralight
2008 Grand Cherokee 3.0L Diesel (255 hp @ 2900 rpm / 430 lb-ft @ 1,400-2,800 rpm)
3P ProPride Hitch
RV Mods
Wandering RV Life
|
|
|
10-22-2014, 09:06 PM
|
#15
|
Senior Member
Join Date: Dec 2012
Posts: 1,255
|
Quote:
Originally Posted by WestCoastRV'er
WoW. Very clean installation.
|
That's just because my "octopus pit" can't be seen in that picture. LOL
Which brings up another suggestion... mark EVERYTHING and keep detailed wiring drawings, equipment details, dates, and serial #s tucked in somewhere close.
Took me once to learn that tid bit the hard way. I remember my first response to the service tech vividly.. ," now WHAT on God's green earth would prompt you to put the serial number THERE??"
Had to dismantle near a quarter of the "octopus pit" to get there and it turned out it wasn't even the problem. LOL
If you ever sell your rig and send your solar set-up along with, the new owner will thank you. Or... if you're like me at all... that was all put together a couple of years ago and there has been a couple of times I'm scratchin my noggin thinkin "now where does that one go again?".
It's all good fun.
|
|
|
11-06-2014, 09:07 AM
|
#16
|
Junior Member
Join Date: Aug 2014
Posts: 4
|
Make that a 250 amp, not watt fuse, I am sure it is just a typo.
Nice system, you should be happy with it.
|
|
|
11-06-2014, 10:03 AM
|
#17
|
Senior Member
Join Date: Aug 2010
Location: Canada
Posts: 223
|
Upgrading to Lithium Batteries
Yes that was an error in my diagram. More changes to come. Tried running my microwave using the 2000 watt inverter and found that the battery bank ( 2 x T105) could not supply enough current and the voltage drop caused the inverter to have an E01 fault error (under voltage). I even tried 1 ft 1/0 cable from battery -> inverter.
I could just add 2 more T-105 batteries and that would fix the issue but I think this is my opportunity to do the upgrade to my battery bank. So now I'm researching Lithium Ion batteries. I'm looking at starting with a 100AH battery and adding to it over time.
Advantage:
1. Batteries can be moved to compartment where solar charger and inverter are located. Shorter 4/0 cable run <2ft
2. 70% less weight for same amount of usable AMP HOURS
3. Faster Charging of battery bank
4. 2000+ charge cycles. Batteries may last 8+ years
5. Efficient solar charging.
Disadvantage:
1. Initial Cost (50AH battery $500-700 depending on brand)
Lithium Battery Links:
Smart Battery - Lithium
Stark Power Battery - Lithium
Charger:
Progressive Dynamic - Lithium Charger
.
.
.
__________________
2011 2902ss Rockwood Ultralight
2008 Grand Cherokee 3.0L Diesel (255 hp @ 2900 rpm / 430 lb-ft @ 1,400-2,800 rpm)
3P ProPride Hitch
RV Mods
Wandering RV Life
|
|
|
11-06-2014, 10:49 AM
|
#18
|
Junior Member
Join Date: Aug 2014
Posts: 4
|
Those L.I. batteries are very nice. I went with the T-125, they are 240 AH batteries (6) with the same footprint as a T-105 at the 225 AH.
I would go with that unless you have a fat wallet, like you stated, they are expensive.
|
|
|
11-06-2014, 11:43 AM
|
#19
|
Senior Member
Join Date: Feb 2014
Posts: 2,832
|
You might also look at the Odyssey TPPL batts as they can be charged OR discharged at at least twice their rated amp hours and deeply discharged to the 20-30% level without impact on life. They are also pricey but much more in line with good AGMS (which they are!) than with Lithiums. Since your problem is not a lack of capacity...but the current % limitations of wet cells...this would seem to be the most cost effective solution.
__________________
________
Cam